Are these hung correctly, without any nails?
|
|
#2
|
||||
|
||||
|
Yes, they appear to be correct. Those are top flange hangers, which extend over and are nailed into the top of the I-beam (which the inspector can't confirm) and they should have two nails (one per side) into the bottom chord of the abutting joist. I can't tell from the photo whether the bottom chords are nailed.
There are other situations in which an engineer will require the other holes you see to be filled, but you won't when you're looking at one of those situations without a set of plans... not your job as an inspector. The hangers had no glue installed before the joists were dropped into the hangers and so some may squeak, but that's a quality issue, not a structural issue. I wouldn't call anything about these hangers as a defect. ![]() Kenton Shepard, NACHI member # 04082383 Peak to Prairie Inspection Service Certified Master Inspector (CMI) Inspection of Conventional, Log, Strawbale and Historic Homes (303) 258-8289 |
|
#3
|
||||
|
||||
|
Quote:
I also just found this. http://www.strongtie.com/products/installation/itt.html Last edited by ccurrins; 9/4/08 at 1:17 AM. |
|
#4
|
|||
|
|||
|
Please Note:
Richard A. Hetzel is a non-member guest and is in no way affiliated with InterNACHI or its members.
If there is a hole in the hanger, there usually should be a nail in it, and nailing should be in accordance with the manufacturer's written instructions. Nail quantities and types can affect the load-carrying capacity of the hanger. Tthe hanger manufacturer's instructions are vitally important, and should be read and understood when selecting and installing hangers.
|
|
#5
|
|||
|
|||
|
Please Note:
Brian A. MacNeish is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
|
|
#6
|
|||
|
|||
|
Please Note:
Richard A. Hetzel is a non-member guest and is in no way affiliated with InterNACHI or its members.
The addition iin blue above is true and equally important, and is appreciated.
The video linked above shows a tab which is bent over the top of the bottom flange of a composite joist and nailed there. But Mr. MacNeish is correct, the manufacturers' recommendations of both hanger and joist are equally important. |
|
#7
|
||||
|
||||
|
Come on down...
Texas Professional Real Estate Inspectors Association ANNOUNCEMENT![]() badair http://www.adairinspection.com 972-487-5634 Dallas & Garland, TX 75228 & 75042 Residential-Commercial-Construction-EIFS-Infrared Thermography TREC # 4563 EDI: EIFS-MA TX # 39 04080595 Voted, by a slim margin, InterNACHI U.S. Member of the Year 2008 life is the random lottery of events followed by numerous narrow escapes...accept the good http://www.gunlaws.com/images/unitys.gif |
|
#8
|
|||
|
|||
|
Please Note:
Brian A. MacNeish is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
|
|
#9
|
||||
|
||||
|
Quote:
The top mount hangers are not installed correctly per Manufactures installation guide. http://www.ilevel.com/literature/TJ-4002.pdf The hangers should hang plumb and TJI's used as headers should have backer blocks and or filler blocks to enamble the hanger to be nailed properly to provide uplift, and rotation factors that are usually set factors in the design. I would recommend an Architectural review of this framing to see if it meets the proper installation of the design. It appears that Manufactures recommended installation procedures might not have been followed. I don't think it will go anywhere, but need to note it the way it is. Hope this helps a little. Marcel Cyr Home Inspections IAC2 Certified NACHI04070211 http://co.nachi.org/inachiawards/inachiawards551.html http://co.nachi.org/inachiawards Commercial Builder Ouellet Associaties Inc. |
|
#10
|
|||
|
|||
|
Please Note:
jkogel is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
John Kogel www.allsafehome.ca |
|
#11
|
||||
|
||||
|
Quote:
|
|
#12
|
||||
|
||||
|
Just received this!
The Simpson Strongtie Class is cancelled. The hotel reservations have been cancelled but please call to confirm. Due to hurricane Ike, the Gulf Coast contingency of inspectors would likely not be able to attend due to gas shortage unknown condition of home and family power still not restored to 70% of customers (Centerpoint) The class is in process of being rescheduled, TPREIA will notify you...if you are not able to attend alternate date, your registration money will be refunded. There are communities of the gulf coast that are wastelands. Pray for your fellow Texans. Regards Mike Mike Cothran Texas Professional Real Estate Inspectors Association Vice President Greater Houston Chapter of TPREIA Immediate Past President TPREIA.com badair http://www.adairinspection.com 972-487-5634 Dallas & Garland, TX 75228 & 75042 Residential-Commercial-Construction-EIFS-Infrared Thermography TREC # 4563 EDI: EIFS-MA TX # 39 04080595 Voted, by a slim margin, InterNACHI U.S. Member of the Year 2008 life is the random lottery of events followed by numerous narrow escapes...accept the good http://www.gunlaws.com/images/unitys.gif |
|
#13
|
||||
|
||||
|
Quote:
Barry, were you affected by that storm where you are? Marcel Cyr Home Inspections IAC2 Certified NACHI04070211 http://co.nachi.org/inachiawards/inachiawards551.html http://co.nachi.org/inachiawards Commercial Builder Ouellet Associaties Inc. |
|
#14
|
|||
|
|||
|
As a builder I have been using I-joists for about 12 years and I love them however one must pay attention that subcontractors understand their limitations.
Some of the common problems I have found are: 1. Improper fastening (wrong nails, wrong nailing pattern etc) 2. Not utilizing backer and crush blocks as called for 3. Improper cutting (when used as rafters) and improper notching 4. Improper band boards being used or bandboard (rimboard) not bearing on foundation sill plate 5. Improper spacing and / or OSB / Plywood not sheeted correctly 6. Improper nailing patterns on almost all LVL, Glulams and Paralams 7. Trimmer joist not doubled and nailed as required 8. Insulation not installed correctly in crawlspace when I-joist are more then 16" O.C. 9. Joist web stiffners not employed were required 10. Wrong hangers being utilized, especially around LVL, Gluelams, etc. All manufactures drop off installation instructions (usually several copies) to the jobsite as well as technical data sheets left for the code official to review or take put on file for that project............ask to see same. Jeff |
|