If a firewall is required between the garage and the house, why is it I seldom see one? Did a 3 year old townhouse this week and there was no separation at all. (Behind the studs in the attached photo is the attached garage.)
What exactly should the separation be composed of? Sheetrock? That black wall board? Should the material have any special identification??? If there is any opening at all, that would be a concern right? I see the firewalls all the time between condo/townhome units, but I hardly ever see it between the house and garage. When did that rule come into being? If the house is a 1973 job, like my mother's, was the code applicable then? Would you recommend installation of the firewall to an older home?
Joe Funderburk, CMI Alpha & Omega Home Inspections, LLC Inspecting Upstate SC & Charlotte Metro, NC NACHI ID: NACHI05120170 www.aohomeinspection.com |
|
#2
|
||||
|
||||
|
Joe,
The wall separating the garage from the house needs to have 1/2-inch-thick (one hour rating) gypsum board on the garage side using Type X gypsum board, as well as fire tape (in some juridictions) to seal joints on drywall and gypsum board. If there is any habitable space above the garage, (which in your case-there's not) 1/2-inch gypsum board is required on the garage ceiling. In addition, all of the supporting walls need to be clad with 1/2-inch gypsum board. Basically, you should see a fire-rated floor-to-ceiling assembly. When the soffit area of the garage and the house are common, the fire wall shall extend through the soffit. |
|
#3
|
||||
|
||||
|
Quote:
|
|
#4
|
||||
|
||||
|
Quote:
Safety of human life doesn't have a date.... |
|
#5
|
|||
|
|||
|
Quote:
|
|
#6
|
||||
|
||||
|
How 'bout this barrier? The board says "Caution: May smolder or burn if ignited."
How do I find out if the gypsum board you mentioned is "Type X"? Where is the label when I see it installed on a wall already?
Joe Funderburk, CMI Alpha & Omega Home Inspections, LLC Inspecting Upstate SC & Charlotte Metro, NC NACHI ID: NACHI05120170 www.aohomeinspection.com |
|
#7
|
||||
|
||||
|
David, where you mentioned soffit area, that should read attic area...
B.A. King Home Inspections, LLC www.BAKingHomeInspections.com Serving Charlotte NC area and Rock Hill SC areas. CMI Certified Master Inspector and Independent 704 301-3207 |
|
#8
|
|||
|
|||
|
Quote:
|
|
#9
|
||||
|
||||
|
Last edited by mboyett; 4/9/09 at 10:37 PM.. |
|
#10
|
||||
|
||||
|
Quote:
|
|
#11
|
||||
|
||||
|
Quote:
When the soffit area of the garage and the house are common, the fire wall shall extend through the soffit. In other words, No gaps should be visible period. |
|
#12
|
|||
|
|||
|
Quote:
|
|
#13
|
||||
|
||||
|
Quote:
I'm simply referring to a home inspection. I was off by an eigth of an inch but I'm quite sure the manufacturers won't be. |
|
#14
|
|||
|
|||
|
Please Note:
ckratzer is a non-member guest and is in no way affiliated with InterNACHI or its members.
5/8 type x fire rated as already mentioned.
Its always stamped on the edge.You just can't see it once it's mudded and taped. However if there is a door between the garage and living space the door jamb will be a bit wider , to accept 1/2" on one side and 5/8" on the garage side,than any other entry jamb in the house if fire rock is present.One also needs to know if the framing is 2 x 4 or 6 to make an accurate assesment. One may also be able to tell at an outlet or switch minus it's cover if it isn't fitted to snuggly to the rock. okay....my knife is out and I'm lying on the pointy end... go ahead somebody jump on me. |
|
#15
|
||||
|
||||
|
One more opinion:
The difference between 1/2" and 5/8" rock? (aside from the fire-rating) 5/8" is alot heavier.....well 25% heavier, harder to carry, harder to cut, harder to hang. My opinion from a builder's perspective, 1/2" rock doesn't work so well on a stud wall or ceiling that is framed at 2' O.C. When you feel that the wall-board is wobbly, or when you see that it has sagged from the ceiling at regular 2' intervals, it could be because it is 1/2" rock instead of 5/8", hung on 2' centers. Ed |
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| Evaporative cooler in garage | chellickson | HVAC | 9 | 7/23/07 1:08 AM |
| Plywood/sheetrock garage firewall | Al Barb | Interior | 4 | 2/16/07 12:47 AM |
| Giant hole in the garage firewall for HVAC VENTS | mpeterson | Structural | 14 | 2/3/07 6:54 AM |