Default Gaps in vapor barrier

Today I was in a crawl space and the vapor barrier that was just installed had large gaps down the middle and around the edges. I recommended that the vapor barrier should be continuous without gaps. The home owner called the contractor that installed it, btw is a large pest control chain. and they said they only cover 80-90 % of the crawl space to prevent it from getting too dry. I had never heard of this! All the research I have done says to overlap and seal the vapor barrier to the foundation etc.
Anyone ever hear of this? We live in an area with a high water table, moisture problems in crawls is common.
Reply With Quote
  #2  
Old 9/22/08, 7:21 PM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 14,008
Default Re: Gaps in vapor barrier

Quote:
Originally Posted by jsmith21 View Post
Today I was in a crawl space and the vapor barrier that was just installed had large gaps down the middle and around the edges. I recommended that the vapor barrier should be continuous without gaps. The home owner called the contractor that installed it, btw is a large pest control chain. and they said they only cover 80-90 % of the crawl space to prevent it from getting too dry. I had never heard of this! All the research I have done says to overlap and seal the vapor barrier to the foundation etc.
Anyone ever hear of this? We live in an area with a high water table, moisture problems in crawls is common.
The Contractor was full of BS.
You called it right Jon.

Well done.

Here is a little excerpt on the subject.

Control Moisture in Your Crawl Space

If your home has a crawl space, now is a good time to inspect it for any signs of moisture accumulation.
A surprising number of homes with moisture problems such as wet windows, mildew on the walls and ceiling, or damp attic insulation can trace their moisture source to a damp crawl space.

Every crawl space should have a ground moisture barrier installed over the bare soil.
A lot of moisture travels from the ground into the air, even in crawl spaces that appear to be dry.

Bare ground can also allow soil gases such as radon, petroleum vapors, or fertilizer residues to enter the home.
If you find bare ground in your crawl space, you should install a ground moisture barrier.
The most common type is a continuous sheet of polyethylene plastic. It can be either clear or black, and should be at least 6 mils (one mil = 1/1000 inch) thick so that it doesn't tear.
An even better option is reinforced polyethylene, a tough white material that is stronger than normal polyethylene.
Either type should be overlapped at the seams, and sealed with builder's tape or construction adhesive to create an airtight barrier. Cut your ground moisture barrier plenty big so it can be turned up the foundation walls a foot or two.
Seal these edges to the foundation with construction adhesive.
Here builders tape is used to seal the ground moisture barrier at a seam, at a post and at a tear in the plastic.

You'll need to find an access hatch into your crawl space, either from the outdoors or through the floor inside your home. Wear good protective clothing, and bring a bright light so you can see to all the far corners. Watch out for protruding nails or other sharp objects, bare wires, or parts of the structure that you could hit your head on.
If your home already has a ground moisture barrier, be sure it is in good condition. You may need to repair any holes or tears, seal the seams, and seal the edges to the foundation. Your home will be drier and healthier as a result of these labors.

Hope this helps a little.

Marcel



http://www.themainehomeinspector.com/
Serving all of Kennebec County and Central Maine
Cyr Home and Commercial Property Inspections

IAC2 Certified
http://co.nachi.org/inachiawards
Inachi 2009 US Member of the Year




Master Shingle Applicator
Shingle Technology
Ouellet Associaties Inc.
http://www.oaconstruction.com/
Reply With Quote
  #3  
Old 9/22/08, 10:05 PM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 6,342
Default Re: Gaps in vapor barrier

Quote:
Originally Posted by mcyr View Post
The Contractor was full of BS.
You called it right Jon.

Well done.
Marcel has his number...



____________________________________________
"An Education, not just an Inspection"

Larry Kage, CMI
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector and Infrared Thermographer serving the Traverse City, Michigan area and beyond.


ITC/FLIR CERTIFIED BUILDING SCIENCES THERMOGRAPHER

ITC/FLIR CERTIFIED LEVEL 1 THERMOGRAPHER
Reply With Quote
  #4  
Old 9/22/08, 10:39 PM
rbrady's Avatar
rbrady rbrady is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Eureka, CA
Posts: 619
Default Re: Gaps in vapor barrier

I had a pest contractor tell someone the exact same thing last week. I know I heard something about that before myself. I think it had something to do with being too dry for the wood floors.

We have a very moderate climate here, so I don't think it matters as much. I have NEVER seen a vapor barrier with sealed seams here.



"An expert is a person who has made all the mistakes that can be made in a very narrow field"
Niels Bohr

"Learn all you can from the mistakes of others. You won't have time to make them all yourself"
Alfred Sheinwold


Eureka, Fortuna & Arcata, CA
Reply With Quote
  #5  
Old 9/23/08, 2:52 AM
Mark Reusch Mark Reusch is offline
InterNACHI Member
 
Join Date: Aug 2006
Location: Simpsonville, SC
Posts: 463
Send a message via Yahoo to mreusch
Default Re: Gaps in vapor barrier

Quote:
Originally Posted by mcyr View Post
The Contractor was full of BS.
You called it right Jon.

Well done.

Here is a little excerpt on the subject.

Control Moisture in Your Crawl Space

If your home has a crawl space, now is a good time to inspect it for any signs of moisture accumulation.
A surprising number of homes with moisture problems such as wet windows, mildew on the walls and ceiling, or damp attic insulation can trace their moisture source to a damp crawl space.

Every crawl space should have a ground moisture barrier installed over the bare soil.
A lot of moisture travels from the ground into the air, even in crawl spaces that appear to be dry.

Bare ground can also allow soil gases such as radon, petroleum vapors, or fertilizer residues to enter the home.
If you find bare ground in your crawl space, you should install a ground moisture barrier.
The most common type is a continuous sheet of polyethylene plastic. It can be either clear or black, and should be at least 6 mils (one mil = 1/1000 inch) thick so that it doesn't tear.
An even better option is reinforced polyethylene, a tough white material that is stronger than normal polyethylene.
Either type should be overlapped at the seams, and sealed with builder's tape or construction adhesive to create an airtight barrier. Cut your ground moisture barrier plenty big so it can be turned up the foundation walls a foot or two.
Seal these edges to the foundation with construction adhesive.
Here builders tape is used to seal the ground moisture barrier at a seam, at a post and at a tear in the plastic.

You'll need to find an access hatch into your crawl space, either from the outdoors or through the floor inside your home. Wear good protective clothing, and bring a bright light so you can see to all the far corners. Watch out for protruding nails or other sharp objects, bare wires, or parts of the structure that you could hit your head on.
If your home already has a ground moisture barrier, be sure it is in good condition. You may need to repair any holes or tears, seal the seams, and seal the edges to the foundation. Your home will be drier and healthier as a result of these labors.

Hope this helps a little.

Marcel
Hey Marcel may I share this with some others? I love giving them little hints like this.
Reply With Quote
  #6  
Old 9/23/08, 11:51 AM
Vern Mitchinson's Avatar
Vern Mitchinson Vern Mitchinson is offline
InterNACHI Member
 
Join Date: Nov 2004
Location: Edmonton, Ab
Posts: 1,227
Default Re: Gaps in vapor barrier

Quote:
Originally Posted by mcyr View Post
The Contractor was full of BS.
You called it right Jon.

Well done.

Here is a little excerpt on the subject.

Control Moisture in Your Crawl Space

If your home has a crawl space, now is a good time to inspect it for any signs of moisture accumulation.
A surprising number of homes with moisture problems such as wet windows, mildew on the walls and ceiling, or damp attic insulation can trace their moisture source to a damp crawl space.

Every crawl space should have a ground moisture barrier installed over the bare soil.
A lot of moisture travels from the ground into the air, even in crawl spaces that appear to be dry.

Bare ground can also allow soil gases such as radon, petroleum vapors, or fertilizer residues to enter the home.
If you find bare ground in your crawl space, you should install a ground moisture barrier.
The most common type is a continuous sheet of polyethylene plastic. It can be either clear or black, and should be at least 6 mils (one mil = 1/1000 inch) thick so that it doesn't tear.
An even better option is reinforced polyethylene, a tough white material that is stronger than normal polyethylene.
Either type should be overlapped at the seams, and sealed with builder's tape or construction adhesive to create an airtight barrier. Cut your ground moisture barrier plenty big so it can be turned up the foundation walls a foot or two.
Seal these edges to the foundation with .
Here builders tape is used to seal the ground moisture barrier at a seam, at a post and at a tear in the plastic.

You'll need to find an access hatch into your crawl space, either from the outdoors or through the floor inside your home. Wear good protective clothing, and bring a bright light so you can see to all the far corners. Watch out for protruding nails or other sharp objects, bare wires, or parts of the structure that you could hit your head on.
If your home already has a ground moisture barrier, be sure it is in good condition. You may need to repair any holes or tears, seal the seams, and seal the edges to the foundation. Your home will be drier and healthier as a result of these labors.

Hope this helps a little.

Marcel
Regular Construction adhesive is not recommended because when it cures it does not stick to the poly. Acoustical sealent is the recommended product because it stays sticky for a long time. The rest of the statement is right on the money.



Vern Mitchinson CET CMI
Past President
International Association of Certified Home Inspectors. Alberta
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Gaps in Foundation Blocks rnewland Structural 12 7/18/08 7:26 PM
Wide gaps in outside deck railing jbanning Exterior 6 9/20/06 6:56 PM


All times are GMT -4. The time now is 3:59 AM.


Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts