Default Re: Did you post this pricture of a deteriorating lintel?

Quote:
Originally Posted by smcintire View Post
This was a building that I inspected several years ago. The steel support beams were heavily corroded and had expanded to several times their original size, which caused upward pressure on the brick work. I am sure water intrusion freezing and thawing did not help either. I found one apartment unit that the walls were torn out, and was able to see the beams from the back side. If I can find those pictures I will post them. Thanks for the memories
Cool I would love to see them as we all would.
Reply With Quote
Need a home inspection in Maine? Check out InterNACHI's listing of Maine certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #32  
Old 10/12/10, 2:39 PM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is offline
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,917
Default Re: Did you post this pricture of a deteriorating lintel?

These are the pictures from yesterdays FEEMA inspection.
I was shocked at the displacement all over this building complex from lack of flashing ,downspout placement,ac units not sealed and poor roofing.
It shows how problems develop over time from more than one issue.
looking at that casement you can see why I figured the other one would cause problems also from the original post.
This is a 2 story duplex building.
[ATTACH][ATTACH][ATTACH]did-you-post-pricture-deteriorating-lintel-4808-casement-1024x768-.jpg[/ATTACH][/ATTACH][/ATTACH]
Attached Thumbnails
did-you-post-pricture-deteriorating-lintel-4808-1-1024x768-.jpg   did-you-post-pricture-deteriorating-lintel-4808-ac-sleeve-1024x768-.jpg   did-you-post-pricture-deteriorating-lintel-dsc02463-1024x768-.jpg  
Reply With Quote
  #33  
Old 10/12/10, 6:00 PM
ROBERT V. YOUNG's Avatar
ROBERT V. YOUNG ROBERT V. YOUNG is offline
InterNACHI Member
 
Join Date: Mar 2010
Location: Montreal.
Posts: 5,050
Default Re: Did you post this pricture of a deteriorating lintel?

Quote:
Originally Posted by belliott View Post
These are the pictures from yesterdays FEEMA inspection.
I was shocked at the displacement all over this building complex from lack of flashing ,downspout placement,ac units not sealed and poor roofing.
It shows how problems develop over time from more than one issue.
looking at that casement you can see why I figured the other one would cause problems also from the original post.
This is a 2 story duplex building.
[ATTACH][ATTACH][ATTACH]Attachment 39509[/ATTACH][/ATTACH][/ATTACH]
What is FEEMA BOB?
I am in Montreal Quebec and nor familiar with that organization.
Are they out to help flood victims and hurricane disaster families.
As a first response to shelter and food.
Yes that residential building was built bad from what I see and maybe underlying ground issues aiding in the movement.
Clay, lack of drainage, pyrite.



montrealbuildinginspectionservice.com
montreal-home-inspection-services.com
home-inspections-montreal.com
homeinspectionsservicesmontreal.com
ROBERT YOUNG'S MONTREAL HOME INSPECTION SERVICE INC.
Certified Inspecteur Professionnel Certifié en Bâtiment membre de InterNACHI ACHI , Chapters - OntarioAchi et du M.I.C.Q (CPI) - (CHI)
OFFICE (514) 489-1887 MOBILE (514) 441-3732 TOLL FREE 1- 855-819-1816
Reply With Quote
  #34  
Old 10/12/10, 6:25 PM
ROBERT V. YOUNG's Avatar
ROBERT V. YOUNG ROBERT V. YOUNG is offline
InterNACHI Member
 
Join Date: Mar 2010
Location: Montreal.
Posts: 5,050
Default Re: Did you post this pricture of a deteriorating lintel?

Someone please explain to me why my post are coming back to me over and over again.
I will post my problem on the message board.



montrealbuildinginspectionservice.com
montreal-home-inspection-services.com
home-inspections-montreal.com
homeinspectionsservicesmontreal.com
ROBERT YOUNG'S MONTREAL HOME INSPECTION SERVICE INC.
Certified Inspecteur Professionnel Certifié en Bâtiment membre de InterNACHI ACHI , Chapters - OntarioAchi et du M.I.C.Q (CPI) - (CHI)
OFFICE (514) 489-1887 MOBILE (514) 441-3732 TOLL FREE 1- 855-819-1816
Reply With Quote
  #35  
Old 10/12/10, 7:28 PM
ROBERT V. YOUNG's Avatar
ROBERT V. YOUNG ROBERT V. YOUNG is offline
InterNACHI Member
 
Join Date: Mar 2010
Location: Montreal.
Posts: 5,050
Default Re: Did you post this pricture of a deteriorating lintel?

Quote:
Originally Posted by mthomas2 View Post
OK, found the original post:

http://www.nachi.org/bbsystem/viewtopic.php?t=16410

Given that there is extensive oxide jacking at the lintels above windows, and taking a close look at the openings below both cracking sills, it still seems to me that it's much more likely we are looking at oxide jacking at rusting lintels above closed-in AC openings than freeze/thaw jacking due to water intrusion at the windows:









OK I am going to come in and hopefully explain myself with out putting my foot in-my mouth.
The information I am giving you was passed to me through learning by piratical not theory.
> Observation and explanation from foreman and lead Masons as I learned all my life.
>ON THE JOB TRAINING.
>I have seen similar problems and asked why.
!> look at parapet wall and roof's copping.
I surmise that weather interned the wall through copping and flashing and roof flashing mostly and caused lateral pressures on parapet as frost built up.
There was also a lot going on for as you mentioned the lentils swelled applying uplift and movement from expansion or contraction of the brick field all lead to what problems you are looking at.
I am just observing the photo for what I think is an answer and please there are others that have more to contribute besides myself.
I do not pin point 1 particular weak link in the chain so to speak but several factors combined to allow this much damage to take place.
I will state that proper maintenance would have controlled the erosion.
A manageable yearly or biyearly or even every 4years to inspect and repair the problems.
It would control large events such as this from happening and aid the building exterior to stop it (the cracking, shifting, uplift, movement dead in its tracks or at the very least slow down the erosion..



montrealbuildinginspectionservice.com
montreal-home-inspection-services.com
home-inspections-montreal.com
homeinspectionsservicesmontreal.com
ROBERT YOUNG'S MONTREAL HOME INSPECTION SERVICE INC.
Certified Inspecteur Professionnel Certifié en Bâtiment membre de InterNACHI ACHI , Chapters - OntarioAchi et du M.I.C.Q (CPI) - (CHI)
OFFICE (514) 489-1887 MOBILE (514) 441-3732 TOLL FREE 1- 855-819-1816
Reply With Quote
  #36  
Old 10/12/10, 7:56 PM
ROBERT V. YOUNG's Avatar
ROBERT V. YOUNG ROBERT V. YOUNG is offline
InterNACHI Member
 
Join Date: Mar 2010
Location: Montreal.
Posts: 5,050
Default Re: Did you post this pricture of a deteriorating lintel?

Mr.Thomas.
I forgot to mention ,windows the weakest link in the chain on brick veneer walls.
After copping .FOR ME.
I will post last years example of an estimate I preformed.
Look at all,all the windows in the building.
Look for any and all openings.
Does not matter how small the opening and pay attention to the ''upper part'' of the frame please and go out side with good binauculars and look at all lentals for any breakage or missing masonary were the lintil sits on the brick 4 inches or maybe more.
Just an idea.
If you do not get back to me its OK but please post your findings for all..
>caulk that has shrank, caulk that has cracked etc. look at windows with a fine tooth comb so to speak.
The weather enters the wall cavity through openings in any way it can enter.
In the winter the inside being warm out side being cold the weather (air) that has entered goes up the walls cavity being drafted by the warn inside wall.
The cold brick surface attracts the moisture in the humid air and attaches itself to the bricks surface and frost forms.
It goes trough cycles of thaw and freeze all winter long and expands the brick and breaks down the nail for the ties or even the ties themselves depending what they are made-of.
So please pay attention to the windows for I have seen brick field repaired only to have it break down again shortly after with the owner not knowing why.
An engineer could not explain why only how to repair.
But a window installer and mason told her and explained the process to her and I was on the money in that case.
It causes havoc inside the walls cavity. breaking down brick pins or anchors (wall ties) nails what ever you want to call them.
I can not tell you if you need an engineer but a good chimerical building inspector would give you a good heads up.
Good luck and if you can post total pictures of the building-north-east-West-and South I would-love to take a look.



montrealbuildinginspectionservice.com
montreal-home-inspection-services.com
home-inspections-montreal.com
homeinspectionsservicesmontreal.com
ROBERT YOUNG'S MONTREAL HOME INSPECTION SERVICE INC.
Certified Inspecteur Professionnel Certifié en Bâtiment membre de InterNACHI ACHI , Chapters - OntarioAchi et du M.I.C.Q (CPI) - (CHI)
OFFICE (514) 489-1887 MOBILE (514) 441-3732 TOLL FREE 1- 855-819-1816
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
First 10 members to post win the entire InterNACHI Inspection Graphics Library. gromicko General Inspection Discussion 61 11/30/10 8:07 AM
First 20 members to post win How to Perform Deck Inspections book. gromicko Exterior Inspections 41 12/21/09 9:23 PM
First 20 members to post win Structural Issues for Home Inpectors book. gromicko Structural Inspections 64 12/21/09 9:05 PM


All times are GMT -4. The time now is 2:55 PM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts