Full two story brick veneer front with only 1" of foundation support. Home is six years old, no evidence of wall movement. I guess the wall ties are holding the wall in place.
![]() ![]()
Last edited by jevans; 6/27/10 at 8:50 PM.. |
| Need a home inspection in Georgia? Check out InterNACHI's listing of Georgia certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine. |
|
#2
|
||||
|
||||
|
Picture #1 looked like there was an angle iron under the brick.I've seen angle iron attached to the foundation and the brick setting on that.
|
|
#3
|
|||
|
|||
|
No angle iron present.
|
|
#4
|
||||
|
||||
|
LEED Green Associates InachiAwardsPortal: Inachi US Member of the Year Award 2009 |
|
#5
|
|||
|
|||
|
Thanks Marcel
|
|
#6
|
||||
|
||||
|
How do you find this stuff Marcel?? The great and powerful OZ
Infraspection Institute Level 1 Certified Infrared Thermographer Fogarty Inspection Services Group of Knoxville TN Home inspections, Commercial Inspections, Thermal Imaging, Mold, Enviromental Testing and Radon Testing for Knoxville TN, Oak Ridge TN, Maryville, Clinton, Farragut, Lenoir City, Pigeon Forge, Sevierville and all the surrounding areas. 865-256-5397 www.homeinspectorknoxville.com www.moldandradon.com www.thermal-inspection.net www.commercial-building-inspector.net |
|
#7
|
||||
|
||||
|
Looks like 2/3rd"s to me (hehe)
|
|
#8
|
||||
|
||||
|
Bob, what is that supposed to mean ??
Joe Keresztury JWK Inspections Home Inspections in San Antonio, Schertz, Cibolo, New Braunfels, Boerne and all surrounding South Texas areas www.jwkhomeinspections.com |
|
#9
|
||||
|
||||
|
Read the link.
Needs 2/3rds support. Corbelled, unreinforced masonry can overhang a foundation wall by up to 1/3 it's bed depth with 2/3 bearing on the concrete wall. |
|
#10
|
|||
|
|||
|
Hey Bob,
Just to clarify your response, at least 2/3rds is unsupported (2 1/2"). Agent contacted the builder regarding a structural warranty, builder claims the warranty only covers the 1st year. I plan to follow up on this one, would like to know the proposed fix. |
|
#11
|
||||
|
||||
|
2-1/2"x5"x5/16" galvanized steel angle bolted to the wall with quick bolts.
LEED Green Associates InachiAwardsPortal: Inachi US Member of the Year Award 2009 |
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| Why do brick spall? | mbryan | Exterior Inspections | 68 | 9/1/11 10:10 PM |
| Common Defects List by Age of House | trausch | Inspection Education & Training | 10 | 6/12/06 4:52 AM |
| Massachusetts Clay Brick Education | ajalowsky | Miscellaneous Discussion for Inspectors | 2 | 2/22/06 6:34 PM |