Structural Contains discussions about the structural portion of a home inspection. This includes foundations, framing, et cetera.

Reply
 
LinkBack Thread Tools
  #1  
Old 3/25/06, 11:03 AM
Gary Schering, II's Avatar
Gary Schering, II Gary Schering, II is offline
InterNACHI Member
 
Join Date: Apr 2005
Location: Hamilton, OH
Posts: 695
Default h clips

Inspected a house about 30 yrs old and found that no h clips had been installed. Is this a concern?



"I have not failed, I have just found a 1000's way's that didn't work" Thomas Edison

www.newbeginningshomeinspection.com
Reply With Quote
  #2  
Old 3/25/06, 11:12 AM
Gerry Beaumont's Avatar
Gerry Beaumont Gerry Beaumont is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: Clearwater, FL
Posts: 5,749
Send a message via AIM to gbeaumont Send a message via MSN to gbeaumont Send a message via Yahoo to gbeaumont
Default Re: h clips

Quote:
Originally Posted by nbhi
Inspected a house about 30 yrs old and found that no h clips had been installed. Is this a concern?
Gary,

there are too many variables to be able to answer that question, such as thickness, OC between rafters, thickness of sheathing, and whether or not is was marked "for spacing"

Regards

Gerry



Virtue is more to be feared than vice, because its excesses are not subject to the regulation of conscience.
Adam Smith (1723-1790)

Commercial property Inspection Tampa, Orlando, Sarasota, Jacksonville, Ft Launderdale, Miami, Florida.
NACHI cell 484-429-5466
NACHI02121106
Reply With Quote
  #3  
Old 3/25/06, 11:47 AM
Gary Schering, II's Avatar
Gary Schering, II Gary Schering, II is offline
InterNACHI Member
 
Join Date: Apr 2005
Location: Hamilton, OH
Posts: 695
Default Re: h clips

Gerry, what then do u recommed for wording? When inspecting the roof are we looking 4 things like thickness, OC, etc?



"I have not failed, I have just found a 1000's way's that didn't work" Thomas Edison

www.newbeginningshomeinspection.com

Last edited by nbhi; 3/27/06 at 7:21 AM..
Reply With Quote
  #4  
Old 3/25/06, 12:15 PM
Gerry Beaumont's Avatar
Gerry Beaumont Gerry Beaumont is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: Clearwater, FL
Posts: 5,749
Send a message via AIM to gbeaumont Send a message via MSN to gbeaumont Send a message via Yahoo to gbeaumont
Default Re: h clips

Gary,

you need to look for the manufactures imprint on the sheets to see what the specification is.

I would recommend that you take this course from APA it's free

http://www.wooduniversity.org/

register and take unit 3

Regards

Gerry



Virtue is more to be feared than vice, because its excesses are not subject to the regulation of conscience.
Adam Smith (1723-1790)

Commercial property Inspection Tampa, Orlando, Sarasota, Jacksonville, Ft Launderdale, Miami, Florida.
NACHI cell 484-429-5466
NACHI02121106
Reply With Quote
  #5  
Old 3/27/06, 7:18 AM
Robert J. OConnor's Avatar
Robert J. OConnor Robert J. OConnor is offline
Active Poster
 
Join Date: Jul 2003
Location: East Northport, NY
Posts: 741
Default Re: h clips

In addition to getting a little more background information, look for visible signs of defects at the sheathing edges around mid span between the rafters, such as buckling or bowing. H-clips become more important with thinner panels and OSB type sheathing, possibly combined with larger rafter spacing (such as the usual 2'-0" roof truss spacing).

Also, if you are in an area that does not have significant snow, wind, or earthquake loading it is more likely that thinner roof sheathing is used where H-clips become more important to help support minimum roof live loads from people on the roof (e.g. roofing construction).

JMO & 2-nickels ...



Robert O'Connor, PE
Consulting Engineer & Inspector
LIU CW Post Adjunct Professor
NACHI Education Committee
www.reporthost.com/rjo

I am absolutely amazed sometimes by how much thought goes into doing things wrong ...
Reply With Quote
  #6  
Old 3/27/06, 7:49 AM
rwand1 rwand1 is offline
Active Poster
 
Join Date: Sep 2005
Location: Caledon, ON
Posts: 7,987
Please Note: rwand1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: h clips

I don't think H-clips have been around for thirty years, probably within the last 20 years at least. But then again....
Reply With Quote
  #7  
Old 3/27/06, 3:07 PM
Stephen Enomoto's Avatar
Stephen Enomoto Stephen Enomoto is offline
InterNACHI Member
 
Join Date: Nov 2004
Location: Kapolei, HI
Posts: 117
Default Re: h clips

H- clips were not being used 30 years ago in Hawaii (and I would imagine the rest of the nation.) We started using them around 22 years ago after Huricane Iwa. This changed alot of requirements with regards to home building.

I would check with your AHJ to see when they became a requirement in your area.



"You expect the best . . We'll provide no less"
Stephen Enomoto
Horizon Home Inspection LLC
www.horizonhome.net
steve@horizonhome.net

President: Hawai'i NACHI (O'ahu Chapter)
Reply With Quote
  #8  
Old 3/29/06, 8:40 PM
Larry Ewens's Avatar
Larry Ewens Larry Ewens is offline
InterNACHI Member
 
Join Date: Feb 2005
Location: Brantford, On
Posts: 778
Send a message via AIM to lewens
Default Re: h clips

In my humble opinion H clips are used because the framers and builders are too cheep to use proper tounge and groove sheeting on the roof and could get away with inferior crap.
Larry



Larry Ewens
1578 Colborne St
Brantford On
Nachi ID #05022485
Just my usual 12.5 cents


http://acissbrant.blogspot.com/

Reply With Quote
  #9  
Old 3/29/06, 8:45 PM
Timothy J. Gardner Timothy J. Gardner is offline
InterNACHI Member
 
Join Date: Sep 2003
Location: Moneta, VA
Posts: 270
Default Re: h clips

Larry,

Tell us how you REALLY feel

tg
Reply With Quote
  #10  
Old 3/31/06, 7:53 PM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 12,359
Default Re: h clips

I am getting a little frustrated with this H-clip scene, because 30 years plus ago, a sheet of plywood used to lay flat on the roof or the floor.

Doesn't that raise a red flag? Today, you could make skies with the 5/8" plywood. No wonder that someone invented the h-clip. It would not surprise me that it was the manufacturer himself. Ironically, I was unable to find the background on the h-clip, hmmmm.

Didn't this problem start when Contractors started to save a few bucks and intall 1/2" plywood on the roofs instead of 5/8"?

It is amazing how some people will go to the extremity of actually designing something or product to compensate for the lack of ethical Manufacturing Products the way they were.
Saving labour and Money is what it is all about.

Marcel
</IMG>
Reply With Quote
  #11  
Old 4/1/06, 12:03 AM
Marcel Gratton's Avatar
Marcel Gratton Marcel Gratton is offline
InterNACHI Member
 
Join Date: Jan 2004
Location: Gatineau, QC
Posts: 788
Default Re: h clips

Quote:
Originally Posted by rwand1
I don't think H-clips have been around for thirty years, probably within the last 20 years at least. But then again....
I build my first house in the mid 70's and used H-Clips with roof sheathing panels as per CMHC *Wood Framed House Construction* recommendations; many factors came into play as Gerry mentioned including geographic area (snow loads)...

H-Clips in addition to re-enforce roof sheathing also provides spacing for expansion. Panels expand as wood normally does when moisture content increases.

As someone said: *Saving labour and Money is what it is all about*...



Marcel Gratton, CMI
On The Level Inspection
Gatineau, QC
http://onthelevelinspection.com/
Reply With Quote
  #12  
Old 4/27/09, 4:49 PM
Richard W. Washington's Avatar
Richard W. Washington Richard W. Washington is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Katy, TX
Posts: 802
Default Re: h clips

So what is the rule on spacing for the H-clips? I normally have seen them about every 2' but wonder if a 6' space between two is ok? The rest of the attic had a clip between each of the 2 rafters but one area had quite a gap. Do you call it out and how would they fix it other than pulling the shingles and felt off? I'm not sure this pic is going to be too clear.
Attached Thumbnails
h-clips-dsc054455173.jpg  



Richard W. Washington, owner
RW Home Inspections, Inc.
www.RWHOMEINSPECTIONS.com
Texas Real Estate Commission (TREC)
Professional Inspector License #7238
Texas Professional Real Estate Inspectors Member (TPREIA)-Greater Houston Chapter
InterNACHI member since 2004
Based in Katy, serving Houston and all surrounding communities
Reply With Quote
  #13  
Old 4/27/09, 5:38 PM
Marcel Gratton's Avatar
Marcel Gratton Marcel Gratton is offline
InterNACHI Member
 
Join Date: Jan 2004
Location: Gatineau, QC
Posts: 788
Default Re: h clips

Quote:
Originally Posted by rwashington View Post
So what is the rule on spacing for the H-clips? I normally have seen them about every 2' but wonder if a 6' space between two is ok? The rest of the attic had a clip between each of the 2 rafters but one area had quite a gap. Do you call it out and how would they fix it other than pulling the shingles and felt off? I'm not sure this pic is going to be too clear.
They are usually installed between trusses. If they were omitted, I recommend installing 2X4's between trusses for proper sheathing support.



Marcel Gratton, CMI
On The Level Inspection
Gatineau, QC
http://onthelevelinspection.com/
Reply With Quote
Find an InterNACHI certified Texas Home Inspector (and anywhere else in North America)
  #14  
Old 4/27/09, 11:09 PM
Jeffery L. Haynes Jeffery L. Haynes is offline
InterNACHI Member
 
Join Date: Aug 2008
Location: Concord, NC
Posts: 1,395
Default Re: h clips

They are suppose to be every two foot.......often what happens is they fall out during installation. I don't know how many of you have stood on a two story 10/12 pitch roof with a 4x8 sheet of 1/2 plywood blowing in the wind all the while trying to get the plywood to fit into the clips without them falling down to the to the ground while keeping your balance........it can be a challenge. I definitely don't want to have to be lifting a 3/4 inch plywood or osb over my head while standing on a roof......plus its just not needed.....its overkill. I thought we were suppose to be building smarter and better........isn't that what Green is all about......but I digress....plywood clips have been around at least since the 70's.
While some older building practices are fine.....many are not as is evident by the problems we see in older homes. I will take 3/4 Advantech over the 1/2 plywood & 5/8 particle board any day........as well as the 3/4 diagonal 1x6 with 1/2 ply over same. Many of the materials used today are far superior to what was used back then.

Marcel is correct in that when 7/16 osb is installed on rafters or trusses at 24" o.c. their would be clips or blocks under same.
Reply With Quote
  #15  
Old 4/28/09, 11:09 PM
Kenton H. Shepard, CMI's Avatar
Kenton H. Shepard, CMI Kenton H. Shepard, CMI is offline
InterNACHI Member
 
Join Date: Aug 2004
Location: Boulder, CO
Posts: 2,487
Send a message via ICQ to kshepard
Default Re: h clips

Quote:
Originally Posted by nbhi View Post
Inspected a house about 30 yrs old and found that no h clips had been installed. Is this a concern?
It's an engineer's or architect's call whether to install them. If you don't see them it's not a defect unless you know for a fact that they were required in the jurisdiction in which the home is located at the time the home was built. Many, many homes have been built without them. I would never call lack of them a defect without documentation showing that they were required.

Their purpose is to help support panel edges, not act as spacers, since sheathing is butted tight to them. When they're used, it's usually one per rafter bay.




Kenton Shepard, InterNACHI member # 04082383
Certified Master Inspector (CMI)
EXPERT WITNESS

Director of Green Building
Director for International Development

(303) 717-8940
(303) 258-8289

Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Lack of H clips and warranty poliner Exterior 16 2/2/08 5:51 AM
No "H" clips? jbreazeale Structural 7 5/17/07 3:28 PM
HI nightmares in the news and other clips psiposs General Inspection Discussion 1 4/18/07 2:17 AM
H clips dmacy Structural 15 12/8/06 5:23 PM


All times are GMT -4. The time now is 2:03 PM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts