Default Hangers?

Fellow HI's.


Here is question I can not find an answer for. Did an inspection yesterday at a house (I guess you could call it that) that has manufactured wood I beams installed. The question is.....is there a certain type of hanger used for wood I beams or is a hanger just a hanger? Any help would be greatly appreciated.



John J. Passailaigue Jr.
NACHI05062580
Auburn Home Inspection
Auburn, Alabama
WAR EAGLE!
Reply With Quote
  #2  
Old 9/5/06, 10:57 AM
Erby Crofutt's Avatar
Erby Crofutt Erby Crofutt is offline
InterNACHI Member
 
Join Date: Sep 2002
Location: Georgetown, KY
Posts: 1,198
Default Re: Hangers?

Beams!!! or joists???

Beams are usually supported from below.

Joists go on hangers.
Reply With Quote
  #3  
Old 9/5/06, 1:01 PM
ccbrands1 ccbrands1 is offline
Active Poster
 
Join Date: Jan 2006
Posts: 220
Please Note: ccbrands1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Hangers?

i'd check manufacturer's directions.

lots of different hangers out there.

some can be used for engineered or non engineered applications.

some can only be used for one or the other.

any pics?

try these sites

http://www.strongtie.com/products/Ca...?source=topnav

or

http://www.tamlyn.com/index_files/To...WoodIJoist.htm
Reply With Quote
  #4  
Old 9/5/06, 3:40 PM
William J. Decker's Avatar
William J. Decker William J. Decker is offline
InterNACHI Member
 
Join Date: Nov 2004
Location: Skokie, IL
Posts: 7,785
Default Re: Hangers?

1) Usually, regular joist hangers can be used. Always check with the manufacturer, but LP OSB I joists are OK with it.
2) Make sure that the just didn't toenail the suckers.
3) Check spacing between joists. Usually 16" OC, but can also be 24" OC. Again check with manufacturer.
4) They usually allow 2-3", once in a while, to handle a partition wall above or some such.
5) All the infor is usually printed right on the joist.



Will Decker, CMI
ILL License # 450.0002240
Board Certified Master Inspector
Decker Home Services, LLC
Chicago and Northern Suburban Home Inspections
Office: (847) 676-8393
Cell: (847) 609-2345
Home: (847) 673-2702

wjd@DeckerHomeServices.com
www.DeckerHomeServices.com

Learn, Educate, Serve and have fun doing it!
Reply With Quote
  #5  
Old 9/5/06, 4:32 PM
John J. Passailaigue, Jr.'s Avatar
John J. Passailaigue, Jr. John J. Passailaigue, Jr. is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Auburn, AL
Posts: 409
Send a message via AIM to jpassailaigue
Default Re: Hangers?

ok- somebody give me a quick class on how to install a picture...I have had a brain cramp from looking at the IBC book today.



John J. Passailaigue Jr.
NACHI05062580
Auburn Home Inspection
Auburn, Alabama
WAR EAGLE!
Reply With Quote
  #6  
Old 9/5/06, 4:44 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 32,090
Default Re: Hangers?

Quote:
Originally Posted by jpassailaigue
ok- somebody give me a quick class on how to install a picture...I have had a brain cramp from looking at the IBC book today.
See following tutorial:

http://www.nachi.org/tutorials/tutor...mb-attachments
Reply With Quote
  #7  
Old 9/5/06, 5:16 PM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 19,798
Default Re: Hangers?

Hi. John;

In most cases with joist hangers, it depends on what kind of joist we are talking about. In cases of regular stick building, with conventional joist or rafters, regular lumber yard hangers will suffice.

In cases with structural Engineered Lumber framing, it is most appropriately designed with the system from an Engineer or Architect, where it will be specified for it's use. If not, then maybe contacting the Manufacturer of the product, and usually their recommendation to specific hangers will be listed with the design of the floor system or roof system.
Most of the hangers manufactured are of a long line of designers and can only be qualified and selected by Engineers of the Manufacturer or a Structural Designer if involved.
I added this link for your review of the many possibilities of uses.

http://www.strongtie.com/

Hope this helps.

Marcel
Reply With Quote
  #8  
Old 9/5/06, 5:37 PM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 8,848
Default Re: Hangers?

Typically, conventional joists use a face mount flange hanger and I-joists use a top mount flange hanger:
Attached Thumbnails
hangers-u-face_mnt_cwp-small-.gif.gif
Views:	32
Size:	14.1 KB
ID:	5434   hangers-itt-top_flange_cwp-small-.gif.gif
Views:	21
Size:	14.2 KB
ID:	5435  
Reply With Quote
  #9  
Old 9/5/06, 7:18 PM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 19,798
Default Re: Hangers?

These are just three example; therefore, there needs to be some engineering involved. I would think.



Marcel
Reply With Quote
  #10  
Old 9/5/06, 7:19 PM
Peter C. Russell's Avatar
Peter C. Russell Peter C. Russell is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Alton Bay NH
Posts: 3,998
Default Re: Hangers?

Just a fact to point out, When inspecting newer houses with MFG. I joists for floors, when installed they need to be installed slightly lower than the beam to allow for expansion and contraction, so if you see flooring in a newer home buckling check the I joists in the basement. Many times a builder will install them flush to the main carrying beam and they tend to expand pushing the sub floor up.
Reply With Quote
  #11  
Old 9/5/06, 7:25 PM
rwand1 rwand1 is offline
Active Poster
 
Join Date: Sep 2005
Location: Caledon, ON
Posts: 7,861
Please Note: rwand1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Hangers?

Watch out for nailing. Find many that have not been fully nailed.
Reply With Quote
  #12  
Old 9/5/06, 7:25 PM
Peter C. Russell's Avatar
Peter C. Russell Peter C. Russell is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Alton Bay NH
Posts: 3,998
Default Re: Hangers?

Actually what I meant to say is the main beam that the I joists are attached to tend to shrink thus making the joist push the sub floor up. Here in NE we buy kiln dry lumber which I believe is dried for about 30 minutes and then out in the yard up for sale, always green and worse in the winter because it freezes in the yard and doesnt dry until the heat goes on.
Reply With Quote
  #13  
Old 9/5/06, 8:09 PM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 19,798
Default Re: Hangers?

Peter, you can correct me if I am wrong, but the last Project I did with TJI's or I joist, it was reccommended that the underlayment span the girder beams by 1/4". Not backing it up with a link is my downfall I guess. Sometimes they are not readily accessible. The theory or fact behind that is, since the carrying beam of the floor structure is more of a massive volume, it tends to shrink less than the members attached to it. So, therefore, shrinkage if existing in the floor members perpendicular to the main supporting beam exist, the 1/4" will compensate without creating a bump in the flooring material.

JMHO.

Marcel

Marcel
</IMG></IMG>
Reply With Quote
  #14  
Old 9/6/06, 8:30 PM
Peter C. Russell's Avatar
Peter C. Russell Peter C. Russell is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Alton Bay NH
Posts: 3,998
Default Re: Hangers?

Marcel, not sure if we are on the same page, I was referring to the joist not the sub floor or underlayment. I was referring to an I joist that is connected to a stick framed carrying beam that is usually made out of 2x10s the I joist will not shrink but the main carrying beam will thus pushing against the sub floor. Your thoughts?
Reply With Quote
  #15  
Old 9/7/06, 10:25 AM
Kenton H. Shepard, CMI's Avatar
Kenton H. Shepard, CMI Kenton H. Shepard, CMI is offline
InterNACHI Member
 
Join Date: Aug 2004
Location: Boulder, CO
Posts: 3,417
Send a message via ICQ to kshepard
Default Re: Hangers?

Peter, with top flange hangers beam shrinkage won't matter, the Joists will still be in the same position relative to the top of the beam. I've never seen I-joists installed on a beam in which the tops of the beam and joists were supposed to be flush without using top flange hangers although I'm sure someone somewhere has decided to use up those hangers that've been stashed away in his garage and save $25.

All in all, we don't have to confirm compliance to engineering. I called one roof system in which the framers had nailed truss-bearing hangers with siding nails (40% smaller diameter and a different alloy) but unless it looks bad or you know it's wrong, why call it?

Joist layout would be called out by an engineer and it might be 12", 16", 19" or 24" on center (center to center, not in between). Unless the floor or roof exhibits exfcessive deflection, joist spacing is not our problem. If it does, then call out excessive deflection. -Kent




Kenton Shepard, InterNACHI member # 04082383
Certified Master Inspector (CMI)
InterNACHI Director of International Development
Director of Green Building

EXPERT WITNESS SERVICE
Conventional and Log homes

(303) 717-8940
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Joist Hangers at Cantilevered Rim pdickerson Exterior Inspections 21 8/18/07 6:19 PM
Pipe hangers Ian Gills Plumbing Inspections 4 5/11/07 5:17 PM
3-2 mono roof truss anchor dthomas2 Structural Inspections 8 10/2/06 11:36 PM


All times are GMT -4. The time now is 3:06 PM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts