Doing a phase inspection, my client specifically instructed the builder to contact me prior to pouring concrete....(he was suppose to provide me his flow schedule)......needless to say that didn't happen. As they were pouring I was notified......I was able to go out there; temperature 23 degree, pour made on a fill lot (waiting for engineer letter), accelerant used 2% (not sure what type), and still waiting to find out about PSI used, any air entrainment etc.
The failed to cover concrete during curing (temperatures below freezing) and actually started to build upon it in less than 48 hours of pour. The framer stated (broken english) that thy will finish framing home in 2 days..... rest assure my client will not be happy. It was a bit hard to see in the dark (they are still framing as I write this) but I can tell they used common nails in the foundation straps, fastening same to pressure treated lumber. If client goes forward, they will have quite a bit of nails to pull out....... |
| Need a home inspection in Illinois? Check out InterNACHI's listing of Illinois certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine. |
|
#2
|
||||
|
||||
|
Damn Jeff...
What did you do? Kenton Shepard, InterNACHI member # 04082383 Certified Master Inspector (CMI) InterNACHI Director of International Development Director of Green Building EXPERT WITNESS SERVICE Conventional and Log homes (303) 717-8940
|
|
#3
|
|||
|
|||
|
Hi Kenton,
The client is looking at walking away from the home........ she will meet with the builder today and let me know. I advised the client that I wanted speak with the site supervisor to ask some basic questions and for him to provide me documentation to assure us that the foundation was sound. I initially requested: 1. All concrete ticket stubs to show any amount of water that was added. 2. Concrete supplier order detailing mix, slump, acclerants if any, type of cement, air entrainment details, and temperature of water that was added during the mix. 3. Engineer soil verification letter. 4. What precautions were being made to protect the foundation in light of the fact the forecast is still calling for subfreezing temps throughout the week and especially at night. 5. To call me days in advance to inspect the footers. (so far I have gotten squat) I went to the site yesterday because based upon their actions I suspected they may be your typical fast track builder and low and behold all the walls were up and the roof is being framed today.......they will finish up Monday. I will be out of town at the International Builders Show next week so will not be able to inspect the framing for at least a week........hopefully they will wait until I get back....but then again I would not be surprised if she walks away from the home. I looked at the foundation anchor straps and you can tell they used common paslode nails (not galvanized) on all pressure treated lumber. I didn't say a word about that yet........will see what my client wants do today when we speak. The client is very particular and rightfully so.........she spoke with about a dozen home inspectors prior to selecting me...........and she knew all the right questions to ask. She then followed it up with checking my references and recent inspections I performed going back to last year. I wanted to have a meeting with the builder and/or their site supervisor prior to construction so that we could work out any details about one another's expectations so that the job would flow well and our client would be happy...............amazing how all this could have been avoided with a 15 minute meeting. As of now if they go forward I have already advised the client that an engineer will need to be brought into the equation to do further testing on the foundation......in addition I will be requesting that additional prep work be done for tile......most builders will lay ceramic tile directly onto the concrete slab which can be very problematic, especially in cases like this. In a economy where every home sale is precious, this company and site supervisor screwed up big time. |
|
#4
|
||||
|
||||
|
You were there Jeff, I wasn't - however - I worked on high-rise and other commercial & industrial structures for many years. Granted, most of my work was on the West Coast, but it was quite common to start framing (both steel and lumber) on slab/deck pours within 24 hours of finish.
Obviously, the quality, mix and additives of the concrete make all the difference. Ultimately, the results of the concrete-integrity are determined by the testing laboratory and unless there is a significant failure rate in the testing, there isn't much that can be said. As for the slab/framing anchors, I can't speak to that. CA has much different standards than most other states. We are in SDC1 & SDC2 categories throughout the state. IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ® Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net |
|
#5
|
|||
|
|||
|
Hi Jeff,
Most people don't realize how much is involved with concrete.............the mix, prep, on-site pour etc......... I have yet to get any info from the site supervisor.....quite frankly I don't think he will give it to me because I suspect he used a standard mix and 2% Calcium Chloride and figured the temps would get up to the upper 50's which for the most part they were in the 20's. There was quite a bit of bleeding however I have yet to find out the slump. When I was building in Ohio, I worked with a large framing contractor who had a contract with numerous track builders.......they would pour one day and we would frame the next.....they would put straw down so that we would not leave footprints in the concrete...........pretty pathetic. I later would work with an old master builder from New England......we would pour the footing one day and the foundation the next......then stay off of it for about 4 weeks. He had been building for about 40 years.........he said he never had a leak in any foundation / basement. I thoroughly enjoyed working with him...........he was pretty much a master of all trades. At anyrate, commercial work is so much nicer in the fact that its more controlled and of course you typically have more professional workers. I have been talking to my partner (contracting side of the business) about getting more into commercial work...... we have a couple small commercial up fits and hopefully one small commercial building to do........however the competition is tough.........people coming in from all over the US to bid on job for next to nothing.......but I digress. If I were a betting man I would say the client will walk. I met her to get paid and during the meeting the builder/rep called and she chewed him a new one.......telling him that she was going to walk from the deal......... in the end she said she would meet him tomorrow and decide at that time. Seeing what I have already, I am pretty confident she will not be happy. I enjoy doing phase inspections but I do wish the GC's would meet with me prior to construction...........it would make everyone's job that much easier. Most of the data I read advises to give the foundation anywhere from 3 - 7 days rest during winter pours. If the builder would have let me know that he was going to build in less than 48 hours I would have had him do several samples for field test.........right now we have squat, other than the foundation to test. |
|
#6
|
|||
|
|||
|
Please Note:
Brian A. MacNeish is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
|
|
#7
|
|||
|
|||
|
Quote:
As you know concrete gets stronger with age.......not that its necessary to wait that long however I do believe many problems can and do arise within in the residential side of construction because of builders being in too much of a hurry to collect the paycheck. In the south....at least I will say the Carolinas, many of the basements are block........I personally think doing a poured basement is stronger and less chance of cracks / leaks. |
|
#8
|
||||
|
||||
|
Please Note:
prichardson is a non-member guest and is in no way affiliated with InterNACHI or its members.
It sounds like they might have a few problems, but I don't think building on concrete too fast is one of them. It is typical and accepted construction practice to begin framing on a slab after 24 hours.
|
|
#9
|
|||
|
|||
|
You actually expect the builder to wait a week on you??? Lot's of luck on that one. With all due respect if I was the builder I'd work a LITTLE closer with you but you sir aren't his boss and have no authority over how/when he does his job. You'd get laughed right off of the jobsite around here demanding stuff from builders. AHJ's can get away with that but not us.
George Russell George Russell Professional Inspections Austin,Texas TREC # 10215 512-296-9538 http://georgerussellprofessionalinspections.com/ http://www.facebook.com/austinhomeinspections |
|
#10
|
|||
|
|||
|
George,
No where did I say that I was his boss.......don't know why one would think that, no did I expect him to wait a week to build however to build under the current wx condition without following reasonable guidelines setforth by numerous concrete institutes / networks........just shows that they want to them up as fast as they can without regard to what is best for the home. I had a conversation with the sup last night and let him know we are both have the same goal in mind, that being looking after the construction of our clients home. Phillip, pouring in cold weather (in this case less than 25 degrees) and building the next day is not an acceptable practice. See ACI306R The sup did admit that they typically pour one day and build the next.......... just as I suspected. I have learned that rebar in fact was used (although I did not see any in the footings or slab... at least that which was visible when I got there) and Calcium Chloride was used as an accerlant......unless the rebar was coated, there could be a problem. I have asked for the blueprints to look at same.... No insulation blankets were used and even though he said he used plastic, none was in place any time I drove by. I did advice the sup some of the common problems I find with new homes...... I also pointed out to him that he may want to look carefully at the nails used in pressure treated lumber. I can about guarantee that when they install the trusses they will nail the bottom chord to all interior walls. I did advice the sup that I was in Florida at the International Builder's Show the rest of the week and asked that he hold off on installing insulation until I get back for which he agreed.........will let you know what comes of this project. |
|
#11
|
||||
|
||||
|
Jeffery
I have done contract administration & construction inspection for over 30 years and I have learned a few things along the way. There are only two basic things that motivate a contractor; Making Money and Losing Money. Unless you have the authority to control either of them in writing by way of a signed contract your job function will be reduced from an inspector to an observer. Most clients do not fully understand construction contracts and/or contract administration. Clients need to be educated when bidding a construction project of any significant size. They should have a detailed contract, detailed construction specifications, detailed drawings, detailed work schedules, an established paperwork management system to track RFIs, change orders, plan changes and finally a problem/issue escalation protocol with required weekly progress meetings. I know it sounds like allot but its nothing compared to the time and headaches you and/or your client will endure if the contractor gets behind schedule, goes over budget, goes bankrupt and everyone gets dragged into court. Typically I find most clients pick a contractor out of the phone book and before they call someone to oversee the work they have already signed a contract. The contract, prepared by the contractor, typically gives the client no control over the quality of workmanship and no references to material or code specifications. In my opinion this is the biggest mistake people make when deciding to build a new home. |
|
#12
|
|||
|
|||
|
Quote:
I was present when she chewed them a new one and they were very eager to please her, more importantly fulfill their agreement with her in allowing me to do a phased inspection in a reasonable manner. So far I have witnessed part of the footers in which no rebar was present although the plans supposedly call for it, concrete practices which do not follow cold weather pour, still plates using improper fasteners and I when I get back in state and conduct the dry-in stage inspection I will find a whole host of other issues. I am still awaiting documents detailing the concrete pour as well as the plans themselves. The client has already called them and advised them I better have them by the time I get back or she is walking. Service is any business is a key element to success........ I know from the homes I have built that while I am into make a profit, I know more importantly that profit means very little in comparison to my reputation / referrals that I get from a happy client. There have been a few (very few thankfully) in which I lost money (my fault) in order to make the client happy and they knew that.....(some even offered to pay more however I refused to accept payment).... in return I win the client over for life............but yes, for the most part GC are looking at bottom line.....at least the big track builder are using that model. Will keep all abreast as to how it pans out..... regards |
|
#13
|
||||
|
||||
|
This does not sound good and may not be easily resolved. I would advise the buyer to get a construction attorney involved just to make sure no mistakes are made on her part that could affect something in the future ie. the deposit.
If rebar was spec'd then the soil test must have had some issues or the plans were drawn up by someone that was playing it extra safe. I am thinking this is a basic 2200-2500sf tract house. I am amazed at the casual attitude some of the builder reps have even when the buyer is a very picky detailed person. I had one that would have ended up badly if the builder had not made repairs and produced engineers letters very quickly as demanded by the buyer based on my reports. Some builders are happy to let some buyers walk away since they know the finish work will never suit them. The act of allowing the framing to begin on a project with questions in the air about the foundation are simply astounding. B.A. King Home Inspections, LLC www.BAKingHomeInspections.com Serving Charlotte NC area and Rock Hill SC areas. CMI Certified Master Inspector and Independent License NC2449 and SC1597 704 301-3207 "Discovery consists in seeing what everyone else has seen and thinking what no one else has thought." - Albert Szent-Gyvrgyi, Nobel Prize for Medicine 1937 |
| Need a home inspection in Illinois? Check out InterNACHI's listing of Illinois certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine. |
|
#14
|
||||
|
||||
|
The problem is (as Randy indicated) the "questions" were not raised by anyone with the authority to effect a change. In other words, "no harm, no foul."
IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ® Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net |
|
#15
|
||||
|
||||
|
Quote:
Why would the buyer hire an inspector and not utilize the information? I have seen projects halted many times by my clients based on my reports. When I was hired to go back for a reinspection, the superintendents usually thank me since they have had a day or two to cool off. B.A. King Home Inspections, LLC www.BAKingHomeInspections.com Serving Charlotte NC area and Rock Hill SC areas. CMI Certified Master Inspector and Independent License NC2449 and SC1597 704 301-3207 "Discovery consists in seeing what everyone else has seen and thinking what no one else has thought." - Albert Szent-Gyvrgyi, Nobel Prize for Medicine 1937 |
![]() |