  #1  
Old 8/15/07, 8:24 PM
Tom Yeager Tom Yeager is offline
InterNACHI Member
 
Join Date: Jul 2007
Location: Broomfield, CO
Posts: 40
Default Fire wall

This is an access to the master bathroom "jacuzzi" tub motor. It is in the wall of the garage. Would there be any reason this is NOT a firewall breech?
Attached Thumbnails
fire-wall-p8150142-2-.jpg.JPG
Views:	138
Size:	30.8 KB
ID:	13962   fire-wall-p8150147-2-.jpg.JPG
Views:	130
Size:	43.5 KB
ID:	13963  



Tom Yeager
Owner/Certified Inspector
Inspect-It 1st
303-464-9090
www.tyeagerinspects.com
NEHA Radon Certification # 104169 RT
NACHI Certified Home Inspector
Reply With Quote
  #2  
Old 8/15/07, 9:04 PM
gbeaumont's Avatar
gbeaumont gbeaumont is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: Clearwater, FL
Posts: 6,261
Send a message via AIM to gbeaumont Send a message via MSN to gbeaumont Send a message via Yahoo to gbeaumont
Default Re: Fire wall

Hi Tom,

in a word, NOPE!!

Regards

Gerry



"To realize our true destiny, we must be guided not by a myth from our past, but by a vision of our future."
(Mark B Adams)

Commercial property Inspection Tampa, Orlando, Sarasota, Jacksonville, Ft Launderdale, Miami, Florida.
NACHI cell 484-429-5466
NACHI02121106

Reply With Quote
  #3  
Old 8/15/07, 10:44 PM
Richard A. Hetzel Richard A. Hetzel is offline
Unmoderated Guest
 
Join Date: Apr 2007
Location: Tobyhanna, Pennsylvania
Posts: 598
Please Note: Richard A. Hetzel is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Fire wall

Technically, the wall between a garage and a dwelling unit is not required to have any particular fire resistance rating, so, again technically, it is not a fire wall. However, the IRC does address "Opening Protection" for openings between the garage and residence, in R309.1 in the 2003 New York version, and that louver doesn't meet any of the several specifications in the code for the kind of closure required.
Reply With Quote
  #4  
Old 8/15/07, 10:53 PM
Brian A. MacNeish Brian A. MacNeish is offline
Banned
 
Join Date: Apr 2007
Location: CANADA
Posts: 4,638
Please Note: Brian A. MacNeish is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Fire wall

In Canada, it may be. We don't require that the wall be fire rated but that it be airtight with no holes through it so as to stop gas or fumes from entering the home. Any person door (no doors from bedrooms to garage) from the house to the garage must have an auto-closing device installed and be airtight/ weatherstripped.

In the picture, the code official may have to determine if there is any air leakage sites around the tub enclosure; it will be easier for them to call for a gasketed door instead of the heating/ventilation grille.
Reply With Quote
  #5  
Old 8/15/07, 11:00 PM
Mario A. Kyriacou, CHI's Avatar
Mario A. Kyriacou, CHI Mario A. Kyriacou, CHI is offline
ESOP Committee Member
 
Join Date: Jun 2006
Location: Toronto, Ontario, Canada
Posts: 5,851
Default Re: Fire wall

Quote:
Originally Posted by Brian A. MacNeish
In Canada, it may be. We don't require that the wall be fire rated but that it be airtight with no holes through it so as to stop gas or fumes from entering the home. Any person door (no doors from bedrooms to garage) from the house to the garage must have an auto-closing device installed and be airtight/ weatherstripped.

In the picture, the code official may have to determine if there is any air leakage sites around the tub enclosure; it will be easier for them to call for a gasketed door instead of the heating/ventilation grille.
Good post Brian!!

You are very knowledgeable about the OBC. Why are you not a member of NACHI?





'Imagination is more important than knowledge' (sometimes)
Mario Kyriacou CHI CMI-NACHI Canadian Member of the Year 2007

www.360degreeshomeinspections.com
Tel.# 416-722-6132
e-mail torontohomeinspector@yahoo.com
Reply With Quote
  #6  
Old 8/15/07, 11:54 PM
homebild homebild is offline
Active Poster
 
Join Date: Nov 2006
Location: Pennsylvania
Posts: 195
Please Note: homebild is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Fire wall

Quote:
Originally Posted by Richard A. Hetzel
Technically, the wall between a garage and a dwelling unit is not required to have any particular fire resistance rating, so, again technically, it is not a fire wall. However, the IRC does address "Opening Protection" for openings between the garage and residence, in R309.1 in the 2003 New York version, and that louver doesn't meet any of the several specifications in the code for the kind of closure required.
Not True.

Under the International Residential Code there is required a fire-rating of 20 minutes between an attached garage wall and the dwelling.

This is accomplished by way of 1/2" drywall which establishes a 20 minute fire-rating and by having any doors between the garage and dwelling also to be 20 minute fre-rated.

Unless it can be demonstrated that the required access panel cover to the 'jacuzzi' is at least 20 minute fire-rated...it is illegal under any IRC Code.
Reply With Quote
  #7  
Old 8/16/07, 1:00 AM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,050
Default Re: Fire wall

Quote:
Originally Posted by Richard A. Hetzel
Technically, the wall between a garage and a dwelling unit is not required to have any particular fire resistance rating,
I disagree. In CA, a specific rating is required.

In the IRC, it's not called a "firewall," but their intent is clear.

R309.2 Separation Required.

[Commentary] Numerous potential hazards exist within garages because occupants of dwelling units tend to store a variety of hazardous materials there. Along with this and the potential for carbon monoxide build-up within the garage, the IRC requires that the garage be separated from the dwelling unit and the attic with at least 1/2-inch (12.7 mm) gypsum board or other equivalent material. If a habitable room is above the garage, the separation must be at least 5/8-inch (15.9 mm) Type X gypsum board or equivalent.

There are two primary reasons for providing an enhanced fire endurance for a garage ceiling located beneath a habitable room. First, a fire occurring in a garage may well go undetected for an extended period prior to activation of a detector or other visual alerting. Second, the inherent fire load and hazardous household activities associated with a garage necessitate this additional level of protection if fire suppression forces are to have a reasonable opportunity to contain a garage fire to the area of origin. [continued. . .]



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #8  
Old 8/16/07, 3:13 AM
W. Michael Chris's Avatar
W. Michael Chris W. Michael Chris is offline
InterNACHI Member
 
Join Date: May 2005
Location: Santa Clara, UT
Posts: 1,122
Default Re: Fire wall

Tom, I think your question has been answered by others, most the time around here the contractors don't install access panels of any kind . . . and as I talk with my clients, hardly anyone has uses the "jacuzzi" in there present home . . . I have one in my home without access (lived in home about 8 years now), but I can probably count on both hands the number of times it's been used . . . I know I'm off subject, sorry, just wanted to type I guess.



Mike Chris, Santa Clara, Utah
NACHI: #05051385
HouseNspect@gmail.com
www.housenspect.com
activerain

"A man's home is his castle . . . until the queen arrives."
Reply With Quote
  #9  
Old 8/16/07, 11:59 AM
Richard A. Hetzel Richard A. Hetzel is offline
Unmoderated Guest
 
Join Date: Apr 2007
Location: Tobyhanna, Pennsylvania
Posts: 598
Please Note: Richard A. Hetzel is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Fire wall

Quote:
Under the International Residential Code there is required a fire-rating of 20 minutes between an attached garage wall and the dwelling.
Where in the Code is this requirement stated? I can't find it. It's not in R309.2 where it could have been if that is what was intended. Again, I'm looking at the 2003 IRC. (not the NY version as I stated earlier...I wish they would make them different colors) In fact, the NY version is amended to specifically require a 3/4 hour fire resistance rating for vertical separations (walls).
Reply With Quote
  #10  
Old 8/16/07, 1:24 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,050
Default Re: Fire wall

Quote:
Originally Posted by Richard A. Hetzel
Where in the Code is this requirement stated? I can't find it. It's not in R309.2 where it could have been if that is what was intended.
To repeat my last post, even though 309.2 does not specifically state the required rating, the intent is clear.

If you back-up to 309.1, you'll see the requirement for a 20 minute door.

R309.1 Opening protection. Openings from a private garage directly into a room used for sleeping purposes shall not be permitted. Other openings between the garage and residence shall be equipped with solid wood doors not less than 1-3/8 inches (35 mm) in thickness, solid or honeycomb core steel doors not less than 1-3/8 inches (35 mm) thick, or 20-minute fire-rated doors.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #11  
Old 8/16/07, 2:35 PM
Tom Yeager Tom Yeager is offline
InterNACHI Member
 
Join Date: Jul 2007
Location: Broomfield, CO
Posts: 40
Default Re: Fire wall

Thank you everyone for your thought provoking input! I guess I was thinking that they could somehow insist the tub enclosure is fire rated, but then I found in my "Code Check" that 2003 IRC 309.2 is summarized:

"Min. 1/2 in. gyp board ON GARAGE SIDE of walls common to house."

Here is how I wrote it up:

Safety Concern - Improper bath tub access cover. At the time of inspection, no cover was installed but it appears the intended cover is on the floor in front of it. Fire resistive separation between the garage and living space must be maintained on the garage side of the walls common to the house. This cover must be approved fire rated material and installed correctly (sealed) for adequate fire safety protection.

Thanks again!



Tom Yeager
Owner/Certified Inspector
Inspect-It 1st
303-464-9090
www.tyeagerinspects.com
NEHA Radon Certification # 104169 RT
NACHI Certified Home Inspector
Reply With Quote
  #12  
Old 8/17/07, 5:51 PM
Kenton H. Shepard, CMI's Avatar
Kenton H. Shepard, CMI Kenton H. Shepard, CMI is offline
InterNACHI Member
 
Join Date: Aug 2004
Location: Boulder, CO
Posts: 3,417
Send a message via ICQ to kshepard
Default Re: Fire wall

So... if the garage is drywalled with 1/2 drywall and fire-taped, it's compliant... What's the jacuzzi got to do with anything except that the cover was on the floor instead of installed when the inspector arrived?
I don't see anything to call unless the garage was not drywalled and firetaped, in which case the jacuzzi cover is a breach.




Kenton Shepard, InterNACHI member # 04082383
Certified Master Inspector (CMI)
InterNACHI Director of International Development
Director of Green Building

EXPERT WITNESS SERVICE
Conventional and Log homes

(303) 717-8940
Reply With Quote
  #13  
Old 8/17/07, 6:25 PM
Brian E. Kelly's Avatar
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 15,973
Default Re: Fire wall

Quote:
Originally Posted by kshepard
So... if the garage is drywalled with 1/2 drywall and fire-taped, it's compliant... What's the jacuzzi got to do with anything except that the cover was on the floor instead of installed when the inspector arrived?
I don't see anything to call unless the garage was not drywalled and firetaped, in which case the jacuzzi cover is a breach.
Louvered metal covers are fire rated for about a millisecond Kenton.
Reply With Quote
  #14  
Old 8/17/07, 8:58 PM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 19,788
Default Re: Fire wall

This might help;

http://www.usinspect.com/garages/Structure.asp


Wall Separation - The living area adjacent to the attached garage should be separated with a minimum 1/2 inch gypsum board. This separation is required in order to prevent toxic exhaust gases and gasoline vapors, which are heavier than air, from entering the residence. Therefore, the walls and ceilings that separate the garage from living space must be free of any holes or voids. If the wall adjacent to living space has a door, the door should be installed with a curb, be self-closing, and the weather stripping should provide a tight seal around the door.

Roof Structure - The structural requirements and design of a roof should meet the same criteria as the residence. Houses built today typically utilize roof trusses, while older housing employed conventional framing, which are rafters and joists. Ceiling structures of garages are frequently modified to accommodate an access panel or disappearing stairs. This may result in improper modification of the joists or trusses. Headers are needed for conventional framing, and if trusses have to be cut, an engineered reinforcement system may be required. Areas over garages are frequently used for storage of personal items; possibly overloading joists or trusses. The garage attic area should be separated from the residence by a firewall, assuming there is access from the garage into the attic area. The roof structure should not be sagging or putting unnecessary pressure on the outside walls. Generally trusses are engineered and braced individually and as a system, and are typically dependable structures. Conventionally built roof systems are also dependable, however, there are workmanship short cuts that may compromise the roof system (i.e. garages may not have any ceiling joists or adequate ceiling joists). This will put considerable pressure on the outside walls. The rafters may be over spanned, or may not have proper collar ties. Check for bowing at the center of the sidewalls and for excessive roof deflections.



Door from the garage to the residence - The interior door should have a tight seal all the way around to prevent seepage of exhaust or gas fumes. This door should be fire-resistant, such as metal clad or solid core wood. You may also see 1 3/8” hollow core interior doors with a sheet of metal on the garage side. This may be accepted in many areas, however, its fire protection is negligible. As a safety feature, the door should be self-closing. Many municipalities have requirements for fire-rated doors and frames. Because the door should resist a twenty-minute fire, there should be no glass or other openings in the door itself.

Fire Step - The slab of the garage should be a minimum of 4 inches lower than the slab entering the house to reduce the potential of gasoline or exhaust fumes from entering the property.
Marcel
Reply With Quote
  #15  
Old 8/17/07, 9:41 PM
Brian E. Kelly's Avatar
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 15,973
Default Re: Fire wall

Quote:
Fire Step - The slab of the garage should be a minimum of 4 inches lower than the slab entering the house to reduce the potential of gasoline or exhaust fumes from entering the property.
Did US Inspect just make this Fire Step part up??????
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
"UFER" Ground? see last paragraph. jtedesco1 Electrical Inspections 19 8/23/11 3:56 PM
VIDEO--Bowed Basement Wall, Cracks etc john bubber Structural Inspections 75 7/21/08 5:25 PM
Escape, Fire & Smoke Alarms badair Interior Inspections 14 1/28/08 7:21 AM
Garage fire rated wall jlybolt Interior Inspections 3 6/18/06 6:21 PM