Default Does anybody else have a problem with this??

Brand new house to close June 21.

The opening to the bulkhead from the basement is 40" wide. The double sill plate spanning this opening has two floor joists within the opening. Am I crazy to recommend a header be installed?

Handrail posts are not secured with any type of bolt, only 5 galvanized nails. A problem here?? I think so.

Also found a 2x8 floor joist with a 3" crack, from the bottom up.

The house is supposed to be built to National Home Builders Code, by contract. Does anybody know if the "header" or deck post installations follow this code?

Thanks,
Attached Thumbnails
does-anybody-else-have-problem-img_01041.jpg   does-anybody-else-have-problem-img_01531.jpg  



Scott Falvey
Clear View Home Inspections, LLC
Newbury, NH
NACHI#05051292
www.clearviewhomeinspectionsllc.com
Reply With Quote
  #2  
Old 6/8/07, 10:44 PM
rcramer's Avatar
rcramer rcramer is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Belleville, IL
Posts: 128
Default Re: Does anybody else have a problem with this??

In the first picture, the installation is ok, as the rim joist is acting as the header supporting the joist. In the second picture, did you look on the underside of the framing for a bolt, or is the post sanwiched between two joist?



Robert Cramer
Five Star Property Inspections
Your Best & Safest Choice
www.fivestarpi.com
1-877-378-2774
Reply With Quote
  #3  
Old 6/8/07, 10:57 PM
Claude Lawrenson's Avatar
Claude Lawrenson Claude Lawrenson is offline
InterNACHI Member
 
Join Date: Dec 2003
Location: Tecumseh-Windsor, ON
Posts: 2,122
Default Re: Does anybody else have a problem with this??

Agree - with the "Robert's" comment with respect to the rim joist.



Cheers, Claude Lawrenson NACHI03121515
Inspection Support Services Inc.
"Those who can do. Those who CARE, teach" or
“Teaching is the highest form of understanding.” Aristotle
Reply With Quote
  #4  
Old 6/8/07, 10:58 PM
sfalvey sfalvey is offline
InterNACHI Member
 
Join Date: May 2005
Location: Newbury, NH
Posts: 393
Default Re: Does anybody else have a problem with this??

I did look underneath, there are no bolts and if I remember correctly, the post is not sandwiched between the joists.

Thanks for your input.



Scott Falvey
Clear View Home Inspections, LLC
Newbury, NH
NACHI#05051292
www.clearviewhomeinspectionsllc.com
Reply With Quote
  #5  
Old 6/9/07, 9:26 AM
Richard A. Hetzel Richard A. Hetzel is offline
Unmoderated Guest
 
Join Date: Apr 2007
Location: Tobyhanna, Pennsylvania
Posts: 598
Please Note: Richard A. Hetzel is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Does anybody else have a problem with this??

Quote:
The house is supposed to be built to National Home Builders Code, by contract.
Is there such a code? I couldn't find any evidence of it on the NAHB website.

Even if there were, the IRC would override it in 48 states, and whatever code has been adopted elsewhere would, also.
Reply With Quote
  #6  
Old 6/9/07, 12:01 PM
jkogel jkogel is offline
Active Poster
 
Join Date: Jan 2007
Location: Sooke, BC
Posts: 699
Please Note: jkogel is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Does anybody else have a problem with this??

I don't like that riser for the stairs in pic#2, the way it hangs in the air at the upper end and is cut too deeply at the notches, that is shabby.
Reply With Quote
  #7  
Old 6/9/07, 12:45 PM
Dennis R. Goudreau Dennis R. Goudreau is offline
InterNACHI Member
 
Join Date: Jun 2007
Location: Nashua, NH
Posts: 2,074
Default Re: Does anybody else have a problem with this??

Scott
pg 104 section R502.10 of the IRC states that openings in floor frameing shall be framed with a header & trimmer joist when the header joist span does not exceed 4 ft the header joist may be a single member of the same size as the floor joist.single trimmer joist may be used to carry a single header joist that is located within 3 ft of the trimmer joist bearing the rest deals with a larger span, also the IRC says nothing on fastners of handrails
Reply With Quote
  #8  
Old 6/9/07, 4:04 PM
Kenton H. Shepard, CMI's Avatar
Kenton H. Shepard, CMI Kenton H. Shepard, CMI is offline
InterNACHI Member
 
Join Date: Aug 2004
Location: Boulder, CO
Posts: 3,417
Send a message via ICQ to kshepard
Default Re: Does anybody else have a problem with this??

Lack of header isn't great but not suprising where they're trying to maintain headroom. I'd mention it but wouldn't make a big deal out of it.

Posts will eventually be loose as over time thermal expansion and contraction wil enlarge the nail holes. Poor construction practice but not presently a defect unless it's already loose.




Kenton Shepard, InterNACHI member # 04082383
Certified Master Inspector (CMI)
InterNACHI Director of International Development
Director of Green Building

EXPERT WITNESS SERVICE
Conventional and Log homes

(303) 717-8940
Reply With Quote
  #9  
Old 6/9/07, 6:09 PM
cbuell's Avatar
cbuell cbuell is offline
Active Poster
 
Join Date: Feb 2004
Location: Shorline, WA
Posts: 380
Please Note: cbuell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Does anybody else have a problem with this??

Are you sure the rim hasn't been "doubled" across the opening?
Reply With Quote
  #10  
Old 6/9/07, 7:20 PM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 19,798
Default Re: Does anybody else have a problem with this??

Quote:
Originally Posted by cbuell
Are you sure the rim hasn't been "doubled" across the opening?
That would be a possibility, but you would have to pull the insulation away to look and if that were the case of the doubled rim joist, joist hangers would be appropriate since the sill plate is not really a ledger board.

If the railing holds up to a 200 lb. force, I would not worry about it.

Marcel
Reply With Quote
  #11  
Old 6/9/07, 9:09 PM
sfalvey sfalvey is offline
InterNACHI Member
 
Join Date: May 2005
Location: Newbury, NH
Posts: 393
Default Re: Does anybody else have a problem with this??

I went back and looked at the deck today just to make sure I was corrct in what I saw.

The end post to the house is bolted in with carriage bolts, the corner post has 5 nails on 2 sides and so does the end post by the stairs.

I should also mention the deck is not flashed, when I pulled on the stair handrail the bottom step closest to the house lifted off the ground (diagonally) and the stairs are not on any footing just a couple of inches of crushed stone.

I don't think the rimjoist is doubled, if it were the joists would not extend as far onto the sill plates as they do. I do have a copy of the 2006 IRC, but being new to looking at codes, I am having a hard time finding what I am looking for.

I have also never heard the term trimmer joist, what exactly is that and what is its design?

Thanks.



Scott Falvey
Clear View Home Inspections, LLC
Newbury, NH
NACHI#05051292
www.clearviewhomeinspectionsllc.com
Reply With Quote
  #12  
Old 6/9/07, 9:13 PM
rwand1 rwand1 is offline
Active Poster
 
Join Date: Sep 2005
Location: Caledon, ON
Posts: 7,861
Please Note: rwand1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Does anybody else have a problem with this??

I have yet to see anyone flash a deck at the rim joist.
Reply With Quote
  #13  
Old 6/9/07, 10:01 PM
Richard A. Hetzel Richard A. Hetzel is offline
Unmoderated Guest
 
Join Date: Apr 2007
Location: Tobyhanna, Pennsylvania
Posts: 598
Please Note: Richard A. Hetzel is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Does anybody else have a problem with this??

A trimmer joist refers to an opening in a floor, where headers are installed at the ends of the opening perpendicular to the floor joists. The joists adjacent to the opening are usually doubled unless the opening is really small, and these are called trimmer joists.

The single 2x8 or 2x10 rim joist is more than adequate to act as a header across a 40-inch opening, assuming a 12-foot joist span and two stories of wall above the opening. Joist hangers would have been desirable on the two joists that are supported over the opening. I think there are one-side joist hangers that could be added.

The stair stringer in the picture, if you look closely, is connected to a plank nailed to the side of the deck. You can see the end grain of it. There normally isn't a footing under the bottom riser of an exterior stair, but often, a concrete pad is poured, and the stringers rest on it. Gravel isn't as neat, but it's acceptable.
Reply With Quote
  #14  
Old 6/9/07, 10:13 PM
sfalvey sfalvey is offline
InterNACHI Member
 
Join Date: May 2005
Location: Newbury, NH
Posts: 393
Default Re: Does anybody else have a problem with this??

Quote:
Originally Posted by Richard A. Hetzel
A trimmer joist refers to an opening in a floor, where headers are installed at the ends of the opening perpendicular to the floor joists. The joists adjacent to the opening are usually doubled unless the opening is really small, and these are called trimmer joists.

The single 2x8 or 2x10 rim joist is more than adequate to act as a header across a 40-inch opening, assuming a 12-foot joist span and two stories of wall above the opening. Joist hangers would have been desirable on the two joists that are supported over the opening. I think there are one-side joist hangers that could be added.

The stair stringer in the picture, if you look closely, is connected to a plank nailed to the side of the deck. You can see the end grain of it. There normally isn't a footing under the bottom riser of an exterior stair, but often, a concrete pad is poured, and the stringers rest on it. Gravel isn't as neat, but it's acceptable.
Thanks for the info. I will note it in my report.



Scott Falvey
Clear View Home Inspections, LLC
Newbury, NH
NACHI#05051292
www.clearviewhomeinspectionsllc.com
Reply With Quote
  #15  
Old 6/9/07, 10:20 PM
sfalvey sfalvey is offline
InterNACHI Member
 
Join Date: May 2005
Location: Newbury, NH
Posts: 393
Default Re: Does anybody else have a problem with this??

Quote:
Originally Posted by rwand1
I have yet to see anyone flash a deck at the rim joist.
I wasn't refering to flashing at the rim joist (sorry if there was confusion), but it is typical for it to be at the ledger board and it is not seen here.

Thanks,



Scott Falvey
Clear View Home Inspections, LLC
Newbury, NH
NACHI#05051292
www.clearviewhomeinspectionsllc.com
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Fetch Report problem mhazelwood Miscellaneous Discussion for Inspectors 7 11/12/07 11:12 AM
Is MAC a problem bemelander General Inspection Discussion 3 9/6/07 11:44 AM
Camera Problem nwagner Miscellaneous Discussion for Inspectors 19 7/30/07 10:10 PM
Plumbing problem at home. mnahrgang Plumbing Inspections 25 7/10/07 5:32 PM