This was on a detatched garage wall. The wall wasn't bowed. There was vertical hairline cracks down the entire wall(about 20'). Any ideas on what might be the cause?
![]()
Bobby Hamilton Bloodhound Home Inspection Services Youngstown Home Inspection Austintown Ohio Home Inspection Providing home inspections, state licensed termite inspections and radon testing in Youngstown, Boardman, Canfield, Poland, Howland, Warren and surrounding Northeast Ohio areas.
|
|
#2
|
||||
|
||||
|
Possible water drainage or intrusion problem maybe, then freezes. Hard to tell from just those two pics, but that would be my guess at first.
Ian Niquette Square One Home Inspection Markesan WI 53946 www.squareonehomeinspection.com Active Rain Network INACHI Awards Portal Want To Exchange Links? What we've got here is......failure......to communicate.....
|
|
#3
|
||||
|
||||
|
Please Note:
dgagneur is a non-member guest and is in no way affiliated with InterNACHI or its members.
Maybe it's just me and it's certainly hard to tell from these pics, but that top row (right side) looks like it might be tipped toward the house. That could put the entire weight on one edge of the block which could cause the block to crack. (This is in reference to the second pic).
|
|
#4
|
||||
|
||||
|
Was cracking uniform thought the home perimeter or just on one side. If one side, was it uniform throughout that side?
Kenton Shepard, InterNACHI member # 04082383 Certified Master Inspector (CMI) InterNACHI Director of International Development Director of Green Building EXPERT WITNESS SERVICE Conventional and Log homes (303) 717-8940
|
|
#5
|
|||
|
|||
|
Please Note:
Richard A. Hetzel is a non-member guest and is in no way affiliated with InterNACHI or its members.
It appears that the cracks are vertical, in a relatively straight line, with no displacement, either vertical from side to side of the crack, or horizontal, with one side moved out or in compared to the other. That would suggest expansion cracking, but not with so many cracks on one wall. The cracks are not likely caused by foundation settlement, or any impact, or any severe loading condition. The only remaining explanation is witchcraft. which I usually reserve only for electrical issues.
|
|
#6
|
||||
|
||||
|
Quote:
Bobby Hamilton Bloodhound Home Inspection Services Youngstown Home Inspection Austintown Ohio Home Inspection Providing home inspections, state licensed termite inspections and radon testing in Youngstown, Boardman, Canfield, Poland, Howland, Warren and surrounding Northeast Ohio areas.
|
|
#7
|
||||
|
||||
|
What is the required footer depth there? Looks like a handyman project with poor footers.
B.A. King Home Inspections, LLC www.BAKingHomeInspections.com Serving Charlotte NC area and Rock Hill SC areas. CMI Certified Master Inspector and Independent 704 301-3207 "Discovery consists in seeing what everyone else has seen and thinking what no one else has thought." - Albert Szent-Gyvrgyi, Nobel Prize for Medicine 1937 |
|
#8
|
|||
|
|||
|
Please Note:
Richard A. Hetzel is a non-member guest and is in no way affiliated with InterNACHI or its members.
If the FOOTINGS were defective, there would have been vertical displacement, and there is not. It's a mystery.
|
|
#9
|
||||
|
||||
|
Found this artical relative to the problem above.
Hope it helps a little. It has been a recent trend among architects / developers / builders to utilize single wythe cmu for low rise residential structures. The Masonry Industry has always promoted using a wall system that is designed with inherent redundancy against water penetration. Cavity walls with a clear drainage / airspace are always suggested for this reason. In the real world, however, this redundancy in design usually takes a back seat to economy. Since the margin for error is tighter when using these single wythe walls, there are several measures that should be taken during the design phase, during construction and throughout the life of the building. The major objective in designing dry concrete masonry walls is to keep water from entering or penetrating the wall. In addition to precipitation, moisture can find its way into masonry walls from a number of different sources. Dry concrete masonry walls are obtained when the design and construction addresses the movement of water into, through, and out of the wall. This includes detailing and protecting roofs, windows, joints, and other features to ensure water does not penetrate the wall. The following moisture sources need to be considered in the design for dry concrete masonry walls. Driving Rain Moisture in liquid form can pass through concrete masonry units and mortar when driven by a significant force. However, these materials generally are too dense for water to pass through quickly. If water enters the wall, it often can be traced to the masonry unit-mortar interface due to improperly filled joints or lack of bond between the unit and the mortar - emphasizing the importance of proper mortar selection, handling and installation. Cracks caused by building movements, or gaps between adjoining building segments (roofs, floors, windows, doors, etc.) and masonry walls are other common points of water entry. For this reason as an inspector, you should be looking for control joints in the block walls spaced no more than 30 feet apart. Capillary Suction Untreated masonry materials typically take on water through capillary forces. The amount of water depends on the capillary suction characteristics of the masonry and mortar. Integral water repellents greatly reduce the absorption characteristics of the units and mortar, but may not be able to prevent all moisture migration if there is a significant head pressure – 2 in. (51 mm) or more. Post-applied surface treatments reduce the capillary suction of masonry at the treated surface as well but have little effect on the interior of the units. Water as vapor diffuses toward a lower vapor pressure. This means it will move from the higher toward the lower relative humidity regions assuming no pressure or temperature differential. Vapor in air of the same humidity and pressure, but of different temperatures, will move from the higher temperature to the lower. As air is cooled, it becomes more saturated and when it reaches a temperature called the dew point, the water vapor will condense into liquid form. Integral water repellents make masonry materials hydrophobic, thereby significantly decreasing their water absorption and wicking characteristics. While these admixtures can limit the amount of water that can pass through units and mortar, they have little impact on moisture entering through relatively large cracks and voids in the wall. Therefore, even with the incorporation of integral water repellents, proper detailing of control joints and quality workmanship to preclude beeholes and unfilled or inadequate mortar joints is still essential. Another advantage of integral water repellents is that they not only help to keep water out but also inhibit the migration of water to the interior face of the wall by capillary suction. This integral water repellent, (Dry-Block for example) only adds a few cents to the cost of the block and our biggest manufacturer in Chicago, does not sell split face units without dry-block in it - a pro-active measure that has reduced the amount of callbacks for them and for myself. For colored architectural masonry it is recommended that a clear surface treatment be post-applied whether or not integral water repellent admixtures are used. Most post-applied coatings and surface treatments are compatible with integral water repellents although this should be verified with the product manufacturers before applying. When using standard units for single-wythe walls, an application of portland cement plaster (stucco), paint, or opaque elastomeric coatings works well. Coatings containing elastomerics have the advantage of being able to bridge small gaps and cracks. Walls incorporating integral water repellents should not be cleaned with a high-pressure wash as it drives water into the masonry. Acidic washes should not be used since they may reduce the water repelling properties of treated masonry. Keeping the masonry wall clean, as the construction progresses, using a brush and water minimizes cleaning efforts after the mortar has hardened. Consult the integral water repellent manufacturer for detailed cleaning recommendations. If I were building one of these buildings, I would do the following and this could be a nice checklist to use when inspecting such structures. 1. Use a block from a reputable manufacturer that contains integral water repellent. 2. Use real Portland / cement / lime mortar (not a pre-mixed masonry cement which contains air -entrainment additives) Type N - It is important to note that when using integral water repellents, there is a mortar additive that goes with it that needs to be added to EVERY batch of mortar used on the job- this keeps the mortar from absorbing moisture. 3. Detail walls with all flashing details suggested by the Masonry Advisory Council and NCMA. Use a quality flashing material, not the cheapest stuff available, such as IPCO self adhered rubberized asphalt flashing (www.illinoisproducts.com) 4. Specify hot dipped galvanized ladder type joint reinforcement in the bed joints of the block spaced at 16" o.c. vertically (every other course). 5. Specify and indicate control joints on project drawings in accordance with industry standards (no more than 30 feet apart) 6. Supervise the construction process insuring that all mortar joints are full and properly tooled (concave or vee joints) 7. Taking a belt and suspenders approach - apply a quality water repellent coating that is made specifically for concrete block. 8. Monitor the building closely looking for any cracks - caulk them. 9. Re-apply the water repellent coating periodically - 5-10 yrs. or as recommended by the manufacturer. 10. When mortar joints begin to show erosion, cracking or excessive wear - a proper repointing should be performed. We take our cars for oil changes every few months, and have them serviced regularly - remember that a building requires maintenance to perform properly just like our cars do. http://www.maconline.org/tech/materi...ycmuwalls.html Marcel LEED Green Associates InachiAwardsPortal: Inachi US Member of the Year Award 2009 |
|
#10
|
||||
|
||||
|
Austintown, Ohio, is about the same as we are in New Hampshire; cold/warm/cold/warm, repeat. Marcel's reply looks good. We see a lot of those situations here especially with something wicked porous like concrete block. Moisture, freeze, moisture, freeze... end up with cracks everywhere unless it is moisture-proofed in some fashion.
Harry "Bud" McClard Serving All of New Hampshire |
|
#11
|
|||
|
|||
|
Please Note:
Richard A. Hetzel is a non-member guest and is in no way affiliated with InterNACHI or its members.
Freeze-thaw cycles would probably cause spalling of the block surface, but I fail to see how they would cause the perfectly-straight closely-spaced vertical cracks pictured. I doubt that the wall is long enough to require control joints, so expansion-contraction cycles are probably not the cause either.
One question: are the cracks visible INSIDE the building also? |
|
#12
|
||||
|
||||
|
This depends on when it was built and who layed the CMU. Improper type mortar and lack of mortar moisture levels in the mortar is my guess.
When they lay CMU, if the CMU is too dry, it can cause the CMU to draw moisture out of the mortar, at the surface, and cause incomplete curing. Consistant harilines along the upper or side CMU is a clue. Kinda like when they pour a sidewalk or slab and don't keep it moist while it cures. If it drys before the curing is complete (usually, a couple of days), these cracks occur. Regularly see it in split faced block, around here. Hope this helps; Will Decker, CMI ILL License # 450.0002240 Board Certified Master Inspector Decker Home Services, LLC Chicago and Northern Suburban Home Inspections Office: (847) 676-8393 Cell: (847) 609-2345 Home: (847) 673-2702 wjd@DeckerHomeServices.com www.DeckerHomeServices.com Learn, Educate, Serve and have fun doing it! |
|
#13
|
||||
|
||||
|
I have seen this problem on heated garages and out buildings with uninsulated exterior block walls. Inside surface tries to expand while outside surface contracts. Especially when they use one of those 150,000 BTU Kerosene Heaters with a blower that heats up the inside area real fast.
"It's not what you believe that matters...it matters what you believe!" |
|
#14
|
|||
|
|||
|
Please Note:
Richard A. Hetzel is a non-member guest and is in no way affiliated with InterNACHI or its members.
Bingo, Mr. Lott...that's the best explanation so far, If the pictured garage has a heater in it.
|
|
#15
|
||||
|
||||
|
Quote:
Bobby Hamilton Bloodhound Home Inspection Services Youngstown Home Inspection Austintown Ohio Home Inspection Providing home inspections, state licensed termite inspections and radon testing in Youngstown, Boardman, Canfield, Poland, Howland, Warren and surrounding Northeast Ohio areas.
|
![]() |