  #1  
Old 6/23/08, 9:35 PM
Nathan W. Swilling Nathan W. Swilling is offline
New User
 
Join Date: Jan 2008
Posts: 49
Please Note: Nathan W. Swilling is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Cutout of joist for toilet drain

Does this look kosher? The joist is about 2" thick and 7" wide. It looks like the cutout is more than 1/3 of the width of the beam. One joist is supported with some extra lumber, but it still doesn't look that great.
Attached Thumbnails
cutout-joist-toilet-drain-img_5144.jpg   cutout-joist-toilet-drain-img_5145.jpg  
Reply With Quote
  #2  
Old 6/23/08, 9:38 PM
Mark Nahrgang's Avatar
Mark Nahrgang Mark Nahrgang is offline
InterNACHI Member
 
Join Date: Apr 2007
Location: Saint Peters, MO
Posts: 3,946
Default Re: Cutout of joist for toilet drain

Structural defects in both pictures. Greater than 1/3 the joist depth, as well as closer than 2 inches to the edge...
Reply With Quote
  #3  
Old 6/23/08, 10:00 PM
relliott's Avatar
relliott relliott is offline
Active Poster
 
Join Date: Aug 2006
Location: HARWOOD HTS, il
Posts: 8,570
Please Note: relliott is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Cutout of joist for toilet drain

also cracked .
Reply With Quote
  #4  
Old 6/24/08, 8:45 AM
Nathan W. Swilling Nathan W. Swilling is offline
New User
 
Join Date: Jan 2008
Posts: 49
Please Note: Nathan W. Swilling is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Cutout of joist for toilet drain

So, what's the remedy? Would sandwiching it in OSB do the trick? How far on both sides?
Reply With Quote
  #5  
Old 6/24/08, 10:43 AM
Michael Roberson's Avatar
Michael Roberson Michael Roberson is offline
InterNACHI Member
 
Join Date: May 2008
Location: Scottville, Mi
Posts: 930
Default Re: Cutout of joist for toilet drain

This is one of those things that Home Inspecters like to comment " refer to a licenced contractor or structural engineer"

Having said that, OSB sandwidch would make it stronger, but would NOT fix the problem, the joists are almost cut in half.
Reply With Quote
  #6  
Old 6/24/08, 11:05 AM
Carla Horne's Avatar
Carla Horne Carla Horne is offline
InterNACHI Member
 
Join Date: Feb 2003
Location: Meredith, NH
Posts: 511
Default Re: Cutout of joist for toilet drain

Hi,
ceiling joists/overlays are mainly outward pressure support. hard to say from a picture but I would say that an upright from the joist up to the rafter would do the trick.
if that were a floor joist there would be a problem.
Carla
Reply With Quote
  #7  
Old 6/24/08, 11:30 AM
relliott's Avatar
relliott relliott is offline
Active Poster
 
Join Date: Aug 2006
Location: HARWOOD HTS, il
Posts: 8,570
Please Note: relliott is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Cutout of joist for toilet drain

Thought it was a floor joist
Reply With Quote
  #8  
Old 6/24/08, 11:47 AM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 12,356
Default Re: Cutout of joist for toilet drain

Bob, sure looks like a floor to me.

I am seeing a new framed wall and some subflooring and two different size pipes.

I don't think we are seeing the whole picture from those two pics.

The title calls it a toilet drain, so must be an attic being finsished as a bathroom, so now the ceiling joist are floor joist.

The span of those might be sized wrong for this new load also.

More information is required.

Marcel




Cyr Home and Commercial Property Inspections

IAC2 Certified
NACHI04070211
http://co.nachi.org/inachiawards


Commercial Builder
CertainTeed
Master Shingle Applicator
Shingle Technology
Ouellet Associaties Inc.
http://www.oaconstruction.com/
Reply With Quote
  #9  
Old 6/24/08, 12:56 PM
Nathan W. Swilling Nathan W. Swilling is offline
New User
 
Join Date: Jan 2008
Posts: 49
Please Note: Nathan W. Swilling is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Cutout of joist for toilet drain

Yes, it's a (now) a floor joist. It was a ceiling joist, but we're refinishing an attic and putting in a bathroom.

The joists are around 22" on center, if I recall correctly. They are a full 2" thick, and 7" wide. The span is around 12' or so. I talked about the joists with a structural engineer, and he didn't seem to have any problem (before the cutout - of course).
Reply With Quote
  #10  
Old 6/24/08, 2:07 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 18,489
Default Re: Cutout of joist for toilet drain

It's not acceptable the way it is and needs reinforcement with a product like THIS

Here is a animation Choose the hole reinforcer

Photo Gallery



"Never underestimate the difficulty of changing false beliefs by facts."
Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI
InspectraPro
or
Minnesota Home Inspector


Last edited by mlarson; 6/24/08 at 2:13 PM..
Reply With Quote
  #11  
Old 6/24/08, 3:21 PM
relliott's Avatar
relliott relliott is offline
Active Poster
 
Join Date: Aug 2006
Location: HARWOOD HTS, il
Posts: 8,570
Please Note: relliott is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Cutout of joist for toilet drain

Marcel....
You ever see this product of Mikes being used?
Reply With Quote
  #12  
Old 6/24/08, 3:37 PM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 12,356
Default Re: Cutout of joist for toilet drain

Nope.

The problem here is renovations being made with attic framing now becoming a floor, where as before was just holding up the ceiling. This is a job for a licensed Architect.

The previous post is indicating a bathroom floor framed with 2x7" framing at 22" o.c. for a span of 12'-0".

This type of framing is inadequate for the span at 12'.

Those members are to small to get the loading required for a floor. 30# live load, 10# dead loading.

If the riser from below had been located as such that the branch soil piping would run parallel to the framing, these holes would be unnecessary, but the framing is still inadequate for this attic framing to become a floor.

Recommend engineering by a qualified Architect required, for redisign and alterations.





Cyr Home and Commercial Property Inspections

IAC2 Certified
NACHI04070211
http://co.nachi.org/inachiawards


Commercial Builder
CertainTeed
Master Shingle Applicator
Shingle Technology
Ouellet Associaties Inc.
http://www.oaconstruction.com/
Reply With Quote
  #13  
Old 6/24/08, 3:40 PM
relliott's Avatar
relliott relliott is offline
Active Poster
 
Join Date: Aug 2006
Location: HARWOOD HTS, il
Posts: 8,570
Please Note: relliott is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Cutout of joist for toilet drain

Marcel , didn't he mean 2x8.

Also besides that issue I have seen them rais ethe toilet on to a platform.

This way the pipe can be above the joists.
Reply With Quote
  #14  
Old 6/24/08, 4:10 PM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 12,356
Default Re: Cutout of joist for toilet drain

Hi. Bob,

I believe this is an unsurfaced lumber framing.

The joists are around 22" on center, if I recall correctly. They are a full 2" thick, and 7" wide. The span is around 12' or so. I talked about the joists with a structural engineer, and he didn't seem to have any problem (before the cutout - of course).

And I am assumming he meant 24" centers.

If we are looking at new framing in the pic to be a knee wall, plateform for toilet might open a headroom problem,

Like I said before, too much information missing.

Recommend design by an Architect.

This apprears to be a 1930 built structure by the remnants of knob and tube. So god knows what the framing is like in that place.

Marcel




Cyr Home and Commercial Property Inspections

IAC2 Certified
NACHI04070211
http://co.nachi.org/inachiawards


Commercial Builder
CertainTeed
Master Shingle Applicator
Shingle Technology
Ouellet Associaties Inc.
http://www.oaconstruction.com/
Reply With Quote
  #15  
Old 6/24/08, 5:25 PM
relliott's Avatar
relliott relliott is offline
Active Poster
 
Join Date: Aug 2006
Location: HARWOOD HTS, il
Posts: 8,570
Please Note: relliott is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Cutout of joist for toilet drain

Oh you caught that porclein knob too.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Inspector in hot water after approving unit without drain rcooke Canadian Inspectors 6 2/20/08 4:59 PM
Max load allowed on 2x2 ledger bking Structural 4 12/23/07 3:05 PM
French drain tied into main drain rwashington Plumbing 6 2/17/07 12:04 AM
Frost, Ice, & Condensation @ RIM JOIST Sean M. Jeric HVAC 4 2/5/07 7:56 PM


All times are GMT -4. The time now is 5:35 AM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts