There is 2x10 for rafter material being used. In the northern states r-38 is required in ceilings, how would you insulate the rafters if it was a vaulted ceiling (meaning they want to attach drywall directly to the rafters for a sloped ceiling) 2x10 measures 9 1/2" in depth, what materials would you use to acheive the r-38 requirments and yet have the 1" air gap against the roof deck sheating???

Ridge insulation then batts of some sort?????????????????
Reply With Quote
  #2  
Old 3/27/07, 11:24 AM
phinsperger's Avatar
phinsperger phinsperger is offline
Active Poster
 
Join Date: Dec 2003
Location: Orangeville, ON
Posts: 1,845
Please Note: phinsperger is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Insulation requirements question

Yes. That's one way. Working from the underside of the roof deck;- staple up your vents,- then put up the batts in between the rafters- then put up rigid foam insulation sheets covering both the batts and the rafters- then drywall.It will perform better because of the thermal bridge break. If you are diligent in sealing up the seams of the foam sheets it will also provide as a very good vapor barrier.
Reply With Quote
  #3  
Old 3/27/07, 4:33 PM
brepanshek brepanshek is offline
Active Poster
 
Join Date: May 2006
Location: York, PA
Posts: 235
Please Note: brepanshek is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Insulation requirements question

How would this give you the required R-38??
Batt insulation (R value ??) + ridge insulation board (R value ??) = R-38
describe the types of insulation materials you would use.
Reply With Quote
  #4  
Old 3/27/07, 6:59 PM
Robert J. OConnor's Avatar
Robert J. OConnor Robert J. OConnor is offline
Active Poster
 
Join Date: Jul 2003
Location: East Northport, NY
Posts: 741
Default Re: Insulation requirements question

Quote:
Originally Posted by phinsperger
Yes. That's one way. Working from the underside of the roof deck;- staple up your vents,- then put up the batts in between the rafters- then put up rigid foam insulation sheets covering both the batts and the rafters- then drywall.It will perform better because of the thermal bridge break. If you are diligent in sealing up the seams of the foam sheets it will also provide as a very good vapor barrier.
Careful ... because typical batts already has a vapor barrier on the back side of the paper. You don't want a double vapor barrier that may trap moisture.

JMO



Robert O'Connor, PE
Consulting Engineer & Inspector
LIU CW Post Adjunct Professor
NACHI Education Committee
www.reporthost.com/rjo

I am absolutely amazed sometimes by how much thought goes into doing things wrong ...
Reply With Quote
  #5  
Old 3/27/07, 7:04 PM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 12,356
Default Re: Insulation requirements question

Quote:
Originally Posted by brepanshek
How would this give you the required R-38??
Batt insulation (R value ??) + ridge insulation board (R value ??) = R-38
describe the types of insulation materials you would use.
Hi. Brian;

Paul directed you well, he just did not quote you any values.
Maybe I can help you with that.

Once you have installed your baffle vents for continuous venting from soffit to ridge vent, the only comfortable space left for insulation (batt) is 8".

Batt insulation has an R-Value of 3.14 per inch so this would equal 25.12. or a high density would be r- 30.
Required R-Values for roofs in the NorthEast is R-38 38.
Deficit -12.88


Paul recommended Polystyrene, I believe and that is 5.00 p.i. 2" = 10

Polyisocyanurate has an R-Value of 7.20 P. I. 1 &1/2" = 10.8 2"= 14.4

Either one, you would have to strap the ceiling in order to sheetrock, unless one wants to use extra long screws.

Alternatives:

Icceynene Spray foam open cell 3.6 R-Value per inch

Polyurethane Spray foam closed cell 6-7 R-Value per inch

One has more insulating values as well as price.

Hope this helps.

Marcel




Cyr Home and Commercial Property Inspections

IAC2 Certified
NACHI04070211
http://co.nachi.org/inachiawards


Commercial Builder
CertainTeed
Master Shingle Applicator
Shingle Technology
Ouellet Associaties Inc.
http://www.oaconstruction.com/

Last edited by mcyr; 3/27/07 at 8:43 PM..
Reply With Quote
  #6  
Old 3/27/07, 8:13 PM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 5,730
Default Re: Insulation requirements question

Quote:
Originally Posted by mcyr


Once you have installed your baffle vents for continuous venting from soffit to ridge vent, the only comfortable space left for insulation (batt) is 9".


Pssst!...Marcel. 2x10's are 9 1/4", minus 1" for the venting equals 8 1/4"...but you are giving some valuable information.



____________________________________________
"An Education, not just an Inspection"

Larry Kage
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector and Infrared Thermographer serving the Traverse City, Michigan area and beyond.


ITC/FLIR CERTIFIED BUILDING SCIENCES THERMOGRAPHER

ITC/FLIR CERTIFIED LEVEL 1 THERMOGRAPHER
Reply With Quote
  #7  
Old 3/27/07, 8:46 PM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 12,356
Default Re: Insulation requirements question

Sorry Larry;

Thanks for the warning, just too many numbers in my head I guess.
Corrected my post, hope I got it right this time. ha. ha.


Marcel




Cyr Home and Commercial Property Inspections

IAC2 Certified
NACHI04070211
http://co.nachi.org/inachiawards


Commercial Builder
CertainTeed
Master Shingle Applicator
Shingle Technology
Ouellet Associaties Inc.
http://www.oaconstruction.com/
Reply With Quote
  #8  
Old 3/27/07, 9:05 PM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 5,730
Default Re: Insulation requirements question

Ahhh...no "warning" meant, Marcel...just funnin' ya...

You are a wealth of good info, thanks.



____________________________________________
"An Education, not just an Inspection"

Larry Kage
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector and Infrared Thermographer serving the Traverse City, Michigan area and beyond.


ITC/FLIR CERTIFIED BUILDING SCIENCES THERMOGRAPHER

ITC/FLIR CERTIFIED LEVEL 1 THERMOGRAPHER
Reply With Quote
  #9  
Old 3/27/07, 9:48 PM
phinsperger's Avatar
phinsperger phinsperger is offline
Active Poster
 
Join Date: Dec 2003
Location: Orangeville, ON
Posts: 1,845
Please Note: phinsperger is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Insulation requirements question

You can also use a foil faced ridged foam like Energy Sheild for example. Because the foil reflects radiant heat it adds an effective ~R2.2 to the value of the foam for any given thickness. Mineral wool batts also have a slightly higher R value than fiberglass.

Last edited by phinsperger; 3/27/07 at 9:49 PM.. Reason: typo
Reply With Quote
  #10  
Old 3/28/07, 1:51 AM
Randy L. Thomas Randy L. Thomas is offline
New User
 
Join Date: Mar 2007
Location: Oregon
Posts: 11
Please Note: Randy L. Thomas is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Insulation requirements question

Be aware that the code allows for R-30 (normally batts) for vaulted ceilings and R-38 (normally blown-in) for flat ceilings. The vaulted ceiling allowance is good for up to 50% of the ceiling surface area. Anything over that requires R-38. As mentioned in thread above, if there is inadequate space for conventional insulation, then higher R-value material must be used.
Reply With Quote
  #11  
Old 3/29/07, 8:32 PM
Larry Ewens's Avatar
Larry Ewens Larry Ewens is offline
InterNACHI Member
 
Join Date: Feb 2005
Location: Brantford, On
Posts: 778
Send a message via AIM to lewens
Default Re: Insulation requirements question

Two by strapping would take care of the problem. It will give you the required 1" air space and enough left to insulate to required value. The only problem I see is the strapping may interfere with the window height.
Larry



Larry Ewens
1578 Colborne St
Brantford On
Nachi ID #05022485
Just my usual 12.5 cents


http://acissbrant.blogspot.com/

Reply With Quote
  #12  
Old 3/29/07, 8:35 PM
Larry Ewens's Avatar
Larry Ewens Larry Ewens is offline
InterNACHI Member
 
Join Date: Feb 2005
Location: Brantford, On
Posts: 778
Send a message via AIM to lewens
Default Re: Insulation requirements question

Quote:
Originally Posted by roconnor
Careful ... because typical batts already has a vapor barrier on the back side of the paper. You don't want a double vapor barrier that may trap moisture.

JMO
This is strange as I have not seen paper backed batts since the sixties.
Larry



Larry Ewens
1578 Colborne St
Brantford On
Nachi ID #05022485
Just my usual 12.5 cents


http://acissbrant.blogspot.com/

Reply With Quote
  #13  
Old 3/29/07, 8:43 PM
Keith R. Braun's Avatar
Keith R. Braun Keith R. Braun is offline
InterNACHI Member
 
Join Date: Oct 2006
Location: Buffalo, NY
Posts: 103
Default Re: Insulation requirements question

Purchased at the local Home Depot when I insulated my own 2x10 cathedral ceiling: styrofoam baffles & r-30 owens corning fiberglass(kraft faced)
Code in Buffalo called for r-30.



Keith R. Braun,

Western New York Chapter

Vice President for Education
Reply With Quote
  #14  
Old 3/31/07, 10:40 AM
Robert J. OConnor's Avatar
Robert J. OConnor Robert J. OConnor is offline
Active Poster
 
Join Date: Jul 2003
Location: East Northport, NY
Posts: 741
Default Re: Insulation requirements question

Quote:
Originally Posted by lewens
This is strange as I have not seen paper backed batts since the sixties.
Larry
Not sure what type of insulation is used in you area, but in my neck of the woods almost all the faced insulation blankets are made with kraft paper facing that has a tar like coating on the back side which serves as a vapor retarder which is just called paper faced batts ... e.g.

http://www.jmhomeinsulation.com/howt...&install=Batts

JMO



Robert O'Connor, PE
Consulting Engineer & Inspector
LIU CW Post Adjunct Professor
NACHI Education Committee
www.reporthost.com/rjo

I am absolutely amazed sometimes by how much thought goes into doing things wrong ...
Reply With Quote
  #15  
Old 3/31/07, 3:18 PM
homebild homebild is offline
Active Poster
 
Join Date: Nov 2006
Location: Pennsylvania
Posts: 195
Please Note: homebild is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Insulation requirements question

Quote:
Originally Posted by brepanshek
There is 2x10 for rafter material being used. In the northern states r-38 is required in ceilings, how would you insulate the rafters if it was a vaulted ceiling (meaning they want to attach drywall directly to the rafters for a sloped ceiling) 2x10 measures 9 1/2" in depth, what materials would you use to acheive the r-38 requirments and yet have the 1" air gap against the roof deck sheating???

Ridge insulation then batts of some sort?????????????????
Careful.

Pennsylvania allows a wide variety of compliance paths for energy conservation and Code complinace, and R-38 is not always required for ceiling insulation in Pennsylvania.

One can use Chapter 11 of the IRC 2006, the 2006 Pennsylvania Alternative Energy Code, the Department of Energy RESCheck software, and many various alternative complinace methods and approaches under the 2006 IECC.

R-38 for ceiling insulation is not written in stone in Pennsylvania and most designs do not include R-38 anymore.

The IECC allows, for example, that in a cathedral ceiling, you can use R-30 and still comply with the Code provided that the area of the cathedral ceiling with less than R-38 insulation is less than 500 square feet. (404.2.2 2006 IECC)

REScheck and other performance based compliance methods allows one to reduce ceiling insulation R-values provided wall insulation, window U-factors, or heating and cooling system efficiciencies are increased to make up the difference.

If you suspect a less-than-expected level of insulation on Pennsylvania, have your client refer to the local Residential Energy Codes Inspector for the municipality to verify the structure is compliant.

You can see the Pennsylvania Alternative Energy Code online here:

http://www.dli.state.pa.us/landi/lib/landi/ucc/pa_alternative_2006.pdf

You can see the Department of Energy RESCheck and other types of performance based software here:

http://www.energycodes.gov/

Last edited by homebild; 3/31/07 at 3:21 PM.. Reason: q
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
IAC2 In new residential construction mcyr IAC2 Forum 0 10/9/07 7:45 PM
PIC of State Rep and sponsor of new NACHI H.I. Bill in NH. gromicko Misc. Discussion 53 8/30/06 6:58 PM
sub flooring insulation Question? cpetty General Inspection Discussion 10 3/6/06 10:23 PM


All times are GMT -4. The time now is 4:41 AM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts