Default Insulated, Enclosed, Unventilated Attic Question

House is brand new with a tile roof. The roof sheathing was insulated with foam (which I have never seen). The soffits were completely insulated, and there was no other visible entrance point for ventilation. There was no ventilation at all to the attic that I could see. The ceilings were uninsulated.

Is this acceptable? I thought that attic ventilation was required at a rate of: 1 to 150 sq. ft.

Another question: won't the attic be hot as Hades if it's enclosed? How will the lack of ceiling insulation affect the living space?

And, how will the insulation on the sheathing affect leak detection???

This was my first tile roof structure. Is this the latest in building techniques and something unique to tile roofs?

Photos show insulated roof sheathing, insulated soffits, uninsulated ceiling.

insulated-enclosed-unventilated-attic-question-030707-132-small-.jpg.jpg
Views:	432
Size:	42.4 KB
ID:	9773 insulated-enclosed-unventilated-attic-question-030707-144-small-.jpg.jpg
Views:	385
Size:	32.0 KB
ID:	9774 insulated-enclosed-unventilated-attic-question-030707-153-small-.jpg.jpg
Views:	366
Size:	32.7 KB
ID:	9775



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com



Last edited by jfunderburk; 3/7/07 at 10:11 PM..
Reply With Quote
  #2  
Old 3/7/07, 9:46 PM
tdietrich1's Avatar
tdietrich1 tdietrich1 is offline
InterNACHI Member
 
Join Date: Oct 2006
Location: Northampton County - Pa
Posts: 1,954
Send a message via Yahoo to tdietrich1
Default Re: Insulated, Enclosed, Unventilated Attic Question

imho:

If the underside of the sheathing is insulated, then the attic has become part of the houses environmental envelope. So you wouldn't ventilate a room, you don't ventilate the attic space.

tom
Reply With Quote
  #3  
Old 3/7/07, 10:31 PM
Bruce A. King's Avatar
Bruce A. King Bruce A. King is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: York, SC
Posts: 3,103
Default Re: Insulated, Enclosed, Unventilated Attic Question

That method is more common further north I believe.

I wonder what the r-value is of that expanding foam.

The construction of the tile roof and whatever they used under it and in the valleys should be high end quality on a house like that and leaks won't be a problem. If it leaks, it won't be noticeable until the tile sags about 15 years later?

Here is a link

http://www.buildingscience.com/docum...iew?searchterm=



B.A. King Home Inspections, LLC
www.BAKingHomeInspections.com
Serving Charlotte NC area and Rock Hill SC areas.
CMI Certified Master Inspector and Independent
704 301-3207



"Discovery consists in seeing what everyone else has seen and thinking what no one else has thought."
- Albert Szent-Gyvrgyi, Nobel Prize for Medicine 1937
Reply With Quote
  #4  
Old 3/7/07, 11:02 PM
Brian E. Kelly's Avatar
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 15,857
Default Re: Insulated, Enclosed, Unventilated Attic Question

I have seen fibergalss batts and cellulose sheets installed up next to the sheathing before Joe, but I have never seen the sprayed in foam. Neato.
Reply With Quote
  #5  
Old 3/8/07, 7:23 AM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is online now
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 18,917
Default Re: Insulated, Enclosed, Unventilated Attic Question

Becoming more and more popular up here mostly for inaccessible attics.

Provides an r-factor of around 6-7.

Marcel

http://www.pasprayfoam.com/Pa-Spray-...-ceilings.html
Reply With Quote
  #6  
Old 3/8/07, 9:47 AM
Mark A. Timpani, CMI's Avatar
Mark A. Timpani, CMI Mark A. Timpani, CMI is offline
InterNACHI Member
 
Join Date: May 2004
Location: Tucson, AZ
Posts: 2,131
Default Re: Insulated, Enclosed, Unventilated Attic Question

Yes, it is an acceptable practice in Tucson.




"Be Proud of Your Home, Go With Pride!"
'Not just a Home Inspection, but an Education'

Pride Property Inspections provides professional Home Inspections throughout Tucson and Southern Arizona including Pima, Cochise, Pinal, Santa Cruz, Graham counties.

Reply With Quote
  #7  
Old 3/8/07, 12:08 PM
Harold E. Miller's Avatar
Harold E. Miller Harold E. Miller is offline
InterNACHI Member
 
Join Date: Feb 2006
Location: Camano Island, WA
Posts: 708
Default Re: Insulated, Enclosed, Unventilated Attic Question

http://www.jlconline.com/cgi-local/v...177f0000010565

Article in this months JLC on this subject of unvented attics. Good read.
Reply With Quote
  #8  
Old 3/8/07, 1:30 PM
staylor5's Avatar
staylor5 staylor5 is offline
InterNACHI Member
 
Join Date: Jan 2007
Location: Freehold, NJ
Posts: 108
Default Re: Insulated, Enclosed, Unventilated Attic Question

I think it provides r-6 or r-7 per inch. so a 2x6 would have about an r-30+. Althought I would imagine that baffles would help ventilation for the sheathing.

Last edited by staylor5; 3/8/07 at 3:20 PM..
Reply With Quote
  #9  
Old 3/8/07, 2:30 PM
Patrick J. Cloninger's Avatar
Patrick J. Cloninger Patrick J. Cloninger is offline
InterNACHI Member
 
Join Date: Jun 2006
Location: Knoxville, TN
Posts: 288
Default Re: Insulated, Enclosed, Unventilated Attic Question

Joe,

I wish I could give you a good answer but all I can say is that in Knoxville, TN where I am tile roofs are vented the same as asphalt shingle roofs for the most part. I have inspected quite a few and have not seen any like the one you did.



Patrick J. Cloninger



Serving Knoxville and surrounding counties
Reply With Quote
  #10  
Old 3/8/07, 4:20 PM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 7,707
Send a message via Yahoo to jfunderburk
Default Re: Insulated, Enclosed, Unventilated Attic Question

Found this in the '06 IRC:

"R806.4 Conditioned attic assemblies. Unvented conditioned
attic assemblies (spaces between the ceiling joists of the top
story and the roof rafters) are permitted under the following
conditions:
1. No interior vapor retarders are installed on the ceiling
side (attic floor) of the unvented attic assembly.

2. An air-impermeable insulation is applied in direct contact
to the underside/interior of the structural roof deck.
“Air-impermeable” shall be defined by ASTM E 283.
Exception: In Zones 2B and 3B, insulation is not
required to be air impermeable.

3. In the warm humid locations as defined in Section
N1101.2.1:
3.1. For asphalt roofing shingles: A 1-perm (5.7 ×
10-11 kg/s ⋅ m2 ⋅ Pa) or less vapor retarder (determined
using Procedure B of ASTM E 96) is
placed to the exterior of the structural roof deck;
that is, just above the roof structural sheathing.
3.2. For wood shingles and shakes: a minimum continuous
1/4-inch (6 mm) vented air space separates
the shingles/shakes and the roofing felt
placed over the structural sheathing.

4. In Zones 3 through 8 as defined in Section N1101.2, sufficient
insulation is installed to maintain the monthly
average temperature of the condensing surface above
45°F (7°C). The condensing surface is defined as either
the structural roof deck or the interior surface of an
air-impermeable insulation applied in direct contact with
the underside/interior of the structural roof deck.
“Air-impermeable” is quantitatively defined by ASTM
E 283. For calculation purposes, an interior temperature
of 68°F (20°C) is assumed. The exterior temperature is
assumed to be the monthly average outside temperature."



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #11  
Old 3/8/07, 4:24 PM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 7,707
Send a message via Yahoo to jfunderburk
Default Re: Insulated, Enclosed, Unventilated Attic Question

Said this in my report: "The attic is called a "conditioned attic assembly". It is designed to be unvented. Air-impermeable foam insulation is applied in direct contact to the underside/interior of the structural roof deck approximately 6 inches thick. There is no ceiling insulation, in accordance with this construction technique. We cannot determine the R-value of conditioned attics and recommend that you consult with the builder or an insulation specialist to ascertain the efficiency rating."

My wife wonders why I spend so much time on the computer. Every time you think you know something, you run into something weird.



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #12  
Old 3/8/07, 7:38 PM
tdietrich1's Avatar
tdietrich1 tdietrich1 is offline
InterNACHI Member
 
Join Date: Oct 2006
Location: Northampton County - Pa
Posts: 1,954
Send a message via Yahoo to tdietrich1
Default Re: Insulated, Enclosed, Unventilated Attic Question

My Motto:

"If you can't dazzle them with brilliance, baffle them with bull****".

Reply With Quote
  #13  
Old 3/14/07, 12:43 PM
whandley's Avatar
whandley whandley is offline
Active Poster
 
Join Date: Sep 2004
Location: Laguna Niguel, CA
Posts: 2,093
Please Note: whandley is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Insulated, Enclosed, Unventilated Attic Question

Quote:
Originally Posted by mtimpani
Yes, it is an acceptable practice in Tucson.
Hey Mark,

With your average summer temperature around 140-150F don't you need more than an R6 - R7 value?
Reply With Quote
  #14  
Old 3/14/07, 2:07 PM
Brian T. Stevens's Avatar
Brian T. Stevens Brian T. Stevens is offline
InterNACHI Member
 
Join Date: Feb 2005
Location: Whitehall, Mi
Posts: 29
Send a message via MSN to bstevens
Default Re: Insulated, Enclosed, Unventilated Attic Question

That type of insulation is becoming more common here in Michigan where vaulted ceilings are being built. Venting is achieved by installing the chutes to the underside of the sheeting from soffit to peak and then the foam is sprayed in top of the chutes and the ceiling finnish material applied on top of that after it has cured. Tile roofs arn't that common here so I can't comment on how it might be vented however it may be vented in the same manner where you wouldn't see it from the interior of the attic.

Just what I know here.

Brian
Reply With Quote
  #15  
Old 3/14/07, 2:15 PM
wforsyth's Avatar
wforsyth wforsyth is offline
Active Poster
 
Join Date: Feb 2006
Location: Brinnon, Wa
Posts: 7,864
Please Note: wforsyth is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Insulated, Enclosed, Unventilated Attic Question

That's the spray foam insulation I was talking about in the post about the copper pipe that looks like it has asbestos coating it. Same thing as here, or looks like it.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Question about pull down attic stairs waksell Interior Inspections 33 4/2/07 12:11 AM
Home Warranty Attic Insulation Question jhawes Canadian Inspectors 2 12/4/06 2:54 AM


All times are GMT -4. The time now is 8:32 PM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts