There is 2x10 for rafter material being used. In the northern states r-38 is required in ceilings, how would you insulate the rafters if it was a vaulted ceiling (meaning they want to attach drywall directly to the rafters for a sloped ceiling) 2x10 measures 9 1/2" in depth, what materials would you use to acheive the r-38 requirments and yet have the 1" air gap against the roof deck sheating???
Ridge insulation then batts of some sort????????????????? |
|
#2
|
||||
|
||||
|
Please Note:
phinsperger is a non-member guest and is in no way affiliated with InterNACHI or its members.
Yes. That's one way. Working from the underside of the roof deck;- staple up your vents,- then put up the batts in between the rafters- then put up rigid foam insulation sheets covering both the batts and the rafters- then drywall.It will perform better because of the thermal bridge break. If you are diligent in sealing up the seams of the foam sheets it will also provide as a very good vapor barrier.
|
|
#3
|
|||
|
|||
|
Please Note:
brepanshek is a non-member guest and is in no way affiliated with InterNACHI or its members.
How would this give you the required R-38??
Batt insulation (R value ??) + ridge insulation board (R value ??) = R-38 describe the types of insulation materials you would use. |
|
#4
|
||||
|
||||
|
Quote:
JMO Robert O'Connor, PE Consulting Engineer & Inspector LIU CW Post Adjunct Professor NACHI Education Committee www.reporthost.com/rjo I am absolutely amazed sometimes by how much thought goes into doing things wrong ... |
|
#5
|
||||
|
||||
|
Quote:
Paul directed you well, he just did not quote you any values. Maybe I can help you with that. Once you have installed your baffle vents for continuous venting from soffit to ridge vent, the only comfortable space left for insulation (batt) is 8". Batt insulation has an R-Value of 3.14 per inch so this would equal 25.12. or a high density would be r- 30. Required R-Values for roofs in the NorthEast is R-38 38. Deficit -12.88 Paul recommended Polystyrene, I believe and that is 5.00 p.i. 2" = 10 Polyisocyanurate has an R-Value of 7.20 P. I. 1 &1/2" = 10.8 2"= 14.4 Either one, you would have to strap the ceiling in order to sheetrock, unless one wants to use extra long screws. Alternatives: Icceynene Spray foam open cell 3.6 R-Value per inch Polyurethane Spray foam closed cell 6-7 R-Value per inch One has more insulating values as well as price. Hope this helps. Marcel Cyr Home and Commercial Property Inspections IAC2 Certified NACHI04070211 http://co.nachi.org/inachiawards Commercial Builder CertainTeed Master Shingle Applicator Shingle Technology Ouellet Associaties Inc. http://www.oaconstruction.com/ Last edited by mcyr; 3/27/07 at 8:43 PM.. |
|
#6
|
|||
|
|||
|
Quote:
Pssst!...Marcel. 2x10's are 9 1/4", minus 1" for the venting equals 8 1/4"...but you are giving some valuable information. ____________________________________________ "An Education, not just an Inspection" Larry Kage Lake Ann (Traverse City), Michigan 49650 231 929 3525 Professional Inspector and Infrared Thermographer serving the Traverse City, Michigan area and beyond. ITC/FLIR CERTIFIED BUILDING SCIENCES THERMOGRAPHER ITC/FLIR CERTIFIED LEVEL 1 THERMOGRAPHER
|
|
#7
|
||||
|
||||
|
Sorry Larry;
Thanks for the warning, just too many numbers in my head I guess. Corrected my post, hope I got it right this time. ha. ha. Marcel Cyr Home and Commercial Property Inspections IAC2 Certified NACHI04070211 http://co.nachi.org/inachiawards Commercial Builder CertainTeed Master Shingle Applicator Shingle Technology Ouellet Associaties Inc. http://www.oaconstruction.com/ |
|
#8
|
|||
|
|||
|
Ahhh...no "warning" meant, Marcel...just funnin' ya...
You are a wealth of good info, thanks. ____________________________________________ "An Education, not just an Inspection" Larry Kage Lake Ann (Traverse City), Michigan 49650 231 929 3525 Professional Inspector and Infrared Thermographer serving the Traverse City, Michigan area and beyond. ITC/FLIR CERTIFIED BUILDING SCIENCES THERMOGRAPHER ITC/FLIR CERTIFIED LEVEL 1 THERMOGRAPHER
|
|
#9
|
||||
|
||||
|
Please Note:
phinsperger is a non-member guest and is in no way affiliated with InterNACHI or its members.
You can also use a foil faced ridged foam like Energy Sheild for example. Because the foil reflects radiant heat it adds an effective ~R2.2 to the value of the foam for any given thickness. Mineral wool batts also have a slightly higher R value than fiberglass.
Last edited by phinsperger; 3/27/07 at 9:49 PM.. Reason: typo |
|
#10
|
|||
|
|||
|
Please Note:
Randy L. Thomas is a non-member guest and is in no way affiliated with InterNACHI or its members.
Be aware that the code allows for R-30 (normally batts) for vaulted ceilings and R-38 (normally blown-in) for flat ceilings. The vaulted ceiling allowance is good for up to 50% of the ceiling surface area. Anything over that requires R-38. As mentioned in thread above, if there is inadequate space for conventional insulation, then higher R-value material must be used.
|
|
#11
|
||||
|
||||
|
Two by strapping would take care of the problem. It will give you the required 1" air space and enough left to insulate to required value. The only problem I see is the strapping may interfere with the window height.
Larry Larry Ewens 1578 Colborne St Brantford On Nachi ID #05022485 Just my usual 12.5 cents ![]() http://acissbrant.blogspot.com/ |
|
#12
|
||||
|
||||
|
Quote:
Larry Larry Ewens 1578 Colborne St Brantford On Nachi ID #05022485 Just my usual 12.5 cents ![]() http://acissbrant.blogspot.com/ |
|
#13
|
||||
|
||||
|
Purchased at the local Home Depot when I insulated my own 2x10 cathedral ceiling: styrofoam baffles & r-30 owens corning fiberglass(kraft faced)
Code in Buffalo called for r-30. Keith R. Braun, Western New York Chapter Vice President for Education |
|
#14
|
||||
|
||||
|
Quote:
http://www.jmhomeinsulation.com/howt...&install=Batts JMO Robert O'Connor, PE Consulting Engineer & Inspector LIU CW Post Adjunct Professor NACHI Education Committee www.reporthost.com/rjo I am absolutely amazed sometimes by how much thought goes into doing things wrong ... |
|
#15
|
|||
|
|||
|
Please Note:
homebild is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
Pennsylvania allows a wide variety of compliance paths for energy conservation and Code complinace, and R-38 is not always required for ceiling insulation in Pennsylvania. One can use Chapter 11 of the IRC 2006, the 2006 Pennsylvania Alternative Energy Code, the Department of Energy RESCheck software, and many various alternative complinace methods and approaches under the 2006 IECC. R-38 for ceiling insulation is not written in stone in Pennsylvania and most designs do not include R-38 anymore. The IECC allows, for example, that in a cathedral ceiling, you can use R-30 and still comply with the Code provided that the area of the cathedral ceiling with less than R-38 insulation is less than 500 square feet. (404.2.2 2006 IECC) REScheck and other performance based compliance methods allows one to reduce ceiling insulation R-values provided wall insulation, window U-factors, or heating and cooling system efficiciencies are increased to make up the difference. If you suspect a less-than-expected level of insulation on Pennsylvania, have your client refer to the local Residential Energy Codes Inspector for the municipality to verify the structure is compliant. You can see the Pennsylvania Alternative Energy Code online here: http://www.dli.state.pa.us/landi/lib/landi/ucc/pa_alternative_2006.pdf You can see the Department of Energy RESCheck and other types of performance based software here: http://www.energycodes.gov/ Last edited by homebild; 3/31/07 at 3:21 PM.. Reason: q |
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| IAC2 In new residential construction | mcyr | IAC2 Forum | 0 | 10/9/07 7:45 PM |
| PIC of State Rep and sponsor of new NACHI H.I. Bill in NH. | gromicko | Misc. Discussion | 53 | 8/30/06 6:58 PM |
| sub flooring insulation Question? | cpetty | General Inspection Discussion | 10 | 3/6/06 10:23 PM |