Temporay Screw Jacks.
...not fastened, secured or supported by footings..... Need to keep the handle in place as the base of the jack is pushing thru the slab...... Joseph P. Hagarty joseph.hagarty@comcast.net Main Line Inspections, Inc. Phone: 610-399-3675 Email: MainLineHI@comcast.net http://pa.nachi.org/mainlinepa/about.html http://www.householdinspector.com National President / NACHI (2003-2004) NACHI Education Committee Member Last edited by jhagarty; 2/18/08 at 4:34 PM.. |
|
#2
|
|||
|
|||
|
Please Note:
jbreazeale is a non-member guest and is in no way affiliated with InterNACHI or its members.
Looks like it's been there for a while, too, judging from the rust on the foot. And what does all that tell us about the slab?
|
|
#3
|
|||
|
|||
|
Please Note:
Richard A. Hetzel is a non-member guest and is in no way affiliated with InterNACHI or its members.
Concentrated load at base of column requires a properly sized footing. The floor slab alone is probably insufficient, as evidenced by the base plate pushing through the slab. Coumns need to be mechanically fastened to beam and footing.
|
|
#4
|
||||
|
||||
|
Nice carrying beam....Along with all the other defects, the bearing ends aren't even situated into pockets.
At least it has support posts. This main carrying beam (below) is being held in place with strapping secured to a floor joist. No support post whatsoever. "Click to Enlarge" Attachment 11485 Last edited by dvalley; 10/7/07 at 4:40 PM.. |
|
#5
|
||||
|
||||
|
David,
Any chance that "beam" isn't bearing but instead being used to stiffen the floor for ceramic tile or stone installation? It looks poorly done in either case. |
|
#6
|
||||
|
||||
|
Quote:
Besides that, I don't even care if it's a carrying beam or not. You don't strap a beam to the floor joists above. Duh.... Attachment 11486 Last edited by dvalley; 10/7/07 at 4:40 PM.. |
|
#7
|
|||
|
|||
|
Polish support beam
1st Inspection Services Bruce M. Graham III Gainesville, FL 32608 352 871 8989 Florida Licensed Home Inspector #HI10 Radon Measurment Technician # R2279 NACHI05091592 ICC 5268478 www.1stinspectionsfl.com www.bungalowstomansions.com |
|
#8
|
||||
|
||||
|
Quote:
Looks like a job by "Fly By Night Construction Specialists" |
|
#9
|
|||
|
|||
|
Please Note:
Alan Russell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Can we all sing the Mousecateer Construction Comapny's theme song...
MIC.....KEY..... |
|
#10
|
||||
|
||||
|
Quote:
Attachment 11509 Last edited by dvalley; 10/7/07 at 4:40 PM.. |
|
#11
|
|||
|
|||
|
Please Note:
Richard A. Hetzel is a non-member guest and is in no way affiliated with InterNACHI or its members.
Beam supporting joists supporting beam...why didn't I think of that?
|
|
#12
|
|||
|
|||
|
Please Note:
homebild is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
Structural Engineer or Architect required to evaluate loads, footings, column connections, girder sizes, spans, etc.... |
|
#13
|
|||
|
|||
|
Please Note:
Alan Russell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
myself!! |
|
#14
|
||||
|
||||
|
Quote:
|
|
#15
|
|||
|
|||
|
Please Note:
Richard A. Hetzel is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
|
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| Heavy timber posts and support beam | hziegenbein | Structural Inspections | 4 | 9/24/07 8:22 PM |
| Crack in Support Beam | Berry T. Wilson | Structural Inspections | 6 | 5/26/07 3:15 PM |
| Steel beam lateral support | Mark Ellison | Structural Inspections | 10 | 1/16/07 10:40 PM |
| Support post for Beam, is this right? | mlong | Structural Inspections | 74 | 7/25/06 7:47 PM |