Refresher:
The secondary emergency exit required in a bedroom is usually a window. The dimensions of the openings are to ensure the residents an escape route, but equally important, they allow firefighters with a backpack to enter. The opening must be at least 24" high and at least 20" wide. with a net area of 5.7 sq.ft. The window sill must not be higher than ____" from the floor. UBC - 310.4 IRC - 310.1, 310.1.1, 310.1.2,3 |
|
#2
|
||||
|
||||
|
Please Note:
rgrizzle is a non-member guest and is in no way affiliated with InterNACHI or its members.
44" I believe F.B.C. chapter 10 section 1025
|
|
#3
|
||||
|
||||
|
Quote:
The opening must be a minimum of 24" high and a minimum of 20" wide. and not less than 5.7 sq. ft. and no more than 44" high. That means that at 24" high, the window opening would have to be 34.2" wide to meet the 5.7 s.f. criteria. NFPA 101 Marcel LEED Green Associates InachiAwardsPortal: Inachi US Member of the Year Award 2009 |
|
#4
|
||||
|
||||
|
Marcel,
You are correct! I put a calculator to it! Wow! |
|
#5
|
|||
|
|||
|
Please Note:
Richard A. Hetzel is a non-member guest and is in no way affiliated with InterNACHI or its members.
The 44-inch sill height is correct, but states which have adopted the most recent versions of the IBC may have a different (more stringent, meaning closer to the floor) requirement. I don't have a 2006 code handy to check.
|
|
#6
|
||||
|
||||
|
Quote:
This is why we see so many new homes built with all the double hung windows the same size, first and second floor, unless your in Mass. which I think is 3.2. One thing to remember is casement windows can meet egress but be much smaller if they have egress hardware on them which the clear opening is achieved when the window is cranked open to a full 90 degrees. |
|
#7
|
||||
|
||||
|
Your right Peter, the Casement would be the best option to meet those needs and the next best in my opinion would be a single or double hung when it is 36" wide, but that is a big window.
Marcel LEED Green Associates InachiAwardsPortal: Inachi US Member of the Year Award 2009 |
|
#8
|
||||
|
||||
|
Quote:
IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ® Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net |
|
#9
|
|||
|
|||
|
Please Note:
Randy L. Thomas is a non-member guest and is in no way affiliated with InterNACHI or its members.
Be careful not to forget about the exception to that 5.7 sf rule...that is only required for windows that are not GRADE FLOOR OPENINGS. A grade floor window is basically a first floor window that a fireman could reach without the help of a ladder. Such windows only require 5.0 sf of opening. That is true for both IBC and IRC codes.
|
|
#10
|
|||
|
|||
|
I inspected a home two weeks ago and the owner was present and was a fireman. I asked him if he finds trapped victims in homes where the windows are too small to exit through them and he said yes, quite often they do find people that have died due to too small of egress windows. He said to write up too small of windows in a forceful way to prevent deaths.
Pillar To Post Professional Home Inspection of SW Utah Serving all of Iron and Washington Counties including the cities of St. George, Cedar City, Beaver, Brian Head, Duck Creek and more. Check out our website www.pillarposthomeinspection.com Growing our business by leaps and bounds every day!! Frank G. Ross Certified Home Inspector C.T.R.
(Certified ~ Trained ~ Reliable) |
|
#11
|
||||
|
||||
|
Thread resurrection here...
So this casement at 13-1/2" clear width and 35-1/2" clear height is something to write up. Darin Redding, CPI Housecall Property Inspections san diego home inspection rental inspection | warranty inspection Facebook Like darin@sandiegohomeinspect.com 619-663-8740 home inspector in San Diego, Carlsbad, Poway, La Mesa, El Cajon, Chula Vista. |
|
#12
|
|||
|
|||
|
Quote:
|
|
#13
|
||||
|
||||
|
thank you sir
Darin Redding, CPI Housecall Property Inspections san diego home inspection rental inspection | warranty inspection Facebook Like darin@sandiegohomeinspect.com 619-663-8740 home inspector in San Diego, Carlsbad, Poway, La Mesa, El Cajon, Chula Vista. |
| Need a home inspection in North Carolina? Check out InterNACHI's listing of North Carolina certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine. |
|
#14
|
||||
|
||||
|
Please Note:
prichardson is a non-member guest and is in no way affiliated with InterNACHI or its members.
2009 NC Building Code1026.2 Emergency escape and rescue openings shall have a minimum net clear opening of 5.7 square feet.
This is meant for firefighters and rescue personnel to be able to break out area for entrance while wearing equipment 1026.2.1The minimum net clear opening height dimension shall be 24"(610mm). The net clear opening width dimension shall be 20 inches(508mm). The net clear opening shall be the result of normal operation of the opening. This is the normal opening of the sash so a person can go through. It is not required to have 5.7 sq ft of opening under normal operation of window. This is how a single hung window can meet the code, if the opening when you raise the sash is a least 20 inches wide and 24 inches in height. Also no more than 44" from floor. For classrooms serving grade 5 and younger, no more than 32" from floor |
|
#15
|
||||
|
||||
|
Thanks PR for the detailed response. Question - what is the best way to have the code book you referenced, e-copy, website subscription, hard copy? I would like to have one in my library for reference.
Darin Redding, CPI Housecall Property Inspections san diego home inspection rental inspection | warranty inspection Facebook Like darin@sandiegohomeinspect.com 619-663-8740 home inspector in San Diego, Carlsbad, Poway, La Mesa, El Cajon, Chula Vista. |
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| Bedroom window sill heights | jlybolt | Interior Inspections | 12 | 7/5/07 3:46 PM |
| CPA of Health Canada reminding us of corded window coverings. | gromicko | Canadian Inspectors | 4 | 4/23/07 8:31 AM |
| Master bedroom has no window... | jonofrey | Exterior Inspections | 43 | 10/27/06 10:26 PM |