#1
|
||||
|
||||
|
Moisture Testing of Concrete Slabs When 3 lbs is not 3 lbs Fig. 1: Problems such as these warped and bubbled floor tiles can be caused by moisture and moisture-induced high pH levels beneath the flooring materials Fig. 2: Typical calcium chloride test kit containing a dish, calcium chloride crystals, and a plastic dome The long-awaited day has come, the project is complete, and everyone involved is eager to show off the new look of the facility. But wait a minute. Something is terribly wrong. Adhesive is bleeding through joints between the floor tiles, and there are bubbles in the sheet goods (Fig. 1) and epoxy flooring. Worse yet, there is a noticeable odor in the air. Sabotage? No, unfortunately what is occurring on this project has become all too common across the country. Such problems are being caused by moisture and moisture-induced high pH levels beneath flooring materials. How can this be? The slabs were tested for moisture, and the results appeared to comply with the requirements of the flooring material manufacturer. To understand what happened on this project and many others, we must examine a test method that is commonly used in the U.S. to quantify the moisture vapor emission rate (MVER) of a concrete subfloor. The method, the calcium chloride test developed by the Rubber Manufacturers Association (RMA) in the 1950s, is now published as ASTM F 18691 by ASTM International. MVER testing by the calcium chloride method involves placing an open dish containing a specified, known weight of anhydrous calcium chloride crystals beneath a plastic dome that is sealed to the concrete surface for 60 to 72 hours (Fig. 2). During the test, the crystals absorb moisture vapor in the air beneath the plastic dome. At the end of the exposure period, the difference between the initial and final weight of the crystals is used to calculate the MVER in pounds of water per thousand square feet per 24 hours (commonly referred to simply as “lbs”). By Peter Craig and George Donnelly 24 september 2006 / Concrete international Today, manufacturers of most flooring materials and coatings require that the MVER not exceed a 3-lb or, in some cases, a 5-lb limit. WHAT HAPPENED? So how do floors that initially test to an acceptable level end up testing to a much higher rate after a problem develops? We’ve found that the following five conditions can contribute to artificially low emission-test results, inaccurate results, or an increase in moisture within the slab once the flooring is installed. Curing, sealing, or bondbreaking compounds Curing, sealing, or bondbreaking compounds are commonly used in concrete slab construction and inhibit the release of free moisture from within the slab. These materials are designed to provide moisture retention for curing, surface densification, or the free release of concrete tilt-up wall panels cast on the slab. Most flooring material manufacturers and flooring standards require that these materials be removed before the flooring is installed. Testing conducted over a curing, sealing, or bondbreaking compound will result in a considerably lower MVER than will exist after the material is removed. Adhesive residue from previous flooring Adhesive residue is found on most remodeling projects. Testing surfaces without fully removing these residues can lead to artificially low test results. In all cases, we must realize that, while each test occupies less than 1 ft 2 (0.09 m 2) of floor area, the results are considered to represent the surrounding 1000 ft2 (90 m2). Preparation of the test site must assure that the concrete surface is free from any material or substance that could hinder the free release of moisture from the slab. Light, dry vacuumgrinding is the most practical and reliable means of properly preparing a concrete slab surface for testing. HVAC system operation Conducting calcium chloride tests before doors and windows are installed or before heating, ventilation, and air conditioning (HVAC) systems have been activated can result in MVERs that are different than those that would be measured with the building under its normal operating environment. Bare concrete is a hygroscopic material that will take on or give up moisture depending upon its surroundings. For calcium chloride test results to be as meaningful as possible, it’s essential that the tests be conducted with ambient conditions above the slab that are close to the building’s normal operating environment. Because flooring installations are frequently scheduled to occur before HVAC systems are in operation, this is often a difficult requirement to meet. ASTM F 1869 sets requirements for calcium chloride testing that include the testing environment. The standard allows testing in environments that are not under HVAC control within certain reasonable parameters (75 ± 10 °F [23.9 ± 5.6 °C] and 50 ± 10% relative humidity). Temporary forced drying of the top surface of the concrete may bring calcium chloride test results to a desired level, only to result in flooring problems at a later date due to moisture redistribution within the concrete once the slab is covered. Redistribution of moisture Most experts in moisture testing believe that the calcium chloride test is an indicator of moisture present in only the top 1/2 to 3/4 in. (13 to 19 mm) of the slab. As slab-on-ground concrete dries from the top down, it’s common for a closed-in, uncovered slab to have a lower moisture content in the top portion of the slab than in the lower regions. Once the slab is covered, moisture will redistribute within the slab, which most often leads to a higher amount of moisture in the upper region than when the emission tests were conducted. Redistribution of moisture within the slab after it’s covered is a major contributor to higher emission results being observed when the floor is retested after a problem has developed. Below-slab vapor retarder Without effective, low-permeance moisture protection directly beneath the slab, moisture migrating from sources below the floor can, over time, lead to an increase in the moisture content of the slab after the flooring material is installed. 2 Once the slab is covered, relative humidity beneath the slab will often measure close to 100% regardless of the depth of the water table or soil moisture content. The relative humidity in the slab will also increase and can also rise close to 100%. Without an effective vapor retarder directly beneath the slab even a properly measured 3-lb floor will not remain 3 lb for very long once the floor is covered. WHAT CAN WE DO? The following suggestions for conducting calcium chloride tests can help provide the most meaningful test results for evaluation: Always completely remove curing, sealing, and bondbreaking compounds or adhesive residue by dry, mechanical methods such as light vacuum grinding before conducting the tests; Always conduct tests when ambient conditions reflect the normal operating environment of the facility. On projects where HVAC systems are not active, insist on closing in a number of rooms or spaces where conditions can either be brought to anticipated normal conditions or into compliance with the environmental requirements of ASTM F 1869; Concrete international / september 2006 25 Conduct testing using both the standard ASTM F 1869 method and a modified method that can give an indication of the effects on MVER that are likely after the floor is covered. In this modified method, curing, sealing, and bondbreaking compounds or adhesive residue are completely removed from a 20 x 40 in. (0.5 x 1.0 m) area, half of which is then covered with aluminum foil, solid vinyl, or rubber for a period of time before the start of testing. The time period for moisture to equalize within the slab will vary; therefore, the longer one can leave the area covered before the start of testing the better. In no case should the time period be less than 1 week, and 2 to 4 weeks is recommended when the schedule will allow. Weight down the cover material to be sure it remains in direct contact with the slab surface. After the cover period, conduct two calcium chloride tests at each location. First, remove the cover material, and immediately place one test kit on the surface of the concrete that has just been uncovered. Next, place a second test kit on the prepared concrete surface adjacent to the area that was covered. The comparative results of these tests serve as an indicator of changes in MVER that are likely to occur once the floor is covered; Use internal relative humidity testing (ASTM F 21703) to complement and help with the interpretation of calcium chloride test results. In-place concrete relative humidity tests are widely used in Europe to determine when a flooring installation can proceed safely. In 2003, ASTM F 2170 was introduced in the U.S. for relative humidity testing in concrete. The test procedure calls for measuring the internal relative humidity of concrete (Fig. 3) at a depth of 40% of the slab thickness below the slab surface 72 hours after the drilled test holes and sleeves have been installed. The target level for in-place relative humidity given in ASTM F 7104 is 75% or lower, but several floor covering manufacturers allow a maximum of 80%. It’s important that the sensors are left in place long enough to reach a stable reading. This time period will vary with the type of sensor used and can take up to 3 hours. If sensors are not installed in the sleeves for the entire test period, it’s recommended that they be installed the night before the readings are taken; and If any moisture test result is to be relied upon, it’s important to remember that adequate moisture protection must be in-place directly beneath the slab so that moisture levels within the concrete will not increase significantly once the flooring is installed. Without it, the MVER may increase over time once flooring or coating material is installed. WHO SHOULD CONDUCT THE TESTS? Preinstallation moisture and pH testing should be conducted by personnel qualified to conduct the tests in accordance with ASTM standards. Interpretation or evaluation of the moisture and pH test results should be made only by those experienced with the testing methods, moisture migration, conditions, influences, and the floor covering manufacturer’s requirements. The calibration of test equipment should be maintained and checked before Fig. 3: The internal relative humidity at a depth of 40% of the slab thickness is measured with a digital meter connected to a hygrometer sensor installed in a hole drilled after the slab has hardened: (a) a common system uses a hand-held meter and a probe that’s plugged into plastic sleeves installed in the slab; and (b) a recently developed system uses a self-contained probe and meter that remain in the slab (a) (b) NOTICE TO ACI MEMBERS ACI officers to be elected via web-based baloting The Board of Direction at its Fall 2005 meeting agreed to transition toward web-based balloting, instead of letter balloting, for the annual election of ACI’s officers. In January 2006, a letter ballot to revise the Bylaws to allow for web-based balloting was mailed to and overwhelmingly approved by ACI’s voting members. Later this year, ACI members with a valid and current e-mail address will receive an e-mail notification when the ballot is open, along with a link to access the ballot from the ACI website. Secure website protocols will ensure that only eligible voters are able to access the ballot and that only one ballot is cast per voter. Members without Internet access but still wishing to participate in the balloting may request a hard copy ballot—to be completed and returned to ACI headquarters by the due date. All requests can be directed to: Jeri Kolodziej, Manager, Governance Support American Concrete Institute P.O. Box 9094 Farmington Hills, Michigan USA 48333 Telephone: (24 26 september 2006 / Concrete international Fig. 4: A properly installed, low-permeability vapor retarder prevents moisture from migrating up through the slab Photo courtesy of William Munyan the start of each project. No flooring installation should proceed without the approval of those responsible for the installation warranty. If ample concrete drying time can’t be provided in the construction schedule, a topical moisture and pH suppression system should be incorporated into the project costs from the very beginning. WHAT SHOULD WE EXPECT? Properly conducted calcium chloride tests often result in values higher than the 3-lb MVER required by most flooring material manufacturers. The normal construction timeline seldom provides sufficient time or an adequate environment for a new slab to dry and test to a 3-lb requirement. Knowledge of the ambient conditions before and during calcium chloride testing can help determine if reaching the target MVER is achievable. Rewetting a concrete surface after a period of drying has been shown to increase the MVER. 5 Because an open slab surface will take on moisture from the air, testing during and after periods of high ambient relative humidity will make achieving a 3-lb MVER difficult, if not impossible. Even if the ambient relative humidity is subsequently reduced, reaching a 3-lb MVER may not be possible within a short period of time. Because it’s measured at a depth of 40% of the slab’s thickness, the internal relative humidity test is far less sensitive to ambient conditions than the calcium chloride test. Slab temperature is a consideration and is recorded by the sensor, along with the concrete’s internal relative humidity. Concrete internal relative humidity test results can not only help determine the moisture-related suitability of a concrete subfloor, but they can also help determine whether the inability to reach a 3-lb emission rate is the result of ambient conditions prior to the test or moisture present at a high level deeper within the concrete. A new type of stay-in-place relative humidity sensor has been recently introduced that can help the project team monitor the drying of new concrete placements. Several of these sensors are installed in each slab placement once the roof is on, the building closed in and watertight, and any curing compound is removed. When the weekly readings reach a relative humidity less than 80%, the testing firm can be contacted to conduct the full ASTMcompliant, preinstallation moisture study with reasonable confidence of favorable results. This approach can save thousands of dollars in repetitive moisture testing costs. RECOMMENDATIONS Most problems with floor coverings over concrete slabs-on-ground can be avoided by using a properly designed slab system (Fig. 4) and providing ample drying time or using commercial drying services. A low-permeance vapor-retarding material, properly installed and in direct contact with the underside of the slab, greatly reduces the likelihood of moisture moving from the ground into the concrete and shortens the concrete drying time. 2 Concrete to receive floor coverings or coatings can be cured with dry, wet-strength curing paper or lay-flat polyethylene for up to 7 days. These methods don’t retard the loss of moisture from the slab beyond the curing period. Slabs cast in the open, however, are subject to rewetting until the building is enclosed and watertight. If a curing compound is used for initial curing or rewetting protection for slabs placed in the open, the material must be completely removed from the slab surface as soon as the building is considered watertight. Otherwise, a letter of compatibility must be obtained from both the floor covering and adhesive manufacturers. Our experience has been that most manufacturers of flooring materials will not issue such a letter, making removal of the curing compound a requirement. Removal should not be delayed beyond enclosure of the building to provide as much drying time as possible before moisture testing. Finally, the slab must be reliably tested and the data presented to the flooring manufacturer, flooring contractor, general contractor, architect, owner, and any other party associated with the flooring installation. We’re fully aware that these recommendations go well beyond what is presently being done or required on most projects. Given the very common, serious, and costly nature of flooring failures, however, it’s believed that these measures are necessary to reduce the risk of flooring problems and the significant cost associated with failure of the flooring system. Marcel Cyr Home and Commercial Property Inspections CMI IAC2 Certified NACHI04070211 http://co.nachi.org/inachiawards/inachiawards551.html http://co.nachi.org/inachiawards Commercial Builder Ouellet Associaties Inc. http://www.oaconstruction.com/ |
|
#2
|
||||
|
||||
|
Marcel,
It has been my experience that these tests are conducted after the problem has arisen, not before the flooring has been installed. Most any flooring comes with installation instructions and most want the materials to acclimate while slab moisture test takes place. This is rarely done and usually happens in a 12-24 hour period by placing a garbage bag or some other piece of plastic down with duct tape at best. No discoloration or wet spot by morning, let's get ready to rumble! I can't tell you the number of professional and DIY jobs I've seen torn out because of impatience, ignorance, and inadequate testing methods. Thanks for the article. badair ADAIR INSPECTION 972-487-5634 Residential-Commercial-Construction-EIFS-Infrared Thermography TREC # 4563 EDI: EIFS-MA TX # 39 2008 US Member of the Year life is the random lottery of events followed by numerous narrow escapes...accept the good |
|
#3
|
||||
|
||||
|
The common favorite is strip centers where the dry goods storage area is at the back of the lease. Exactly where the utility leave out was. 6x quarry or 12x vinyl installed. Owner/manager complains about all of the boxes have this concentic wet pattern on the bottom, tiles are loose, and there is this whiteish stuff in the joints that keeps reappearing after thorough cleaning.
"What's causing this?," is always their question. badair ADAIR INSPECTION 972-487-5634 Residential-Commercial-Construction-EIFS-Infrared Thermography TREC # 4563 EDI: EIFS-MA TX # 39 2008 US Member of the Year life is the random lottery of events followed by numerous narrow escapes...accept the good |
|
#4
|
||||
|
||||
|
There goes the old anybody can have a beautiful floor;"Just peel and stick, save hundreds by doing it yourself!" Good article Marcel, thanks.
|
|
#5
|
||||
|
||||
|
Timely article.
Our office received a call last Friday from someone looking for this particular type of testing for a new commercial space. Our office does not offer this particular service but we were able to direct them on to a local company that was able to provide and complete the needed testing. Joseph P. Hagarty joseph.hagarty@comcast.net Main Line Inspections, Inc. Phone: 610-399-3675 Email: MainLineHI@comcast.net http://pa.nachi.org/mainlinepa/about.html http://www.householdinspector.com National President / NACHI (2003-2004) NACHI Education Committee Member |
|
#6
|
||||
|
||||
|
Here's a thread on floor testing:
http://www.nachi.org/forum/showthrea...ting+institute Linas Dapkus Lockport,Il. 60441 #06012294 Chicago Home Inspector Chicago Home Inspection Chicago Home Inspector Linas Dapkus My Chicago Home Inspection Chicago Home Inspection Today |
|
#7
|
||||
|
||||
|
Thanks guys and real happy some have enjoyed it.
The writer Peter Craig, used to work in Topsam, Maine near Brunswick as a manager of a concrete product wholesaler for Contractors on Concrete Products of any kind. The Company was JK Sales Inc. Now been sold to Gagne & Sons. New the man personally, and has been consulting concrete slab problems for quite a few years now. Really knows his stuff. I have been using the Chloride moisture test for quite a few years because of the Manufacturers requirements and warranties. Flooring failures can be very expensive. I apologize for the format layout, but this was a PDF and had no clue how to post it. Don't ask me how I did it. ha. ha. Marcel </IMG></IMG></IMG> Cyr Home and Commercial Property Inspections CMI IAC2 Certified NACHI04070211 http://co.nachi.org/inachiawards/inachiawards551.html http://co.nachi.org/inachiawards Commercial Builder Ouellet Associaties Inc. http://www.oaconstruction.com/ |
|
#8
|
||||
|
||||
|
Quote:
Understanding, preventing, detecting and correcting moisture in concrete floors Flooring failures attributed to moisture-related concrete problems are at near epidemic proportions today. Coatings, carpet, vinyl, rubber, wood, laminates and most floor coverings are affected to one degree or another by pH issues and excess water vapor emissions through a concrete slab. I’ve often said, “Bad concrete has been very good to me.” As a technical specialist in the commercial resilient flooring industry, concrete issues are an almost daily topic of discussion, and my clients need answers. Flooring failures attributed to moisture-related concrete problems are at near epidemic proportions today. Coatings, carpet, vinyl, rubber, wood, laminates and most floor coverings are affected to one degree or another by pH issues and excess water vapor emissions through a concrete slab. Moisture causes gaps between tiles, adhesive oozing, bumps, dents, cupping, bubbles, indentations, wheel marks and more. Left uncorrected, these problems can evolve into health and safety issues caused by mold, mildew and floors lifting. Here’s a crash course on concrete floors and the issues related to flooring installed over concrete. I hope it will go a long way to helping you to understand what could go wrong. First, using the right terminology is helpful because words like “cement” and “curing” are often misused. “Cement” isn’t the finished product, but is the grey powdery ingredient in concrete. Cement powder, water, sand and aggregate (rocks) bond together to form concrete. There’s no such thing as “a cement floor.” Another common misunderstanding is that “cured” means the concrete is ready for floor coverings. The term “28-day cure” is the approximate time a 4-in. slab takes to cure, and is often used as a guideline for when to install a floor. However, after 28 days, the concrete isn’t dry because curing and drying aren’t the same things. Curing is the chemical reaction that bonds those ingredients together to make concrete. Drying refers to evaporating the excess water (about 2/3 of the water in the mix) from the concrete after the curing process is complete. The industry standard, ASTM F 710, Standard Practice for Preparing Concrete Floors to Receive Resilient Flooring, describes the process and uses the terms cure and dry in the same sentence - “New concrete slabs shall be properly cured and dried before installation of resilient flooring.” How long to dry? The drying time before slabs are ready for moisture testing depends on atmospheric conditions and mix design, according to F 710. A 4-in. thick slab allowed to dry from only one side typically requires 90 days to 120 days to achieve a moisture vapor emission rate (MVER) of 3 lb. water/1,000 sq. ft. per 24 hr (the resilient flooring industry standard MVER). Suspended slabs -– the second floor and above -- often contain a lot more water, and take even longer to dry. As noted in ASTM F 710, lightweight concrete, floors containing lightweight aggregate or excess water, and those that dry from only one side, such as concrete on metal deck construction, may need a much longer drying time. One laboratory study found that at ideal conditions (70°F, 50% relative humidity) it took 46 days for a standard mix to dry and 168 days for a lightweight mix. Those were both under ideal conditions – concrete with the right amount of water at the perfect temperature and humidity. In the real world it takes even longer. Just as important as sealing your building’s roof is sealing the floor against moisture intrusion. ASTM F 710 says that every concrete floor slab on or below grade intended to receive resilient flooring should have a moisture retarder (often improperly called a vapor barrier) installed below the slab. The vapor retarder is often left out of the project to save money and speed the finishing of the concrete. Many failures on first-floor and lower-level slabs are caused by a missing or damaged vapor retarder. Who’s responsible for failures? The concrete contractor sometimes gets blamed. But if the concrete is mixed and placed according to the architect’s specifications, one can’t blame the contractor, unless extra water gets added to the truck or the vapor retarder gets damaged. Bad adhesive is rarely the cause because adhesive is almost never defective, but it can be attacked by moisture and the elevated pH levels that come with it. The floor maintenance team often gets the rap, but a floor must be under a lot of water for a long time for the adhesive to let go. Most often, in new buildings, the flooring is installed before the concrete has completely dried, the curing compound was never removed, or the climate control system isn’t yet operational. Then, when the building is occupied and the interior conditioned air is dry, the floor covering blocks the movement of excess moisture that migrates upward through the slab. In older buildings, a missing vapor retarder or external sources such as leaks, exterior grading or sprinklers can cause moisture to pass through a slab. The good news is that testing can detect moisture movement long before a floor covering is installed. Test when and where? The short answer is everywhere and always. ASTM F 710 recommends testing concrete slabs for moisture, regardless of age or elevation. Every floor covering manufacturer and adhesive producer says the same thing about old or new concrete from the basement to the penthouse. To say “It looks dry,” “It feels dry” or “It smells dry” isn’t enough. Taping a plastic sheet to the floor for a day or two also has been proven to be an inaccurate indicator. The easy-to-use electronic meters that test for moisture in concrete yield only a spot test that isn’t a good basis for a global go or no-go decision for a flooring installation. The floor covering industry recognizes two methods for testing concrete for moisture. The first is the 50-plus-year-old test now known as ASTM F 1869, Standard Test Method for Measuring Moisture Vapor Emission Rate of Concrete Subfloor Using Anhydrous Calcium Chloride. This test uses a kit consisting of a dish of calcium chloride that is sealed on a clean section of concrete beneath a plastic dome for three days (Figure 1). Because the salt is hydroscopic, the weight gain can be used to establish the moisture vapor emission rate. Most resilient flooring and carpet can tolerate a maximum MVER of 3 lb. or 5 lb., depending on the product. If done correctly, F 1869 measures moisture emissions from the top 5 cm or so of the concrete. While this is a good test for surface moisture, it doesn’t measure what’s inside the slab. ![]() Figure 1. The weight gain in a sample of calcium chloride correlates with the mass flow rate of water vapor leaving the concrete surface. Getting that data requires using ASTM F 2170, Standard Test Method for Determining Relative Humidity in Concrete Floor Slabs Using In-Situ Probes. This is probably the best predictor of future moisture problems (Figure 2). It involves drilling holes in the floor to measure the humidity inside the slab. This is truly the latest technology for moisture testing and is very quickly being recognized by flooring manufacturers throughout the world. ![]() Figure 2. Drilling a hole is the first step in testing with ASTM F 2170. What if it fails A number of measures can accelerate the drying process on a new slab. Get the building’s climate control system up and running -- raise the temperature, reduce the humidity, get the air moving. If a curing compound was used on the floor, remove it. Commercial dehumidifiers and drying equipment are used in water damaged buildings and also can used to dry a new concrete slab. Consider surface-applied vapor retarders to block moisture emission from the slab. These products need to be researched thoroughly before being used. Look at the manufacturer’s reputation, track record, warranty and insurance coverage to be sure that you’ll be covered if the product fails. Check with the floor covering or adhesive manufacturer for additional guidance. Preventing moisture problems in new floors is all about the proper specification. Using concrete with less water and larger aggregate can make a difference, as can using the cover cure method instead of curing compounds. Always use a vapor retarder between a slab and the ground. Sealing beneath the slab is just as important as sealing above the roof. Placing the concrete beneath some roof-like structure prevents rain exposure and helps the concrete dry faster, as does getting the HVAC system up and running as soon as possible. Concrete is an ancient material that can last for thousands of years. Placed correctly, concrete floors can accept any floor covering to yield a long-lasting and durable wearing surface in almost any type of space. However, because of the fast-track nature of a lot of today’s construction projects, the installation often is rushed and failures occur. So, it’s important to know what to ask for, how to test, and what to do if you discover a problem. Christopher Capobianco owns Flooring Answers in Patchogue, Long Island, N.Y. Contact him at www.FlooringAnswers.com and (631) 275-6494. Marcel Cyr Home and Commercial Property Inspections CMI IAC2 Certified NACHI04070211 http://co.nachi.org/inachiawards/inachiawards551.html http://co.nachi.org/inachiawards Commercial Builder Ouellet Associaties Inc. http://www.oaconstruction.com/ |
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| Building Science- research from respected sources | Brian A. MacNeish | Ancillary Services & Additional Topics | 12 | 2/13/08 12:33 PM |
| IAC2 In new residential construction | mcyr | IAC2 Forum | 0 | 10/9/07 7:45 PM |
| bbbb | mcyr | Structural | 1 | 8/19/07 11:26 PM |
| Moisture control for slab on grade in protecting floor finishes | mcyr | General Inspection Discussion | 2 | 8/13/07 8:53 PM |
| Can someone explain why wood in contact with concrete causes rot? | gromicko | Misc. Discussion | 45 | 4/9/07 3:23 AM |