Default Cantilevered Balcony

I know in the past that Balcony cantilevers has been a hotly debated topic so I'm posting the information below for reference. The information is from the Florida Building Code but is the exact language that is contained in the International Building Code. Hope you find the information useful on your next cantilever deck inspection.

TABLE R502.2.3.3(2) CANTILEVER SPANS FOR FLOOR JOISTS SUPPORTING EXTERIOR BALCONYa, b, e, f

Member Size Spacing Maximum Cantilever Span
(Uplift Force at Backspan Support in lb)c, d
2 × 8 12″ 42″ (139) 2 × 8 16″ 36″ (151) 2 × 10 12″ 61″ (164) 2 × 10 16″ 53″ (180) 2 × 10 24″ 43″ (212) 2 × 12 16″ 72″ (22 2 × 12 24″ 58″ (279)

For SI:1 inch = 25.4 mm, 1 pound per square foot = 0.0479 kPa.

a. Spans are based on No. 2 Grade lumber of Douglas fir-larch, hem-fir, southern pine, and spruce-pine-fir for repetitive (3 or more) members.

b. Ratio of backspan to cantilever span shall be at least 2:1.

c. Connections capable of resisting the indicated uplift force shall be provided at the backspan support.

d. Uplift force is for a backspan to cantilever span ratio of 2:1. Tabulated uplift values are permitted to be reduced by multiplying by a factor equal to 2 divided by the actual backspan ratio provided (2/backspan ratio).

e. A full-depth rim joist shall be provided at the cantilevered end of the joists. Solid blocking shall be provided at the cantilevered support.



Mark S. Tyson

M Tyson construction LLC
Tyson Home Inspections

Certified General Contractor #1516843
Florida Licensed Home Inspector #1824
Member N.A.C.H.I.
IAC2 certified
Member Florida Building Officials Association
http://www.TysonHomeInspections.com
Reply With Quote
  #2  
Old 3/8/11, 1:23 PM
Mark S. Tyson Mark S. Tyson is offline
InterNACHI Member
 
Join Date: Jun 2009
Location: Fort Pierce, Fl.
Posts: 359
Default Re: Cantilevered Balcony

TABLE R502.2.3.3(2) CANTILEVER SPANS FOR FLOOR JOISTS SUPPORTING EXTERIOR BALCONYa, b, e, f
Member Size
Spacing
Maximum Cantilever Span
(Uplift Force at Backspan Support in lb)c, d
2 × 8
12″
42″ (139)
2 × 8
16″
36″ (151)
2 × 10
12″
61″ (164)
2 × 10
16″
53″ (180)
2 × 10
24″
43″ (212)
2 × 12
16″
72″ (22
2 × 12
24″
58″ (279)


For SI:1 inch = 25.4 mm, 1 pound per square foot = 0.0479 kPa.

a. Spans are based on No. 2 Grade lumber of Douglas fir-larch, hem-fir, southern pine, and spruce-pine-fir for repetitive (3 or more) members.

b. Ratio of backspan to cantilever span shall be at least 2:1.

c. Connections capable of resisting the indicated uplift force shall be provided at the backspan support.

d. Uplift force is for a backspan to cantilever span ratio of 2:1. Tabulated uplift values are permitted to be reduced by multiplying by a factor equal to 2 divided by the actual backspan ratio provided (2/backspan ratio).

e. A full-depth rim joist shall be provided at the cantilevered end of the joists. Solid blocking shall be provided at the cantilevered support.


This should be a bit easier too read



Mark S. Tyson

M Tyson construction LLC
Tyson Home Inspections

Certified General Contractor #1516843
Florida Licensed Home Inspector #1824
Member N.A.C.H.I.
IAC2 certified
Member Florida Building Officials Association
http://www.TysonHomeInspections.com
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Balcony issue kdolin Exterior Inspections 4 11/21/10 5:18 PM
BALCONY Inspections in FLORIDA (Commercial) jacaron Florida Inspectors 3 10/31/09 9:09 AM
Balcony FUBAR jfunderburk Exterior Inspections 4 6/25/09 6:27 AM
Cantilevered Balcony Erol Kartal Structural Inspections 12 12/9/08 12:04 AM


All times are GMT -4. The time now is 1:31 PM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts