Does this look kosher? The joist is about 2" thick and 7" wide. It looks like the cutout is more than 1/3 of the width of the beam. One joist is supported with some extra lumber, but it still doesn't look that great.
|
|
#2
|
||||
|
||||
|
Structural defects in both pictures. Greater than 1/3 the joist depth, as well as closer than 2 inches to the edge...
|
|
#3
|
||||
|
||||
|
Please Note:
relliott is a non-member guest and is in no way affiliated with InterNACHI or its members.
also cracked .
|
|
#4
|
|||
|
|||
|
Please Note:
Nathan W. Swilling is a non-member guest and is in no way affiliated with InterNACHI or its members.
So, what's the remedy? Would sandwiching it in OSB do the trick? How far on both sides?
|
|
#5
|
||||
|
||||
|
This is one of those things that Home Inspecters like to comment " refer to a licenced contractor or structural engineer"
Having said that, OSB sandwidch would make it stronger, but would NOT fix the problem, the joists are almost cut in half. |
|
#6
|
||||
|
||||
|
Hi,
ceiling joists/overlays are mainly outward pressure support. hard to say from a picture but I would say that an upright from the joist up to the rafter would do the trick. if that were a floor joist there would be a problem. Carla |
|
#7
|
||||
|
||||
|
Please Note:
relliott is a non-member guest and is in no way affiliated with InterNACHI or its members.
Thought it was a floor joist
|
|
#8
|
||||
|
||||
|
Bob, sure looks like a floor to me.
I am seeing a new framed wall and some subflooring and two different size pipes. I don't think we are seeing the whole picture from those two pics. The title calls it a toilet drain, so must be an attic being finsished as a bathroom, so now the ceiling joist are floor joist. The span of those might be sized wrong for this new load also. More information is required. Marcel Cyr Home and Commercial Property Inspections IAC2 Certified NACHI04070211 http://co.nachi.org/inachiawards Commercial Builder CertainTeed Master Shingle Applicator Shingle Technology Ouellet Associaties Inc. http://www.oaconstruction.com/ |
|
#9
|
|||
|
|||
|
Please Note:
Nathan W. Swilling is a non-member guest and is in no way affiliated with InterNACHI or its members.
Yes, it's a (now) a floor joist. It was a ceiling joist, but we're refinishing an attic and putting in a bathroom.
The joists are around 22" on center, if I recall correctly. They are a full 2" thick, and 7" wide. The span is around 12' or so. I talked about the joists with a structural engineer, and he didn't seem to have any problem (before the cutout - of course). |
|
#10
|
||||
|
||||
|
It's not acceptable the way it is and needs reinforcement with a product like THIS
Here is a animation Choose the hole reinforcer Photo Gallery "Never underestimate the difficulty of changing false beliefs by facts." Last edited by mlarson; 6/24/08 at 2:13 PM.. |
|
#11
|
||||
|
||||
|
Please Note:
relliott is a non-member guest and is in no way affiliated with InterNACHI or its members.
Marcel....
You ever see this product of Mikes being used? |
|
#12
|
||||
|
||||
|
Nope.
The problem here is renovations being made with attic framing now becoming a floor, where as before was just holding up the ceiling. This is a job for a licensed Architect. The previous post is indicating a bathroom floor framed with 2x7" framing at 22" o.c. for a span of 12'-0". This type of framing is inadequate for the span at 12'. Those members are to small to get the loading required for a floor. 30# live load, 10# dead loading. If the riser from below had been located as such that the branch soil piping would run parallel to the framing, these holes would be unnecessary, but the framing is still inadequate for this attic framing to become a floor. Recommend engineering by a qualified Architect required, for redisign and alterations. Cyr Home and Commercial Property Inspections IAC2 Certified NACHI04070211 http://co.nachi.org/inachiawards Commercial Builder CertainTeed Master Shingle Applicator Shingle Technology Ouellet Associaties Inc. http://www.oaconstruction.com/ |
|
#13
|
||||
|
||||
|
Please Note:
relliott is a non-member guest and is in no way affiliated with InterNACHI or its members.
Marcel , didn't he mean 2x8.
Also besides that issue I have seen them rais ethe toilet on to a platform. This way the pipe can be above the joists. |
|
#14
|
||||
|
||||
|
Hi. Bob,
I believe this is an unsurfaced lumber framing. The joists are around 22" on center, if I recall correctly. They are a full 2" thick, and 7" wide. The span is around 12' or so. I talked about the joists with a structural engineer, and he didn't seem to have any problem (before the cutout - of course). And I am assumming he meant 24" centers. If we are looking at new framing in the pic to be a knee wall, plateform for toilet might open a headroom problem, Like I said before, too much information missing. Recommend design by an Architect. This apprears to be a 1930 built structure by the remnants of knob and tube. So god knows what the framing is like in that place. Marcel Cyr Home and Commercial Property Inspections IAC2 Certified NACHI04070211 http://co.nachi.org/inachiawards Commercial Builder CertainTeed Master Shingle Applicator Shingle Technology Ouellet Associaties Inc. http://www.oaconstruction.com/ |
|
#15
|
||||
|
||||
|
Please Note:
relliott is a non-member guest and is in no way affiliated with InterNACHI or its members.
Oh you caught that porclein knob too.
|
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| Inspector in hot water after approving unit without drain | rcooke | Canadian Inspectors | 6 | 2/20/08 4:59 PM |
| Max load allowed on 2x2 ledger | bking | Structural | 4 | 12/23/07 3:05 PM |
| French drain tied into main drain | rwashington | Plumbing | 6 | 2/17/07 12:04 AM |
| Frost, Ice, & Condensation @ RIM JOIST | Sean M. Jeric | HVAC | 4 | 2/5/07 7:56 PM |