I found this beveled double LVL on a framing inspection that also holds up the end of another large LVL beam.

I reported the need for the engineers drawing since I knew it could be correct as is but had some doubts due to the loads on it.

The builder sent my client the drawing and specs, it indicated a 5 1/2 inch heel at the end of the beam and a 5/12 bevel slope. An email also came with it that stated " the calculations are correct on the beam".

I went back for the predrywall and framing reinspection and actually measured it since I knew it did not have a 5 1/2 inch heel.

In case the pictures ended up too small, the heel came out to be 4 inches and the bevel was wrong too so its back to the drawing board......

I hope I get to go back and see what the repair looks like.
Attached Thumbnails
beveled-lvl-beam-imgp0132.jpg   beveled-lvl-beam-001.jpg   beveled-lvl-beam-002.jpg   beveled-lvl-beam-003.jpg  



B.A. King Home Inspections, LLC
www.BAKingHomeInspections.com
Serving Charlotte NC area and Rock Hill SC areas.
CMI Certified Master Inspector and Independent
License NC2449 and SC1597
704 301-3207



"Discovery consists in seeing what everyone else has seen and thinking what no one else has thought."
- Albert Szent-Gyvrgyi, Nobel Prize for Medicine 1937
Reply With Quote
Need a home inspection in Maine? Check out InterNACHI's listing of Maine certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 9/14/10, 8:32 PM
Kenneth Dolin's Avatar
Kenneth Dolin Kenneth Dolin is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: Palm Beach County, Florida
Posts: 502
Default Re: Beveled LVL beam

let us know



Ken Dolin
Kenco Home Inspections
WWW.Kenco.org
State of Florida Licensed Home Inspector HI 59
Reply With Quote
  #3  
Old 9/14/10, 9:16 PM
Bruce A. King's Avatar
Bruce A. King Bruce A. King is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: York, SC
Posts: 3,207
Default Re: Beveled LVL beam

They provided a new engineers drawing and letter that indicates the beveled beam is still within the design numbers.



B.A. King Home Inspections, LLC
www.BAKingHomeInspections.com
Serving Charlotte NC area and Rock Hill SC areas.
CMI Certified Master Inspector and Independent
License NC2449 and SC1597
704 301-3207



"Discovery consists in seeing what everyone else has seen and thinking what no one else has thought."
- Albert Szent-Gyvrgyi, Nobel Prize for Medicine 1937
Reply With Quote
  #4  
Old 9/14/10, 9:46 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,058
Default Re: Beveled LVL beam

The heel should be measured at the minimum bearing point, which is generally 1-1/2". Is that about where your third picture is?



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #5  
Old 9/14/10, 10:46 PM
Bruce A. King's Avatar
Bruce A. King Bruce A. King is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: York, SC
Posts: 3,207
Default Re: Beveled LVL beam

Quote:
Originally Posted by jpope View Post
The heel should be measured at the minimum bearing point, which is generally 1-1/2". Is that about where your third picture is?
No, the 2nd picture is the heel as indicated on both of the engineers drawings. The end of the beam should have been 5 1/2 inches tall according to the original plans which would have made the height in the third picture over 7 inches.

What did you mean by the 1 1/2 inches? The top plate is 3 1/2 inches bearing surface.



B.A. King Home Inspections, LLC
www.BAKingHomeInspections.com
Serving Charlotte NC area and Rock Hill SC areas.
CMI Certified Master Inspector and Independent
License NC2449 and SC1597
704 301-3207



"Discovery consists in seeing what everyone else has seen and thinking what no one else has thought."
- Albert Szent-Gyvrgyi, Nobel Prize for Medicine 1937
Reply With Quote
  #6  
Old 9/14/10, 11:25 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,058
Default Re: Beveled LVL beam

Generally, beams and such require a minimum end-bearing of 1-1/2" on their support, whether it be a "plate" or other type of supporting wall.

So the heel can technically be 5-1/2" at that point, which is about half way onto the plate. Anything past that is just "extra."



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #7  
Old 9/14/10, 11:41 PM
Bruce A. King's Avatar
Bruce A. King Bruce A. King is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: York, SC
Posts: 3,207
Default Re: Beveled LVL beam

The engineers drawing showed the entire 3 1/2 inches of bearing surface as being used or required. LVL beams typically require 3 1/2 inches due to the extremely high loads. Sawn lumber beams are good for only 1 1/2 bearing in most cases.



B.A. King Home Inspections, LLC
www.BAKingHomeInspections.com
Serving Charlotte NC area and Rock Hill SC areas.
CMI Certified Master Inspector and Independent
License NC2449 and SC1597
704 301-3207



"Discovery consists in seeing what everyone else has seen and thinking what no one else has thought."
- Albert Szent-Gyvrgyi, Nobel Prize for Medicine 1937
Reply With Quote
  #8  
Old 9/14/10, 11:47 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,058
Default Re: Beveled LVL beam

Quote:
Originally Posted by bking View Post
The engineers drawing showed the entire 3 1/2 inches of bearing surface as being used or required.
That's really all that matters. I've seen glue-lams and LVL's at 1-1/2", but it's up to the engineer.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Deflected Cantelevered Beam pdickerson Structural Inspections 4 4/3/08 10:16 AM
Steel beam bearing 1 1/2" scosta Structural Inspections 17 6/12/06 9:01 PM


All times are GMT -4. The time now is 1:28 PM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts