Interesting finding. I was asked to inspect the installation of the subfloor in this home and found the following. The floor joists are 2" x 10" - 16" o.c. attached to built-up 2" x 12" beams. The home is approximately 30' wide with the beams spaced 10" o.c. (joist span 10'). The floor joists are cantilevered approximately 5" on all exterior walls. There is a gable roof but the attic was not entered to determine the type framing.
Looks like this platform was constructed for brick veneer that was not installed. The floor joist on the gable ends do not have blocking installed and are only supported by the beams every 10'. This does not appear to be adequate to me. I would like your input on 2 issues. 1) would blocking between these joists provide adequate support? 2) would the installation of brick veneer be sufficient to bear the load of the end walls since the sill plate is not covering both the block/brick? There is adequate footing for a veneer wall. Any input would be appreciated. |
|
#2
|
||||
|
||||
|
Quote:
That the decking overhangs the foundation wall 5" is indicative of a foundation contractor that doesn't know how to read drawings, or the homeowner/contractor was trying to save money on concrete. The 5" cantalever is well within the specs allowable for this type of thing but to me there is more to this than a 5" overhang. Ask to see the drawings and have a good look at the design of the building. Something is definately amiss here. Larry Larry Ewens 1578 Colborne St Brantford On Nachi ID #05022485 Just my usual 12.5 cents ![]() http://acissbrant.blogspot.com/ |
|
#3
|
|||
|
|||
|
Please Note:
rrichards2 is a non-member guest and is in no way affiliated with InterNACHI or its members.
The cantilever around the house may have been a provision for a future foundation wall finish stone, brick etc as mentioned before. However, the floor joist framing on two ends of this house is wrong. The second to last joist should be doubled up and lookouts/stringers should projected out at 16" o.c to create the overhang/cantilever , all with proper hangers installed. The current configuration is not providing any structural support.
I would recommend immediate repairs by a qualified framing contractor. Roy |
|
#4
|
|||
|
|||
|
Please Note:
Steven Brewster is a non-member guest and is in no way affiliated with InterNACHI or its members.
Sorry for the misconception Larry, sometimes my thinkin goes faster than my fingers. What I was trying to say, the approx. 5" cantilever is about right to install brick veneer against the foundation wall (block). It appears the veneer has been omitted at some point in the construction. Any way back to the original questions I posted, any feedback?
|
|
#5
|
||||
|
||||
|
Quote:
Attachment 3335 click to enlarge I've never seen such an excessive overhang on any building. There's something wrong here... In pic #3...what's holding this side of the house in place? It appears to be an empty cavity. Is this a manufactured home that was placed on top of this poured foundation. Last edited by dvalley; 10/7/07 at 4:41 PM.. |
|
#6
|
|||
|
|||
|
Please Note:
Steven Brewster is a non-member guest and is in no way affiliated with InterNACHI or its members.
Attached is a detailed drawing of what a brick & CMU stem wall should look like. Just seems to me it will be difficult to add this additional brick properly to support the wall load.
I was told a few hours ago that the brick was omitted by the purchaser and would be installed sometime in the future. What a place to cut costs!!!! |
|
#7
|
|||
|
|||
|
Please Note:
rrichards2 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
Roy R. Last edited by rrichards2; 5/7/06 at 11:26 PM.. |
|
#8
|
|||
|
|||
|
Please Note:
Steven Brewster is a non-member guest and is in no way affiliated with InterNACHI or its members.
Roy, I tend to disagree. If you study the details of the diagram I submitted earlier and view the photos below, the brick has got to carry some of the load. Picture this type stem wall as a brick curtain wall with CMU supports. Same principle. At least thats the way I understand it.
|
|
#9
|
||||
|
||||
|
1. It's possible that blocking the last joist bay might be sufficient, but that's a call for a Structural Engineer. It's a cantelever calculation and framing members supporting cantelevers are supposed to extend two thirds of the overhang distance to the interior of the bldg.
2. Any part of the building bearing a load should be designed for that purpose. Seems to me that a veneer resting on a ledge might be sufficient depending on the veneer and foundation construction but then again, maybe not. I see it as requiring engineering calculations. my 2¢ -Kent |
|
#10
|
|||
|
|||
|
Please Note:
rrichards2 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Maybe I should have added that I am a trade certified carpenter and general contractor. I have been building and renovating homes for more than 20 years. Brick or no brick, the joist framing on this house is still wrong. The rim joist that is floating in the air right now and end nailed to that beam is not providing any structural support for that exterior wall above it. I would suspect you might find some cracks on the interior wall by now or will soon.
|
|
#11
|
|||
|
|||
|
Please Note:
Steven Brewster is a non-member guest and is in no way affiliated with InterNACHI or its members.
I agree with you Roy that this is wrong but if the brick stem wall had been installed initially (as pictured in the earlier diagram with proper sill plate/bolted) no problem would exist. I was interested in what others might do to correct this deficiency.
As well, I have been remodeling for over 10 yrs. .Thanks for the input. |
|
#12
|
|||
|
|||
|
Please Note:
rrichards2 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
down there blow away whenever the wind picks up. Good luck. |
|
#13
|
|||
|
|||
|
Please Note:
Steven Brewster is a non-member guest and is in no way affiliated with InterNACHI or its members.
Lucky you, no tornados or hurricanes to blow you away. Thanks for your input.
|
|
#14
|
|||
|
|||
|
Please Note:
rrichards2 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
However, not as often as you guys. |
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| floor joists | Kyra Bloom | Interior | 19 | 11/23/07 10:38 AM |
| Where do I put the Aquarium? | mcyr | Structural | 3 | 11/6/07 3:05 PM |
| What's Wring With This Picture: Bored Holes in Floor Joists? | homebild | Structural | 17 | 5/4/07 8:33 AM |
| Rigid duct straped to ceiling joists? | badair | HVAC | 4 | 10/25/06 5:14 AM |
| Ceiling discoloration from joists? | dtaylor | General Inspection Discussion | 4 | 8/3/06 12:27 AM |