Does anyone know if a garage connected to the home by roofline and an open breeze-way closed by a slider at one end is required to have drywall fire separation and a solid door?
Last edited by kgerhauser; 10/18/07 at 4:01 PM.. |
|
#2
|
||||
|
||||
|
What is the condition of the interior walls of the Garage (Framed and/or Drywall)?
Are Rooflines and Attics provided with adequate Fire separation? Joseph P. Hagarty, CMI joseph.hagarty@comcast.net Main Line Inspections, Inc. Phone: 610-399-3675 Email: MainLineHI@comcast.net http://pa.nachi.org/mainlinepa/about.html http://www.householdinspector.com National President / NACHI (2003-2004) NACHI Education Committee Member |
|
#3
|
||||
|
||||
|
1947/99 remodel framed, eave of garage connects to side of home, no roofline separation.
Last edited by kgerhauser; 10/18/07 at 4:55 PM.. |
|
#4
|
|||
|
|||
|
Please Note:
Richard A. Hetzel is a non-member guest and is in no way affiliated with InterNACHI or its members.
"The garage shall be separated from the residence and the attic area by not less than 1/2-inch gypsum board applied to the garage side."
That's from the 2003 International Residential Code. I think other versions will have similar or identical wording. The code anticipates either attached garages or separate garages, but not the arrangement pictured. I think if I were a code official, I would require at least a gypsum board ceiling and gypsum board on the common wall with the breezeway, which isn't really a breezeway any longer because of the closure at one end. However, the house pictured may pre-date any such code requirements, so if I were an inspector, I would write it as an area of concern and suggest that the homeowner consider installing the gypsum board for his or her own safety and peace of mind, with words such as "may not meet modern standards for garage fire safety". Leave the code interpretation to the local building official, where it belongs. |
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| "UFER" Ground? see last paragraph. | jtedesco1 | Electrical Inspections | 19 | 8/23/11 4:56 PM |
| Escape, Fire & Smoke Alarms | badair | Interior Inspections | 14 | 1/28/08 8:21 AM |
| Garage fire protection question | bwooddell | Structural Inspections | 10 | 6/23/07 7:52 PM |
| Garage fire rated wall | jlybolt | Interior Inspections | 3 | 6/18/06 7:21 PM |