House is brand new with a tile roof. The roof sheathing was insulated with foam (which I have never seen). The soffits were completely insulated, and there was no other visible entrance point for ventilation. There was no ventilation at all to the attic that I could see. The ceilings were uninsulated.
Is this acceptable? I thought that attic ventilation was required at a rate of: 1 to 150 sq. ft. Another question: won't the attic be hot as Hades if it's enclosed? How will the lack of ceiling insulation affect the living space? And, how will the insulation on the sheathing affect leak detection??? This was my first tile roof structure. Is this the latest in building techniques and something unique to tile roofs? Photos show insulated roof sheathing, insulated soffits, uninsulated ceiling. ![]() Joe Funderburk, CMI Alpha & Omega Home Inspections, LLC Inspecting Upstate SC & Charlotte Metro, NC NACHI ID: NACHI05120170 www.aohomeinspection.com Last edited by jfunderburk; 3/7/07 at 10:11 PM.. |
|
#2
|
||||
|
||||
|
imho:
If the underside of the sheathing is insulated, then the attic has become part of the houses environmental envelope. So you wouldn't ventilate a room, you don't ventilate the attic space. tom |
|
#3
|
||||
|
||||
|
That method is more common further north I believe.
I wonder what the r-value is of that expanding foam. The construction of the tile roof and whatever they used under it and in the valleys should be high end quality on a house like that and leaks won't be a problem. If it leaks, it won't be noticeable until the tile sags about 15 years later? Here is a link http://www.buildingscience.com/docum...iew?searchterm= B.A. King Home Inspections, LLC www.BAKingHomeInspections.com Serving Charlotte NC area and Rock Hill SC areas. CMI Certified Master Inspector and Independent 704 301-3207 |
|
#4
|
|||
|
|||
|
I have seen fibergalss batts and cellulose sheets installed up next to the sheathing before Joe, but I have never seen the sprayed in foam. Neato.
"Never ever threaten anyone in Camoflage" Tim Wilson "Not everyone follows the same path" Governor Sanford, musings on the Appalachian Trail
|
|
#5
|
||||
|
||||
|
Becoming more and more popular up here mostly for inaccessible attics.
Provides an r-factor of around 6-7. Marcel http://www.pasprayfoam.com/Pa-Spray-...-ceilings.html Cyr Home and Commercial Property Inspections IAC2 Certified NACHI04070211 http://co.nachi.org/inachiawards Commercial Builder CertainTeed Master Shingle Applicator Shingle Technology Ouellet Associaties Inc. http://www.oaconstruction.com/ |
|
#6
|
||||
|
||||
|
Yes, it is an acceptable practice in Tucson.
"Be Proud of Your Home, Go With Pride!" 'Not just a Home Inspection, but an Education' Pride Property Inspections provides professional Home Inspections throughout Tucson and Southern Arizona including Pima, Cochise, Pinal, Santa Cruz, Graham counties. |
|
#7
|
||||
|
||||
|
Please Note:
hmiller is a non-member guest and is in no way affiliated with InterNACHI or its members.
http://www.jlconline.com/cgi-local/v...177f0000010565
Article in this months JLC on this subject of unvented attics. Good read. |
|
#8
|
||||
|
||||
|
I think it provides r-6 or r-7 per inch. so a 2x6 would have about an r-30+. Althought I would imagine that baffles would help ventilation for the sheathing.
Last edited by staylor5; 3/8/07 at 3:20 PM.. |
|
#9
|
||||
|
||||
|
Joe,
I wish I could give you a good answer but all I can say is that in Knoxville, TN where I am tile roofs are vented the same as asphalt shingle roofs for the most part. I have inspected quite a few and have not seen any like the one you did. |
|
#10
|
||||
|
||||
|
Found this in the '06 IRC:
"R806.4 Conditioned attic assemblies. Unvented conditioned attic assemblies (spaces between the ceiling joists of the top story and the roof rafters) are permitted under the following conditions: 1. No interior vapor retarders are installed on the ceiling side (attic floor) of the unvented attic assembly. 2. An air-impermeable insulation is applied in direct contact to the underside/interior of the structural roof deck. “Air-impermeable” shall be defined by ASTM E 283. Exception: In Zones 2B and 3B, insulation is not required to be air impermeable. 3. In the warm humid locations as defined in Section N1101.2.1: 3.1. For asphalt roofing shingles: A 1-perm (5.7 × 10-11 kg/s ⋅ m2 ⋅ Pa) or less vapor retarder (determined using Procedure B of ASTM E 96) is placed to the exterior of the structural roof deck; that is, just above the roof structural sheathing. 3.2. For wood shingles and shakes: a minimum continuous 1/4-inch (6 mm) vented air space separates the shingles/shakes and the roofing felt placed over the structural sheathing. 4. In Zones 3 through 8 as defined in Section N1101.2, sufficient insulation is installed to maintain the monthly average temperature of the condensing surface above 45°F (7°C). The condensing surface is defined as either the structural roof deck or the interior surface of an air-impermeable insulation applied in direct contact with the underside/interior of the structural roof deck. “Air-impermeable” is quantitatively defined by ASTM E 283. For calculation purposes, an interior temperature of 68°F (20°C) is assumed. The exterior temperature is assumed to be the monthly average outside temperature." Joe Funderburk, CMI Alpha & Omega Home Inspections, LLC Inspecting Upstate SC & Charlotte Metro, NC NACHI ID: NACHI05120170 www.aohomeinspection.com |
|
#11
|
||||
|
||||
|
Said this in my report: "The attic is called a "conditioned attic assembly". It is designed to be unvented. Air-impermeable foam insulation is applied in direct contact to the underside/interior of the structural roof deck approximately 6 inches thick. There is no ceiling insulation, in accordance with this construction technique. We cannot determine the R-value of conditioned attics and recommend that you consult with the builder or an insulation specialist to ascertain the efficiency rating."
My wife wonders why I spend so much time on the computer. Every time you think you know something, you run into something weird. Joe Funderburk, CMI Alpha & Omega Home Inspections, LLC Inspecting Upstate SC & Charlotte Metro, NC NACHI ID: NACHI05120170 www.aohomeinspection.com |
|
#12
|
||||
|
||||
|
My Motto:
"If you can't dazzle them with brilliance, baffle them with bull****". |
|
#13
|
||||
|
||||
|
Please Note:
whandley is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
With your average summer temperature around 140-150F don't you need more than an R6 - R7 value? |
|
#14
|
||||
|
||||
|
That type of insulation is becoming more common here in Michigan where vaulted ceilings are being built. Venting is achieved by installing the chutes to the underside of the sheeting from soffit to peak and then the foam is sprayed in top of the chutes and the ceiling finnish material applied on top of that after it has cured. Tile roofs arn't that common here so I can't comment on how it might be vented however it may be vented in the same manner where you wouldn't see it from the interior of the attic.
Just what I know here. Brian |
|
#15
|
||||
|
||||
|
Please Note:
wforsyth is a non-member guest and is in no way affiliated with InterNACHI or its members.
That's the spray foam insulation I was talking about in the post about the copper pipe that looks like it has asbestos coating it. Same thing as here, or looks like it.
|
![]() |