Default Collar tie

Inspected a house, 85yrs. young yesterday and when I inspected the attic, this is what I found. There is no ridge rafter and no collar ties. The joint where the two rafters connect are good. Not sure if I should call this out. Again, this home is 85 yrs. young and no problems as of yet.

collar-tie-copy-p2070075.jpg



"I have not failed, I have just found a 1000's way's that didn't work" Thomas Edison

www.newbeginningshomeinspection.com
Reply With Quote
  #2  
Old 2/8/09, 2:41 PM
Claude Lawrenson's Avatar
Claude Lawrenson Claude Lawrenson is offline
InterNACHI Member
 
Join Date: Dec 2003
Location: Tecumseh-Windsor, ON
Posts: 2,122
Default Re: Collar tie

Generally I would not call out the need to add collar ties unless you observed dipping or bowing in the roof plane.

From your photo the roof framing looks fairly straight (without significantly noticeable bows in the structural framing).



Cheers, Claude Lawrenson NACHI03121515
Inspection Support Services Inc.
"Those who can do. Those who CARE, teach" or
“Teaching is the highest form of understanding.” Aristotle
Reply With Quote
  #3  
Old 2/8/09, 2:57 PM
bdoles2's Avatar
bdoles2 bdoles2 is offline
Active Poster
 
Join Date: Aug 2006
Location: Atlanta, GA
Posts: 3,071
Please Note: bdoles2 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Collar tie

Looks to be typical for a home of that age. If there are no signs of sagging or any other defect in regards to support, I wouldn't bother with it being in my report.

But I have on occasion inserted an illustration to explain the dynamics behind a collar tie.
Reply With Quote
  #4  
Old 2/8/09, 3:06 PM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,681
Default Re: Collar tie

I agree with both.

If there are no obvious issues with bowing or sagging of the rafters or exterior studded walls after all these years, then there's no need to upgrade.
Reply With Quote
  #5  
Old 2/8/09, 3:26 PM
nbhi's Avatar
nbhi nbhi is offline
InterNACHI Member
 
Join Date: Apr 2005
Location: Hamilton, OH
Posts: 715
Default Re: Collar tie

Thanks to all. That was my thought also.



"I have not failed, I have just found a 1000's way's that didn't work" Thomas Edison

www.newbeginningshomeinspection.com
Reply With Quote
  #6  
Old 2/8/09, 7:22 PM
jkogel jkogel is offline
Active Poster
 
Join Date: Jan 2007
Location: Sooke, BC
Posts: 699
Please Note: jkogel is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Collar tie

My step-dad's garage stood for about 90 years with no collar ties and only two 12' joists holding 24' long walls together. The roof caved in about a month ago with a foot of wet snow on it. The end of one of the joists was rotten and the nails finally let go.

John Kogel
www.allsafehome.ca
Reply With Quote
  #7  
Old 2/9/09, 9:16 AM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 8,343
Send a message via Yahoo to jfunderburk
Default Re: Collar tie

I think I would still point out their absence and say the construction technique doesn't conform to current standards but may have been typical when the house was built. Say that there is no visible sagging and you see no reason to upgrade, but that they can get a 2nd opinion if they desire. Would not put it in the Summary as a significant issue.



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #8  
Old 2/9/09, 2:29 PM
Erby Crofutt's Avatar
Erby Crofutt Erby Crofutt is offline
InterNACHI Member
 
Join Date: Sep 2002
Location: Georgetown, KY
Posts: 1,198
Default Re: Collar tie

Y'all that talked about sagging might want to read a bit more about the difference in location and purpose of collar ties versus rafter ties.

In short, RAFTER TIES help prevent sagging. COLLAR TIES are there to prevent uplift.

The picture shown is typical for the age of the home. Rafter opposing rafter with the ceiling joists acting as rafter ties.
Reply With Quote
  #9  
Old 2/9/09, 9:06 PM
Mario A. Kyriacou, CHI's Avatar
Mario A. Kyriacou, CHI Mario A. Kyriacou, CHI is offline
ESOP Committee Member
 
Join Date: Jun 2006
Location: Toronto, Ontario, Canada
Posts: 5,851
Default Re: Collar tie

Erby is correct.





'Imagination is more important than knowledge' (sometimes)
Mario Kyriacou CHI CMI-NACHI Canadian Member of the Year 2007

www.360degreeshomeinspections.com
Tel.# 416-722-6132
e-mail torontohomeinspector@yahoo.com

Last edited by mkyriacou; 10/17/09 at 1:03 AM..
Reply With Quote
  #10  
Old 2/10/09, 12:03 PM
Jeffery L. Haynes Jeffery L. Haynes is offline
InterNACHI Member
 
Join Date: Aug 2008
Location: Concord, NC
Posts: 3,492
Default Re: Collar tie

I simply ask myself this....."does the issue adversely effect the home in any manner of which would reasonably be of interest to my client?"

Construction and installation methods are going to change to some degree however how are they effecting the home now.


regards

Jeff
Reply With Quote
  #11  
Old 2/10/09, 12:23 PM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,681
Default Re: Collar tie

Quote:
Originally Posted by jhaynes View Post
I simply ask myself this....."does the issue adversely effect the home in any manner of which would reasonably be of interest to my client?"

Construction and installation methods are going to change to some degree however how are they effecting the home now.


regards

Jeff
Absolutely NOT.

Report what you see and you're job is done.
Reply With Quote
  #12  
Old 2/10/09, 12:24 PM
Claude Lawrenson's Avatar
Claude Lawrenson Claude Lawrenson is offline
InterNACHI Member
 
Join Date: Dec 2003
Location: Tecumseh-Windsor, ON
Posts: 2,122
Default Re: Collar tie

Good reference guide for construction terminology
http://www.ahfc.state.ak.us/iceimage...n_appderef.pdf


Collar tie
A horizontal member used to tie a pair of opposing rafters together. May be high to hold the upper joint together or may be low to serve as a ceiling joist. Also called a collar beam.



Cheers, Claude Lawrenson NACHI03121515
Inspection Support Services Inc.
"Those who can do. Those who CARE, teach" or
“Teaching is the highest form of understanding.” Aristotle
Reply With Quote
  #13  
Old 2/10/09, 5:58 PM
Jeffery L. Haynes Jeffery L. Haynes is offline
InterNACHI Member
 
Join Date: Aug 2008
Location: Concord, NC
Posts: 3,492
Default Re: Collar tie

Quote:
Originally Posted by dvalley View Post
Absolutely NOT.

Report what you see and you're job is done.
Hi David,

I respectfully disagree........ while inspectors are "generalists" many inspectors have extensive knowledge in various fields.........if a licensed electrician can make a call in regards to an area of his expertise then so be it............clients (and agents) find it annoying for an inspector to constantly be referring the client to a specialist.

I have 30 years in construction, in particular with framing as well as several other disciplines / phases of residential construction.....which is why agents love to hire me..............I seldom refer them to other trade specialist if I know the answer.............that is what I am getting at.

Sorry if I failed to make my self clear on that.

Let me also say that our state standards of practice clearly states that we are to report on any "systems or components so inspected which do not function as intended, allowing for normal wear and tear, and/or adversely affect the habitability of the dwelling......"

regards....

Jeff

PS. Also, if it has not already been stated; many of these style homes, typically built (thrown together) after WWII for the many veterans coming home...........taking into consideration that many counties didn't even have building inspections on this units, it was pretty much up to the contractor to ensure that such dwelling was safe. Like others have said, unless that roof is sagging........if its been doing well for 50 years then I wouldn't write it up........at least not in our "summary page" which is specially for items that are deficient or require further investigation.


Reply With Quote
  #14  
Old 2/10/09, 10:48 PM
Kenton H. Shepard, CMI's Avatar
Kenton H. Shepard, CMI Kenton H. Shepard, CMI is offline
InterNACHI Member
 
Join Date: Aug 2004
Location: Boulder, CO
Posts: 3,417
Send a message via ICQ to kshepard
Default Re: Collar tie

Quote:
Originally Posted by clawrenson View Post
Good reference guide for construction terminology
http://www.ahfc.state.ak.us/iceimage...n_appderef.pdf


Collar tie
A horizontal member used to tie a pair of opposing rafters together. May be high to hold the upper joint together or may be low to serve as a ceiling joist. Also called a collar beam.
Local nomenclature aside, that's simply a bad definition.
I've never heard the term "collar beam" used by anyone who was qualified in either log homes or conventional homes.
Collar ties go in the upper third of the roof and prevent uplift.
Rafter ties go low in the roof and tie the bottoms of opposing rafters together to keep the tops of the walls from spreading and the ridge from sagging.

Framing without a ridge was standard practice for many years. Lack of a ridge in a home from that era is only a defect if the ridgeline sags due to a missing ridge. I've never seen a ridgeline sag because no ridge was installed. It's pretty much always because of the lack of rafter ties or severely undersized and sagging rafters. Almost always the former.




Kenton Shepard, InterNACHI member # 04082383
Certified Master Inspector (CMI)
InterNACHI Director of International Development
Director of Green Building

EXPERT WITNESS SERVICE
Conventional and Log homes

(303) 717-8940

Last edited by kshepard; 2/10/09 at 10:54 PM..
Reply With Quote
  #15  
Old 2/11/09, 12:13 AM
Claude Lawrenson's Avatar
Claude Lawrenson Claude Lawrenson is offline
InterNACHI Member
 
Join Date: Dec 2003
Location: Tecumseh-Windsor, ON
Posts: 2,122
Default Re: Collar tie

How about this one:
http://irc.nrc-cnrc.gc.ca/pubs/ir/ir225/ir225.pdf



Cheers, Claude Lawrenson NACHI03121515
Inspection Support Services Inc.
"Those who can do. Those who CARE, teach" or
“Teaching is the highest form of understanding.” Aristotle
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Czech collar ties srowe Exterior Inspections 4 12/8/08 1:54 PM
How high do collar ties need to be? Nathan W. Swilling Structural Inspections 12 1/8/08 11:41 PM
vent collar fix by new home builder srowe Exterior Inspections 5 1/28/07 4:03 PM
Collar Ties rkoehler Interior Inspections 11 5/10/06 7:01 AM
Collar Ties--When Required? jfunderburk Structural Inspections 7 5/6/06 1:49 PM


All times are GMT -4. The time now is 1:32 PM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts