Default Joist blocking

Am I missing something here?

Shouldn't these joists be blocked at the ends if they are not attached to the adjacent joist to prevent them from rotating laterally?

joist-blocking-dscf1711-small-.jpg.JPG
Views:	135
Size:	44.4 KB
ID:	9308

joist-blocking-dscf1713-small-.jpg.JPG
Views:	94
Size:	43.2 KB
ID:	9309



Jeffrey Wortham
ANS Inspections, Inc.
www.ansinspections.com
630.276.8440
638 Langford Drive
Bolingbrook, IL 60440
NACHI ID:04050181
Reply With Quote
  #2  
Old 2/20/07, 12:17 AM
Claude Lawrenson's Avatar
Claude Lawrenson Claude Lawrenson is offline
InterNACHI Member
 
Join Date: Dec 2003
Location: Tecumseh-Windsor, ON
Posts: 1,567
Default Re: Joist blocking

Up here in Canada - this can be resolved by cross-bridging at third points or near mid-span? Solid blocking could also be used. Unless you see this as a code issue in your area.



Cheers, Claude Lawrenson NACHI03121515
Inspection Support Services Inc.

"It is not the strongest of the species that survives nor the most intelligent, but the one most responsive to change." -Charles Darwin
Reply With Quote
  #3  
Old 2/20/07, 10:23 AM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,022
Default Re: Joist blocking

Bridging and blockings are usually installed in center spans when the underside is not getting a drywall ceiling.

These joists should be attached to each other with hardware and toe-nailed to the beam below it. With the spacing in your pic, the joists don't appear to be attached to each other.

"Click to Enlarge"
Attachment 9311

Last edited by dvalley; 10/7/07 at 5:42 PM..
Reply With Quote
  #4  
Old 2/20/07, 12:18 PM
whandley's Avatar
whandley whandley is offline
Active Poster
 
Join Date: Sep 2004
Location: Laguna Niguel, CA
Posts: 2,104
Please Note: whandley is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Joist blocking

Hey David, what do you think about this framing alteration? New, never lived in 4500'sf, wood frame/stucco structure. Found this added/altered roof framing configuration in one of the two attics. Appears the material was scabbed in after original construction. Don't know why painted material was used. I first thought maybe prior fire damage during original rough framing.

Thoughts?

Last edited by whandley; 7/21/07 at 2:52 AM..
Reply With Quote
  #5  
Old 2/20/07, 1:31 PM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 12,359
Default Re: Joist blocking

Quote:
Originally Posted by whandley
Hey David, what do you think about this framing alteration? New, never lived in 4500'sf, wood frame/stucco structure. Found this added/altered roof framing configuration in one of the two attics. Appears the material was scabbed in after original construction. Don't know why painted material was used. I first thought maybe prior fire damage during original rough framing.

Thoughts?
Harry O travels a lot I guess.

Must have dismanteled old swing sets or barricads to get the lumbe and never pounded a nail in his life.

That is unbelievable.
Hate to see what everything else looks like.

Marcel




Cyr Home and Commercial Property Inspections

IAC2 Certified
NACHI04070211
http://co.nachi.org/inachiawards


Commercial Builder
CertainTeed
Master Shingle Applicator
Shingle Technology
Ouellet Associaties Inc.
http://www.oaconstruction.com/
Reply With Quote
  #6  
Old 2/20/07, 3:39 PM
Thomas H. Dietrich's Avatar
Thomas H. Dietrich Thomas H. Dietrich is offline
InterNACHI Member
 
Join Date: Oct 2006
Location: Northampton County - Pa
Posts: 1,954
Send a message via Yahoo to tdietrich1
Default Re: Joist blocking

I know this isn't a code forum, and we all aren't code enforcement officers, but understanding where the building codes stand, helps me.

2006 IRC R502.7.1 "Bridging" Summery, not a concern unless the joist exceed a nominal 2x12.

Are these bigger than 2 by 12's?

tom
Reply With Quote
  #7  
Old 2/20/07, 6:18 PM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,022
Default Re: Joist blocking

Quote:
Originally Posted by whandley
Hey David, what do you think about this framing alteration? New, never lived in 4500'sf, wood frame/stucco structure. Found this added/altered roof framing configuration in one of the two attics. Appears the material was scabbed in after original construction. Don't know why painted material was used. I first thought maybe prior fire damage during original rough framing.

Thoughts?
You've got to be shi+ting me. Who the hell (in their right state of mind) is going to consider this rafter install legit?

I can't believe they went and stole that highway fencing and tried to use it to support a roofing load.
Reply With Quote
  #8  
Old 2/20/07, 6:22 PM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,022
Default Re: Joist blocking

I posted the wrong pic. This pic illustrates the support on a steel beam.

"Click to Enlarge"
Attachment 9321

Last edited by dvalley; 10/7/07 at 5:42 PM..
Reply With Quote
  #9  
Old 2/21/07, 11:43 PM
Kenton H. Shepard, CMI's Avatar
Kenton H. Shepard, CMI Kenton H. Shepard, CMI is offline
InterNACHI Member
 
Join Date: Aug 2004
Location: Boulder, CO
Posts: 2,487
Send a message via ICQ to kshepard
Default Re: Joist blocking

Quote:
Originally Posted by whandley
Hey David, what do you think about this framing alteration? New, never lived in 4500'sf, wood frame/stucco structure. Found this added/altered roof framing configuration in one of the two attics. Appears the material was scabbed in after original construction. Don't know why painted material was used. I first thought maybe prior fire damage during original rough framing.

Thoughts?
Will, judging from the quality of the top cuts and the nailing, the carpenter spent the money he was supposed to use to buy lumber on beer. Looks like his soberer buddy cut the bottoms of the overframe jacks.




Kenton Shepard, InterNACHI member # 04082383
Certified Master Inspector (CMI)
EXPERT WITNESS

Director of Green Building
Director for International Development

(303) 717-8940
(303) 258-8289

Reply With Quote
  #10  
Old 2/22/07, 12:22 AM
Kenton H. Shepard, CMI's Avatar
Kenton H. Shepard, CMI Kenton H. Shepard, CMI is offline
InterNACHI Member
 
Join Date: Aug 2004
Location: Boulder, CO
Posts: 2,487
Send a message via ICQ to kshepard
Default Re: Joist blocking

Quote:
Originally Posted by jwortham1
Am I missing something here?

Shouldn't these joists be blocked at the ends if they are not attached to the adjacent joist to prevent them from rotating laterally?
Yes Jeffrey, the joists should be blocked above the beam with solid blocking.

Anti-rotational devices can be installed in midspan, using either blocks or bridging (X-bracing), but they don't use midspans in many places any more. That's because they almost all SQUEAK and they aren't necessary.




Kenton Shepard, InterNACHI member # 04082383
Certified Master Inspector (CMI)
EXPERT WITNESS

Director of Green Building
Director for International Development

(303) 717-8940
(303) 258-8289

Reply With Quote
  #11  
Old 2/22/07, 9:10 AM
jwortham1 jwortham1 is offline
InterNACHI Member
 
Join Date: Jun 2006
Location: Bolingbrook, IL
Posts: 723
Default Re: Joist blocking

Thanks guys.

I recommended they be blocked and after some time looking at framing guides and the like, I am confident that blocking is needed.

I appreciate the input.



Jeffrey Wortham
ANS Inspections, Inc.
www.ansinspections.com
630.276.8440
638 Langford Drive
Bolingbrook, IL 60440
NACHI ID:04050181
Reply With Quote
  #12  
Old 2/22/07, 12:58 PM
Robert J. OConnor's Avatar
Robert J. OConnor Robert J. OConnor is offline
Active Poster
 
Join Date: Jul 2003
Location: East Northport, NY
Posts: 741
Default Re: Joist blocking

Quote:
Originally Posted by tdietrich1
2006 IRC R502.7.1 "Bridging" Summery, not a concern unless the joist exceed a nominal 2x12.
The IRC is a good "guide" for HI's. However, the provisions of R502.7.1 refer to larger joists (larger than 2x12 which is unusual) that need help keeping them from twisting between the end supports. Any required "bridging" is spaced no more than 8' apart.

However, it is considered good practice by many to install bridging/blocking between supports even for smaller joists about every 8' to 10' to help stiffen up a floor, even though it may not be required by codes.

All joists (not just ones larger than 2x12) need restraint at the ends ... which is usually done with a connection to the header/rim joist at the outside walls and solid blocking between the joists over interior walls/beams (per IRC R502.7)

JMO & 2-Nickels ...



Robert O'Connor, PE
Consulting Engineer & Inspector
LIU CW Post Adjunct Professor
NACHI Education Committee
www.reporthost.com/rjo

I am absolutely amazed sometimes by how much thought goes into doing things wrong ...
Reply With Quote
  #13  
Old 2/22/07, 1:13 PM
wforsyth's Avatar
wforsyth wforsyth is offline
Active Poster
 
Join Date: Feb 2006
Location: Brinnon, Wa
Posts: 7,928
Please Note: wforsyth is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Joist blocking

Quote:
Originally Posted by kshepard
Will, judging from the quality of the top cuts and the nailing, the carpenter spent the money he was supposed to use to buy lumber on beer. Looks like his soberer buddy cut the bottoms of the overframe jacks.
That is exactly what I was thinking. Someone pocketed the money.
Wow! That's one of the most blatant things I've ever seen. Very cocky and they must consider that nobody is going to tag them for it.
Reply With Quote
  #14  
Old 2/23/07, 3:54 AM
jbreazeale jbreazeale is offline
Active Poster
 
Join Date: Aug 2006
Location: Sardis, MS
Posts: 621
Please Note: jbreazeale is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Joist blocking

Dang, boys and girls, thet thar is one of thuh sorriest cuttin' n' nalen jobs ah ever seen. My Daddy and Granddaddy, master carpenters both, would roll over in their graves if they saw something like that. They wouldn't have let me get away with something like that on a chicken roost!
Reply With Quote
  #15  
Old 2/24/07, 11:48 AM
homebild homebild is offline
Active Poster
 
Join Date: Nov 2006
Location: Pennsylvania
Posts: 195
Please Note: homebild is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Joist blocking

Rob O'Conner said:

Quote:
"All joists (not just ones larger than 2x12) need restraint at the ends ... which is usually done with a connection to the header/rim joist at the outside walls and solid blocking between the joists over interior walls/beams (per IRC R502.7)"
According to what we have been instructed as IRC certfied Resdiential Code Inspectors by the ICC, The IRC R 502.7 does NOT require lateral support above girders overwhich floor joists intersect except in Seismic Zones D1 and D2.

The fact they are lapped and nailed to each other is enough to satisfy the lateral restraint at the ends requirement.

Hence, the joists in the original photo require no solid blocking between them unless the house is in an active earthquake zone or other local codes require it.

It is certainly a good idea to block joists over center bearing girders, and I am not arguing against the practice, but no requirement exists to block between floor joists when they terminate over a grider under the IRC except in high probablity earthquake zones... as the ICC explains it.

Last edited by homebild; 2/24/07 at 12:03 PM..
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Deck joist blocking/bridging jbancroft Structural 7 10/4/07 10:16 AM
Frost, Ice, & Condensation @ RIM JOIST Sean M. Jeric HVAC 4 2/5/07 7:56 PM
Proper notching of floor joist djohnson6 Structural 4 1/21/07 11:15 AM


All times are GMT -4. The time now is 3:33 PM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts