I would say about 50% of the crawlspaces I inspect have cross bracing installed between each joist but never compleated. Meaning the top end was nailed but the bottm ends were not.
I have also observed that no twisting or movement issues were found and many homes are 20 years or older. Would you consider this an issue after 30 years of no problems and would you recommend they be finished. Infraspection Institute Level 1 Certified Infrared Thermographer Fogarty Inspection Services Group of Knoxville TN Home inspections, Commercial Inspections, Thermal Imaging, Mold, Enviromental Testing and Radon Testing for Knoxville TN, Oak Ridge TN, Maryville, Clinton, Farragut, Lenoir City, Pigeon Forge, Sevierville and all the surrounding areas. 865-256-5397 www.homeinspectorknoxville.com www.moldandradon.com www.thermal-inspection.net www.commercial-building-inspector.net |
| Need a home inspection in New York? Check out InterNACHI's listing of New York certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine. |
|
#2
|
||||
|
||||
|
i use the Bridging comment from this whenever encountered, ymmv and others prolly have differing opinions
http://www.awc.org/pdf/wcd1-300.pdf ADAIR INSPECTION 972-487-5634 Commercial-Residential-Construction-EIFS-Infrared Thermography TREC # 4563 EDI: EIFS-MA TX # 39 2008 US Member of the Year life is the random lottery of events followed by numerous narrow escapes accept the good |
|
#3
|
||||
|
||||
|
Thanks Barry,
Obviously after 30 years with no ill effects it should be fine but I will make a note of it. Infraspection Institute Level 1 Certified Infrared Thermographer Fogarty Inspection Services Group of Knoxville TN Home inspections, Commercial Inspections, Thermal Imaging, Mold, Enviromental Testing and Radon Testing for Knoxville TN, Oak Ridge TN, Maryville, Clinton, Farragut, Lenoir City, Pigeon Forge, Sevierville and all the surrounding areas. 865-256-5397 www.homeinspectorknoxville.com www.moldandradon.com www.thermal-inspection.net www.commercial-building-inspector.net |
|
#4
|
||||
|
||||
|
Quote:
montrealbuildinginspectionservice.com montreal-home-inspection-services.com home-inspections-montreal.com homeinspectionsservicesmontreal.com ROBERT YOUNG'S MONTREAL HOME INSPECTION SERVICE INC. Certified Inspecteur Professionnel Certifié en Bâtiment membre de InterNACHI ACHI , Chapters - OntarioAchi et du M.I.C.Q (CPI) - (CHI) OFFICE (514) 489-1887 MOBILE (514) 441-3732 TOLL FREE 1- 855-819-1816 |
|
#5
|
||||
|
||||
|
Sean
The bridging prevents rotation of the joist and helps distribute any concentrated floor loads to adjacent joists. While it may not have been a problem for 20 years, if the new owner puts a baby grand piano on that floor a problem could occur. So I agree with others you should mention the defect and move on. |
|
#6
|
||||
|
||||
|
Quote:
I agree THE RIGHT TRAK CIAQP, IAC2 Certified Master Inspector kwoodinspections@hotmail.com www.kwood.inspectorpages.com www.homegauge.com/shgi/THERIGHTTRAKIAQ www.linkedin.com/in/kevinwoodiaq OOVOO account kwoodinspections Cell: 705-971-2096 Ph : 705-946-2676 |
|
#7
|
||||
|
||||
|
ADAIR INSPECTION 972-487-5634 Commercial-Residential-Construction-EIFS-Infrared Thermography TREC # 4563 EDI: EIFS-MA TX # 39 2008 US Member of the Year life is the random lottery of events followed by numerous narrow escapes accept the good |
|
#8
|
||||
|
||||
|
I agree with reporting the issue and moving on.
I would also explain during our post inspection meeting; that properly installed bridging belongs in the system and give several short explanations of what can occur if left untended. Squeaking, twisting joists, possible nail lift, slight rolling floor plane and the age of the home relative to the floors condition so far. Whats happened over time, if anything. Would this be wrong in anyone's opinion? Thanks for any replies........Robert montrealbuildinginspectionservice.com montreal-home-inspection-services.com home-inspections-montreal.com homeinspectionsservicesmontreal.com ROBERT YOUNG'S MONTREAL HOME INSPECTION SERVICE INC. Certified Inspecteur Professionnel Certifié en Bâtiment membre de InterNACHI ACHI , Chapters - OntarioAchi et du M.I.C.Q (CPI) - (CHI) OFFICE (514) 489-1887 MOBILE (514) 441-3732 TOLL FREE 1- 855-819-1816 |
|
#9
|
||||
|
||||
|
Quote:
Quote:
JMO & 2-Nickels ... Robert O'Connor, PE Consulting Engineer & Inspector LIU CW Post Adjunct Professor NACHI Education Committee www.reporthost.com/-rjo I am absolutely amazed sometimes by how much thought goes into doing things wrong ... |
|
#10
|
||||
|
||||
|
If the floor joists are heavy enough. They do not need cross bracing.
Braun Inspection Consultants Serving Jefferson City, Columbia, Sedalia, Fulton and Lake of the Ozarks
|
|
#11
|
||||
|
||||
|
I agree with Randy, I have installed bridging in floor framing since the early 60's, and it is required to provide a complete diaphragm for proper load support. In the post above, the builder forgot or was to lazy to crawl in and finish the job. It may have lasted this long, only because it was not required to carry the floor load if the framing was the right size for the span. It just went on to provide a floor that was bouncy and never had a concentrated load to accentuate a problem to the framing members.
it was nailed in before the sub flooring and when the sub floor was complete, you went underneath and finished nailing it. It was not meant for rotation, but more for completing the diaphragm to make the floor system more stable and less bounce. Any load imposed on the floor system is distributed equally rather than on just the immediate area. I found this article that says the same thing. http://www.tpub.com/content/construc...s/14044_24.htm Floor plans or specifications usually call for bridging between joists. Bridging holds the joists in line and helps distribute the load carried by the floor unit. It is usually required when the joist spans are more than 8 feet. Joists spanning between 8 and 15 feet need one row of bridging at the center of the span. For longer spans, two rows of bridging spaced 6 feet apart are required. CROSS BRIDGING.— Also known as herringbone bridging, cross bridging usually consists of 1- by 3-inch or 2- by 3-inch wood. It is installed as shown in figure 1-26. Cross bridging is toenailed at each Figure 1-26.—Wood cross bridging. end with 6d or 8d nails. Pieces are usually precut on a radial-arm saw. Nails are started at each end before the cross bridging is placed between the joists. The usual procedure is to fasten only the top end of the cross bridging. The nails at the bottom end are not driven in until the subfloor has been placed. Otherwise the joist could be pushed out of line when the bridging is nailed in. No one is going to convince me that it is only required for higher depth joist. Higher depth joist like bar joist, yes, rotation under load comes into play and the bridging is playing a double role. Standard home floor framing is a different application. Nothing is going to rotate, it will bend and fail. Higher web members in commercial or engineered floor joist, will rotate and fail. LEED Green Associates InachiAwardsPortal: Inachi US Member of the Year Award 2009 |
|
#12
|
|||
|
|||
|
Quote:
InterNachi Awards Portal: http://co.nachi.org/inachiawards/ ____________________________________________ "An Education, not just an Inspection" Larry Kage, CMI Lake Ann (Traverse City), Michigan 49650 231 929 3525 Professional Inspector serving the Traverse City, Michigan area and beyond.
|
|
#13
|
||||
|
||||
|
Quote:
Hypothetically ( flooring systems ) are subject to loads the interacting structural components exert within the surrounding field. Squash blocks and bridging are both needed. Loads , be it horizontal or vertically placed in or on any given element within the field might play a roll in causing movement. That is the reason for the bridging. The live or constant( dead ) load or loads are shared among the united field. Nailing and the importance of a tight bridging all come together to act a one united field. Code Reference: IRC 2003/2006, R502.7.1 NCA/TB/LTB Bridging http://www.strongtie.com/products/co...NCA-TB-LTB.asp Just an opinion from years of education, observation and repair James. A link to common carpentry terms. http://www.carpentry-pro-framer.com/...try-terms.html montrealbuildinginspectionservice.com montreal-home-inspection-services.com home-inspections-montreal.com homeinspectionsservicesmontreal.com ROBERT YOUNG'S MONTREAL HOME INSPECTION SERVICE INC. Certified Inspecteur Professionnel Certifié en Bâtiment membre de InterNACHI ACHI , Chapters - OntarioAchi et du M.I.C.Q (CPI) - (CHI) OFFICE (514) 489-1887 MOBILE (514) 441-3732 TOLL FREE 1- 855-819-1816 |
| Need a home inspection in New York? Check out InterNACHI's listing of New York certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine. |
|
#14
|
||||
|
||||
|
Again I agree with you Robert. I have seen the results of no bridging in a proper designed house. The floor sagged in the center on both side of the beam. This was no wimpy construction either. The floor installers put shims under the sub floor to level it about 2 inches down. Moisture may have been a factor in softening the joists and sub floor but if bracing was put in at this location no movement would have occurred.
THE RIGHT TRAK CIAQP, IAC2 Certified Master Inspector kwoodinspections@hotmail.com www.kwood.inspectorpages.com www.homegauge.com/shgi/THERIGHTTRAKIAQ www.linkedin.com/in/kevinwoodiaq OOVOO account kwoodinspections Cell: 705-971-2096 Ph : 705-946-2676 |
|
#15
|
||||
|
||||
|
Guys, bridging is for keeping a joist from rotating, not for transferring load. Sure some load can be transfered from one joist to an adjacent one thru bridging, but the amount of load transfered is next to nothing.
Old style bridging was often 1x3 or 1x4 pieces of lumber with the ends cut to fit the joists, with two small 6d or 8d nails thru the sloped cut end. Load would be transfered to an adjacent joist thru shear and withdrawal of those nails. And the wood is often split. The values are not even worth calculating they are so small. Anyone who has removed them (I have) knows how easily they come out. Metal bridging is no better. It's often a metal strap with just one nail at each end. And only one of the two straps in a typical cross pattern is effective in transferring load (the other one actually relaxes). So the amount of load transfered to an adjacent joist from each nailed strap is typically equal to the shear value for a single 8d or 10d nail. The newer claw-end nail on bridging is even less effective. Again, not even worth calculating. JMO & 2-Nickels ... Robert O'Connor, PE Consulting Engineer & Inspector LIU CW Post Adjunct Professor NACHI Education Committee www.reporthost.com/-rjo I am absolutely amazed sometimes by how much thought goes into doing things wrong ... Last edited by roconnor; 8/11/11 at 4:02 PM.. |
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| Donation Ideas for Japan - Red Cross | tspargo | Miscellaneous Discussion for Inspectors | 8 | 3/14/11 12:39 PM |
| Donate to The Haiti Red Cross | jmckenna1 | Miscellaneous Discussion for Inspectors | 10 | 1/16/10 10:44 PM |
| Cross Bridges not fastened ... | Ron Smith | Structural Inspections | 10 | 4/10/06 9:54 PM |