Default Cracked Collar tie near rafter ..need advise

Attic appear ok, except for a cracked collar tie. The crack
was where the tie was nailed to the rafter.....How should
I write it up...what recommendations.

David
Reply With Quote
Need a home inspection in Hawaii? Check out InterNACHI's listing of Hawaii certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 4/19/11, 10:26 AM
Tom Leahy Tom Leahy is offline
InterNACHI Member
 
Join Date: Dec 2009
Location: Arlington, Texas
Posts: 358
Default Re: Cracked Collar tie near rafter ..need advise

It was hard to tell by the pic, but when I blew it up, seem to be only split at the end at the top edge. Looked like less than 1/2 inch and I wouldn't be concerned with it. Couldn't see how many nails other than the one at the split.

Is that a 1x6 collar? I know the IRC states 1 (inch) x 4 (inch) minimum. We all know that a 1x isn't 1 inch and just wonder if others call that out or not.



Fort Worth Home Inspector
Dallas Home Inspector
Reply With Quote
  #3  
Old 4/19/11, 10:38 AM
David Nasser's Avatar
David Nasser David Nasser is offline
InterNACHI Member
 
Join Date: Mar 2006
Location: Moreno Valley, CA
Posts: 771
Default Re: Cracked Collar tie near rafter ..need advise

Quote:
Originally Posted by tleahy View Post
It was hard to tell by the pic, but when I blew it up, seem to be only split at the end at the top edge. Looked like less than 1/2 inch and I wouldn't be concerned with it. Couldn't see how many nails other than the one at the split.

Is that a 1x6 collar? I know the IRC states 1 (inch) x 4 (inch) minimum. We all know that a 1x isn't 1 inch and just wonder if others call that out or not.
its a 1 by 6...and the other ties were fine. Should I recommend a repair?
Could someone say...the inspector should have noted it.
Reply With Quote
  #4  
Old 4/19/11, 11:15 AM
Tom Leahy Tom Leahy is offline
InterNACHI Member
 
Join Date: Dec 2009
Location: Arlington, Texas
Posts: 358
Default Re: Cracked Collar tie near rafter ..need advise

Quote:
Originally Posted by dnasser View Post
its a 1 by 6...and the other ties were fine. Should I recommend a repair?
Could someone say...the inspector should have noted it.
No harm in mentioning I suppose. As far as structurally, no issue (imo).

The only thing that I would've written up is the nails. They require a minimum of (2) 8 penny nails on each end. If they only used 2 and the 1 that was nailed high and split is now not performing its intended function.



Fort Worth Home Inspector
Dallas Home Inspector
Reply With Quote
  #5  
Old 4/19/11, 11:53 AM
David Nasser's Avatar
David Nasser David Nasser is offline
InterNACHI Member
 
Join Date: Mar 2006
Location: Moreno Valley, CA
Posts: 771
Default Re: Cracked Collar tie near rafter ..need advise

Quote:
Originally Posted by tleahy View Post
No harm in mentioning I suppose. As far as structurally, no issue (imo).

The only thing that I would've written up is the nails. They require a minimum of (2) 8 penny nails on each end. If they only used 2 and the 1 that was nailed high and split is now not performing its intended function.
thanks..

David
Reply With Quote
  #6  
Old 4/19/11, 10:16 PM
Kenton H. Shepard, CMI's Avatar
Kenton H. Shepard, CMI Kenton H. Shepard, CMI is offline
InterNACHI Member
 
Join Date: Aug 2004
Location: Boulder, CO
Posts: 3,417
Send a message via ICQ to kshepard
Default Re: Cracked Collar tie near rafter ..need advise

Quote:
Originally Posted by dnasser View Post
Attic appear ok, except for a cracked collar tie. The crack
was where the tie was nailed to the rafter.....How should
I write it up...what recommendations.

David
David, collar ties have to be installed in the upper third of the roof. This doesn't look like it qualifies. Rafter ties... even more structurally important than collar ties... should be installed as low as possible. These things seemed to be installed about halfway, meaning that it's a lack of knowledge on the part of whoever installed it.

Check out the Mastering Roof Inspection series on the NACHI web site. It has an article that explains this clearly.




Kenton Shepard, InterNACHI member # 04082383
Certified Master Inspector (CMI)
InterNACHI Director of International Development
Director of Green Building

EXPERT WITNESS SERVICE
Conventional and Log homes

(303) 717-8940
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
New article on collar ties and rafter ties inxil InterNACHI & RealMatcher Blogs 1 7/8/09 12:15 PM
Collar Ties vs. Rafter Ties. Please proof this new article. gromicko General Inspection Discussion 0 7/1/09 8:55 PM
NACHI releases new, free, online Structural Issues for Home Inspectors course. gromicko Inspection Education & Training 36 12/14/08 5:48 PM
How high do collar ties need to be? Nathan W. Swilling Structural Inspections 12 1/8/08 11:41 PM
Ridge Board....What's That? pabernathy Structural Inspections 35 2/22/07 11:25 PM


All times are GMT -4. The time now is 1:35 PM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts