Default Girder end bearing

I had a new house today that had a steel "I" beam resting in a pocket on a poured concrete foundation wall. I could not verifiy 3" of bearing or ventilation as builder sealed the opening with mortar.

My question: Is there supposed to be 1/2" ventilation around steel or wood girder end bearings?
I can not find the 1/2" Vetilation anywhere in the06' IRC.
Am i correct in that thought?
I recall reading that somewhere.

Thank you



Michael J. Ashburn
Ashburn Inspections
724-838-1665 / 412-856-1665

Last edited by mashburn; 2/6/08 at 7:29 AM..
Reply With Quote
  #2  
Old 11/3/07, 6:00 PM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is online now
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 12,362
Default Re: Girder end bearing

I don't really see anything wrong here, but most likely over the years, the mortar will crack and might spall off due to the expansion and contraction of the steel. Since the beam has a primer on it, it should not be a problem.

The biggest thing would be bearing, but then you can't inspect it so note it as such.

Marcel





Cyr Home and Commercial Property Inspections

IAC2 Certified
NACHI04070211
http://co.nachi.org/inachiawards


Commercial Builder
CertainTeed
Master Shingle Applicator
Shingle Technology
Ouellet Associaties Inc.
http://www.oaconstruction.com/
Reply With Quote
  #3  
Old 11/3/07, 9:54 PM
Richard A. Hetzel Richard A. Hetzel is offline
Active Poster
 
Join Date: Apr 2007
Location: Tobyhanna, Pennsylvania
Posts: 596
Please Note: Richard A. Hetzel is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Girder end bearing

One would have to know the design load carried by the girder in order to know what amount of bearing was required, and one would also have to know whether a bearing plate sufficient to transfer the load to the concrete was provided. Since these items cannot be verified, do what Marcel said.
Reply With Quote
  #4  
Old 11/4/07, 8:13 AM
Michael J. Ashburn's Avatar
Michael J. Ashburn Michael J. Ashburn is offline
InterNACHI Member
 
Join Date: May 2006
Location: Greensburg, PA
Posts: 280
Default Re: Girder end bearing

Thank you, I did note that verbally and in the report that it was not able to be inspected.
The question I have now is, are end-bearing beams required to have 1/2" space around bearing pocket for ventilation.
Any comments
Thank you again.



Michael J. Ashburn
Ashburn Inspections
724-838-1665 / 412-856-1665
Reply With Quote
  #5  
Old 11/4/07, 8:22 AM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,022
Default Re: Girder end bearing

Quote:
Originally Posted by mashburn
Thank you, I did note that verbally and in the report that it was not able to be inspected.
The question I have now is, are end-bearing beams required to have 1/2" space around bearing pocket for ventilation.
Any comments
Thank you again.
Michael,

No, Steel beams do not require air gaps at the bearing end. That steel beam install is fine.

"Click to Enlarge"
girder-end-bearing-beam-steel-support.jpgsupport.JPG
Views:	37
Size:	72.7 KB
ID:	15797


Wood beams do require air gaps due to rotting.

"Click to Enlarge"
girder-end-bearing-beam_pocket.jpg

If the cavity is too big, I always recommend wedging in this pocket to prevent twisting of the beam.
Reply With Quote
  #6  
Old 11/4/07, 8:25 AM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is online now
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 12,362
Default Re: Girder end bearing

Quote:
Originally Posted by mashburn
Thank you, I did note that verbally and in the report that it was not able to be inspected.
The question I have now is, are end-bearing beams required to have 1/2" space around bearing pocket for ventilation.
Any comments
Thank you again.
Typically, the beams wood or steel are always left open, and insulated later if the basement gets finished.
Some foundation contractors use something like this to create the beam pocket.



Beam Pocket

The Beam Pocket is a reusable tapered steel boxout that leaves a void pocket at the top of the foundation wall for steel or wooden beams. The standard 6 x 8 x 4 deep size comes with a handle for easy carrying and removal.







Marcel




Cyr Home and Commercial Property Inspections

IAC2 Certified
NACHI04070211
http://co.nachi.org/inachiawards


Commercial Builder
CertainTeed
Master Shingle Applicator
Shingle Technology
Ouellet Associaties Inc.
http://www.oaconstruction.com/
Reply With Quote
  #7  
Old 11/4/07, 8:35 AM
Michael J. Ashburn's Avatar
Michael J. Ashburn Michael J. Ashburn is offline
InterNACHI Member
 
Join Date: May 2006
Location: Greensburg, PA
Posts: 280
Default Re: Girder end bearing

Thank you for the clarification Marcel and David.
I appreciate your help.
The buyers father is a contractor and we both had the thinking that even steel beams needed a small gap for venting.

David, who's did the illustrations are those? Carson Dunlap?



Michael J. Ashburn
Ashburn Inspections
724-838-1665 / 412-856-1665
Reply With Quote
  #8  
Old 11/4/07, 8:50 AM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,022
Default Re: Girder end bearing

Quote:
Originally Posted by mashburn
David, who's did the illustrations are those? Carson Dunlap?
Yes.....Here
Reply With Quote
  #9  
Old 11/4/07, 4:10 PM
afrost afrost is offline
Active Poster
 
Join Date: Jan 2007
Location: Conway, NH
Posts: 356
Please Note: afrost is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Girder end bearing

Quote:
Originally Posted by dvalley

If the cavity is too big, I always recommend wedging in this pocket to prevent twisting of the beam.
wedging with wood can allow the moisture in the concrete to leach into the wood wedge and the beam. wood needs to be isolated from concrete (or be pressure treated) so the wood beam should have something to isolate the wood from the concrete - like a pice of 30# felt.

as far as twising goes, solid blocking or bridging is used to prevent twisting of beams and joists.
Reply With Quote
  #10  
Old 11/4/07, 4:30 PM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,022
Default Re: Girder end bearing

Quote:
Originally Posted by afrost
wedging with wood can allow the moisture in the concrete to leach into the wood wedge and the beam. wood needs to be isolated from concrete (or be pressure treated) so the wood beam should have something to isolate the wood from the concrete - like a pice of 30# felt.

as far as twising goes, solid blocking or bridging is used to prevent twisting of beams and joists.
Wedging with block or 2X4 is what I was referring to. How's someone going to find an angle at that location.

So you're telling me that if you see a wood beam with no felt protection, you're going to write that up?

Give me a break.....
Reply With Quote
  #11  
Old 11/4/07, 4:52 PM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is online now
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 12,362
Default Re: Girder end bearing

David;
I think he must have seen fig. 16 on this link.

http://www.fpl.fs.fed.us/documnts/us...73chapter2.pdf

Typically, framers around here leave the pocket a little lower than the size of the beam to be installed and latter install pressure treated lumber to the proper elevation.

This little felt game is a little to much expected for builders to even think about.

And yes to ventilation, because I never see any of these beams pockets filled in and if I would, it would be called out as unable to verify bearing and potential to wood rot due to moisture being wicked in and the condensation on the end of the beam suseptable due being so close to the exterior extremities of the foundation face exterior.

How's that Dave? will that help them? ha. ha.

Marcel




Cyr Home and Commercial Property Inspections

IAC2 Certified
NACHI04070211
http://co.nachi.org/inachiawards


Commercial Builder
CertainTeed
Master Shingle Applicator
Shingle Technology
Ouellet Associaties Inc.
http://www.oaconstruction.com/
Reply With Quote
  #12  
Old 11/4/07, 11:44 PM
Kenton H. Shepard, CMI's Avatar
Kenton H. Shepard, CMI Kenton H. Shepard, CMI is offline
InterNACHI Member
 
Join Date: Aug 2004
Location: Boulder, CO
Posts: 2,487
Send a message via ICQ to kshepard
Default Re: Girder end bearing

Here's one with plenty of air flow. Friday's inspection.




Kenton Shepard, InterNACHI member # 04082383
Certified Master Inspector (CMI)
EXPERT WITNESS

Director of Green Building
Director for International Development

(303) 717-8940
(303) 258-8289


Last edited by kshepard; 10/2/08 at 2:38 AM..
Reply With Quote
  #13  
Old 11/5/07, 12:15 AM
William J. Decker's Avatar
William J. Decker William J. Decker is offline
InterNACHI Member
 
Join Date: Nov 2004
Location: Skokie, IL
Posts: 6,526
Default Re: Girder end bearing

steel girders can be grouted. The grouting will cause (eventually) rusting of the beam end, but not for a Looong time.

Wood beams should be ventilated.



Will Decker, CMI
ILL License # 450.0002240
Board Certified Master Inspector
Decker Home Services, LLC
Chicago and Northern Suburban Home Inspections
Office: (847) 676-8393
Cell: (847) 609-2345
Home: (847) 673-2702

wjd@DeckerHomeServices.com
www.DeckerHomeServices.com

Learn, Educate, Serve and have fun doing it!
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Where do I put the Aquarium? mcyr Structural 3 11/6/07 4:05 PM
Bearing wall support modifications bwooddell Structural 1 5/18/07 12:44 PM
Insufficient end bearing? jclark1 Structural 3 9/12/06 2:43 PM
Proper End Bearing..? crichiii Structural 13 8/28/06 9:47 PM
Post Bearing Requirement hspinnler Structural 8 1/25/06 3:10 AM


All times are GMT -4. The time now is 6:20 PM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts