Default Giant hole in the garage firewall for HVAC VENTS

Hey Everybody
I saw this yesterday the AC/Furnace were on the outside of the house in a small addition built for that reason. The problem is that the vents now run through the garage attic through the fire wall into the main house attic. Is this OK?
Attached Thumbnails
giant-hole-garage-firewall-heating-venting-air-conditioning-vents-new-nachi-pic.jpg  
Reply With Quote
  #2  
Old 1/31/07, 2:34 PM
James H. Bushart's Avatar
James H. Bushart James H. Bushart is offline
InterNACHI Member
 
Join Date: Dec 2004
Location: Southwest Missouri
Posts: 20,489
Default Re: Giant hole in the garage firewall for HVAC VENTS

No...and that wiring really sucks, too.



James H. Bushart

Professional Building Analyst, BPI
Missouri, Kansas and Arkansas
314-803-2167
Inspecting in Aurora, Branson, Carthage, Granby, Joplin, Kimberling City, Monett, Mount Vernon, Neosho, Nixa, Purdy, Reed Spring, Republic, Springfield and surrounding areas.

Reply With Quote
  #3  
Old 1/31/07, 2:41 PM
Michael Peterson Michael Peterson is offline
InterNACHI Member
 
Join Date: Nov 2005
Location: Ramona, Ca
Posts: 29
Default Re: Giant hole in the garage firewall for HVAC VENTS

Yea I think that it was someone trying to flip this place. The electrical in this pic was nice compared to the rest of the house I dont think that anything was done right.
Reply With Quote
  #4  
Old 1/31/07, 11:10 PM
wsiegel wsiegel is offline
Active Poster
 
Join Date: Oct 2006
Location: Hialeah, Fl
Posts: 2,542
Please Note: wsiegel is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Giant hole in the garage firewall for HVAC VENTS

I see that all the time. I write it up as a breach in the fire wall. The wall needs to be properly sealed and fire caulked by a licensed contractor.

It covers my arse, but I can bet you that no one has ever repaired one of those breaches.
Reply With Quote
  #5  
Old 1/31/07, 11:16 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 7,760
Default Re: Giant hole in the garage firewall for HVAC VENTS

There's so many other things wrong, but to your question, if the ceiling of the garage is fire-rated, it's okay. Was the garage ceiling drywalled?



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #6  
Old 2/1/07, 1:30 AM
Michael Peterson Michael Peterson is offline
InterNACHI Member
 
Join Date: Nov 2005
Location: Ramona, Ca
Posts: 29
Default Re: Giant hole in the garage firewall for HVAC VENTS

The ceiling is drywalled. Does that create the proper firebreak? I talked to my HVAC guy and he said that it is really common here (first time I have seen it) and that as long as the vent passing through is metal that it is ok because it wont carry a flame but he talking about commercial property and couldn't give me a straight answer about residential.

Last edited by mpeterson; 2/1/07 at 1:32 AM.. Reason: Changing the font
Reply With Quote
  #7  
Old 2/1/07, 3:22 AM
jhugenroth jhugenroth is offline
InterNACHI Member
 
Join Date: May 2004
Location: Fresno, CA
Posts: 1,152
Please Note: jhugenroth is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Giant hole in the garage firewall for HVAC VENTS

Quote:
Originally Posted by mpeterson
The ceiling is drywalled. Does that create the proper firebreak?
Yes, if there are no openings in the drywall.
Reply With Quote
  #8  
Old 2/1/07, 8:04 AM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,684
Default Re: Giant hole in the garage firewall for HVAC VENTS

Here's an illustration of what you should have in the garage...

"Click to Enlarge"
Attachment 8847

Last edited by dvalley; 10/7/07 at 5:42 PM..
Reply With Quote
  #9  
Old 2/1/07, 12:31 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 7,760
Default Re: Giant hole in the garage firewall for HVAC VENTS

Quote:
Originally Posted by mpeterson
The ceiling is drywalled. Does that create the proper firebreak? I talked to my HVAC guy and he said that it is really common here (first time I have seen it) and that as long as the vent passing through is metal that it is ok because it wont carry a flame but he talking about commercial property and couldn't give me a straight answer about residential.
Boy, could you make that any smaller?

Your "HVAC guy" either didn't understand the condition, or doesn't know what he's talking about.

If the attic space is separated from the garage with a rated assembly, then the duct has not compromised the "firewall."



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #10  
Old 2/1/07, 1:31 PM
gnovian gnovian is offline
InterNACHI Member
 
Join Date: Jul 2006
Location: Ventura, CA
Posts: 21
Default Re: Giant hole in the garage firewall for HVAC VENTS

wow......continues to amaze me on the things we see......firewall needs to be address along with the electrical issues
Reply With Quote
  #11  
Old 2/1/07, 2:38 PM
Robert M. Anaya Robert M. Anaya is offline
InterNACHI Member
 
Join Date: Mar 2005
Location: Yorktown, VA
Posts: 11
Default Re: Giant hole in the garage firewall for HVAC VENTS

I agree with Jeff. If their is no breach in the garage ceiling and the sheetrock is of the right fire rating, then there is no breach in the firewall.
Reply With Quote
  #12  
Old 2/1/07, 4:40 PM
brepanshek brepanshek is offline
Active Poster
 
Join Date: May 2006
Location: York, PA
Posts: 235
Please Note: brepanshek is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Giant hole in the garage firewall for HVAC VENTS

I totally agree with Jeff, I think that junction box is rated for up to 25 conductors, just missing coverplate
Reply With Quote
  #13  
Old 2/1/07, 5:30 PM
Michael Peterson Michael Peterson is offline
InterNACHI Member
 
Join Date: Nov 2005
Location: Ramona, Ca
Posts: 29
Default Re: Giant hole in the garage firewall for HVAC VENTS

Thanks Everybody

That was a huge help. You guys should have seen the rest of the electrical
Reply With Quote
  #14  
Old 2/3/07, 12:36 AM
thejnicki's Avatar
thejnicki thejnicki is offline
InterNACHI Member
 
Join Date: Dec 2004
Location: Vacaville, CA
Posts: 251
Default Re: Giant hole in the garage firewall for HVAC VENTS

Flex duct work cannot pass through any type of firewall, some jurisdictions allow ridid ducts, others require a damper.
Reply With Quote
  #15  
Old 2/3/07, 6:54 AM
Bruce M. Graham, III's Avatar
Bruce M. Graham, III Bruce M. Graham, III is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Gainesville, FL
Posts: 2,025
Default Re: Giant hole in the garage firewall for HVAC VENTS

If the ceiling was intact that was not a fire wall, Ok so how many of you have seen fire rated pull down stairs, I have only seen two. The AHJ is on the fence with this but I right it up every time.



Bungalows to Mansions
Professional Inspection Services, LLC dba
1st Inspection Services
Bruce M. Graham III
Gainesville, FL 32608
352 871 8989
Florida Licensed Home Inspector #HI10
NACHI05091592
ICC 5268478
www.1stinspectionsfl.com
www.bungalowstomansions.com
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Garage air vents rnapper Structural Inspections 6 9/29/11 5:09 PM
Garage Firewall jfunderburk Structural Inspections 19 4/9/06 8:23 PM


All times are GMT -4. The time now is 9:50 PM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts