  #1  
Old 3/26/07, 5:59 PM
Robert Skinner Robert Skinner is offline
InterNACHI Member
 
Join Date: Sep 2004
Location: Helotes, TX
Posts: 24
Default Fire Resistive Barrier for townhomes

Need help ASAP.
Anyone know of a requirement for townhome attics having 1/2 inch drywall on the underside of the rafters adjacent to the common walls. See photos.
Attached Thumbnails
fire-resistive-barrier-townhomes-p1010002.jpg   fire-resistive-barrier-townhomes-p1010003.jpg  
Reply With Quote
  #2  
Old 3/26/07, 6:46 PM
Kenton H. Shepard, CMI's Avatar
Kenton H. Shepard, CMI Kenton H. Shepard, CMI is offline
InterNACHI Member
 
Join Date: Aug 2004
Location: Boulder, CO
Posts: 2,487
Send a message via ICQ to kshepard
Default Re: Fire Resistive Barrier for townhomes

Quote:
Originally Posted by rskinner
Need help ASAP.
Anyone know of a requirement for townhome attics having 1/2 inch drywall on the underside of the rafters adjacent to the common walls. See photos.
I ran into it at some point when I was a carpenter. Seems to me they wanted to ensure that fire had no access through which it could jump from one unit to the next through the rafter bay above the rake wall. A valid concern.




Kenton Shepard, InterNACHI member # 04082383
Certified Master Inspector (CMI)
EXPERT WITNESS

Director of Green Building
Director for International Development

(303) 717-8940
(303) 258-8289

Reply With Quote
  #3  
Old 3/26/07, 7:01 PM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 12,359
Default Re: Fire Resistive Barrier for townhomes

Basically what Kenton said, sometimes the relationship between where the fire break wall is and the rafter above are not conducive to each other and is easier to just sheetrock the rafter bays, which makes it easier to seal.

One question;

Why would they use dense glass drywall in lieu of a cheaper regular type X. ??

Just curious.

Marcel
</IMG></IMG>




Cyr Home and Commercial Property Inspections

IAC2 Certified
NACHI04070211
http://co.nachi.org/inachiawards


Commercial Builder
CertainTeed
Master Shingle Applicator
Shingle Technology
Ouellet Associaties Inc.
http://www.oaconstruction.com/
Reply With Quote
  #4  
Old 3/26/07, 7:07 PM
Kenton H. Shepard, CMI's Avatar
Kenton H. Shepard, CMI Kenton H. Shepard, CMI is offline
InterNACHI Member
 
Join Date: Aug 2004
Location: Boulder, CO
Posts: 2,487
Send a message via ICQ to kshepard
Default Re: Fire Resistive Barrier for townhomes

Quote:
Originally Posted by mcyr

Why would they use dense glass drywall in lieu of a cheaper regular type X. ??

Just curious.

Marcel
</IMG></IMG>
I wondered about type x too, Marcel. I've never heard of dense glass drywall, though. How do you recognize it and what's it usually used for?




Kenton Shepard, InterNACHI member # 04082383
Certified Master Inspector (CMI)
EXPERT WITNESS

Director of Green Building
Director for International Development

(303) 717-8940
(303) 258-8289

Reply With Quote
  #5  
Old 3/26/07, 7:21 PM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 12,359
Default Re: Fire Resistive Barrier for townhomes

Kenton, in the second picture I can see just a little of the GP insigna and the fiberous yellow paper would indicate to me to be as this link. We use it all the time for exterior sheathing behind brick veneers.

http://www.gp.com/build/product.aspx...4&hierarchy=pc

Hope this helps.

Marcel




Cyr Home and Commercial Property Inspections

IAC2 Certified
NACHI04070211
http://co.nachi.org/inachiawards


Commercial Builder
CertainTeed
Master Shingle Applicator
Shingle Technology
Ouellet Associaties Inc.
http://www.oaconstruction.com/
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
"UFER" Ground? see last paragraph. jtedesco1 Electrical 6 9/15/08 8:57 AM
Escape, Fire & Smoke Alarms badair Interior 14 1/28/08 8:21 AM
About Air Barriers mcyr General Inspection Discussion 5 9/29/07 11:10 PM
Fire rating abolt Structural 13 9/21/07 9:45 PM


All times are GMT -4. The time now is 3:09 PM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts