  #1  
Old 6/30/10, 3:12 PM
Jeff Manders Jeff Manders is offline
InterNACHI Member
 
Join Date: Oct 2008
Posts: 11
Default Deck joist connected directly to house band?

I was inspecting this house this morning and the deck joists appear to be attached directly to the rim joist (house band) via deck joist hangers. There is a ledger board attached to rim joist with ledger bolts where the deck stairs are, but for only 36 inches (the entire width of the deck is roughly 15 ft.).

I haven't seen a deck installed like this, but I'm assuming there might be a support issue as well as water intrusion issues. Please advise. Thanks guys.
Attached Thumbnails
deck-joist-connected-directly-house-band-img_0217.jpg   deck-joist-connected-directly-house-band-img_0222.jpg  
Reply With Quote
Need a home inspection in Kansas? Check out InterNACHI's listing of Kansas certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 6/30/10, 3:23 PM
David A. Andersen's Avatar
David A. Andersen David A. Andersen is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Woodlawn, TN
Posts: 5,927
Default Re: Deck joist connected directly to house band?

I don't see that.

The rim joist of the deck is attached to the house joist, but it is not to sole joist (i beleive for this vantage point).

It even looks like they flashed it (hard to find around here)!



"Insanity: doing the same thing over and over again and expecting a different results." Albert Einstein

David A. Andersen & Associates
Clarksville - Nashville Home Inspector Lic#40
http://www.midtninspections.com
ITC Level III Thermographer Cert#1958
Building Science Thermographer Cert#33784
http://www.thermalimagingscan.com
HVAC Certification EPA Cert#2046620
BPI# 5015804
Link to my Website at: http://www.midtninspections.com/link-submission
Reply With Quote
  #3  
Old 6/30/10, 5:14 PM
Buck Hartley, CMI's Avatar
Buck Hartley, CMI Buck Hartley, CMI is offline
InterNACHI Member
 
Join Date: Nov 2005
Location: Shawnee, KS
Posts: 1,567
Default Re: Deck joist connected directly to house band?

It is flashed correctly.



Mid America Property Inspections, Inc.
Shawnee, KS 66217
www.mapii.com
NACHI # 05110992
KHIRB # 0110-0008
KS-Radon Cert.# KS-MS-0035
KS-Termite Cert. # 18933
M0-Termite Cert. # N 5033

Reply With Quote
  #4  
Old 6/30/10, 7:13 PM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 19,798
Default Re: Deck joist connected directly to house band?

Looks alright to me.
Reply With Quote
  #5  
Old 6/30/10, 7:47 PM
Nick Gromicko's Avatar
Nick Gromicko Nick Gromicko is offline
InterNACHI Member
 
Join Date: Aug 2002
Location: Valley Forge, PA
Posts: 30,614
Default Re: Deck joist connected directly to house band?

http://www.nachi.org/deck-inspections.htm



Nick Gromicko, Certified Master Inspector

Find a Home Inspector
"Just as iron sharpens iron, one man sharpens another." Proverbs 27:17
Reply With Quote
  #6  
Old 7/1/10, 2:14 PM
Jeffery L. Haynes Jeffery L. Haynes is online now
InterNACHI Member
 
Join Date: Aug 2008
Location: Concord, NC
Posts: 3,494
Default Re: Deck joist connected directly to house band?

Look closer guys............

looks like they used screws on a couple of those hangers.......left hanger, left interior.....


Can you blow that up any more....

Jeff
Reply With Quote
  #7  
Old 7/1/10, 3:30 PM
Jeffrey R. Jonas's Avatar
Jeffrey R. Jonas Jeffrey R. Jonas is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Owatonna, MN
Posts: 12,195
Default Re: Deck joist connected directly to house band?

And if you really want to get nit-picky, the lag bolts should be staggered...
Reply With Quote
  #8  
Old 7/1/10, 3:47 PM
Jeffery L. Haynes Jeffery L. Haynes is online now
InterNACHI Member
 
Join Date: Aug 2008
Location: Concord, NC
Posts: 3,494
Default Re: Deck joist connected directly to house band?

Not being nit picky Jeff........if in fact they are screws then you should know that screws are not an acceptable method in attaching joist to hangers.
Reply With Quote
  #9  
Old 7/1/10, 4:45 PM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 19,798
Default Re: Deck joist connected directly to house band?

If nails there is one missing also, but that was not part of the question.
And the lags are wrong and what is that bolt for?
Reply With Quote
  #10  
Old 7/1/10, 5:52 PM
Jeffrey R. Jonas's Avatar
Jeffrey R. Jonas Jeffrey R. Jonas is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Owatonna, MN
Posts: 12,195
Default Re: Deck joist connected directly to house band?

Quote:
Originally Posted by jhaynes View Post
Not being nit picky Jeff........if in fact they are screws then you should know that screws are not an acceptable method in attaching joist to hangers.
Didn't mean to infer that you are being nit-picky with the (possible) screws. I agree with you. My post was stand-alone to the lag bolts. I call out non-staggered lags. Many inspectors argue that it is not necessary to stagger, (as long as lags are used, good enough), and being nit-picky.
Reply With Quote
  #11  
Old 7/1/10, 7:01 PM
gfitzgerald's Avatar
gfitzgerald gfitzgerald is offline
Active Poster
 
Join Date: Jun 2009
Location: Sherman Oaks Ca.
Posts: 335
Please Note: gfitzgerald is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Deck joist connected directly to house band?

I just finished a Pergola in the city of Burbank and if you are familiar with So. Cal you know they are very strict. I used two 1/2 x 5" lags 32" O C and did not stager them. The plan was engineered. I try to cover all my joist hangers and did use joist nails on the one even tho it was not called out on the plan. What to you guys have against screws
Attached Thumbnails
deck-joist-connected-directly-house-band-imgp0843.jpg  
Reply With Quote
  #12  
Old 7/1/10, 7:05 PM
gfitzgerald's Avatar
gfitzgerald gfitzgerald is offline
Active Poster
 
Join Date: Jun 2009
Location: Sherman Oaks Ca.
Posts: 335
Please Note: gfitzgerald is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Deck joist connected directly to house band?

For you electrical guys under the artificial turf is the famous grid bonding system
Reply With Quote
  #13  
Old 7/1/10, 9:02 PM
Jeffrey R. Jonas's Avatar
Jeffrey R. Jonas Jeffrey R. Jonas is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Owatonna, MN
Posts: 12,195
Default Re: Deck joist connected directly to house band?

Quote:
Originally Posted by gfitzgerald View Post
I just finished a Pergola in the city of Burbank and if you are familiar with So. Cal you know they are very strict. I used two 1/2 x 5" lags 32" O C and did not stager them. The plan was engineered. I try to cover all my joist hangers and did use joist nails on the one even tho it was not called out on the plan. What to you guys have against screws
Poor shear strength. Screws are not approved by the manufacturer in joist hangars. There is a specialty screw that is okay instead of lag bolts, but they still should be staggered. They are pretty obvious when you see them. I'm sure Marcel or someone else will jump in with the name of the screws, and more info. As far as your project and it being engineered, first question is by whom? Doesn't really matter, as they technically take responsibility if it fails. That is assuming it actually was, and have the papers to prove it. None-the-less, I call out what I deem to be a safety issue. Everyone else can hash out the details. My job is done.
Reply With Quote
Need a home inspection in Kansas? Check out InterNACHI's listing of Kansas certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #14  
Old 7/2/10, 6:01 AM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 19,798
Default Re: Deck joist connected directly to house band?

The only equivalent to lags for ledger boards.

http://grkfasteners.com/en/RSS_1_2_information.htm

View our RSS™ Promotional Video
Reply With Quote
  #15  
Old 7/2/10, 9:41 AM
Jeffrey R. Jonas's Avatar
Jeffrey R. Jonas Jeffrey R. Jonas is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Owatonna, MN
Posts: 12,195
Default Re: Deck joist connected directly to house band?

Quote:
Originally Posted by mcyr View Post
The only equivalent to lags for ledger boards.

http://grkfasteners.com/en/RSS_1_2_information.htm

View our RSS™ Promotional Video
Thanks Marcel. I knew you would come through.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Where do I put the Aquarium? mcyr Structural Inspections 3 11/6/07 3:05 PM
Family's house is infested with mold rspriggs Ancillary Inspection Services & Additional Topics 6 1/28/06 2:05 AM


All times are GMT -4. The time now is 2:55 PM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts