Default floor joist mechanical damage

Your thoughts regarding these floor joist(s) end bearing is appreciated and or including thoughts regarding repair etc. ie. sister entire joist or a section of the end bearing.

This house is new construction and has been passed by the city inspectors.

Obviously some of the 1.5" end bearing is damaged by toe nailing etc.
Attached Thumbnails
floor-joist-mechanical-damage-pict0158-small-.jpg.JPG
Views:	209
Size:	24.1 KB
ID:	36309   floor-joist-mechanical-damage-pict0165-small-.jpg.JPG
Views:	185
Size:	39.8 KB
ID:	36310   floor-joist-mechanical-damage-pict0173-small-.jpg.JPG
Views:	189
Size:	45.7 KB
ID:	36311  
Reply With Quote
Need a home inspection in Massachusetts? Check out InterNACHI's listing of Massachusetts certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 4/6/10, 6:56 PM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 19,798
Default Re: floor joist mechanical damage

If the members would have been installed per the industry standard, it would not be an issue.
Such minimum bearing as shown does not allow toenailing to prevent spliting. Although it will not go anywhere, it was not properly executed.

It should have been done like this which is typical for beam or bearing wall.
Attached Thumbnails
floor-joist-mechanical-damage-figure24big.gif  
Reply With Quote
  #3  
Old 4/6/10, 7:47 PM
Jeffery L. Haynes Jeffery L. Haynes is online now
InterNACHI Member
 
Join Date: Aug 2008
Location: Concord, NC
Posts: 3,494
Default Re: floor joist mechanical damage

Marcel,

I was just looking for a picture to show the overlap as well. Framing member will split at times which is why the overlap is needed. Yellow Pine is probably the worst.
Can't tell for sure but those nails look like 8d's.

Jeff
Reply With Quote
  #4  
Old 4/6/10, 8:07 PM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 19,798
Default Re: floor joist mechanical damage

Can't tell either Jeff, but something tells me that the span of the member might also have been exceeded, and that is why that happened.

CONNECTION - NAILING

1. Joist to sill or girder, toenail 3-8d
2. Bridging to joist, toenail each end 2-8d
3. 1" 6" (25 mm 152 mm) subfloor or less to each joist, face nail 2-8d
4. Wider than 1" 6" (25 mm 152 mm) subfloor to each joist, face nail 3-8d
5. 2" (51 mm) subfloor to joist or girder, blind and face nail 2-16d
6. Sole plate to joist or blocking, typical face nail 16d at 16" (406 mm) o.c.
Sole plate to joist or blocking, at braced wall panels 3-16d per 16" (406 mm)
7. Top plate to stud, end nail 2-16d
8. Stud to sole plate 4-8d, toenail or 2-16d, end nail
9. Double studs, face nail 16d at 24" (610 mm) o.c.
10.Doubled top plates, typical face nail 16d at 16" (406 mm) o.c.
Double top plates, lap splice 8-16d
11.Blocking between joists or rafters to top plate, toenail 3-8d
12.Rim joist to top plate, toenail 8d at 6" (152 mm) o.c.
13.Top plates, laps and intersections, face nail 2-16d
14.Continuous header, two pieces 16d at 16" (406 mm) o.c. along each edge
15.Ceiling joists to plate, toenail 3-8d
16.Continuous header to stud, toenail 4-8d
17.Ceiling joists, laps over partitions, face nail 3-16d
18.Ceiling joists to parallel rafters, face nail 3-16d
19.Rafter to plate, toenail 3-8d
20.1" (25 mm) brace to each stud and plate, face nail 2-8d
21.1" 8" (25 mm 203 mm) sheathing or less to each bearing, face nail 2-8d
22.Wider than 1" 8" (25 mm 203 mm) sheathing to each bearing, face nail 3-8d
23.Built-up corner studs 16d at 24" (610 mm) o.c.
24.Built-up girder and beams 20d at 32" (813 mm) o.c. at top and bottom and staggered 2-20d at
ends and at each splice
25.2" (51 mm) planks 2-16d at each bearing
26.Wood structural panels and particleboard:2 Subfloor and wall sheathing (to framing): 1/2" (12.7
mm) and less 6d 3


19/32"-3/4" (15 mm-19 mm) 8d
4 or 6d5
7/8"-1" (22 mm-25 mm) 8d


3
11/8"-11/4" (29 mm-32 mm) 10d


4 or 8d5
Combination subfloor-underlayment (to framing): 3/4" (19 mm) and less 6d


5
7/8"-1" (22 mm-25 mm) 8d5

Reply With Quote
  #5  
Old 4/6/10, 8:48 PM
Brian A. MacNeish Brian A. MacNeish is offline
Banned
 
Join Date: Apr 2007
Location: CANADA
Posts: 4,638
Please Note: Brian A. MacNeish is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: floor joist mechanical damage

Quote:
Originally Posted by mcyr View Post
Can't tell either Jeff, but something tells me that the span of the member might also have been exceeded, and that is why that happened.

CONNECTION - NAILING

1. Joist to sill or girder, toenail 3-8d
2. Bridging to joist, toenail each end 2-8d
3. 1" 6" (25 mm 152 mm) subfloor or less to each joist, face nail 2-8d
4. Wider than 1" 6" (25 mm 152 mm) subfloor to each joist, face nail 3-8d
5. 2" (51 mm) subfloor to joist or girder, blind and face nail 2-16d
6. Sole plate to joist or blocking, typical face nail 16d at 16" (406 mm) o.c.
Sole plate to joist or blocking, at braced wall panels 3-16d per 16" (406 mm)
7. Top plate to stud, end nail 2-16d
8. Stud to sole plate 4-8d, toenail or 2-16d, end nail
9. Double studs, face nail 16d at 24" (610 mm) o.c.
10.Doubled top plates, typical face nail 16d at 16" (406 mm) o.c.
Double top plates, lap splice 8-16d
11.Blocking between joists or rafters to top plate, toenail 3-8d
12.Rim joist to top plate, toenail 8d at 6" (152 mm) o.c.
13.Top plates, laps and intersections, face nail 2-16d
14.Continuous header, two pieces 16d at 16" (406 mm) o.c. along each edge
15.Ceiling joists to plate, toenail 3-8d
16.Continuous header to stud, toenail 4-8d
17.Ceiling joists, laps over partitions, face nail 3-16d
18.Ceiling joists to parallel rafters, face nail 3-16d
19.Rafter to plate, toenail 3-8d
20.1" (25 mm) brace to each stud and plate, face nail 2-8d
21.1" 8" (25 mm 203 mm) sheathing or less to each bearing, face nail 2-8d
22.Wider than 1" 8" (25 mm 203 mm) sheathing to each bearing, face nail 3-8d
23.Built-up corner studs 16d at 24" (610 mm) o.c.
24.Built-up girder and beams 20d at 32" (813 mm) o.c. at top and bottom and staggered 2-20d at
ends and at each splice
25.2" (51 mm) planks 2-16d at each bearing
26.Wood structural panels and particleboard:2 Subfloor and wall sheathing (to framing): 1/2" (12.7
mm) and less 6d 3

19/32"-3/4" (15 mm-19 mm) 8d
4 or 6d5

7/8"-1" (22 mm-25 mm) 8d


3

11/8"-11/4" (29 mm-32 mm) 10d


4 or 8d5

Combination subfloor-underlayment (to framing): 3/4" (19 mm) and less 6d


5
7/8"-1" (22 mm-25 mm) 8d5
GAWD!!! You guys are still calling nails by the very old English* designations and not by something plain and simple like "2+1/2 inch common nail". I guess it's a long, long way to metric!!

*From Wiki: "Some types of nails are sized in pennies (symbol, d), a system that originated in England centuries ago."............... I'm sure I read somewhere you folks threw the Brits out or something like that.

Last edited by Brian A. MacNeish; 4/7/10 at 5:41 AM..
Reply With Quote
  #6  
Old 4/7/10, 8:49 PM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 19,798
Default Re: floor joist mechanical damage

Quote:
Originally Posted by Brian A. MacNeish View Post
GAWD!!! You guys are still calling nails by the very old English* designations and not by something plain and simple like "2+1/2 inch common nail". I guess it's a long, long way to metric!!

*From Wiki: "Some types of nails are sized in pennies (symbol, d), a system that originated in England centuries ago."............... I'm sure I read somewhere you folks threw the Brits out or something like that.
I guess we are still old school Brian, but in todays world on th job, if I were to ask for a 20d they would look at me funny. So I ask for a 4" nail.
I wouldn't want to confuse them now would I.?

I took SI Metric back in 1972 and still waiting to use it.
Might be a while.
Reply With Quote
  #7  
Old 4/8/10, 10:20 PM
tneyedli1's Avatar
tneyedli1 tneyedli1 is offline
Active Poster
 
Join Date: Mar 2006
Location: Port Alberni, BC
Posts: 279
Please Note: tneyedli1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: floor joist mechanical damage

Quote:
Originally Posted by mnicholet View Post
Your thoughts regarding these floor joist(s) end bearing is appreciated and or including thoughts regarding repair etc. ie. sister entire joist or a section of the end bearing.

This house is new construction and has been passed by the city inspectors.

Obviously some of the 1.5" end bearing is damaged by toe nailing etc.
Mark:
A simple solution- Inform the client to.......
add a verticle doubled 2 X 4 onto the inside and gusset on the flush side.
An easy repair.

T.Neyedli CHI
www.alphahomeinspections.ca
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Shooting to begin on comprehensive new roofing courses kshepard Inspection Education & Training 4 11/7/09 2:59 PM
Snow Roof Damage Inspectors in Coeur d’Alene, ID 83815 rspriggs Ancillary Inspection Services & Additional Topics 0 1/9/09 3:23 AM
No "H" clips? jbreazeale Structural Inspections 7 5/17/07 2:28 PM


All times are GMT -4. The time now is 3:00 PM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts