  #16  
Old 3/6/11, 3:00 PM
Jeffery L. Haynes Jeffery L. Haynes is online now
InterNACHI Member
 
Join Date: Aug 2008
Location: Concord, NC
Posts: 3,495
Default Re: Opinions on framing design

Simply call for a SE and be done with it otherwise your getting / giving useless opinions.
Reply With Quote
Need a home inspection in North Dakota? Check out InterNACHI's listing of North Dakota certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #17  
Old 3/6/11, 3:04 PM
James E. Braun, CMI's Avatar
James E. Braun, CMI James E. Braun, CMI is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: Jefferson City, MO
Posts: 6,945
Default Re: Opinions on framing design

Quote:
Originally Posted by mtyson View Post
Sean,

A bit difficult to tell from the pictures, but a couple of observations:
minimum bearing for a conventional rafter is 1-1/2" on a wood framed bearing wall and 3" on masonry or concrete. So the 2" is fine.
Minimum nailing to the top plate is (2) 16d common nails so the 8d are suspect.
Can not tell from the picture which way the ceiling joists are running I'm assuming they are not running parallel judging by the seat cut on the rafters on the bearing wall. If that is the case the rafters would be required too have 2"x4" rafter ties or a wall or girder at the ridge.
In both cases the rafters are required too have collar ties or ridge straps.

I was recently told by an engineer that if you use four spikes into a 2x4, you do not need ties. Cutting a birds mouth like Kent suggests and diving the nail four spike at the birds mouth, might be a better way. The reality is; is the contractor going to take the time to cut the birds mouth? I have never see any expect on exterior walls and those on very few homes. Now if you live in areas of huricanes then I would image huricane ties are needed.
Reply With Quote
  #18  
Old 3/6/11, 3:09 PM
Tim Spargo's Avatar
Tim Spargo Tim Spargo is offline
InterNACHI Member
 
Join Date: Jun 2006
Location: Lancaster, CA
Posts: 2,407
Default Re: Opinions on framing design

Quote:
Originally Posted by kshepard View Post
2x4 should have been nailed directly above the garage wall top plate with 16d, and the rafters should have been notched to rest on it. That way you resist lateral loads and have full bearing on the 2x4 and you have enough room at the bottom (level) cut of the rafter to get 2- 16d toenails in one side and one in the other. Poor quality framing. 8d nails are a defective installation in this situation. I'd call for correction by a qualified contractor for the fasteners at least.

Bingo... seat cut and blocking. We do that where stringers drop on concrete, cut a profile of 2x4/6 out of the base of stringers and a PT plate has been applied/tapcon'd/ bolted to concrete/foundation depending on setup. Similar application, just on top of gar wall.



Home Inspections in Palmdale Lancaster California

Tim Spargo
Spec Rite Inspections
Commercial and Residential Inspections
Palmdale Lancaster Santa Clarita CA
661-317-5770








Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
cut floor joice John E. Gibson, #2 General Inspection Discussion 16 9/25/08 9:45 PM