Not much tower crane use here in Maine other than Portland, Maine now and then. Good pick-up Jeff. Marcel LEED Green Associates InachiAwardsPortal: Inachi US Member of the Year Award 2009 |
|
#17
|
||||
|
||||
|
I've raised a tower or two in my time. . .
IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ® Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net |
|
#18
|
||||
|
||||
|
I figured that much Jeff with the previous response.
Was a crane operator myself for awhile when younger and gave it up about 16 years ago, nerves cannot handle it and keep telling everyone that you can't run a crane and run a job at the same time. Was driving me nuts due to the vantage point. 60 ton hydraulic. Marcel LEED Green Associates InachiAwardsPortal: Inachi US Member of the Year Award 2009 |
|
#19
|
||||
|
||||
|
Please Note:
rbrady is a non-member guest and is in no way affiliated with InterNACHI or its members.
Here is a picture of the joist hangers and ledger. If my basic physics are correct the uplift would be about 2 to 1 based on the location of the beam, so if you had 700 pounds at the edge, you would have 1400 pounds of uplift.
Last edited by rbrady; 11/17/08 at 9:38 AM.. Reason: Correct leverage ratio |
|
#20
|
|||
|
|||
|
Please Note:
jkogel is a non-member guest and is in no way affiliated with InterNACHI or its members.
Agreed. Any kid that's built a tree fort could see that design is way wrong. They could have moved the doorway, probably just a garden storage shed, or constructed an arch over the door to support the beam properly. You are right to call for a repair.
John Kogel www.allsafehome.ca |
|
#21
|
|||
|
|||
|
Please Note:
Richard A. Hetzel is a non-member guest and is in no way affiliated with InterNACHI or its members.
How do you arrive at 700 pounds at the edge? Take one joist, assuming the joists are 16 inches on centers. Assume two people are standing back to front at the rail, at say 175 pounds per person. That's 350 pounds on one joist, over an area of 2.67 square feet, incidentally a load of about 130 PSF. The load isn't all at the very edge, so let's say its assumed to be at 12 inches from the beam. If the "main span" is 16 inches, then the uplift at the inside end of the joist is 350 x 16 / 24 = 233 pounds.
All of Simpson's face-mount joist hangers are capable of resisting at least that much uplift, and most will resist many times more, as can be seen here: http://www.strongtie.com/ftp/catalog...-2008-p082.pdf There is nothing wrong with the deck pictured, as long as the hangers are fully nailed as specified by the manufacturer. |
![]() |