Default H clips

Home was a new built in 2005/2006.

Home had rafter framing with OSB.

Question. No H clips. I spoke to builder & he stated that they are not required. He did say that in truss framing they are a good practice to install.

Is what he is staing true about the H clips?
Attached Thumbnails
h-clips-86706-garfield-008-small-.jpg.jpg
Views:	167
Size:	51.9 KB
ID:	7515  
Reply With Quote
  #2  
Old 12/5/06, 12:49 PM
Harold E. Miller's Avatar
Harold E. Miller Harold E. Miller is offline
InterNACHI Member
 
Join Date: Feb 2006
Location: Camano Island, WA
Posts: 713
Default Re: H clips

David
From the picture it appears that the rafters ar approx. 12" OC ? maybe 16" OC at the most... at these limited spans I don't see where H clips would help alot. In this case I don't see a problem.
If it were 24" spans it would be a different story.
The IRC does not refer to H clips under sheathing requirements.
Reply With Quote
  #3  
Old 12/5/06, 12:53 PM
David C. Macy's Avatar
David C. Macy David C. Macy is offline
InterNACHI Member
 
Join Date: Jan 2004
Location: NE. OH
Posts: 2,657
Default Re: H clips

Sometimes it is hard to remenber what is required & what isnt.

You guys on this board are a great help & I appreciate your knowledge & professionalism.
Reply With Quote
  #4  
Old 12/5/06, 12:58 PM
bsumpter bsumpter is offline
InterNACHI Member
 
Join Date: Feb 2005
Location: Martinez, CA
Posts: 232
Default Re: H clips

I didnt see anything in Code Check....



Brian R. Sumpter
First Call Inspections
Proudly serving most Bay Area Counties

www.firstcallinspections.com
Reply With Quote
  #5  
Old 12/5/06, 2:48 PM
Frank M. Carrio, CMI's Avatar
Frank M. Carrio, CMI Frank M. Carrio, CMI is offline
ESOP Committee Member
 
Join Date: Jan 2004
Posts: 4,364
Default Re: H clips

Quote:
Originally Posted by dmacy
Home was a new built in 2005/2006.

Home had rafter framing with OSB.

Question. No H clips. I spoke to builder & he stated that they are not required. He did say that in truss framing they are a good practice to install.

Is what he is staing true about the H clips?
I hope that this is of some help.
Here is what is listed in the IRC International Residential Code {ICC}



TABLE R503.2.1.1(1)
ALLOWABLE SPANS AND LOADS FOR WOOD STRUCTURAL PANELS FOR ROOF AND SUBFLOOR SHEATHING
AND COMBINATION SUBFLOOR UNDERLAYMENT a, b, c


For SI: 1 inch = 25.4 mm, 1 pound per square foot = 0.0479 kN/m2.
a. The allowable total loads were determined using a dead load of 10 psf. If the dead load exceeds 10 psf, then the live load shall be reduced accordingly.
b. Panels continuous over two or more spans with long dimension perpendicular to supports. Spans shall be limited to values shown because of possible effect of concentrated loads.
c. Applies to panels 24 inches or wider.

d. Lumberblocking, panel edge clips (one midway between each support, except two equally spaced between supports when span is 48 inches), tongue-and-groove panel edges, or other approved type of edge support.

e. Includes Structural 1 panels in these grades.
f. Uniform load deflection limitation: 1/180 of span under live load plus dead load, 1/240 of span under live load only.
g. Maximum span 24 inches for 15/32- and 1/2-inch panels.
h. Maximum span 24 inches where 3/4-inch wood finish flooring is installed at right angles to joists.
i. Maximum span 24 inches where 1.5 inches of lightweight concrete or approved cellular concrete is placed over the subfloor.
j. Unsupported edges shall have tongue-and-groove joints or shall be supported with blocking unless minimum nominal 1/4-inch thick underlayment with end and edge joints offset at least 2 inchesor1.5 inches of lightweight concrete or approved cellular concrete is placed over the subfloor, or 3/4-inch woodfinish flooring is installed at right angles to the supports. Allowable uniform live load at maximum span, based on deflection of 1/360 of span, is 100 psf.
k. Unsupported edges shall have tongue-and-groove joints or shall be supported by blocking unless nominal 1/4-inch-thick underlayment with end and edge joints offset at least 2 inches or 3/4-inch wood finish flooring is installed at right angles to the supports. Allowable uniform live load at maximum span, based on deflection of 1/360 of span, is 100 psf, except panels with a span rating of 48 on center are limited to 65 psf total uniform load at maximum span.



Signed, Frank Carrio, CMI
Certified Master Inspector & Consultant
Certified Commercial Building Inspector
Certified, WDI Inspector
Founder & Current President, New Hampshire State Chapter NACHI
NACHI, State Representative for Legislative Affairs
Retired: ICC Certified Member
Retired: Code Compliance Inspector.
Retired: ASTM Committee Member
New Hampshire License #0096
Reply With Quote
  #6  
Old 12/5/06, 3:05 PM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 19,788
Default Re: H clips

David, a little more information I found.

http://www.tecotested.com/AllTechnicalInformation.htm

http://www.tecotested.com/AllTechnicalInformation.htm

http://www.umass.edu/bmatwt/publicat...s_plywood.html

Hope this helps.

Marcel
Reply With Quote
  #7  
Old 12/5/06, 7:13 PM
gbrasseur's Avatar
gbrasseur gbrasseur is offline
Active Poster
 
Join Date: Mar 2006
Location: Colorado Springs, CO
Posts: 418
Please Note: gbrasseur is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: H clips

Where can you find IRC online?
Reply With Quote
  #8  
Old 12/5/06, 7:17 PM
Carl A. Brown's Avatar
Carl A. Brown Carl A. Brown is offline
InterNACHI Member
 
Join Date: Jan 2006
Location: Kansas City, ks
Posts: 10,763
Default Re: H clips

But by putting in the h clips on it makes the 1/8 inch spaceing the mfgr. calls for around the sheets. For proper installation of the OSB!
Reply With Quote
  #9  
Old 12/5/06, 8:55 PM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 19,788
Default Re: H clips

That's right Carl.

Do you think that most Contractors would loggically figure that out?

No brainer to us, but you could not believe how hard it is to pound in that information to some of these people sometimes.

Marcel
Reply With Quote
  #10  
Old 12/5/06, 9:08 PM
homebild homebild is offline
Active Poster
 
Join Date: Nov 2006
Location: Pennsylvania
Posts: 195
Please Note: homebild is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: H clips

You can find some free model ICC codes here:

http://www.ecodes.biz/index.cfm?vals=Free_State

Bear in mind that these are state or jurisdiction specific (although they retain most of the overall code) and not all jurisidictions use the same year model code.

There are also state modification to the adopted ICC codes.

Check your particular state's website for code adoption modifications.

You can find Pennsylvania's here:

http://www.dli.state.pa.us/landi/cwp...a=310&q=210892
Reply With Quote
  #11  
Old 12/5/06, 9:31 PM
Robert J. OConnor's Avatar
Robert J. OConnor Robert J. OConnor is offline
InterNACHI Member
 
Join Date: Jul 2003
Location: Long Island, NY
Posts: 1,288
Default Re: H clips

H-Clips are not always required.

H-Clips or blocking are only required for edge support with thinner panels and/or larger rafter spacing where the panel may sag between rafters/chords without that.

They are also helpful, but not a requirement, to assist with achieving the recommended 1/8" gap between adjacent panels.

Here are a few articles/tables I had handy (the second one has a sample table to go with the notes Frank posted above ... note the allowable span difference with and without "edge support"). Hope they help.

JMO & 2-nickels ...
Attached Files
File Type: pdf APA Sheathing Installation N335.pdf (102.9 KB, 165 views)
File Type: pdf APA-IRC Sheathing Span Table.pdf (32.6 KB, 269 views)
File Type: pdf Sheathing H-Clips - Teco.pdf (138.4 KB, 530 views)



Robert O'Connor, PE
Consulting Engineer & Inspector
LIU CW Post Adjunct Professor
NACHI Education Committee
www.reporthost.com/-rjo

I am absolutely amazed sometimes by how much thought goes into doing things wrong ...
Reply With Quote
  #12  
Old 12/5/06, 9:38 PM
Carl A. Brown's Avatar
Carl A. Brown Carl A. Brown is offline
InterNACHI Member
 
Join Date: Jan 2006
Location: Kansas City, ks
Posts: 10,763
Default Re: H clips

They need to make it code and even on the walls just to make sure the 1/8 inch gap is there! After all the sheets are sized for the spaceing. Then when the houses are built it would be easy for the codes officials to see the spaceing even if there is a housewrap on the structure!
Reply With Quote
  #13  
Old 12/6/06, 8:48 AM
Frank M. Carrio, CMI's Avatar
Frank M. Carrio, CMI Frank M. Carrio, CMI is offline
ESOP Committee Member
 
Join Date: Jan 2004
Posts: 4,364
Default Re: H clips

Quote:
Originally Posted by roconnor
H-Clips are not always required.

H-Clips or blocking are only required for edge support with thinner panels and/or larger rafter spacing where the panel may sag between rafters/chords without that.

They are also helpful, but not a requirement, to assist with achieving the recommended 1/8" gap between adjacent panels.

Here are a few articles/tables I had handy (the second one has a sample table to go with the notes Frank posted above ... note the allowable span difference with and without "edge support"). Hope they help.

JMO & 2-nickels ...
Hi Robert,

I tried to attach the table listed in the IRC and failed to do so. You have provided some valuable information to our fellow NACHI members.

Kudos!



Signed, Frank Carrio, CMI
Certified Master Inspector & Consultant
Certified Commercial Building Inspector
Certified, WDI Inspector
Founder & Current President, New Hampshire State Chapter NACHI
NACHI, State Representative for Legislative Affairs
Retired: ICC Certified Member
Retired: Code Compliance Inspector.
Retired: ASTM Committee Member
New Hampshire License #0096
Reply With Quote
  #14  
Old 12/6/06, 8:57 AM
Frank M. Carrio, CMI's Avatar
Frank M. Carrio, CMI Frank M. Carrio, CMI is offline
ESOP Committee Member
 
Join Date: Jan 2004
Posts: 4,364
Default Icc Codes For Ohio

Hi Dave!

I though that I would let you know that the ICC codes are in effect for all of Ohio.

Ohio Statewide
  • 2003 International Building Code
  • 2003 International Energy Conservation Code
  • 2003 International Existing Building Code
  • 2003 International Fire Code
  • 2003 International Fuel Gas Code
  • 2003 International Mechanical Code
  • 2003 International Plumbing Code
  • 2003 International Residential Code



Signed, Frank Carrio, CMI
Certified Master Inspector & Consultant
Certified Commercial Building Inspector
Certified, WDI Inspector
Founder & Current President, New Hampshire State Chapter NACHI
NACHI, State Representative for Legislative Affairs
Retired: ICC Certified Member
Retired: Code Compliance Inspector.
Retired: ASTM Committee Member
New Hampshire License #0096
Reply With Quote
  #15  
Old 12/8/06, 1:39 AM
Kenton H. Shepard, CMI's Avatar
Kenton H. Shepard, CMI Kenton H. Shepard, CMI is offline
InterNACHI Member
 
Join Date: Aug 2004
Location: Boulder, CO
Posts: 3,417
Send a message via ICQ to kshepard
Default Re: H clips

Quote:
Originally Posted by dmacy
Home was a new built in 2005/2006.

Home had rafter framing with OSB.

Question. No H clips. I spoke to builder & he stated that they are not required. He did say that in truss framing they are a good practice to install.

Is what he is staing true about the H clips?
It's an engineering call. Many, many homes have been built without them. They're a good idea with framing on 24" centers, but you can't call it a defect unless you're looking at a set of plans that call for them and you see them missing. It's not a code inspection.

I never call them if they're missing. I call excessive deflection if I find it, a problem which is sometimes helped by H-clips.




Kenton Shepard, InterNACHI member # 04082383
Certified Master Inspector (CMI)
InterNACHI Director of International Development
Director of Green Building

EXPERT WITNESS SERVICE
Conventional and Log homes

(303) 717-8940
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
h clips nbhi Structural Inspections 23 5/8/09 10:48 PM
Lack of H clips and warranty poliner Exterior Inspections 16 2/2/08 4:51 AM
No "H" clips? jbreazeale Structural Inspections 7 5/17/07 2:28 PM
HI nightmares in the news and other clips psiposs General Inspection Discussion 1 4/18/07 1:17 AM


All times are GMT -4. The time now is 10:51 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts