Default No Sill Plate Under Band Board

I ran across this today in a 16 year old house. All of the band boards were on sill plates, except for this 14 foot section. I know that a treated sill plate keeps the band board from rotting. There are shims underneath the band board so that it isn't in direct contact with the masonry block. Is this OK? If not, what could I say is wrong with it? Thanks in advance.
Attached Thumbnails
no-sill-plate-under-band-board-no_sill_palte.jpg  
Reply With Quote
  #2  
Old 4/8/08, 6:16 PM
Joe Farsetta's Avatar
Joe Farsetta Joe Farsetta is offline
ESOP Committee Member
 
Join Date: Oct 2002
Location: Pearl River, NY
Posts: 3,207
Default Re: No Sill Plate Under Band Board

Sill plate is anchored to foundation wall. It does more than keep the rim joists from rotting...

First question I have is how the primary platform is properly anchored...

Last edited by jfarsetta; 4/8/08 at 8:04 PM..
Reply With Quote
  #3  
Old 4/8/08, 6:18 PM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,020
Default Re: No Sill Plate Under Band Board

Skip,

Sills are required. How's it held down?

I'd red flag this install.

Also, are those joists 30" OC?
Reply With Quote
  #4  
Old 4/8/08, 6:43 PM
Skip Erwin Skip Erwin is offline
New User
 
Join Date: Jun 2006
Posts: 91
Please Note: Skip Erwin is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: No Sill Plate Under Band Board

David, the joists are 24" OC. I didn't see anything anchoring the platform.
Reply With Quote
  #5  
Old 4/8/08, 9:20 PM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 12,356
Default Re: No Sill Plate Under Band Board

Quote:
Originally Posted by Skip Erwin
I ran across this today in a 16 year old house. All of the band boards were on sill plates, except for this 14 foot section. I know that a treated sill plate keeps the band board from rotting. There are shims underneath the band board so that it isn't in direct contact with the masonry block. Is this OK? If not, what could I say is wrong with it? Thanks in advance.
Skip, Hi.

I blow the picture up and I can see this contraption on the right near a wood frame of some sort and it looks like a tie down wrapped around the joist. I do not recognize it.

The joist span is 2' O.C. based on the length of those two bricks, and I see the shimming which looks like back to back cedar shingles used normally for shimming things like that.

But, this has got to be the most unorthodox type of floor framing I have seen in many years.

Obviously that was a crawl, and how did everything else look?

Surprised to see that friction fit batt insulation has not fallen down yet. Was there a kraft paper holding it up?

Just curious.

Marcel




Cyr Home and Commercial Property Inspections

IAC2 Certified
NACHI04070211
http://co.nachi.org/inachiawards


Commercial Builder
CertainTeed
Master Shingle Applicator
Shingle Technology
Ouellet Associaties Inc.
http://www.oaconstruction.com/
Reply With Quote
  #6  
Old 4/8/08, 9:34 PM
Skip Erwin Skip Erwin is offline
New User
 
Join Date: Jun 2006
Posts: 91
Please Note: Skip Erwin is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: No Sill Plate Under Band Board

Marcel,

Everything else was pretty much normal. There was sill plate throughout except for this one section. It's unusual to see joists hangers here in production housing. Batt insulation is typically supported here with metal hangers. They look like a straight section of coat hanger and often fail over time.
Reply With Quote
  #7  
Old 4/8/08, 9:44 PM
Bruce A. King's Avatar
Bruce A. King Bruce A. King is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: York, SC
Posts: 2,221
Default Re: No Sill Plate Under Band Board

They allow roofing felt paper as a "shim" between regular lumber and masonry around here.

Sometimes the foundation straps are only fastened on the outside of the band and not visible after the siding is installed.

While the strapping install method is wrong it is allowed by many AHJ's around here.



B.A. King Home Inspections, LLC
www.BAKingHomeInspections.com
Serving Charlotte NC area and Rock Hill SC areas.
CMI Certified Master Inspector and Independent
704 301-3207
Reply With Quote
  #8  
Old 4/8/08, 9:49 PM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 12,356
Default Re: No Sill Plate Under Band Board

Skip, what was this? Do you recall?

Quote:
contraption on the right near a wood frame of some sort and it looks like a tie down wrapped around the joist. I do not recognize it.
Marcel




Cyr Home and Commercial Property Inspections

IAC2 Certified
NACHI04070211
http://co.nachi.org/inachiawards


Commercial Builder
CertainTeed
Master Shingle Applicator
Shingle Technology
Ouellet Associaties Inc.
http://www.oaconstruction.com/
Reply With Quote
  #9  
Old 4/8/08, 9:55 PM
Skip Erwin Skip Erwin is offline
New User
 
Join Date: Jun 2006
Posts: 91
Please Note: Skip Erwin is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: No Sill Plate Under Band Board

I didn't look for tie downs. I blew the picture up. I can't identifty what's on the right side of the photo.
Reply With Quote
  #10  
Old 4/9/08, 11:52 AM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,020
Default Re: No Sill Plate Under Band Board

Quote:
Originally Posted by Skip Erwin
Marcel,

Everything else was pretty much normal. There was sill plate throughout except for this one section. It's unusual to see joists hangers here in production housing. Batt insulation is typically supported here with metal hangers. They look like a straight section of coat hanger and often fail over time.
If there was a sill plate throughout except for this particular area, then how did they transition the 2" (1.5") difference?

They had to of added something to make the subfloor level.

Do you have a picture of the transition from the silled area to the un-silled area?

Hey...is un-silled even a word?
Reply With Quote
  #11  
Old 4/9/08, 4:55 PM
William Warner's Avatar
William Warner William Warner is offline
InterNACHI Member
 
Join Date: May 2003
Location: Dayton, OH
Posts: 2,027
Default Re: No Sill Plate Under Band Board

Quote:
Originally Posted by mcyr
Skip, what was this? Do you recall?



Marcel
Marcel-

It appears to me to be cobwebs and shadows at the left hand side framing of the scuttle hole.
Reply With Quote
  #12  
Old 4/9/08, 7:43 PM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 12,356
Default Re: No Sill Plate Under Band Board

Quote:
Originally Posted by wwarner
Marcel-

It appears to me to be cobwebs and shadows at the left hand side framing of the scuttle hole.
Bill, did you blow it up? I did to 200 times, and it sure looks funny and unlike a cobweb.

Curious now.

Marcel




Cyr Home and Commercial Property Inspections

IAC2 Certified
NACHI04070211
http://co.nachi.org/inachiawards


Commercial Builder
CertainTeed
Master Shingle Applicator
Shingle Technology
Ouellet Associaties Inc.
http://www.oaconstruction.com/
Reply With Quote
  #13  
Old 4/9/08, 8:18 PM
William Warner's Avatar
William Warner William Warner is offline
InterNACHI Member
 
Join Date: May 2003
Location: Dayton, OH
Posts: 2,027
Default Re: No Sill Plate Under Band Board

Quote:
Originally Posted by mcyr
Bill, did you blow it up? I did to 200 times, and it sure looks funny and unlike a cobweb.

Curious now.

Marcel
Yeah... it does look funny but I think it's just cobwebs.
But I'm no expert...
Reply With Quote
  #14  
Old 4/9/08, 8:26 PM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 12,356
Default Re: No Sill Plate Under Band Board

Quote:
Originally Posted by wwarner
Yeah... it does look funny but I think it's just cobwebs.
But I'm no expert...
Oh, well, thanks Bill. Sometimes a picture dose not tell all when not clearly visible.

Marcel




Cyr Home and Commercial Property Inspections

IAC2 Certified
NACHI04070211
http://co.nachi.org/inachiawards


Commercial Builder
CertainTeed
Master Shingle Applicator
Shingle Technology
Ouellet Associaties Inc.
http://www.oaconstruction.com/
Reply With Quote
  #15  
Old 4/10/08, 2:52 PM
Dennis R. Goudreau Dennis R. Goudreau is offline
InterNACHI Member
 
Join Date: Jun 2007
Location: Nashua, NH
Posts: 1,212
Default Re: No Sill Plate Under Band Board

Quote:
Originally Posted by dvalley
If there was a sill plate throughout except for this particular area, then how did they transition the 2" (1.5") difference?

They had to of added something to make the subfloor level.

Do you have a picture of the transition from the silled area to the un-silled area?

Hey...is un-silled even a word?
I agree with Dave, do you have a picture of the transition,, Dave I think it should be no sill
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Sill plate overhanging stem dbucknavich Structural 9 3/3/08 12:37 AM
Max load allowed on 2x2 ledger bking Structural 4 12/23/07 3:05 PM
Bedroom window sill heights jlybolt Interior 12 7/5/07 3:46 PM
Continuous ADA sill with quality sidelites Vanessa Pesec Exterior 0 4/9/07 3:36 PM
Intermittent Sill Plate jfunderburk Structural 11 12/26/06 11:31 AM


All times are GMT -4. The time now is 1:59 AM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts