Default Gas Fireplace

I did an inspection yesterday that included a fireplace. The fireplace was a traditional gas fireplace with a log set. Screened front, no doors installed. No flue to the exterior or damper installed. The top of the firebox was factory sealed. There was a gas valve but there was no gas to the fireplace. There was no way to exhaust gas in case it was left on. The home is 24 years old and the fireplace appears to have never been used. Is this an acceptable set up, or was the installation not completed? It doesn't feel right to me. What do you think? Stan
Reply With Quote
Find an InterNACHI certified Delaware Home Inspector (and anywhere else in North America)
  #2  
Old 10/31/09, 9:05 AM
Wayne B. Wilson's Avatar
Wayne B. Wilson Wayne B. Wilson is online now
InterNACHI Member
 
Join Date: Aug 2008
Location: Powell, Tn
Posts: 8,230
Default Re: Gas Fireplace

Stan it is most likely a Vent less fireplace. Check with your area to see if they are allowed.
Reply With Quote
  #3  
Old 10/31/09, 9:47 AM
Stan Croenne Stan Croenne is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: Springfield, IL
Posts: 60
Default Re: Gas Fireplace

Thanks for the reply Wayne. I will check. I guess my main concern is if the gas were left on, it would not be exhausted to the exterior. Stan.
Reply With Quote
  #4  
Old 10/31/09, 10:06 AM
Doug Edwards's Avatar
Doug Edwards Doug Edwards is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Florida panhandle
Posts: 4,846
Default Re: Gas Fireplace

That would be true for any gas appliance inside the home. Gas space heaters have been around since Col Sanders was a corporal and they too do not have any venting capabilities. As recommended, check with local authority. I see vent free gas logs in just such a set up as you described all the time.



"War is an ugly thing, but not the ugliest of things; the decayed and degraded state of moral and patriotic feeling which thinks nothing is worth a war, is worse. A man who has nothing which he cares more about than he does about his personal safety is a miserable creature who has no chance at being free, unless made and kept so by the exertions of better men than himself."

- John Stuart Mill







Reply With Quote
  #5  
Old 10/31/09, 10:54 AM
James H. Bushart's Avatar
James H. Bushart James H. Bushart is offline
InterNACHI Member
 
Join Date: Dec 2004
Location: Southwest Missouri
Posts: 20,950
Default Re: Gas Fireplace

One of the many dangers with these so-called "ventless" fireplaces (for they ALL vent into the living space) is the logs. There are logs that are made for gas fireplaces...and there are logs made for gas ventless fireplaces...and cannot be mixed.



James H. Bushart

Professional Building Analyst, BPI
Missouri, Kansas and Arkansas
314-803-2167
Reply With Quote
  #6  
Old 10/31/09, 11:36 AM
Stan Croenne Stan Croenne is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: Springfield, IL
Posts: 60
Default Re: Gas Fireplace

Thanks for your help. Stan
Reply With Quote
  #7  
Old 11/1/09, 1:22 PM
dhelm's Avatar
dhelm dhelm is offline
InterNACHI Member
 
Join Date: Mar 2005
Location: Bellingham, Wa
Posts: 704
Default Re: Gas Fireplace

You really should check your jurisdiction too. I know that here, ventless fireplaces are illegal.



Helm Home Inspection
David Helm, Owner/Inspector
http//www.helmhomeinspections.com
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Hearth size??? jcampbell Inspecting HVAC Systems 32 6/1/08 1:56 PM
The Rumford Fireplace: Safety vs. Efficiency mbryan Interior Inspections 2 4/28/08 4:38 PM
Difficult Chimneys thance Inspecting HVAC Systems 2 1/29/08 8:16 PM


All times are GMT -4. The time now is 10:51 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts