Default No I-Beam

Just wondering. Home had manufactured floor joists and no I-beam. Instead of a beam there was a 2x6 wall supporting the floor joists. Is this acceptable ?
Attached Thumbnails
no-beam-p5060020.jpg  
Reply With Quote
Need a home inspection in Louisiana? Check out InterNACHI's listing of Louisiana certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 5/7/10, 6:47 AM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 19,798
Default Re: No I-Beam

Looks fine to me assumming there is a depressed slab in the area of the bearing wall.
Reply With Quote
  #3  
Old 5/7/10, 8:11 AM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 8,848
Default Re: No I-Beam

Quote:
Originally Posted by dlee2 View Post
Just wondering. Home had manufactured floor joists and no I-beam. Instead of a beam there was a 2x6 wall supporting the floor joists. Is this acceptable ?

It is probably better if, as Marcel said, there is adequate footing under it. The sag potential is reduced but one doesn't have a big open area with the wall there instead of a beam.



InterNachi Awards Portal: http://co.nachi.org/inachiawards/

____________________________________________
"An Education, not just an Inspection"

Larry Kage, CMI
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector serving the Traverse City, Michigan area and beyond.
Reply With Quote
  #4  
Old 5/7/10, 8:19 AM
Marcel Gratton's Avatar
Marcel Gratton Marcel Gratton is offline
InterNACHI Member
 
Join Date: Jan 2004
Location: Gatineau, QC
Posts: 1,778
Default Re: No I-Beam

Quote:
Originally Posted by dlee2 View Post
Just wondering. Home had manufactured floor joists and no I-beam. Instead of a beam there was a 2x6 wall supporting the floor joists. Is this acceptable ?
· Repair: Blocking or strapping shall be provided for the non finished load bearing interior wall in basement to prevent to prevent sideways buckling. It should be fastened to the studs at mid-height.



Marcel Gratton, NACHI04011210, CMI
On The Level Inspection
Gatineau, Québec
http://www.onthelevelinspection.com/
Reply With Quote
  #5  
Old 5/7/10, 11:04 AM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is online now
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,917
Default Re: No I-Beam

Quote:
Originally Posted by mgratton View Post
· Repair: Blocking or strapping shall be provided for the non finished load bearing interior wall in basement to prevent to prevent sideways buckling. It should be fastened to the studs at mid-height.
Anyone have a illustration of blocking and strapping?
Reply With Quote
  #6  
Old 5/7/10, 12:14 PM
Jeffery L. Haynes Jeffery L. Haynes is online now
InterNACHI Member
 
Join Date: Aug 2008
Location: Concord, NC
Posts: 3,495
Default Re: No I-Beam

Guys this is normal building practices (and code)....... as long as there is a footer under the wall (which you will not see) then its fine. And I-beam would do nothing other than exert more weight upon the footer that is carrying all the tributary load.

Being that the pictures are limited, I can not speak on the proper header size and number of jacks without knowing the rough opening as well as the weight being loaded upon the header.

If you as an HI are not familiar with basic structural / framing practice then defer to a GC. Blocking and strapping is not required....it nothing but overkill as far as framing.....it does help out with drywall and fireblocking.

And by the way, a 2x4 wall would have been sufficient as well as long as point loads are accounted for and the house does not exceed 2 1/2 stories.

Jeff


PS. For those who need to sharpen on upon basic framing details or simply want something good to read.....go here. Just realize that there are numerous framing methods....simply because one does not see it in an illustration or your part of the country does not mean its wrong. When I build a spec or custom home I make sure my framer do not double up joist under plumbing walls but rather block out same with blocks in order to keep the plumbers from cutting joist or offsetting plumbing fixtures.....95% of builders dont do that....yet it is just as strong and resolves issues the plumbers might have.

Also, when inspecting I-joist.....make sure you know what you are looking at......many times framers leave out squash blocks, improperly cut the joist or do not pack out doubled joist as is required at times.
Reply With Quote
  #7  
Old 5/7/10, 6:23 PM
Marcel Gratton's Avatar
Marcel Gratton Marcel Gratton is offline
InterNACHI Member
 
Join Date: Jan 2004
Location: Gatineau, QC
Posts: 1,778
Default Re: No I-Beam

Quote:
Originally Posted by jhaynes View Post
Guys this is normal building practices (and code)....... as long as there is a footer under the wall (which you will not see) then its fine.
Jeffery,

Not in my area!

Cheers,



Marcel Gratton, NACHI04011210, CMI
On The Level Inspection
Gatineau, Québec
http://www.onthelevelinspection.com/
Reply With Quote
  #8  
Old 5/7/10, 6:27 PM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 19,798
Default Re: No I-Beam

Marcel, could you elaborate why not in your area? Curious minds want to know.
Reply With Quote
  #9  
Old 5/7/10, 9:25 PM
Marcel Gratton's Avatar
Marcel Gratton Marcel Gratton is offline
InterNACHI Member
 
Join Date: Jan 2004
Location: Gatineau, QC
Posts: 1,778
Default Re: No I-Beam

Quote:
Originally Posted by mcyr View Post
Marcel, could you elaborate why not in your area? Curious minds want to know.
Marcel,

Sorry for not explaining myself better.

What I meant by the comment *not in my area* was in reference to Jeffery's comments that it is normal building practices and code.

For my area, the National Building Code (NBC) 9.23.10.2.(5) reads:

*Where loadbearing interior walls are not finished in accordance with Sentence (2), blocking or strapping shall be fastened to the studs at mid-height to prevent sideways buckling.*

Hope this explains my position on this topic more appropriately.

Cheers,



Marcel Gratton, NACHI04011210, CMI
On The Level Inspection
Gatineau, Québec
http://www.onthelevelinspection.com/
Reply With Quote
  #10  
Old 5/7/10, 9:28 PM
Jeffrey R. Jonas's Avatar
Jeffrey R. Jonas Jeffrey R. Jonas is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Owatonna, MN
Posts: 12,195
Default Re: No I-Beam

Quote:
Originally Posted by mgratton View Post
Marcel,

Sorry for not explaining myself better.

What I meant by the comment *not in my area* was in reference to Jeffery's comments that it is normal building practices and code.

For my area, the National Building Code (NBC) 9.23.10.2.(5) reads:

*Where loadbearing interior walls are not finished in accordance with Sentence (2), blocking or strapping shall be fastened to the studs at mid-height to prevent sideways buckling.*

Hope this explains my position on this topic more appropriately.

Cheers,
Marcel,
What does sentence (2) require for finishing?
Jeff
Reply With Quote
  #11  
Old 5/7/10, 9:39 PM
Jeffery L. Haynes Jeffery L. Haynes is online now
InterNACHI Member
 
Join Date: Aug 2008
Location: Concord, NC
Posts: 3,495
Default Re: No I-Beam

Quote:
Originally Posted by mgratton View Post
Jeffery,

Not in my area!

Cheers,
LOL..... I speak of US practices.... I suspect you all may have greater snow loads however can you elaborate on the code you speak of.
Reply With Quote
  #12  
Old 5/7/10, 9:56 PM
Marcel Gratton's Avatar
Marcel Gratton Marcel Gratton is offline
InterNACHI Member
 
Join Date: Jan 2004
Location: Gatineau, QC
Posts: 1,778
Default Re: No I-Beam

Quote:
Originally Posted by jjonas View Post
Marcel,
What does sentence (2) require for finishing?
Jeff
2) Bracing is not required where walls
a) have an interior finish conforming to the requirements of Section 9.29., or
b) where the walls are
i)clad with panel type siding
ii)diagonally sheathed with lumber, or
iii)sheathed with plywood, OSB, waferboard, gypsum or fibreboard sheating.

Regards,



Marcel Gratton, NACHI04011210, CMI
On The Level Inspection
Gatineau, Québec
http://www.onthelevelinspection.com/
Reply With Quote
  #13  
Old 5/7/10, 10:00 PM
Jeffrey R. Jonas's Avatar
Jeffrey R. Jonas Jeffrey R. Jonas is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Owatonna, MN
Posts: 12,195
Default Re: No I-Beam

Quote:
Originally Posted by mgratton View Post
2) Bracing is not required where walls
a) have an interior finish conforming to the requirements of Section 9.29., or
b) where the walls are
i)clad with panel type siding
ii)diagonally sheathed with lumber, or
iii)sheathed with plywood, OSB, waferboard, gypsum or fibreboard sheating.

Regards,
Correct me if I misinterpreted...

They are saying that Gypsum board is acceptable in place of bracing, blocking, or wood sheathing, to prevent "sideways buckling" ???
Reply With Quote
Need a home inspection in Louisiana? Check out InterNACHI's listing of Louisiana certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #14  
Old 5/7/10, 10:01 PM
Marcel Gratton's Avatar
Marcel Gratton Marcel Gratton is offline
InterNACHI Member
 
Join Date: Jan 2004
Location: Gatineau, QC
Posts: 1,778
Default Re: No I-Beam

Quote:
Originally Posted by jhaynes View Post
LOL..... I speak of US practices.... I suspect you all may have greater snow loads however can you elaborate on the code you speak of.
You get snow also...

Cheers,



Marcel Gratton, NACHI04011210, CMI
On The Level Inspection
Gatineau, Québec
http://www.onthelevelinspection.com/
Reply With Quote
  #15  
Old 5/7/10, 10:06 PM
Marcel Gratton's Avatar
Marcel Gratton Marcel Gratton is offline
InterNACHI Member
 
Join Date: Jan 2004
Location: Gatineau, QC
Posts: 1,778
Default Re: No I-Beam

Quote:
Originally Posted by jjonas View Post
Correct me if I misinterpreted...

They are saying that Gypsum board is acceptable in place of bracing, blocking, or wood sheathing, to prevent "sideways buckling" ???
Correct!



Marcel Gratton, NACHI04011210, CMI
On The Level Inspection
Gatineau, Québec
http://www.onthelevelinspection.com/
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Deflected Cantelevered Beam pdickerson Structural Inspections 4 4/3/08 10:16 AM
Crack in Support Beam Berry T. Wilson Structural Inspections 6 5/26/07 3:15 PM
Steel beam lateral support Mark Ellison Structural Inspections 10 1/16/07 10:40 PM