Structural Inspections Contains discussions about the structural portion of a home inspection. This includes foundations, framing, etc.

 
Reply
 
LinkBack Thread Tools
  #31  
Old 8/15/11, 1:09 PM
ROBERT V. YOUNG's Avatar
ROBERT V. YOUNG ROBERT V. YOUNG is offline
InterNACHI Member
 
Join Date: Mar 2010
Location: Montreal.
Posts: 5,050
Default Re: Floor joist cross bracing

Thanks.
That was the question I had to consider.
Great work as always Mr. O'Connor.



montrealbuildinginspectionservice.com
montreal-home-inspection-services.com
home-inspections-montreal.com
homeinspectionsservicesmontreal.com
ROBERT YOUNG'S MONTREAL HOME INSPECTION SERVICE INC.
Certified Inspecteur Professionnel Certifié en Bâtiment membre de InterNACHI ACHI , Chapters - OntarioAchi et du M.I.C.Q (CPI) - (CHI)
OFFICE (514) 489-1887 MOBILE (514) 441-3732 TOLL FREE 1- 855-819-1816
Reply With Quote
Need a home inspection in New Mexico? Check out InterNACHI's listing of New Mexico certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #32  
Old 8/15/11, 5:16 PM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 19,798
Default Re: Floor joist cross bracing

Thanks Robert, now I just hope some will believe me when I tell them what you are telling us.
Reply With Quote
  #33  
Old 8/16/11, 12:43 PM
Robert J. OConnor's Avatar
Robert J. OConnor Robert J. OConnor is offline
InterNACHI Member
 
Join Date: Jul 2003
Location: Long Island, NY
Posts: 1,288
Default Re: Floor joist cross bracing

Quote:
Originally Posted by mcyr View Post
Thanks Robert, now I just hope some will believe me when I tell them what you are telling us.
Good luck with that ...

I had a tough time, and you guys know me. Maybe the NAHB/HUD design guide quote that references actual testing of joists with bridging ...

http://www.pathnet.org/si.asp?id=676



Robert O'Connor, PE
Consulting Engineer & Inspector
LIU CW Post Adjunct Professor
NACHI Education Committee
www.reporthost.com/-rjo

I am absolutely amazed sometimes by how much thought goes into doing things wrong ...
Reply With Quote
  #34  
Old 8/17/11, 1:16 AM
Kenton H. Shepard, CMI's Avatar
Kenton H. Shepard, CMI Kenton H. Shepard, CMI is offline
InterNACHI Member
 
Join Date: Aug 2004
Location: Boulder, CO
Posts: 3,417
Send a message via ICQ to kshepard
Default Re: Floor joist cross bracing

In 35 years of building (as a carpenter- later as a general contractor) I never heard of any floor system failing because it lacked anti-rotational devices like the bridging or midspan blocks discussed here. I can say from experience that one or the other device should definitely be installed if you want a floor to squeak. Forget glue... it won't help.




Kenton Shepard, InterNACHI member # 04082383
Certified Master Inspector (CMI)
InterNACHI Director of International Development
Director of Green Building

EXPERT WITNESS SERVICE
Conventional and Log homes

(303) 717-8940
Reply With Quote
  #35  
Old 8/17/11, 9:22 AM
Robert J. OConnor's Avatar
Robert J. OConnor Robert J. OConnor is offline
InterNACHI Member
 
Join Date: Jul 2003
Location: Long Island, NY
Posts: 1,288
Default Re: Floor joist cross bracing

Quote:
Originally Posted by kshepard View Post
I can say from experience that one or the other device should definitely be installed if you want a floor to squeak.
I agree ... there is a potential for floor squeaks anywhere there is wood to wood contact without both glue and screws.

Quote:
Originally Posted by kshepard View Post
Forget glue... it won't help.
The newer adhesives are a lot better ... local builders all swear by them. Combine that with screws and you have a really solid squeak-free install. I see it done wrong sometimes where the builder puts down adhesive on too many joists at once, and it starts to set up ... which can actually increase the likelihood of floor squeaks.

JMO & 2-Nickels ...



Robert O'Connor, PE
Consulting Engineer & Inspector
LIU CW Post Adjunct Professor
NACHI Education Committee
www.reporthost.com/-rjo

I am absolutely amazed sometimes by how much thought goes into doing things wrong ...
Reply With Quote
  #36  
Old 8/17/11, 6:35 PM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 19,798
Default Re: Floor joist cross bracing

Robert, here is one from APA, are they wrong too?


Squeaks and Bridging by APA
Reply With Quote
  #37  
Old 8/17/11, 6:49 PM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 19,798
Default Re: Floor joist cross bracing

And yet another here.

http://www.youtube.com/watch?v=0JjRhuxJMFA

and here;


American Forest and Paper Products

Last edited by mcyr; 8/17/11 at 7:28 PM..
Reply With Quote
  #38  
Old 8/18/11, 6:24 AM
Robert J. OConnor's Avatar
Robert J. OConnor Robert J. OConnor is offline
InterNACHI Member
 
Join Date: Jul 2003
Location: Long Island, NY
Posts: 1,288
Default Re: Floor joist cross bracing

Quote:
Originally Posted by mcyr View Post
Robert, here is one from APA, are they wrong too?
Not sure what you are referring to as that link to APA TN-C468N talks about bridging possibly causing squeaks, particularly if some load is transfered to the bridging (yes, a negligible amount can be transfered) and it's not securely nailed.

Here is a current APA Builders Tips guide on preventing floor squeaks ... http://www.apa-europe.org/Languages/.../PDF/Q300L.pdf. Installing bridging isn't included, as it can actually lead to squeaks.

Then ya have a home movie clip of Bubba building his own house where he "got my two by tens" with some of dem dare simpson bridging ... and of course ya have to "tack it with some nails" in order to get a "pretty tight floor system". Here is a clip of that same guy calculating how "tight" it's gonna be ... http://www.youtube.com/watch?v=oldOh..._order&list=UL ... OMG I must be completely wrong ...

What is the quote and page from the AFPA details guide are you referring to? I only see a reference to bridging on Page 7, which talks about installing that if a joist depth-thickness ratio exceeds 6.



Robert O'Connor, PE
Consulting Engineer & Inspector
LIU CW Post Adjunct Professor
NACHI Education Committee
www.reporthost.com/-rjo

I am absolutely amazed sometimes by how much thought goes into doing things wrong ...

Last edited by roconnor; 8/20/11 at 4:47 PM..
Reply With Quote
  #39  
Old 8/18/11, 5:43 PM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 19,798
Default Re: Floor joist cross bracing

Robert, it just seems that every where I look, Bridging is shown everywhere.
Is someone changing the history books showing that bridging is no longer a building standard or a requirement?
That is all I am trying to point out.
If I ever go out and tell a builder that he is wasting his time on installing bridging, I know he will look at me and ask if I came from another planet.
Reply With Quote
  #40  
Old 8/18/11, 8:38 PM
Robert J. OConnor's Avatar
Robert J. OConnor Robert J. OConnor is offline
InterNACHI Member
 
Join Date: Jul 2003
Location: Long Island, NY
Posts: 1,288
Default Re: Floor joist cross bracing

If a builder wants to install them thats fine. It cant hurt, as long as it's installed correctly so that it doesn't create floor squeaks.

But the bottom line is missing bridging is not even an issue worth mentioning on a home inspection.



Robert O'Connor, PE
Consulting Engineer & Inspector
LIU CW Post Adjunct Professor
NACHI Education Committee
www.reporthost.com/-rjo

I am absolutely amazed sometimes by how much thought goes into doing things wrong ...
Reply With Quote
  #41  
Old 8/18/11, 8:42 PM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 19,798
Default Re: Floor joist cross bracing

Well, to be honest, it never worried me either, unless I saw a problem or cause that would have required it. And if it did, it was usually undersized, overspanned.
Just trying to find a balance in the requirements. I test it one of these days and go from there.
Reply With Quote
  #42  
Old 8/19/11, 11:45 AM
Aaron J. Weaver's Avatar
Aaron J. Weaver Aaron J. Weaver is offline
InterNACHI Member
 
Join Date: Aug 2011
Location: Austin, TX
Posts: 5
Default Re: Floor joist cross bracing

Bridging 2006 IRC 502.7.1 - required when joists EXCEED a nominal 2x12 size.
That would be anything more than a 2x12 needs bridging, but a 2x12 does not.
I have never seen any 2x14 joists, but when I do, they will require bridging.

Its is not common practice here to do bridging.

Now, section 502.7 (2006 IRC) DOES require "Lateral restraint at supports" which is different. This section offers some ways to achieve this, and then the last sentence "or shall be otherwise provided with lateral support to prevent rotation" (THIS IS AT SUPPORTS)

How I interpret this is:

Bridging not required.

If I cannot prove the sub floor is attached in accordance with the "or shall be otherwise" sentence) then some lateral support "at supports" is required.

Bridging does not strengthen or stiffen a floor.
We do block between floor joists here to support a line load from a wall above.

If there is some way the requirements from 502.7 are met, and the joists are not larger than a 2x12- 502.7.1 is not a requirement. If you are using 502.7.1 to satisfy 502.7, then I would interpret this to mean it would have to be at the ends.

The code is the minimum, but it is also the standard.
Just because something is a good idea, doesn't make it a requirement.

This only my interpretation and understanding, I may very well be wrong-and I am always learning.

Not to open a can of worms, but there is another can in the ceiling section when discussing strong backs and rat runs.



International Code Council
Residential Combination Inspector
#8006170

Texas Real Estate Commision
Professional Inspector
#10225
Reply With Quote
  #43  
Old 8/19/11, 2:31 PM
JOSE C. FERRER JOSE C. FERRER is offline
InterNACHI Member
 
Join Date: Aug 2011
Posts: 1
Default Re: Floor joist cross bracing

I do reccommend that the botton gets nail aswell, as we all get older we all need more reinforcement.
Reply With Quote
Need a home inspection in New Mexico? Check out InterNACHI's listing of New Mexico certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #44  
Old 8/20/11, 10:43 AM
Erby Crofutt's Avatar
Erby Crofutt Erby Crofutt is offline
InterNACHI Member
 
Join Date: Sep 2002
Location: Georgetown, KY
Posts: 1,198
Default Re: Floor joist cross bracing

I'd agree with Robert IF the joists are smaller than 2x12.

What kicks me is the number of times I've seen them put in on 2x6, 2x8, 2x10 AND even 2x12 where they're nailed at the top but hanging loose at the bottom.

WHY bother putting them in if you're NOT going to finish the job. Just skip that step for crying out loud.
Reply With Quote
  #45  
Old 8/20/11, 6:02 PM
Sean Fogarty's Avatar
Sean Fogarty Sean Fogarty is offline
InterNACHI Member
 
Join Date: Sep 2009
Location: Somewhere in Knoxville TN flipping breakers
Posts: 2,267
Default Re: Floor joist cross bracing

Quote:
Originally Posted by ecrofutt View Post
I'd agree with Robert IF the joists are smaller than 2x12.

What kicks me is the number of times I've seen them put in on 2x6, 2x8, 2x10 AND even 2x12 where they're nailed at the top but hanging loose at the bottom.

WHY bother putting them in if you're NOT going to finish the job. Just skip that step for crying out loud.
Erby,
That's what I essentially see all the time. I wondered the same, why bother? WHich is why I asked. Good info for all.




Infraspection Institute Level 1 Certified Infrared Thermographer

Fogarty Inspection Services Group of Knoxville TN

Home inspections, Commercial Inspections, Thermal Imaging, Mold, Enviromental Testing and Radon Testing for Knoxville TN, Oak Ridge TN, Maryville, Clinton, Farragut, Lenoir City, Pigeon Forge, Sevierville and all the surrounding areas.

865-256-5397

www.homeinspectorknoxville.com

www.moldandradon.com

www.thermal-inspection.net

www.commercial-building-inspector.net
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Donation Ideas for Japan - Red Cross tspargo Miscellaneous Discussion for Inspectors 8 3/14/11 12:39 PM
Donate to The Haiti Red Cross jmckenna1 Miscellaneous Discussion for Inspectors 10 1/16/10 10:44 PM
Cross Bridges not fastened ... Ron Smith Structural Inspections 10 4/10/06 9:54 PM


All times are GMT -4. The time now is 3:00 PM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts