Default Deck Repairs Would you accept?

The deck failed inspection because of the attachment of the girder to the ledger board. orginally it was only nailed to a 2x6 that was nailed to the ledger board above. I suspect at sometime this deck was rebuilt and lowered. The homeowner/contractor repaired the attachement using a simpsons strong time and bolts as shown in the first picture. This failed the reinspection, The second picture shows the follow up repair adding a post bolted to the girder with a deck block as the footer. This passed inspection. I have to question this as the span between posts is 12' and the joists are 2x8. It seems that the deck block does not have a large enough foot print and the span of the joists is questionable. Thoughts on this?
Attached Thumbnails
deck-repairs-would-you-accept-deck-2.jpg   deck-repairs-would-you-accept-deck-3.jpg   deck-repairs-would-you-accept-deck-1.jpg   deck-repairs-would-you-accept-deck-4.jpg  
Reply With Quote
Need a home inspection in South Dakota? Check out InterNACHI's listing of South Dakota certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 7/17/11, 10:59 AM
bdoles2's Avatar
bdoles2 bdoles2 is offline
Active Poster
 
Join Date: Aug 2006
Location: Atlanta, GA
Posts: 3,071
Please Note: bdoles2 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Deck Repairs Would you accept?

IRC Spans:

Based on IRC T502.3.1(2) and 502.8.1

2X8 on 12" centers 14'2" span
2X8 on 16" centers 12'7" span
2X10 on 12" centers 17"9" span
2X10 on 16" centers 15'5" span
- 40lb. live load

Obviously the posts on the post blocks are an improvement. Better than nothing. I'd be more concerned with the fact the joists aren't properly tied to the beams, they are beginning to "tilt". Just a crappy deck job all around if you ask me.
Reply With Quote
  #3  
Old 7/17/11, 11:02 AM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 8,848
Default Re: Deck Repairs Would you accept?

Quote:
Originally Posted by kbrittain View Post
The deck failed inspection because of the attachment of the girder to the ledger board. orginally it was only nailed to a 2x6 that was nailed to the ledger board above. I suspect at sometime this deck was rebuilt and lowered. The homeowner/contractor repaired the attachement using a simpsons strong time and bolts as shown in the first picture. This failed the reinspection, The second picture shows the follow up repair adding a post bolted to the girder with a deck block as the footer. This passed inspection. I have to question this as the span between posts is 12' and the joists are 2x8. It seems that the deck block does not have a large enough foot print and the span of the joists is questionable. Thoughts on this?

This may be helpful:
http://www.awc.org/Publications/DCA/DCA6/DCA6-09.pdf

Who is making the "pass/fail" pronouncements?



InterNachi Awards Portal: http://co.nachi.org/inachiawards/

____________________________________________
"An Education, not just an Inspection"

Larry Kage, CMI
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector serving the Traverse City, Michigan area and beyond.
Reply With Quote
  #4  
Old 7/17/11, 11:09 AM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 19,798
Default Re: Deck Repairs Would you accept?

My exact question Larry, I would still write this deck construction up hard the way it is.
Who's been failing or passing this deck?
Reply With Quote
  #5  
Old 7/17/11, 11:10 AM
Roy D. Cooke, Sr's Avatar
Roy D. Cooke, Sr Roy D. Cooke, Sr is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Brighton, ON
Posts: 14,621
Default Re: Deck Repairs Would you accept?

When I do an inspection ,I write my report and it would include the deck .
If it is wrong I write the deck is incorrect and a hazard needs immediate repair by a Qualified person .
End of story I do not go back to see it the repair person now has the concern with the deck on his shoulders .

... Roy



Need help on inspection call my cell 613-827-2011

I like email Roycooke@hotmail.com

Never wrestle with a pig (however titled) as you just get dirty and the pig has all the fun.



Reply With Quote
  #6  
Old 7/17/11, 2:11 PM
Kenneth R. Brittain Kenneth R. Brittain is offline
InterNACHI Member
 
Join Date: Jul 2011
Location: Charlotte NC
Posts: 224
Default Re: Deck Repairs Would you accept?

It was identified by the buyers home inspector during the first inspection, the buyer called for a reinspection after each repair and it was accepted after the final repair. I just happened to be there when it was reinspected as I know the buyers. The inspector told the buyers to ask the seller if they pulled a permit for the deck construction he guess it was not done under a permit. The deal is done and they have moved in but this has just bugged me.

If you were putting in a poured in place footing it would be a lot larger area then the deck block covers. Reading the deck block instruction they call for close spacing of these blocks to acheive the required bearing area.
Reply With Quote
  #7  
Old 7/17/11, 7:34 PM
Sean Fogarty's Avatar
Sean Fogarty Sean Fogarty is offline
InterNACHI Member
 
Join Date: Sep 2009
Location: Somewhere in Knoxville TN flipping breakers
Posts: 2,267
Default Re: Deck Repairs Would you accept?

I get to see a ton of crappy decks, and if the posts at the ends were set on or in concrete versus the suport blocks then I wouldnt have any issue with that one. If the end post was properly set then the girder beam wouldn't need the attachment to the ledger IMO.. I doubt it would go anywhere now and I personally wouldn't be to critcal on the blocks. That deck is deluxe compared to most I see.

Lowes has handouts for those stupid blocks. They are not designed to suppor anything above 18 inches and you have to place them very close togeather. Most of the time they are never used for their designed purpose.




Infraspection Institute Level 1 Certified Infrared Thermographer

Fogarty Inspection Services Group of Knoxville TN

Home inspections, Commercial Inspections, Thermal Imaging, Mold, Enviromental Testing and Radon Testing for Knoxville TN, Oak Ridge TN, Maryville, Clinton, Farragut, Lenoir City, Pigeon Forge, Sevierville and all the surrounding areas.

865-256-5397

www.homeinspectorknoxville.com

www.moldandradon.com

www.thermal-inspection.net

www.commercial-building-inspector.net
Reply With Quote
  #8  
Old 7/17/11, 10:45 PM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 8,343
Send a message via Yahoo to jfunderburk
Default Re: Deck Repairs Would you accept?

The girder should not 'sandwich' the post. You'll rarely see a deck built perfectly. At least they don't have far to fall.



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #9  
Old 7/19/11, 5:10 PM
Kenneth R. Brittain Kenneth R. Brittain is offline
InterNACHI Member
 
Join Date: Jul 2011
Location: Charlotte NC
Posts: 224
Default Re: Deck Repairs Would you accept?

Insterestingly Charlotte/Mecklenburg NC allows bolting to the post with 2 5/8" galv. bolts, nuts and washers. See figure 5 of their deck pamphlet

http://charmeck.org/mecklenburg/coun...s/deckbroc.pdf

even they are not consistant (see fig 5 in each pamphlet)

http://www.pahi.org/sitebuilderconte...meckcounty.pdf

Last edited by kbrittain; 7/20/11 at 7:57 PM.. Reason: added link to pamphlet
Reply With Quote
  #10  
Old 7/20/11, 9:33 AM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 8,343
Send a message via Yahoo to jfunderburk
Default Re: Deck Repairs Would you accept?

Quote:
Originally Posted by kbrittain View Post
Insterestingly Charlotte/Mecklenburg NC allows bolting to the post with 2 5/8" galv. bolts, nuts and washers. See figure 5 of their deck pamphlet
Why is that "interesting"?



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #11  
Old 7/20/11, 5:36 PM
Robert J. OConnor's Avatar
Robert J. OConnor Robert J. OConnor is offline
InterNACHI Member
 
Join Date: Jul 2003
Location: Long Island, NY
Posts: 1,288
Default Re: Deck Repairs Would you accept?

Quote:
Originally Posted by jfunderburk View Post
Why is that "interesting"?
Because of your post that stated ... "The girder should not 'sandwich' the post".

Some ares do permit the deck beams to be bolted to the face of posts. But it is a weaker connection.



Robert O'Connor, PE
Consulting Engineer & Inspector
LIU CW Post Adjunct Professor
NACHI Education Committee
www.reporthost.com/-rjo

I am absolutely amazed sometimes by how much thought goes into doing things wrong ...
Reply With Quote
  #12  
Old 7/20/11, 5:42 PM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 19,798
Default Re: Deck Repairs Would you accept?

And to know for sure if accepted at all, we would need to see the ammendment to the IRC they have adopted for that jurisdiction, right?
Reply With Quote
  #13  
Old 7/20/11, 7:45 PM
Kenneth R. Brittain Kenneth R. Brittain is offline
InterNACHI Member
 
Join Date: Jul 2011
Location: Charlotte NC
Posts: 224
Default Re: Deck Repairs Would you accept?

Its interesting because most of the information I see calls for the girders to be supported by the post either with a notch or on top with a bracket, but there always seems to be an exception.
Reply With Quote
Need a home inspection in South Dakota? Check out InterNACHI's listing of South Dakota certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #14  
Old 7/20/11, 8:01 PM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 19,798
Default Re: Deck Repairs Would you accept?

And I have not yet seen the exception to the rule in a factual manner yet.
http://www.nachi.org/gallery/exterio...connection.jpg
http://www.nachi.org/gallery/exterio...connection.jpg
http://www.nachi.org/gallery/exterio...st-to-beam.jpg

Reply With Quote
  #15  
Old 7/20/11, 11:41 PM
Robert J. OConnor's Avatar
Robert J. OConnor Robert J. OConnor is offline
InterNACHI Member
 
Join Date: Jul 2003
Location: Long Island, NY
Posts: 1,288
Default Re: Deck Repairs Would you accept?

In my opinion the flush thru bolted connection is more stable, but typically weaker, than a top bearing or notched post attachment. The best connection is a notched post and thru-bolted connection. But many times too much lumber needs to be notched out, or the horizontal cut goes a little too deep, and the connection becomes unstable over time.

The graphic you linked has one small 3/8" or 1/2" thru bolt which is usually not adequate. If designed correctly (min 2 - 5/8" A307 HDG thru bolts at more than adequate edge distances, with split girders for double bolt shear) it has more than sufficient capacity for most decks. For higher capacity connections split rings can be used. Have designed many decks that way, with long service lives.

The AFPA Deck Guide, and many other local guides, do not recommend it or indicate it's prohibited because it is often designed or installed wrong. But I am not aware of any specific restrictions in the IRC (other than for a prescriptive installation) that specifically prohibit a thru-bolted flush girder-beam connection.

JMO & 2-Nickels ...



Robert O'Connor, PE
Consulting Engineer & Inspector
LIU CW Post Adjunct Professor
NACHI Education Committee
www.reporthost.com/-rjo

I am absolutely amazed sometimes by how much thought goes into doing things wrong ...

Last edited by roconnor; 7/21/11 at 8:08 AM..
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Home Inspector law suit rcooke Canadian Inspectors 0 2/18/10 11:48 AM
Using the Prescriptive Residential Deck Construction Guide mcyr Exterior Inspections 0 7/21/09 7:10 PM
Check The Deck wdevries Canadian Inspectors 1 7/9/08 2:00 PM
Max load allowed on 2x2 ledger bking Structural Inspections 4 12/23/07 2:05 PM


All times are GMT -4. The time now is 2:55 PM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts