#1
|
|||
|
|||
|
The deck failed inspection because of the attachment of the girder to the ledger board. orginally it was only nailed to a 2x6 that was nailed to the ledger board above. I suspect at sometime this deck was rebuilt and lowered. The homeowner/contractor repaired the attachement using a simpsons strong time and bolts as shown in the first picture. This failed the reinspection, The second picture shows the follow up repair adding a post bolted to the girder with a deck block as the footer. This passed inspection. I have to question this as the span between posts is 12' and the joists are 2x8. It seems that the deck block does not have a large enough foot print and the span of the joists is questionable. Thoughts on this?
|
| Need a home inspection in South Dakota? Check out InterNACHI's listing of South Dakota certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine. |
|
#2
|
||||
|
||||
|
Please Note:
bdoles2 is a non-member guest and is in no way affiliated with InterNACHI or its members.
IRC Spans:
Based on IRC T502.3.1(2) and 502.8.1 2X8 on 12" centers 14'2" span 2X8 on 16" centers 12'7" span 2X10 on 12" centers 17"9" span 2X10 on 16" centers 15'5" span - 40lb. live load Obviously the posts on the post blocks are an improvement. Better than nothing. I'd be more concerned with the fact the joists aren't properly tied to the beams, they are beginning to "tilt". Just a crappy deck job all around if you ask me. |
|
#3
|
|||
|
|||
|
Quote:
This may be helpful: http://www.awc.org/Publications/DCA/DCA6/DCA6-09.pdf Who is making the "pass/fail" pronouncements? InterNachi Awards Portal: http://co.nachi.org/inachiawards/ ____________________________________________ "An Education, not just an Inspection" Larry Kage, CMI Lake Ann (Traverse City), Michigan 49650 231 929 3525 Professional Inspector serving the Traverse City, Michigan area and beyond.
|
|
#4
|
||||
|
||||
|
My exact question Larry, I would still write this deck construction up hard the way it is.
Who's been failing or passing this deck? LEED Green Associates InachiAwardsPortal: Inachi US Member of the Year Award 2009 |
|
#5
|
||||
|
||||
|
When I do an inspection ,I write my report and it would include the deck .
If it is wrong I write the deck is incorrect and a hazard needs immediate repair by a Qualified person . End of story I do not go back to see it the repair person now has the concern with the deck on his shoulders . ... Roy Need help on inspection call my cell 613-827-2011 I like email Roycooke@hotmail.com Never wrestle with a pig (however titled) as you just get dirty and the pig has all the fun. |
|
#6
|
|||
|
|||
|
It was identified by the buyers home inspector during the first inspection, the buyer called for a reinspection after each repair and it was accepted after the final repair. I just happened to be there when it was reinspected as I know the buyers. The inspector told the buyers to ask the seller if they pulled a permit for the deck construction he guess it was not done under a permit. The deal is done and they have moved in but this has just bugged me.
If you were putting in a poured in place footing it would be a lot larger area then the deck block covers. Reading the deck block instruction they call for close spacing of these blocks to acheive the required bearing area. |
|
#7
|
||||
|
||||
|
I get to see a ton of crappy decks, and if the posts at the ends were set on or in concrete versus the suport blocks then I wouldnt have any issue with that one. If the end post was properly set then the girder beam wouldn't need the attachment to the ledger IMO.. I doubt it would go anywhere now and I personally wouldn't be to critcal on the blocks. That deck is deluxe compared to most I see.
Lowes has handouts for those stupid blocks. They are not designed to suppor anything above 18 inches and you have to place them very close togeather. Most of the time they are never used for their designed purpose. Infraspection Institute Level 1 Certified Infrared Thermographer Fogarty Inspection Services Group of Knoxville TN Home inspections, Commercial Inspections, Thermal Imaging, Mold, Enviromental Testing and Radon Testing for Knoxville TN, Oak Ridge TN, Maryville, Clinton, Farragut, Lenoir City, Pigeon Forge, Sevierville and all the surrounding areas. 865-256-5397 www.homeinspectorknoxville.com www.moldandradon.com www.thermal-inspection.net www.commercial-building-inspector.net |
|
#8
|
||||
|
||||
|
The girder should not 'sandwich' the post. You'll rarely see a deck built perfectly. At least they don't have far to fall.
“The things that will destroy America are peace at any price, prosperity at any cost, safety first instead of duty first, the love of soft living, and the get-rich-quick theory of life.” Theodore Roosevelt Joe Funderburk, CMI Alpha & Omega Home Inspections, LLC Inspecting Upstate SC & Charlotte Metro, NC NACHI ID: NACHI05120170 www.aohomeinspection.com |
|
#9
|
|||
|
|||
|
Insterestingly Charlotte/Mecklenburg NC allows bolting to the post with 2 5/8" galv. bolts, nuts and washers. See figure 5 of their deck pamphlet
http://charmeck.org/mecklenburg/coun...s/deckbroc.pdf even they are not consistant (see fig 5 in each pamphlet) http://www.pahi.org/sitebuilderconte...meckcounty.pdf Last edited by kbrittain; 7/20/11 at 7:57 PM.. Reason: added link to pamphlet |
|
#10
|
||||
|
||||
|
Why is that "interesting"?
“The things that will destroy America are peace at any price, prosperity at any cost, safety first instead of duty first, the love of soft living, and the get-rich-quick theory of life.” Theodore Roosevelt Joe Funderburk, CMI Alpha & Omega Home Inspections, LLC Inspecting Upstate SC & Charlotte Metro, NC NACHI ID: NACHI05120170 www.aohomeinspection.com |
|
#11
|
||||
|
||||
|
Because of your post that stated ... "The girder should not 'sandwich' the post".
Some ares do permit the deck beams to be bolted to the face of posts. But it is a weaker connection. Robert O'Connor, PE Consulting Engineer & Inspector LIU CW Post Adjunct Professor NACHI Education Committee www.reporthost.com/-rjo I am absolutely amazed sometimes by how much thought goes into doing things wrong ... |
|
#12
|
||||
|
||||
|
And to know for sure if accepted at all, we would need to see the ammendment to the IRC they have adopted for that jurisdiction, right?
LEED Green Associates InachiAwardsPortal: Inachi US Member of the Year Award 2009 |
|
#13
|
|||
|
|||
|
Its interesting because most of the information I see calls for the girders to be supported by the post either with a notch or on top with a bracket, but there always seems to be an exception.
|
| Need a home inspection in South Dakota? Check out InterNACHI's listing of South Dakota certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine. |
|
#14
|
||||
|
||||
|
And I have not yet seen the exception to the rule in a factual manner yet.
http://www.nachi.org/gallery/exterio...connection.jpg http://www.nachi.org/gallery/exterio...connection.jpg http://www.nachi.org/gallery/exterio...st-to-beam.jpg LEED Green Associates InachiAwardsPortal: Inachi US Member of the Year Award 2009 |
|
#15
|
||||
|
||||
|
In my opinion the flush thru bolted connection is more stable, but typically weaker, than a top bearing or notched post attachment. The best connection is a notched post and thru-bolted connection. But many times too much lumber needs to be notched out, or the horizontal cut goes a little too deep, and the connection becomes unstable over time.
The graphic you linked has one small 3/8" or 1/2" thru bolt which is usually not adequate. If designed correctly (min 2 - 5/8" A307 HDG thru bolts at more than adequate edge distances, with split girders for double bolt shear) it has more than sufficient capacity for most decks. For higher capacity connections split rings can be used. Have designed many decks that way, with long service lives. The AFPA Deck Guide, and many other local guides, do not recommend it or indicate it's prohibited because it is often designed or installed wrong. But I am not aware of any specific restrictions in the IRC (other than for a prescriptive installation) that specifically prohibit a thru-bolted flush girder-beam connection. JMO & 2-Nickels ... Robert O'Connor, PE Consulting Engineer & Inspector LIU CW Post Adjunct Professor NACHI Education Committee www.reporthost.com/-rjo I am absolutely amazed sometimes by how much thought goes into doing things wrong ... Last edited by roconnor; 7/21/11 at 8:08 AM.. |
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| Home Inspector law suit | rcooke | Canadian Inspectors | 0 | 2/18/10 11:48 AM |
| Using the Prescriptive Residential Deck Construction Guide | mcyr | Exterior Inspections | 0 | 7/21/09 7:10 PM |
| Check The Deck | wdevries | Canadian Inspectors | 1 | 7/9/08 2:00 PM |
| Max load allowed on 2x2 ledger | bking | Structural Inspections | 4 | 12/23/07 2:05 PM |