Default Drywall firewall boundries in attic

Noted two foot wide pieces of drywall nailed to truss's along firewall in a town home built in 1983. I cannot locate any information on this type of fire barrier. ?? any idea's.
Attached Thumbnails
drywall-firewall-boundries-attic-08200701-232resized.jpg  

Last edited by sbenson; 8/20/07 at 4:47 PM.. Reason: add photo
Reply With Quote
  #2  
Old 8/20/07, 6:23 PM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 8,848
Default Re: Drywall firewall boundries in attic

Quote:
Originally Posted by sbenson
Noted two foot wide pieces of drywall nailed to truss's along firewall in a town home built in 1983. I cannot locate any information on this type of fire barrier. ?? any idea's.
Well, with a 3 1/2" opening in the drywall, it's breached anyway....

What showed when you peaked into that breach? Was the block wall cut tight with no gaps below the top cord of the truss next to it?



InterNachi Awards Portal: http://co.nachi.org/inachiawards/

____________________________________________
"An Education, not just an Inspection"

Larry Kage, CMI
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector serving the Traverse City, Michigan area and beyond.
Reply With Quote
  #3  
Old 8/20/07, 6:58 PM
sbenson sbenson is offline
InterNACHI Member
 
Join Date: Dec 2006
Location: Suffolk, Va
Posts: 31
Default Re: Drywall firewall boundries in attic

Block wall extended up past the truss. Truss was butted flush against wall. Roofline's from one unit to next was staggered.



Sam Benson
HomeSpec Residential
Quality Inspections for the Informed Consumer
www.HomeSpec99.com
Reply With Quote
  #4  
Old 8/20/07, 11:06 PM
Claude Lawrenson's Avatar
Claude Lawrenson Claude Lawrenson is offline
InterNACHI Member
 
Join Date: Dec 2003
Location: Tecumseh-Windsor, ON
Posts: 2,122
Default Re: Drywall firewall boundries in attic

First - is this intended to be a firewall or fire separation?

There is a difference between the two.



Cheers, Claude Lawrenson NACHI03121515
Inspection Support Services Inc.
"Those who can do. Those who CARE, teach" or
“Teaching is the highest form of understanding.” Aristotle
Reply With Quote
  #5  
Old 8/21/07, 8:44 AM
Mario A. Kyriacou, CHI's Avatar
Mario A. Kyriacou, CHI Mario A. Kyriacou, CHI is offline
ESOP Committee Member
 
Join Date: Jun 2006
Location: Toronto, Ontario, Canada
Posts: 5,851
Default Re: Drywall firewall boundries in attic

Quote:
Originally Posted by clawrenson
First - is this intended to be a firewall or fire separation?

There is a difference between the two.

Good point Claude!!

"Definitions:
Fire Separation means - A construction assembly that acts as a barrier against the spread of fire. (Note: A fire separation may or may not have a fire rating)
Firewall means - A type of firewall separation of non-combustible construction which sub-divides a building or separates adjoining buildings to resist the spread of fire and which has a fire resistance rating and has structural stability to remain intact under fire conditions for the required fire-rate time.
Fire-Resistance Rating means - The time in hours or fractions thereof that a material or assembly of materials will withstand the passage of flame and the transmission of heat when exposed to fire under specified conditions of Test and Performance criteria, or as determined by extension or interpretation of information derived there from as prescribed in the National Building Code.





'Imagination is more important than knowledge' (sometimes)
Mario Kyriacou CHI CMI-NACHI Canadian Member of the Year 2007

www.360degreeshomeinspections.com
Tel.# 416-722-6132
e-mail torontohomeinspector@yahoo.com
Reply With Quote
  #6  
Old 8/21/07, 11:31 AM
mthomas2 mthomas2 is offline
Active Poster
 
Join Date: Oct 2005
Location: Evanston, IL
Posts: 703
Please Note: mthomas2 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Drywall firewall boundries in attic

What's needed there depends: does that wall extend up above the roof and form a compliant parapet? If not, that gypsym borad is needed, but it's not correctly installed:

R317.2.2 Exception: A parapet is not required in the two cases above when the roof is covered with a minimum class C roof covering, and the roof decking or sheathing is of noncombustible materials or approved fire-retardant-treated wood for a distance of 4 feet (1219 mm) on each side of the wall or walls, or one layer of 5/8-inch (15.9 mm) Type X gypsum board is installed directly beneath the roof decking or sheathing for a distance of 4 feet (1219 mm) on each side of the wall or walls.

Last edited by mthomas2; 8/21/07 at 11:36 AM..
Reply With Quote
  #7  
Old 8/21/07, 1:15 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,058
Default Re: Drywall firewall boundries in attic

There is no "separation" requirement for the roof structure, only the wall, which is CMU and non-combustible.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #8  
Old 8/22/07, 2:51 PM
Richard A. Hetzel Richard A. Hetzel is offline
Unmoderated Guest
 
Join Date: Apr 2007
Location: Tobyhanna, Pennsylvania
Posts: 598
Please Note: Richard A. Hetzel is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Drywall firewall boundries in attic

Quote:
There is no "separation" requirement for the roof structure, only the wall, which is CMU and non-combustible.
Again, beg to differ. If the block wall does not extend as a parapet above the roof, or above the highest roof if there are different heights, then horizontal protection is required on each side of the wall to achieve the required fire-resistance rating.
Reply With Quote
  #9  
Old 8/22/07, 8:33 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,058
Default Re: Drywall firewall boundries in attic

Quote:
Originally Posted by jpope
There is no "separation" requirement for the roof structure
If you disagree, show me your reference.

I am always willing to learn. . .



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net



Last edited by jpope; 8/22/07 at 9:27 PM..
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Nail pops at the base of vaulted ceiling-no roof leak kshepard Interior Inspections 32 9/9/07 2:06 PM
Spray Foam to the Rescue ? mcyr Structural Inspections 3 3/27/07 7:29 PM


All times are GMT -4. The time now is 2:56 PM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts