During a recent inspection I noticed two beam support methods that just don't seem right. It's in a 650,000 sq.ft building.

Pic #1 the beam rests on just slightly more than 1/3 of the wall plate and has been this way for 25 years.

Pic #2 the beam rests on the tip of the wall plate and has been this way for six years.
Attached Thumbnails
beam-support-concern-beam-1.jpg   beam-support-concern-beam-2.jpg  
Reply With Quote
  #2  
Old 7/27/08, 8:33 PM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 18,917
Default Re: Beam Support Concern

Erol, you got mail.
Reply With Quote
  #3  
Old 7/27/08, 8:43 PM
Erol Kartal Erol Kartal is offline
Active Poster
 
Join Date: Feb 2008
Posts: 864
Please Note: Erol Kartal is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Beam Support Concern

Thanks, Marcel. Glad I caught that and glad people like you are at NACHI.
Reply With Quote
  #4  
Old 7/27/08, 8:47 PM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 8,466
Default Re: Beam Support Concern

Would you mind sharing your conclusions?



InterNachi Awards Portal: http://co.nachi.org/inachiawards/

____________________________________________
"An Education, not just an Inspection"

Larry Kage, CMI
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector serving the Traverse City, Michigan area and beyond.
Reply With Quote
  #5  
Old 7/27/08, 8:51 PM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 18,917
Default Re: Beam Support Concern

Erol, I have no problem in you posting my PM for others to see.

It is up to you.

Marcel
Reply With Quote
  #6  
Old 7/27/08, 8:52 PM
Erol Kartal Erol Kartal is offline
Active Poster
 
Join Date: Feb 2008
Posts: 864
Please Note: Erol Kartal is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Beam Support Concern

Quoted From Marcel - The King of Beam.

The first picture is not clear, so I will have to assumme the typical detail for such.

The wall angle clip that you see is usually installed for erection purposes and at times to supplement the bearing capacities for the beam.

Usually the beam would have a beam clip on the end and bolted to cast in place anchor bolts or drilled epoxy bolts.
If this wall clip was designed to carry the load, it is wrong.

If this wall clip was designed to supplement the bolted connection to the concrete it is wrong.

If installed as an erection aid, it is still wrong in placement.

The second picture is a stabilizer clip for a girder bar joist.

It is in the wrong placement for doing it's job as a lateral stabilizer as it was designed for.
Those do not usually get welded. They are meant to provide stability and allow movement under load.
Reply With Quote
  #7  
Old 7/27/08, 8:58 PM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 8,466
Default Re: Beam Support Concern

Thanks guys.



InterNachi Awards Portal: http://co.nachi.org/inachiawards/

____________________________________________
"An Education, not just an Inspection"

Larry Kage, CMI
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector serving the Traverse City, Michigan area and beyond.
Reply With Quote
  #8  
Old 7/28/08, 3:28 AM
dbucknavich dbucknavich is offline
Active Poster
 
Join Date: Feb 2006
Location: Chandler, AZ
Posts: 653
Please Note: dbucknavich is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Beam Support Concern

It appears that there is also not 100% bearing of the beam to the support. That is an automatic issue
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Ridge Beam Support cduphily Exterior Inspections 10 5/13/08 10:24 PM
Heavy timber posts and support beam hziegenbein Structural Inspections 3 9/24/07 4:38 PM
Crack in Support Beam Berry T. Wilson Structural Inspections 5 5/26/07 4:15 PM
Steel beam lateral support Mark Ellison Structural Inspections 10 1/16/07 11:40 PM
Support post for Beam, is this right? mlong Structural Inspections 63 7/25/06 7:34 PM


All times are GMT -4. The time now is 10:03 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts