Default Garage fire separation?

Does anyone know if a garage connected to the home by roofline and an open breeze-way closed by a slider at one end is required to have drywall fire separation and a solid door?
Attached Thumbnails
garage-fire-separation-front.jpg   garage-fire-separation-ext-stoop.jpg  

Last edited by kgerhauser; 10/18/07 at 4:01 PM..
Reply With Quote
  #2  
Old 10/18/07, 4:05 PM
Joseph Hagarty's Avatar
Joseph Hagarty Joseph Hagarty is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: Parkesburg, PA
Posts: 3,434
Default Re: Garage fire separation?

What is the condition of the interior walls of the Garage (Framed and/or Drywall)?

Are Rooflines and Attics provided with adequate Fire separation?



Joseph P. Hagarty
joseph.hagarty@comcast.net
Main Line Inspections, Inc.
Phone: 610-399-3675
Email: MainLineHI@comcast.net

http://pa.nachi.org/mainlinepa/about.html
http://www.householdinspector.com

National President / NACHI (2003-2004)
NACHI Education Committee Member
Reply With Quote
  #3  
Old 10/18/07, 4:08 PM
Karl E. Gerhauser's Avatar
Karl E. Gerhauser Karl E. Gerhauser is offline
InterNACHI Member
 
Join Date: Oct 2006
Location: Coos Bay, OR
Posts: 433
Default Re: Garage fire separation?

1947/99 remodel framed, eave of garage connects to side of home, no roofline separation.
Attached Thumbnails
garage-fire-separation-garage-fire-sep.jpg  

Last edited by kgerhauser; 10/18/07 at 4:55 PM..
Reply With Quote
  #4  
Old 10/18/07, 5:01 PM
Richard A. Hetzel Richard A. Hetzel is offline
Active Poster
 
Join Date: Apr 2007
Location: Tobyhanna, Pennsylvania
Posts: 596
Please Note: Richard A. Hetzel is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Garage fire separation?

"The garage shall be separated from the residence and the attic area by not less than 1/2-inch gypsum board applied to the garage side."

That's from the 2003 International Residential Code. I think other versions will have similar or identical wording. The code anticipates either attached garages or separate garages, but not the arrangement pictured. I think if I were a code official, I would require at least a gypsum board ceiling and gypsum board on the common wall with the breezeway, which isn't really a breezeway any longer because of the closure at one end. However, the house pictured may pre-date any such code requirements, so if I were an inspector, I would write it as an area of concern and suggest that the homeowner consider installing the gypsum board for his or her own safety and peace of mind, with words such as "may not meet modern standards for garage fire safety". Leave the code interpretation to the local building official, where it belongs.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
"UFER" Ground? see last paragraph. jtedesco1 Electrical 6 9/15/08 8:57 AM
Escape, Fire & Smoke Alarms badair Interior 14 1/28/08 8:21 AM
Garage fire protection question bwooddell Structural 10 6/23/07 7:52 PM
Garage fire rated wall jlybolt Interior 3 6/18/06 7:21 PM


All times are GMT -4. The time now is 11:27 AM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts