Home was a new built in 2005/2006.
Home had rafter framing with OSB. Question. No H clips. I spoke to builder & he stated that they are not required. He did say that in truss framing they are a good practice to install. Is what he is staing true about the H clips? |
David
From the picture it appears that the rafters ar approx. 12" OC ? maybe 16" OC at the most... at these limited spans I don't see where H clips would help alot. In this case I don't see a problem. If it were 24" spans it would be a different story. The IRC does not refer to H clips under sheathing requirements. |
Sometimes it is hard to remenber what is required & what isnt.
You guys on this board are a great help & I appreciate your knowledge & professionalism. |
I didnt see anything in Code Check....
Brian R. Sumpter First Call Inspections Proudly serving most Bay Area Counties www.firstcallinspections.com |
Here is what is listed in the IRC International Residential Code {ICC} TABLE R503.2.1.1(1) ALLOWABLE SPANS AND LOADS FOR WOOD STRUCTURAL PANELS FOR ROOF AND SUBFLOOR SHEATHING AND COMBINATION SUBFLOOR UNDERLAYMENT a, b, c For SI: 1 inch = 25.4 mm, 1 pound per square foot = 0.0479 kN/m2. a. The allowable total loads were determined using a dead load of 10 psf. If the dead load exceeds 10 psf, then the live load shall be reduced accordingly. b. Panels continuous over two or more spans with long dimension perpendicular to supports. Spans shall be limited to values shown because of possible effect of concentrated loads. c. Applies to panels 24 inches or wider. d. Lumberblocking, panel edge clips (one midway between each support, except two equally spaced between supports when span is 48 inches), tongue-and-groove panel edges, or other approved type of edge support. e. Includes Structural 1 panels in these grades. f. Uniform load deflection limitation: 1/180 of span under live load plus dead load, 1/240 of span under live load only. g. Maximum span 24 inches for 15/32- and 1/2-inch panels. h. Maximum span 24 inches where 3/4-inch wood finish flooring is installed at right angles to joists. i. Maximum span 24 inches where 1.5 inches of lightweight concrete or approved cellular concrete is placed over the subfloor. j. Unsupported edges shall have tongue-and-groove joints or shall be supported with blocking unless minimum nominal 1/4-inch thick underlayment with end and edge joints offset at least 2 inchesor1.5 inches of lightweight concrete or approved cellular concrete is placed over the subfloor, or 3/4-inch woodfinish flooring is installed at right angles to the supports. Allowable uniform live load at maximum span, based on deflection of 1/360 of span, is 100 psf. k. Unsupported edges shall have tongue-and-groove joints or shall be supported by blocking unless nominal 1/4-inch-thick underlayment with end and edge joints offset at least 2 inches or 3/4-inch wood finish flooring is installed at right angles to the supports. Allowable uniform live load at maximum span, based on deflection of 1/360 of span, is 100 psf, except panels with a span rating of 48 on center are limited to 65 psf total uniform load at maximum span. Signed, Frank Carrio, CMI Certified Master Inspector & Consultant Certified Commercial Building Inspector Certified, WDI Inspector Founder & Current President, New Hampshire State Chapter NACHI NACHI, State Representative for Legislative Affairs Retired: ICC Certified Member Retired: Code Compliance Inspector. Retired: ASTM Committee Member New Hampshire License #0096 |
David, a little more information I found.
http://www.tecotested.com/AllTechnicalInformation.htm http://www.tecotested.com/AllTechnicalInformation.htm http://www.umass.edu/bmatwt/publicat...s_plywood.html Hope this helps. Marcel LEED Green Associates InachiAwardsPortal: Inachi US Member of the Year Award 2009 |
gbrasseur is a non-member guest and is in no way affiliated with InterNACHI or its members.
Where can you find IRC online?
But by putting in the h clips on it makes the 1/8 inch spaceing the mfgr. calls for around the sheets. For proper installation of the OSB!
That's right Carl.
Do you think that most Contractors would loggically figure that out? No brainer to us, but you could not believe how hard it is to pound in that information to some of these people sometimes. Marcel LEED Green Associates InachiAwardsPortal: Inachi US Member of the Year Award 2009 |
homebild is a non-member guest and is in no way affiliated with InterNACHI or its members.
You can find some free model ICC codes here:
http://www.ecodes.biz/index.cfm?vals=Free_State Bear in mind that these are state or jurisdiction specific (although they retain most of the overall code) and not all jurisidictions use the same year model code. There are also state modification to the adopted ICC codes. Check your particular state's website for code adoption modifications. You can find Pennsylvania's here: http://www.dli.state.pa.us/landi/cwp...a=310&q=210892 |
H-Clips are not always required.
H-Clips or blocking are only required for edge support with thinner panels and/or larger rafter spacing where the panel may sag between rafters/chords without that. They are also helpful, but not a requirement, to assist with achieving the recommended 1/8" gap between adjacent panels. Here are a few articles/tables I had handy (the second one has a sample table to go with the notes Frank posted above ... note the allowable span difference with and without "edge support"). Hope they help. JMO & 2-nickels ... Robert O'Connor, PE Consulting Engineer & Inspector LIU CW Post Adjunct Professor NACHI Education Committee www.reporthost.com/-rjo I am absolutely amazed sometimes by how much thought goes into doing things wrong ... |
They need to make it code and even on the walls just to make sure the 1/8 inch gap is there! After all the sheets are sized for the spaceing. Then when the houses are built it would be easy for the codes officials to see the spaceing even if there is a housewrap on the structure!
I tried to attach the table listed in the IRC and failed to do so. You have provided some valuable information to our fellow NACHI members. Kudos! Signed, Frank Carrio, CMI Certified Master Inspector & Consultant Certified Commercial Building Inspector Certified, WDI Inspector Founder & Current President, New Hampshire State Chapter NACHI NACHI, State Representative for Legislative Affairs Retired: ICC Certified Member Retired: Code Compliance Inspector. Retired: ASTM Committee Member New Hampshire License #0096 |
Hi Dave!
I though that I would let you know that the ICC codes are in effect for all of Ohio. Ohio Statewide
I never call them if they're missing. I call excessive deflection if I find it, a problem which is sometimes helped by H-clips. Kenton Shepard, InterNACHI member # 04082383 Certified Master Inspector (CMI) InterNACHI Director of International Development Director of Green Building EXPERT WITNESS SERVICE Conventional and Log homes (303) 717-8940
| h clips | nbhi | Structural Inspections | 23 | 5/8/09 11:48 PM |
| Lack of H clips and warranty | poliner | Exterior Inspections | 16 | 2/2/08 5:51 AM |
| No "H" clips? | jbreazeale | Structural Inspections | 7 | 5/17/07 3:28 PM |
| HI nightmares in the news and other clips | psiposs | General Inspection Discussion | 1 | 4/18/07 2:17 AM |