Default holes in I-Joists

Ran accross this today. I know holes are usually acceptable, but how about two holes next to each other? I advised my client to check with the manufacturer of the i-joists to see what was permissable. Any other opinioins on this one?holes-joists-018.jpg
Reply With Quote
Find an InterNACHI certified Ohio Home Inspector (and anywhere else in North America)
  #2  
Old 6/11/09, 7:21 AM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 18,489
Default Re: holes in I-Joists

Quote:
Originally Posted by jreim View Post
Ran accross this today. I know holes are usually acceptable, but how about two holes next to each other? I advised my client to check with the manufacturer of the i-joists to see what was permissable. Any other opinioins on this one?Attachment 29172
Good advice.

Here is the hole boring guide from G-P's product

http://www.gp.com/build/DocumentView...elementid=4815 (see page 14)

NOTES:
1. Hole locations are based on worst case of simple and multiple span
conditions with uniform floor loads of 40 PSF live load and 10 or 20 PSF dead load,spans from page 3.

2. Holes not greater than 1.5" in diameter can be placed anywhere in the web, but the hole must be spaced a minimum horizontal clear distance of 2 times its diameter (but not less than 1") from any adjacent hole.

3. For holes greater than 1.5" diameter, minimum clear distance between
a) two round holes is 2 times the diameter of the larger hole
b) a round hole and a rectangular hole is the larger of 2 times the hole
diameter or twice the rectangular hole width

4. For multiple holes: The clear distance between the holes must equal or exceed twice the diameter of the largest hole, or twice the longest side of a rectangular hole.

5. A group of round holes at approximately the same location shall be permitted if they meet the requirements for a single round hole circumscribed around them.

6. For joists with more than one span, use the longest span to determine hole location in either span.

7. All holes shown on this chart may be located vertically anywhere within the web; a clear distance of at least 1⁄8"must be maintained from the hole edge to the inner surface of the closest flange.



"Never underestimate the difficulty of changing false beliefs by facts."
Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI
InspectraPro
or
Minnesota Home Inspector

Reply With Quote
  #3  
Old 6/13/09, 1:55 PM
Donald T. Belmont Donald T. Belmont is offline
InterNACHI Member
 
Join Date: Feb 2006
Location: Barre, VT
Posts: 520
Send a message via Yahoo to dbelmont
Default Re: holes in I-Joists

What I wonder is if that is a bearing point for the joist to the left in the pic. Because of the structural behavior of engineered joists there are restrictions about holes the closer you get to a bearing. Generally, if you are outside that restricted area then the hole can be almost as large as the width of the web. If 2 or more holes fit in that area it's generally OK. If the holes won't fit then then next parameter is holes are twice their diameter apart.

But other hole configurations may be just fine. Usually, the material distributor can run a calc on a particular hole configuration to see if it passes muster. Often holes that are outside the published general rules will pass muster just fine.

I imagine there are others but I keep a copy of BC-Calc that lets me run a hole calc if it's an issue. Also sizing's for joists and beams. I don't use it much (maybe once a year) but it's real useful when I need it. Let's me call the close ones on whether I specify an engineer or not. (I keep my calcs to myself)



Don Belmont
email: don@wisehi.com

Are your home inspections priced for profit?
The Service Business Profit Pricing Modeler can answer that question.
Easy, Fast, Accurate, Affordable
Special Pricing for InterNACHI members.
Send me a Private Message for the discount code.

WiseEyes Home and Property Inspections Inc.
Vermont Equine Thermal Imaging
Vermont Home Energy Tune-up



Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Sistered Floor Joists Skip Erwin Structural 16 5/27/08 1:07 AM
Max load allowed on 2x2 ledger bking Structural 4 12/23/07 3:05 PM
Where do I put the Aquarium? mcyr Structural 3 11/6/07 4:05 PM
What's Wring With This Picture: Bored Holes in Floor Joists? homebild Structural 17 5/4/07 9:33 AM


All times are GMT -4. The time now is 5:17 PM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts