Hey Guys-

This beam was in the garage of a split-level (kind of) style home with a living space above it. The beam was (3) 2x8s and the span was 22'. However, on the inside wall, the beam sat directly above the door to the house and there wasn't any other structural support for about another 10' into the house where the next wall sits. Directly inside the garage door to the right is the stairs to go to the upper level. Do you think they ran that all they way to that next wall? What's supporting the beam? Thanks.

Kenny
Attached Thumbnails
garage-support-beam-gedc8548.jpg   garage-support-beam-gedc8576l.jpg   garage-support-beam-gedc8577.jpg  



Rigler Home Inspections
Hays, KS 67601
785-656-0272

Last edited by krigler; 1/21/12 at 7:16 PM..
Reply With Quote
Need a home inspection in Minnesota? Check out InterNACHI's listing of Minnesota certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 1/21/12, 7:30 PM
Randy L. Mayo, PE's Avatar
Randy L. Mayo, PE Randy L. Mayo, PE is offline
InterNACHI Member
 
Join Date: May 2006
Location: Rolla, MO
Posts: 372
Default Re: Garage Support Beam

Kenny

With out knowing the loads involved its difficult to help. Main beams made from 2x12 carrying typical floor loads usually span about 12 feet. Is it possible someone removed a support post from the center of the garage? That piece of sheet metal on the bottom of the beam, would that happen to be in the middle of the garage?





Randy Mayo, P.E.

573-201-8162

www.rlmengineers.com
Reply With Quote
  #3  
Old 1/21/12, 8:28 PM
Kenny Rigler Kenny Rigler is offline
InterNACHI Member
 
Join Date: Apr 2009
Location: Hays, KS
Posts: 255
Default Re: Garage Support Beam

Quote:
Originally Posted by rmayo View Post
Kenny

With out knowing the loads involved its difficult to help. Main beams made from 2x12 carrying typical floor loads usually span about 12 feet. Is it possible someone removed a support post from the center of the garage? That piece of sheet metal on the bottom of the beam, would that happen to be in the middle of the garage?
I didn't consider that, but yes it was about in the middle.



Rigler Home Inspections
Hays, KS 67601
785-656-0272
Reply With Quote
  #4  
Old 1/21/12, 9:32 PM
KEVIN WOOD's Avatar
KEVIN WOOD KEVIN WOOD is online now
InterNACHI Member
 
Join Date: Mar 2006
Location: Sault Ste Marie ON
Posts: 3,112
Default Re: Garage Support Beam

Randy there should also be a full support at the end of this 22 ft beam, so this is double wrong. According to a proper practice the (3) 2x8s need to be supported by (3) 2x8s It can be off by what is pictured but the wall would need to be more than 7 inches or have a steel column and the header would need the same, it is not likely this was done.



THE RIGHT TRAK
CIAQP, IAC2
Certified Master Inspector
kwoodinspections@hotmail.com
www.kwood.inspectorpages.com www.homegauge.com/shgi/THERIGHTTRAKIAQ
www.linkedin.com/in/kevinwoodiaq
OOVOO account kwoodinspections
Cell: 705-971-2096
Ph : 705-946-2676
Reply With Quote
  #5  
Old 1/21/12, 11:30 PM
Randy L. Mayo, PE's Avatar
Randy L. Mayo, PE Randy L. Mayo, PE is offline
InterNACHI Member
 
Join Date: May 2006
Location: Rolla, MO
Posts: 372
Default Re: Garage Support Beam

Kevin

The column support does not have to be 2x8s. Three 2x4 if properly supported can hold a significant amount of weight as a column. If you look closely at your first picture just behind the sheet metal on that beam I can see where some type of support column may have been. I would just call it out as a potential structural issue. The burden of proof then falls on the home owner to prove otherwise.





Randy Mayo, P.E.

573-201-8162

www.rlmengineers.com
Reply With Quote
  #6  
Old 1/21/12, 11:47 PM
Joseph Hagarty,  CMI's Avatar
Joseph Hagarty, CMI Joseph Hagarty,  CMI is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: Parkesburg, PA
Posts: 5,636
Default Re: Garage Support Beam

In addition to the modified Beam
- You have HVAC ducting passing unprotected (which indicates Living Space above). This indicates improper fire separation between home and garage.
- Insulation improperly installed
- Receptacles missing covers



Joseph P. Hagarty
joseph.hagarty@comcast.net
Main Line Inspections, Inc.
Phone: 610-399-3675
Email: MainLineHI@comcast.net

http://pa.nachi.org/mainlinepa/about.html
http://www.householdinspector.com

National President / NACHI (2003-2004)
NACHI Education Committee Member
Reply With Quote
  #7  
Old 1/22/12, 8:45 AM
KEVIN WOOD's Avatar
KEVIN WOOD KEVIN WOOD is online now
InterNACHI Member
 
Join Date: Mar 2006
Location: Sault Ste Marie ON
Posts: 3,112
Default Re: Garage Support Beam

Yes Randy that is a good point and is possible. When I have seen this type of situation it is sometimes under supported by (2) 2x4s in the wall and I would still put a note if there where (3).
The post removed was probably a 8x8 wood post.
Joseph that is correct and the third picture confirms the breach.



THE RIGHT TRAK
CIAQP, IAC2
Certified Master Inspector
kwoodinspections@hotmail.com
www.kwood.inspectorpages.com www.homegauge.com/shgi/THERIGHTTRAKIAQ
www.linkedin.com/in/kevinwoodiaq
OOVOO account kwoodinspections
Cell: 705-971-2096
Ph : 705-946-2676
Reply With Quote
  #8  
Old 1/23/12, 2:16 PM
Kenny Rigler Kenny Rigler is offline
InterNACHI Member
 
Join Date: Apr 2009
Location: Hays, KS
Posts: 255
Default Re: Garage Support Beam

Thanks guys. There were several issues with the electrical and firewall separation. The main beam setting above the doorway just really surprised me.



Rigler Home Inspections
Hays, KS 67601
785-656-0272
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
attached garage ghelder General Inspection Discussion 5 2/23/10 5:40 PM
Garage floor same level as house a safety concern? thorn2 General Inspection Discussion 11 1/25/10 3:33 PM
Garage door inspection procedure bgromicko General Inspection Discussion 5 8/7/09 12:47 PM
Inadequate garage support post? jfunderburk Structural Inspections 29 8/7/09 1:17 AM
Steel beam lateral support Mark Ellison Structural Inspections 10 1/16/07 10:40 PM


All times are GMT -4. The time now is 3:05 PM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts