Hey Guys-

This is wrong correct? I'm seeing a lack of ledger fasteners, only a 2x6 ledger, and no joist hangers.

Where the joists connect on the stair side, is it okay to attach those using screws from the outside like they did, or should there be joist hangers there as well. Just wanted to double-check before I get a call from the builder on this new construction property. Thanks.

Kenny
Attached Thumbnails
back-deck-img_1544.jpg   back-deck-img_1545.jpg   back-deck-img_1547.jpg   back-deck-img_1700.jpg  



Rigler Home Inspections
Hays, KS 67601
785-656-0272
Reply With Quote
Need a home inspection in Ohio? Check out InterNACHI's listing of Ohio certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 11/3/10, 7:52 PM
rsmith24 rsmith24 is offline
InterNACHI Member
 
Join Date: Jun 2010
Location: Michigan
Posts: 1,260
Default Re: Back Deck

Can you get your hand around the handrail? or i should say can you grasp it.




INSPECTIONLOGOS.COM

"I can keep explaining it for you, but I can't understand it for you".
Nick G.
Monroe Home Inspection
Reply With Quote
  #3  
Old 11/3/10, 8:23 PM
Christopher Currins's Avatar
Christopher Currins Christopher Currins is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Godfrey, IL
Posts: 7,626
Default Re: Back Deck

At minimum it needs hangers, and block at ledger board should have at least 1/2" bolts/screws. I can't see enough of ledger board to determine if required number of fasteners were used..



Christopher Currins
Certified, Licensed

Proudly serving the St.Louis Metro

St. Charles, St. Peters, Maryland Heights,
O'Fallon, Florrisant, MO Home Inspector




BLESSED ARE THE CRACKED, FOR THEY ARE THE ONES WHO LET IN THE "LIGHT"!
Reply With Quote
  #4  
Old 11/3/10, 9:07 PM
Robert Ernst Robert Ernst is online now
InterNACHI Member
 
Join Date: Sep 2010
Location: Sparks,NV
Posts: 654
Default Re: Back Deck

It needs to be lag bolted or through bolted to the structure and it does need rust resistant hangers and fasteners. I would also expect to see the joists terminate onto a beam so that front board at the stairs should be doubled up and have a double hanger on the one end and be bolted to the 4x4 on the other end. Also if it's just untreated framing lumber that's not acceptable. It should have at least one continuous railing 34-38" high. Many local building departments have deck cheat sheets.
Reply With Quote
  #5  
Old 11/4/10, 9:41 AM
Kenny Rigler Kenny Rigler is offline
InterNACHI Member
 
Join Date: Apr 2009
Location: Hays, KS
Posts: 255
Default Re: Back Deck

Thanks guys. I think I have plenty to go off of. I was also sent a nice link to a wood deck guide that has lots of information as well:

http://www.awc.org/Publications/DCA/DCA6/DCA6-09.pdf



Rigler Home Inspections
Hays, KS 67601
785-656-0272

Last edited by krigler; 11/4/10 at 10:35 AM..
Reply With Quote
  #6  
Old 11/4/10, 9:45 AM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 8,343
Send a message via Yahoo to jfunderburk
Default Re: Back Deck

There is no visible flashing and it is installed directly against the siding. Looks like Hardiplank, and their instructions prohibit direct contact with other surfaces.



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #7  
Old 11/4/10, 9:50 AM
Kenny Rigler Kenny Rigler is offline
InterNACHI Member
 
Join Date: Apr 2009
Location: Hays, KS
Posts: 255
Default Re: Back Deck

Thanks Joe. I'm with you on the spacing between the deck, but how far does Hardiplank go with no direct contact with other surfaces. Dryer vent, chimney vent, electrical boxes, etc??? Or am I just reading that wrong?
Attached Thumbnails
back-deck-img_1530.jpg   back-deck-img_1537.jpg   back-deck-img_1551.jpg   back-deck-img_1553.jpg  



Rigler Home Inspections
Hays, KS 67601
785-656-0272
Reply With Quote
  #8  
Old 11/4/10, 10:04 AM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 8,343
Send a message via Yahoo to jfunderburk
Default Re: Back Deck

Quote:
Originally Posted by krigler View Post
Thanks Joe. I'm with you on the spacing between the deck, but how far does Hardiplank go with no direct contact with other surfaces. Dryer vent, chimney vent, electrical boxes, etc??? Or am I just reading that wrong?
See page 2.

http://www.jameshardie.com/pdf/insta...eplank-hz5.pdf



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #9  
Old 11/4/10, 10:29 AM
Kenny Rigler Kenny Rigler is offline
InterNACHI Member
 
Join Date: Apr 2009
Location: Hays, KS
Posts: 255
Default Re: Back Deck

Quote:
Originally Posted by jfunderburk View Post
Gotcha...that makes sense. Thanks!



Rigler Home Inspections
Hays, KS 67601
785-656-0272
Reply With Quote
  #10  
Old 11/4/10, 6:57 PM
Kenton H. Shepard, CMI's Avatar
Kenton H. Shepard, CMI Kenton H. Shepard, CMI is offline
InterNACHI Member
 
Join Date: Aug 2004
Location: Boulder, CO
Posts: 3,417
Send a message via ICQ to kshepard
Default Re: Back Deck

Quote:
Originally Posted by ccurrins View Post
At minimum it needs hangers, and block at ledger board should have at least 1/2" bolts/screws. I can't see enough of ledger board to determine if required number of fasteners were used..
That's modern practice, but required? Anyone got an IRC reference?




Kenton Shepard, InterNACHI member # 04082383
Certified Master Inspector (CMI)
InterNACHI Director of International Development
Director of Green Building

EXPERT WITNESS SERVICE
Conventional and Log homes

(303) 717-8940
Reply With Quote
  #11  
Old 11/4/10, 7:40 PM
Christopher Currins's Avatar
Christopher Currins Christopher Currins is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Godfrey, IL
Posts: 7,626
Default Re: Back Deck

Quote:
Originally Posted by kshepard View Post
That's modern practice, but required? Anyone got an IRC reference?
http://www.awc.org/Publications/DCA/DCA6/DCA6-09.pdf

page 12, 13



Christopher Currins
Certified, Licensed

Proudly serving the St.Louis Metro

St. Charles, St. Peters, Maryland Heights,
O'Fallon, Florrisant, MO Home Inspector




BLESSED ARE THE CRACKED, FOR THEY ARE THE ONES WHO LET IN THE "LIGHT"!
Reply With Quote
  #12  
Old 11/4/10, 8:18 PM
Brian E. Kelly's Avatar
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 15,973
Default Re: Back Deck

Just out of curiosity, what is the difference between a "Deck" and a "Landing"?

or is there a difference? I don't know myself
Reply With Quote
  #13  
Old 11/4/10, 8:44 PM
Peter C. Russell's Avatar
Peter C. Russell Peter C. Russell is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Alton Bay NH
Posts: 3,998
Default Re: Back Deck

That looks like a pre-fab set of stairs usually installed on MFG housing, if so the correct joist fasteners may be there just not visible.



Russell Inspection Services
New Hampshire state license # 57
Level I Thermographer, ITC
Certified Building Science Thermographer, ITC
Certified Building Analyst, BPI
Certified Commercial Inspector, ITA
Certified Septic Evaluator, GSDI #148

www.newenglandthermalimaging.com
www.russellinspectionservices.com
www.nhsepticinspection.com
Reply With Quote
Need a home inspection in Ohio? Check out InterNACHI's listing of Ohio certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #14  
Old 11/4/10, 8:58 PM
Kenton H. Shepard, CMI's Avatar
Kenton H. Shepard, CMI Kenton H. Shepard, CMI is offline
InterNACHI Member
 
Join Date: Aug 2004
Location: Boulder, CO
Posts: 3,417
Send a message via ICQ to kshepard
Default Re: Back Deck

Quote:
Originally Posted by ccurrins View Post
That appears to be a document put out by the American Forest and Paper Association and distributed by the American Wood Council.

It says that IRC requirements are bracketed and the information on pp 12 & 13 are not bracketed and so are not building code and not a requirement.

This is mostly a "best practices" document and it's a good document, but I wouldn't call that staircase and landing defective for lack of joist hangers.
If joists are toe-nailed only, each connection should each have 3 in one side and 2 in the other, 16d vinyl-coated sinker or bigger.

It's hard to see the lags into the rim. If ledgers have less than one 1/2" lag a min. of every 24" staggered up and down and two at each side of each break, I call it defective.




Kenton Shepard, InterNACHI member # 04082383
Certified Master Inspector (CMI)
InterNACHI Director of International Development
Director of Green Building

EXPERT WITNESS SERVICE
Conventional and Log homes

(303) 717-8940
Reply With Quote
  #15  
Old 11/4/10, 10:23 PM
Jeffery L. Haynes Jeffery L. Haynes is offline
InterNACHI Member
 
Join Date: Aug 2008
Location: Concord, NC
Posts: 3,492
Default Re: Back Deck

Quote:
Originally Posted by bkelly2 View Post
Just out of curiosity, what is the difference between a "Deck" and a "Landing"?

or is there a difference? I don't know myself
Simply put, their intended purpose......now trying to get a pencil headed building inspector to acknowledge same is another story.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Using the Prescriptive Residential Deck Construction Guide mcyr Exterior Inspections 0 7/21/09 7:10 PM
Roof deck question wdecker Exterior Inspections 3 11/17/08 10:17 PM
Roy Cooke Removed from NACHI rcooke Canadian Inspectors 720 7/20/08 4:10 PM
Illinois State Chapter of InterNACHI DECK FRAMING/CONSTRUCTION COURSE ksitzes Miscellaneous Discussion for Inspectors 6 3/4/08 5:47 PM


All times are GMT -4. The time now is 1:27 PM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts