I have been inspecting several homes in Montana that were built in the early 1900 and have a partial cellar with a partial 3 foot crawl space. The issue I am having is there is no ventilation in the crawl space. Per standards you should have 1/300 ventilation. The weather in western Montanan is very low humidity and the homes do not have any signs of moisture problems. Makes it hard to call out a defect in ventilation when the house has been there for 100 years with no issues.

Does anyone have any input on this or seen this before?

Thanks Dan
Reply With Quote
  #2  
Old 1/17/07, 8:19 PM
David C. Macy's Avatar
David C. Macy David C. Macy is online now
InterNACHI Member
 
Join Date: Jan 2004
Location: Broadview Hts., OH
Posts: 1,465
Default Re: No Crawl Space Ventilation

http://www.askthebuilder.com/543-Cra...ce-Vents.shtml

Ask the buider Tim Carter seems to give good advice & information.
Reply With Quote
  #3  
Old 1/17/07, 9:15 PM
Jason1's Avatar
Jason1 Jason1 is offline
Active Poster
 
Join Date: Nov 2006
Posts: 677
Please Note: Jason1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: No Crawl Space Ventilation

Quote:
Originally Posted by dmccormick
Makes it hard to call out a defect in ventilation when the house has been there for 100 years with no issues.

Does anyone have any input on this or seen this before?

Thanks Dan
Wasn't required when it was built, why would you hold it to current standards?
Reply With Quote
  #4  
Old 1/18/07, 12:35 PM
ccbrands1 ccbrands1 is offline
Active Poster
 
Join Date: Jan 2006
Posts: 220
Please Note: ccbrands1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: No Crawl Space Ventilation

Quote:
Originally Posted by Jason1
Wasn't required when it was built, why would you hold it to current standards?
i agree with this in this situation.

maybe say something like "although no vents were found, ventilation appeared adequate at time of inspection"
Reply With Quote
  #5  
Old 1/18/07, 1:27 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 18,489
Default Re: No Crawl Space Ventilation

The need for ventilation of crawl spaces varies widely depending on local conditions.

I personally live in a house that is 140 years old with a limestone/brick foundation basement and a 1971 addition with a crawl space with CMU. foundation. The crawl space is does not have a vapor barrier and is not ventilated. After 35 years, this non-ventilated and non vapor barriered crawl space has no evidence of excess moisture or WDO. The adjacent basement does show evidence of dryrot and sistered floor joists. The "floor" also does not have a vapor barrier and was no insulation until appx 10 years ago when I purchased it.

So what's the point? Your milage may vary with regard to ventilation requirements you are exposed to on this board. Critical factors are - local building codes, foundation drainage, soil conditions, local weather conditions etc. Be aware of what is needed where you inspect.

Here are some resources to increase your knowledge. An AIA document(PDF) which is a summarry and contains excerpts from a 88 page PATH/HUD document(link below).

Ventilation AIA 18-22-01.pdf

http://www.huduser.org/publications/..._by_design.pdf
Reply With Quote
  #6  
Old 1/18/07, 1:39 PM
hmiller's Avatar
hmiller hmiller is offline
Active Poster
 
Join Date: Feb 2006
Location: Camano Island, WA
Posts: 668
Please Note: hmiller is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: No Crawl Space Ventilation

Quote:
Originally Posted by dmccormick
I have been inspecting several homes in Montana that were built in the early 1900 and have a partial cellar with a partial 3 foot crawl space. The issue I am having is there is no ventilation in the crawl space. Per standards you should have 1/300 ventilation. The weather in western Montanan is very low humidity and the homes do not have any signs of moisture problems. Makes it hard to call out a defect in ventilation when the house has been there for 100 years with no issues.

Does anyone have any input on this or seen this before?

Thanks Dan
Dan
This situation is unique, and I agree it is hard to call it as a defect, when 100 years of evidence show no damage as a result.
I would note that I observed no vents installed, and that no visible evidence of moisture condensation, etc. was found as a result. Basically to inform the buyer what the standards are, but to also let them know that I did not see a material defect as a result of their absence.
The reason I note such conditions is that when they bring a contractor into to do other home improvements, or they sell the house a year later and another inspector tells them they need vents then they will have some understanding about the issue, and not be surprised, ...assuming I missed a serious problem.
You know the last man in theory...they are alway going to believe the last man. But if I can educate the client ahead of time, I believe it reduce chances that they will ask me to pay for something that does not need to be done.
Reply With Quote
  #7  
Old 1/18/07, 6:29 PM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,020
Default Re: No Crawl Space Ventilation

I do not like vented crawlspaces in Massachusetts.

http://www.masscertifiedhomeinspections.com/?D=53
Reply With Quote
  #8  
Old 1/18/07, 6:31 PM
David C. Macy's Avatar
David C. Macy David C. Macy is online now
InterNACHI Member
 
Join Date: Jan 2004
Location: Broadview Hts., OH
Posts: 1,465
Default Re: No Crawl Space Ventilation

The vents are great if you like water intrusion/mold/high dewpoints.
Reply With Quote
  #9  
Old 1/18/07, 6:40 PM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 5,726
Default Re: No Crawl Space Ventilation

I agree with David. Even though vents are required around here, typically, we shut them and stuff 'em with insulation, insulate the perimeter of the crawlspace and stick a heat duct or two down there.



____________________________________________
"An Education, not just an Inspection"

Larry Kage
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector and Infrared Thermographer serving the Traverse City, Michigan area and beyond.


ITC/FLIR CERTIFIED BUILDING SCIENCES THERMOGRAPHER

ITC/FLIR CERTIFIED LEVEL 1 THERMOGRAPHER
Reply With Quote
  #10  
Old 1/27/07, 2:12 PM
Rod A. Musch Rod A. Musch is offline
InterNACHI Member
 
Join Date: May 2006
Location: Galena, MO
Posts: 6
Default Re: No Crawl Space Ventilation

http://resourcecenter.pnl.gov/cocoon/morf/ResourceCenter/article//131

This link has good information regarding a closed crawlspace and some options. The thinking on crawlspace ventilation is changing to more positive moisture control. The picture shows what happens when a crawlspace has no vapor barrior and the vent(s) were closed. It is mold.

no-crawl-space-ventilation-crawl-space-mold4.jpg
Reply With Quote
  #11  
Old 1/31/07, 6:04 PM
Brad G. Knowlton Brad G. Knowlton is offline
InterNACHI Member
 
Join Date: Oct 2005
Location: Artesia, NM
Posts: 21
Default Re: No Crawl Space Ventilation

I inspect in a similar, low humidiy environment, and I see many new homes built with no ventilation in the crawl, or weep holes in brick veneer. The building code enforcement doesn't seem to mind, but even in low humidy, or especially in low humidity climates where an evaporative air conditioner is used, there is considerable moisture that can condense and encourage WDO. I stuggle with writing these up, but I do not find wisdom in blocking off vents. Why are some of you suggesting the vents be blocked?
Reply With Quote
  #12  
Old 2/5/07, 11:34 AM
Robert J. OConnor's Avatar
Robert J. OConnor Robert J. OConnor is offline
Active Poster
 
Join Date: Jul 2003
Location: East Northport, NY
Posts: 741
Default Re: No Crawl Space Ventilation

Any crawl space should be either well ventilated, conditioned/heated, or completely sealed off (not as common).

There have been mold, wood rot, and other problems in older homes that have crawl spaces without good ventilation. The severity depends on the local climate, with less problems for older homes in drier areas without floor insulation or tight construction. The space had some ventilation and was somewhat conditioned/heated due to the lack of insulation without a vapor barrier facing at the floor framing.

BUT, take that same older home and seal up gaps and add modern insulation with a vapor barrier (e.g. tar layer on the back side of modern paper faced batts) ... a common thing homeowners do to "fix" cold floors above crawl spaces ... and you have a recipe for problems, particularly for older dirt floor crawl spaces.

In one crawl space in an older home without adequate ventilation where the homeowner added faced batts insulation between the floor joist bays, my awl went completely through the bottom 2" of the wood framing due to stagnant unheated conditions created by adding the insulation ...

JMO



Robert O'Connor, PE
Consulting Engineer & Inspector
LIU CW Post Adjunct Professor
NACHI Education Committee
www.reporthost.com/rjo

I am absolutely amazed sometimes by how much thought goes into doing things wrong ...

Last edited by roconnor; 2/6/07 at 4:50 AM..
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Return air from crawl space WHI HVAC 8 5/1/07 8:36 AM
Crawl space in under house dnasser Structural 15 2/27/07 8:12 PM
Alkali and efflouresence in crawl space lgerving Structural 0 2/12/07 12:13 PM
Crawl Space Drainage brooke949 Structural 6 8/29/06 2:42 PM


All times are GMT -4. The time now is 3:03 PM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts