Default I-Joist alterations

Observed notching of an I-joist at a recent inspection. PVC piping is 3". I know this is improper, but how can this be repaired? Would you recommend investigation by a licensed g.c. familiar with I-joist aspects or a structural engineer.
Attached Thumbnails
joist-alterations-hpim6705.jpg  
Reply With Quote
  #2  
Old 3/8/09, 5:43 PM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 19,788
Default Re: I-Joist alterations

Quote:
Originally Posted by salstad View Post
Observed notching of an I-joist at a recent inspection. PVC piping is 3". I know this is improper, but how can this be repaired? Would you recommend investigation by a licensed g.c. familiar with I-joist aspects or a structural engineer.

Neither, possibly.

Take a look at page 11 of this PDF.

http://www.ilevel.com/literature/TJ-4000.pdf

Some holes in the web of I-joist are permitted by the manufactures depending on size and location.
Reply With Quote
  #3  
Old 3/8/09, 6:07 PM
Sidney Alstad Sidney Alstad is offline
InterNACHI Member
 
Join Date: Mar 2009
Location: Blue Ridge Mountains, NC
Posts: 124
Default Re: I-Joist alterations

Quote:
Originally Posted by mcyr View Post
Neither, possibly.

Take a look at page 11 of this PDF.

http://www.ilevel.com/literature/TJ-4000.pdf

Some holes in the web of I-joist are permitted by the manufactures depending on size and location.
Question regarding the chart on page 11. If the I-Joist is a 11 7/8 TJI 230 then a 4" notch must be 2 feet from the end of the I-joist, is this correct?

Thank you for your response.
Reply With Quote
  #4  
Old 3/8/09, 6:15 PM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 19,788
Default Re: I-Joist alterations

Quote:
Originally Posted by salstad View Post
Question regarding the chart on page 11. If the I-Joist is a 11 7/8 TJI 230 then a 4" notch must be 2 feet from the end of the I-joist, is this correct?

Thank you for your response.
That is the way I see it, Sidney.

Marcel
Reply With Quote
  #5  
Old 3/8/09, 11:14 PM
tdietrich1's Avatar
tdietrich1 tdietrich1 is offline
InterNACHI Member
 
Join Date: Oct 2006
Location: Northampton County - Pa
Posts: 1,954
Send a message via Yahoo to tdietrich1
Default Re: I-Joist alterations

Wow, look at the size of that spider.

tom
Reply With Quote
  #6  
Old 3/9/09, 6:27 AM
Richard A. Hetzel Richard A. Hetzel is offline
Unmoderated Guest
 
Join Date: Apr 2007
Location: Tobyhanna, Pennsylvania
Posts: 598
Please Note: Richard A. Hetzel is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: I-Joist alterations

Unless I'm reading the chart incorrectly, a four-inch hole can be a minimum of one foot from the end. By the way, it is a hole, not a notch. A "notch" would be a cut from either the top or bottom flange, and that is not favored at all by composite joist manufacturers.
Reply With Quote
  #7  
Old 3/9/09, 8:56 AM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 19,788
Default Re: I-Joist alterations

Quote:
Originally Posted by Richard A. Hetzel View Post
Unless I'm reading the chart incorrectly, a four-inch hole can be a minimum of one foot from the end. By the way, it is a hole, not a notch. A "notch" would be a cut from either the top or bottom flange, and that is not favored at all by composite joist manufacturers.
Richard, I believe you have to go to the chart on the right for square holes. The distance increases to 2'.

Marcel
Reply With Quote
  #8  
Old 3/10/09, 4:54 PM
Richard A. Hetzel Richard A. Hetzel is offline
Unmoderated Guest
 
Join Date: Apr 2007
Location: Tobyhanna, Pennsylvania
Posts: 598
Please Note: Richard A. Hetzel is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: I-Joist alterations

Bingo!
Reply With Quote
  #9  
Old 3/10/09, 7:52 PM
Wayne B. Wilson's Avatar
Wayne B. Wilson Wayne B. Wilson is online now
InterNACHI Member
 
Join Date: Aug 2008
Location: Powell, Tn
Posts: 8,230
Default Re: I-Joist alterations

Quote:
Originally Posted by tdietrich1 View Post
Wow, look at the size of that spider.

tom
Ah thats nothing cant wait for the summer of black widows and brow recluse
Reply With Quote
  #10  
Old 3/16/09, 12:59 AM
Kenton H. Shepard, CMI's Avatar
Kenton H. Shepard, CMI Kenton H. Shepard, CMI is offline
InterNACHI Member
 
Join Date: Aug 2004
Location: Boulder, CO
Posts: 3,417
Send a message via ICQ to kshepard
Default Re: I-Joist alterations

Quote:
Originally Posted by tdietrich1 View Post
Wow, look at the size of that spider.

tom
That's just a grandaddy-long-legs.




Kenton Shepard, InterNACHI member # 04082383
Certified Master Inspector (CMI)
InterNACHI Director of International Development
Director of Green Building

EXPERT WITNESS SERVICE
Conventional and Log homes

(303) 717-8940
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Support beam tied to TJI Joist? crichiii Structural Inspections 1 9/5/08 1:57 PM
Cutout of joist for toilet drain Nathan W. Swilling Structural Inspections 33 6/26/08 1:48 AM
Max load allowed on 2x2 ledger bking Structural Inspections 4 12/23/07 2:05 PM
Frost, Ice, & Condensation @ RIM JOIST Sean M. Jeric Inspecting HVAC Systems 4 2/5/07 6:56 PM


All times are GMT -4. The time now is 10:57 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts