Default Correct Strong-Tie Connection?

Are these hung correctly, without any nails?
Attached Images
File Type: jpg 127.JPG (126.3 KB, 74 views)
File Type: jpg 128.JPG (99.6 KB, 81 views)
File Type: jpg 129.JPG (127.4 KB, 75 views)
Reply With Quote
  #2  
Old 9/4/08, 12:38 AM
Kenton H. Shepard, CMI's Avatar
Kenton H. Shepard, CMI Kenton H. Shepard, CMI is offline
InterNACHI Member
 
Join Date: Aug 2004
Location: Denver, CO
Posts: 1,940
Kenton H. Shepard, CMI is very trusted source of information Kenton H. Shepard, CMI is very trusted source of information Kenton H. Shepard, CMI is very trusted source of information Kenton H. Shepard, CMI is very trusted source of information Kenton H. Shepard, CMI is very trusted source of information Kenton H. Shepard, CMI is very trusted source of information Kenton H. Shepard, CMI is very trusted source of information Kenton H. Shepard, CMI is very trusted source of information Kenton H. Shepard, CMI is very trusted source of information
Send a message via ICQ to kshepard
Default Re: Correct Strong-Tie Connection?

Yes, they appear to be correct. Those are top flange hangers, which extend over and are nailed into the top of the I-beam (which the inspector can't confirm) and they should have two nails (one per side) into the bottom chord of the abutting joist. I can't tell from the photo whether the bottom chords are nailed.

There are other situations in which an engineer will require the other holes you see to be filled, but you won't when you're looking at one of those situations without a set of plans... not your job as an inspector. The hangers had no glue installed before the joists were dropped into the hangers and so some may squeak, but that's a quality issue, not a structural issue.

I wouldn't call anything about these hangers as a defect.





Kenton Shepard, NACHI member # 04082383
Peak to Prairie Inspection Service
Certified Master Inspector (CMI)

Inspection of Conventional,
Log, Strawbale and
Historic Homes
(303) 258-8289

Reply With Quote
  #3  
Old 9/4/08, 1:14 AM
Christopher B. Currins's Avatar
Christopher B. Currins Christopher B. Currins is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Alton, IL
Posts: 2,598
Christopher B. Currins .
Default Re: Correct Strong-Tie Connection?

Quote:
Originally Posted by kshepard
Yes, they appear to be correct. Those are top flange hangers, which extend over and are nailed into the top of the I-beam (which the inspector can't confirm) and they should have two nails (one per side) into the bottom chord of the abutting joist. I can't tell from the photo whether the bottom chords are nailed.

There are other situations in which an engineer will require the other holes you see to be filled, but you won't when you're looking at one of those situations without a set of plans... not your job as an inspector. The hangers had no glue installed before the joists were dropped into the hangers and so some may squeak, but that's a quality issue, not a structural issue.

I wouldn't call anything about these hangers as a defect.

Thanks Kenton. I was pretty comfortable with the install, but not sure. I've seen similar ones that are welded at the top of steel beams. No there were not ANY nails at the bottom or any where else. I'll leave it be.


I also just found this. http://www.strongtie.com/products/installation/itt.html

Last edited by ccurrins; 9/4/08 at 1:17 AM.
Reply With Quote
  #4  
Old 9/4/08, 5:08 PM
Richard A. Hetzel Richard A. Hetzel is online now
Active Poster
 
Join Date: Apr 2007
Location: Tobyhanna, Pennsylvania
Posts: 454
Richard A. Hetzel is generally well trusted
Please Note: Richard A. Hetzel is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Correct Strong-Tie Connection?

If there is a hole in the hanger, there usually should be a nail in it, and nailing should be in accordance with the manufacturer's written instructions. Nail quantities and types can affect the load-carrying capacity of the hanger. Tthe hanger manufacturer's instructions are vitally important, and should be read and understood when selecting and installing hangers.
Reply With Quote
  #5  
Old 9/4/08, 6:13 PM
Brian A. MacNeish Brian A. MacNeish is offline
Active Poster
 
Join Date: Apr 2007
Posts: 2,248
Brian A. MacNeish is often very helpful Brian A. MacNeish is often very helpful Brian A. MacNeish is often very helpful
Please Note: Brian A. MacNeish is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Correct Strong-Tie Connection?

Quote:
Originally Posted by Richard A. Hetzel
If there is a hole in the hanger, there usually should be a nail in it, and nailing should be in accordance with the manufacturer's written instructions. Nail quantities and types can affect the load-carrying capacity of the hanger. The hanger manufacturer's instructions (and beam/joist manufacturer's) are vitally important, and should be read and understood when selecting and installing hangers.
If the chords are made from a glulam product and are not solid wood, driving nails into the side of the chord flange may split the chord. IMO, the bottom of the chord would be better but couldn't find any good info on nailing rec's/practice for the glulam chords.
Reply With Quote
  #6  
Old 9/4/08, 9:23 PM
Richard A. Hetzel Richard A. Hetzel is online now
Active Poster
 
Join Date: Apr 2007
Location: Tobyhanna, Pennsylvania
Posts: 454
Richard A. Hetzel is generally well trusted
Please Note: Richard A. Hetzel is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Correct Strong-Tie Connection?

The addition iin blue above is true and equally important, and is appreciated.

The video linked above shows a tab which is bent over the top of the bottom flange of a composite joist and nailed there.

But Mr. MacNeish is correct, the manufacturers' recommendations of both hanger and joist are equally important.
Reply With Quote
  #7  
Old 9/5/08, 7:10 AM
Barry Adair's Avatar
Barry Adair Barry Adair is offline
InterNACHI Member
 
Join Date: Aug 2004
Location: GARLAND, TX
Posts: 3,167
Barry Adair .
Default Re: Correct Strong-Tie Connection?

Come on down...



Texas Professional Real Estate Inspectors Association ANNOUNCEMENT



badair
http://www.adairinspection.com
972-487-5634
Dallas & Garland, TX 75228 & 75042

Residential-Commercial-Construction-EIFS-Infrared Thermography
TREC # 4563
EDI: EIFS-MA TX # 39
04080595
Voted, by a slim margin, InterNACHI U.S. Member of the Year 2008

life is the random lottery of events followed by numerous narrow escapes...accept the good
http://www.gunlaws.com/images/unitys.gif
Reply With Quote
  #8  
Old 9/5/08, 8:49 AM
Brian A. MacNeish Brian A. MacNeish is offline
Active Poster
 
Join Date: Apr 2007
Posts: 2,248
Brian A. MacNeish is often very helpful Brian A. MacNeish is often very helpful Brian A. MacNeish is often very helpful
Please Note: Brian A. MacNeish is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Correct Strong-Tie Connection?

Quote:
Originally Posted by badair
Come on down...




TPREIA (or Simpson) seems fairly flush.........Free motel room (shared occupancy....that can be arranged!!), free breakfast and lunch !!!! Can you get me a free flight.....I'll probably join!!
Reply With Quote
  #9  
Old 9/6/08, 12:58 PM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 9,708
Marcel R. Cyr has a reputation beyond repute Marcel R. Cyr has a reputation beyond repute Marcel R. Cyr has a reputation beyond repute Marcel R. Cyr has a reputation beyond repute Marcel R. Cyr has a reputation beyond repute Marcel R. Cyr has a reputation beyond repute Marcel R. Cyr has a reputation beyond repute Marcel R. Cyr has a reputation beyond repute Marcel R. Cyr has a reputation beyond repute Marcel R. Cyr has a reputation beyond repute Marcel R. Cyr has a reputation beyond repute
Default Re: Correct Strong-Tie Connection?

Quote:
Originally Posted by ccurrins
Are these hung correctly, without any nails?
From what I can see in the pictures, these appear to be 560 series Silent Floor I-joist by Weyheuser.

The top mount hangers are not installed correctly per Manufactures installation guide.
http://www.ilevel.com/literature/TJ-4002.pdf

The hangers should hang plumb and TJI's used as headers should have backer blocks and or filler blocks to enamble the hanger to be nailed properly to provide uplift, and rotation factors that are usually set factors in the design.

I would recommend an Architectural review of this framing to see if it meets the proper installation of the design.

It appears that Manufactures recommended installation procedures might not have been followed.

I don't think it will go anywhere, but need to note it the way it is.

Hope this helps a little.

Marcel



Cyr Home Inspections
IAC2 Certified
NACHI04070211

http://co.nachi.org/inachiawards/inachiawards551.html
http://co.nachi.org/inachiawards


Commercial Builder
Ouellet Associaties Inc.
Reply With Quote
  #10  
Old 9/7/08, 11:09 AM
jkogel jkogel is online now
Active Poster
 
Join Date: Jan 2007
Location: Sooke, BC
Posts: 571
jkogel is well trusted jkogel is well trusted jkogel is well trusted
Please Note: jkogel is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Correct Strong-Tie Connection?

Quote:
Originally Posted by mcyr

The hangers should hang plumb and TJI's used as headers should have backer blocks and or filler blocks to enable the hanger to be nailed properly to prevent uplift, and rotation factors that are usually set factors in the design.


Marcel
Thanks, Marcel. Once again, you nailed it.

John Kogel
www.allsafehome.ca
Reply With Quote
  #11  
Old 9/7/08, 2:31 PM
Christopher B. Currins's Avatar
Christopher B. Currins Christopher B. Currins is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Alton, IL
Posts: 2,598
Christopher B. Currins .
Default Re: Correct Strong-Tie Connection?

Quote:
Originally Posted by mcyr
From what I can see in the pictures, these appear to be 560 series Silent Floor I-joist by Weyheuser.

The top mount hangers are not installed correctly per Manufactures installation guide.
http://www.ilevel.com/literature/TJ-4002.pdf

The hangers should hang plumb and TJI's used as headers should have backer blocks and or filler blocks to enamble the hanger to be nailed properly to provide uplift, and rotation factors that are usually set factors in the design.

I would recommend an Architectural review of this framing to see if it meets the proper installation of the design.

It appears that Manufactures recommended installation procedures might not have been followed.

I don't think it will go anywhere, but need to note it the way it is.

Hope this helps a little.

Marcel
Thanks Marcel, my impression was that it should have a backer, that open space didn't look right. But, I was not sure. You're the best.
Reply With Quote
  #12  
Old 9/17/08, 7:23 AM
Barry Adair's Avatar
Barry Adair Barry Adair is offline
InterNACHI Member
 
Join Date: Aug 2004
Location: GARLAND, TX
Posts: 3,167
Barry Adair .
Default Re: Correct Strong-Tie Connection?

Just received this!

The Simpson Strongtie Class is cancelled. The hotel reservations have been cancelled but please call to confirm.

Due to hurricane Ike, the Gulf Coast contingency of inspectors would likely not be able to attend due to
gas shortage
unknown condition of home and family
power still not restored to 70% of customers (Centerpoint)

The class is in process of being rescheduled, TPREIA will notify you...if you are not able to attend alternate date, your registration money will be refunded.

There are communities of the gulf coast that are wastelands. Pray for your fellow Texans.
Regards
Mike
Mike Cothran
Texas Professional Real Estate Inspectors Association
Vice President
Greater Houston Chapter of TPREIA
Immediate Past President
TPREIA.com



badair
http://www.adairinspection.com
972-487-5634
Dallas & Garland, TX 75228 & 75042

Residential-Commercial-Construction-EIFS-Infrared Thermography
TREC # 4563
EDI: EIFS-MA TX # 39
04080595
Voted, by a slim margin, InterNACHI U.S. Member of the Year 2008

life is the random lottery of events followed by numerous narrow escapes...accept the good
http://www.gunlaws.com/images/unitys.gif
Reply With Quote
  #13  
Old 9/17/08, 6:40 PM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 9,708
Marcel R. Cyr has a reputation beyond repute Marcel R. Cyr has a reputation beyond repute Marcel R. Cyr has a reputation beyond repute Marcel R. Cyr has a reputation beyond repute Marcel R. Cyr has a reputation beyond repute Marcel R. Cyr has a reputation beyond repute Marcel R. Cyr has a reputation beyond repute Marcel R. Cyr has a reputation beyond repute Marcel R. Cyr has a reputation beyond repute Marcel R. Cyr has a reputation beyond repute Marcel R. Cyr has a reputation beyond repute
Default Re: Correct Strong-Tie Connection?

Quote:
Originally Posted by badair View Post
Just received this!

The Simpson Strongtie Class is cancelled. The hotel reservations have been cancelled but please call to confirm.

Due to hurricane Ike, the Gulf Coast contingency of inspectors would likely not be able to attend due to
gas shortage
unknown condition of home and family
power still not restored to 70% of customers (Centerpoint)

The class is in process of being rescheduled, TPREIA will notify you...if you are not able to attend alternate date, your registration money will be refunded.

There are communities of the gulf coast that are wastelands. Pray for your fellow Texans.
Regards
Mike
Mike Cothran
Texas Professional Real Estate Inspectors Association
Vice President
Greater Houston Chapter of TPREIA
Immediate Past President
TPREIA.com

Barry, were you affected by that storm where you are?

Marcel



Cyr Home Inspections
IAC2 Certified
NACHI04070211

http://co.nachi.org/inachiawards/inachiawards551.html
http://co.nachi.org/inachiawards


Commercial Builder
Ouellet Associaties Inc.
Reply With Quote
  #14  
Old 9/17/08, 9:03 PM
Jeffery L. Haynes Jeffery L. Haynes is offline
InterNACHI Member
 
Join Date: Aug 2008
Location: Concord, NC
Posts: 174
Jeffery L. Haynes is generally well trusted Jeffery L. Haynes is generally well trusted
Default Re: Correct Strong-Tie Connection?

As a builder I have been using I-joists for about 12 years and I love them however one must pay attention that subcontractors understand their limitations.

Some of the common problems I have found are:

1. Improper fastening (wrong nails, wrong nailing pattern etc)
2. Not utilizing backer and crush blocks as called for
3. Improper cutting (when used as rafters) and improper notching
4. Improper band boards being used or bandboard (rimboard) not bearing on foundation sill plate
5. Improper spacing and / or OSB / Plywood not sheeted correctly
6. Improper nailing patterns on almost all LVL, Glulams and Paralams
7. Trimmer joist not doubled and nailed as required
8. Insulation not installed correctly in crawlspace when I-joist are more then 16" O.C.
9. Joist web stiffners not employed were required
10. Wrong hangers being utilized, especially around LVL, Gluelams, etc.

All manufactures drop off installation instructions (usually several copies) to the jobsite as well as technical data sheets left for the code official to review or take put on file for that project............ask to see same.

Jeff
Reply With Quote
  #15  
Old 9/18/08, 7:47 PM
Barry Adair's Avatar
Barry Adair Barry Adair is offline
InterNACHI Member
 
Join Date: Aug 2004
Location: GARLAND, TX
Posts: 3,167
Barry Adair .
Default Re: Correct Strong-Tie Connection?

Quote:
Originally Posted by mcyr View Post
Barry, were you affected by that storm where you are?

Marcel
McHammer,

Not anymore then normal when the weather is fair...we had wind gusts at the house of about 37mph and a few inches of rainfall over the 8th, 9th and 10th. I missed one EIFS inspection and the sellers would not give client an extension