  #1  
Old 11/25/08, 2:33 PM
Bruce A. King's Avatar
Bruce A. King Bruce A. King is online now
InterNACHI Member
 
Join Date: Jan 2005
Location: York, SC
Posts: 2,223
Default mud sill strap/bolting and IRC

Did the IRC reduce the code requirements a few years ago where no strap or bolt is now required within one foot of a mud sill plate splice?



B.A. King Home Inspections, LLC
www.BAKingHomeInspections.com
Serving Charlotte NC area and Rock Hill SC areas.
CMI Certified Master Inspector and Independent
704 301-3207
Reply With Quote
  #2  
Old 11/25/08, 3:10 PM
James H. Bushart's Avatar
James H. Bushart James H. Bushart is offline
InterNACHI Member
 
Join Date: Dec 2004
Location: Cassville, MO
Posts: 13,647
Default Re: mud sill strap/bolting and IRC

The IBC (2308.6) of 2006 requires a bolt or anchor strap not more than 12 and not less than 4 inches from the end of each piece.
Reply With Quote
  #3  
Old 11/25/08, 3:11 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 5,037
Default Re: mud sill strap/bolting and IRC

Not that I am aware. . .

2003 IRC 403.1.6; The wood sole plate at exterior walls on monolithic slabs and wood sill plate shall be anchored to the foundation with anchor bolts spaced a maximum of 6 feet (1829 mm) on center. There shall be a minimum of two bolts per plate section with one bolt located not more than 12 inches (305 mm) or less than seven bolt diameters from each end of the plate section.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net
Reply With Quote
  #4  
Old 11/25/08, 4:26 PM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is online now
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 12,374
Default Re: mud sill strap/bolting and IRC

There is also an exception in the IRC that states foundation anchor straps, spaced as required to provide equivalent anchorage to 1/2"-diameter anchor bolts.

There are numerous types of hold-downs and each of them have there own installation requirements to be followed.

Most strap anchors just don’t have the same capacity (sometimes half the capacity unless they are the heavy duty ones), so you typically need more anchors at a reduced spacing.
Manufacturers usually have tables for substituting strap anchors for anchor bolts, but some judgement is usually needed. Evaluating the required anchorage and what is equivalent to this is beyond a home inspection, and should be done by a building official or engineer.

On achor bolts, I believe if a two story, the spacing is upgraded to 4' o.c.
Correct me if I am wrong.

Hope this helps Bruce.

Marcel






Cyr Home and Commercial Property Inspections

IAC2 Certified
NACHI04070211
http://co.nachi.org/inachiawards


Commercial Builder
CertainTeed
Master Shingle Applicator
Shingle Technology
Ouellet Associaties Inc.
http://www.oaconstruction.com/
Reply With Quote
  #5  
Old 11/25/08, 5:40 PM
Barry Adair's Avatar
Barry Adair Barry Adair is offline
InterNACHI Member
 
Join Date: Aug 2004
Location: TEXAS
Posts: 3,479
Default Re: mud sill strap/bolting and IRC

Quote:
Originally Posted by mcyr View Post
On achor bolts, I believe if a two story, the spacing is upgraded to 4' o.c.
Correct me if I am wrong.

Hope this helps Bruce.

Marcel


Section R403.1.6 Foundation anchorage.
When braced wall panels are supported directly on continuous foundations, the wall
wood sill plate or cold-formed steel bottom track shall be anchored to the foundation in
accordance with this section.
The wood sole plate at exterior walls on monolithic slabs and wood sill plate shall be
anchored to the foundation with anchor bolts spaced a maximum of 6 feet (1829 mm)
on center. There shall be a minimum of two bolts per plate section with one bolt
located not more than 12 inches (305 mm) or less than seven bolt diameters from each
end of the plate section. In Seismic Design Categories D1 and D2, anchor bolts shall
also be spaced at 6 feet (1829 mm) on center and located within 12 inches (305 mm)
from the ends of each plate section at interior braced wall lines when required by
Section R602.10.9 to be supported on a continuous foundation. Bolts shall be at least
1/2 inch (12.7 mm) in diameter and shall extend a minimum of 7 inches (178 mm) into
masonry or concrete. Interior bearing wall sole plates on monolithic slab foundations
shall be positively anchored with approved fasteners. A nut and washer shall be
tightened on each bolt to the plate. Sills and sole plates shall be protected against
decay and termites where required by Sections R318 and R319.


Section 403.1.6.1 Foundation anchorage in Seismic Design Category D2.
In addition to the requirements of Section R403.1.6, the following requirements shall
apply to wood light-frame structures in Seismic Design Category D2 and wood
light-frame townhouses.
1. Plate washers conforming to Section R602.11.1 shall be used on each bolt.
2. Interior braced wall plates shall have anchor bolts spaced at not more than 6 feet
(1829 mm) on center and located within 12 inches (305 mm) from the ends of each
plate section when supported on a continuous foundation.
3
3. Interior bearing wall sole plates shall have anchor bolts spaced at not more than 6
feet (1829 mm) on center and located within 12 inches (305 mm) from the ends of
each plate section when supported on a continuous foundation.
4. The maximum anchor bolt spacing shall be 4 feet (1219 mm) for buildings over two
stories in height.

5. Stepped cripple walls shall conform to Section R602.11.3.



badair
ADAIR INSPECTION
972-487-5634

Residential-Commercial-Construction-EIFS-Infrared Thermography
TREC # 4563
EDI: EIFS-MA TX # 39

2008 US Member of the Year

life is the random lottery of events followed by numerous narrow escapes...accept the good
Reply With Quote
  #6  
Old 11/25/08, 11:40 PM
Richard A. Hetzel Richard A. Hetzel is offline
Active Poster
 
Join Date: Apr 2007
Location: Tobyhanna, Pennsylvania
Posts: 596
Please Note: Richard A. Hetzel is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: mud sill strap/bolting and IRC

I believe anchor bolts on 4-foot centers is good practice, despite the code allowing 6-foot centers. Four feet was the standard before the IRC came into being. The IRC requirements for bolts on short pieces or near ends are a good addition to standard practice, though. I do not like straps at all, Period.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On



All times are GMT -4. The time now is 9:53 PM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts