Anyone see an issue here? House is 16 years old. Screened and roofed porch was probably once a deck. Support posts showed no evidence of fastener attachment to the beams. Ledger was bolted well to the house so movement is unlikely.

(The beam perpendicular to the ledger was not typical also.)

porch-support-posts-060309-005.jpg porch-support-posts-060309-024.jpg porch-support-posts-060309-025.jpg



Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
Find an InterNACHI certified Vermont Home Inspector (and anywhere else in North America)
  #2  
Old 6/3/09, 11:26 PM
Jeffrey R. Jonas's Avatar
Jeffrey R. Jonas Jeffrey R. Jonas is online now
InterNACHI Member
 
Join Date: Feb 2007
Location: Owatonna, MN
Posts: 2,784
Default Re: Porch support posts

Joe,
It appears the ledger is fastened over the brick veneer. If so, this is a no-no.



"You cannot depend on your eyes when your imagination is out of focus"...Mark Twain


Jeffrey R. Jonas
Critical Eye Property Inspections
JRJ Consultants
Owatonna, Minnesota

NACHI07013103
IAC2-01-1567


Reply With Quote
  #3  
Old 6/3/09, 11:30 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 18,489
Default Re: Porch support posts

Same guy built this one.
Attached Thumbnails
porch-support-posts-463-park-cam1-019-small-.jpg.jpg
Views:	65
Size:	48.8 KB
ID:	29049  



"Never underestimate the difficulty of changing false beliefs by facts."
Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI
InspectraPro
or
Minnesota Home Inspector

Reply With Quote
  #4  
Old 6/4/09, 12:50 AM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is online now
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 3,831
Send a message via Yahoo to jfunderburk
Default Re: Porch support posts

Thanks guys. Here's what I came up with.

"There are components of the wood deck that are structurally unsound. The posts were not fastened to the beam in any way we could observe. Through bolts or approved brackets are the recommended method. We can elaborate on this issue, but the entire deck should be evaluated by a competent and licensed contractor and serviced accordingly."

porch-support-posts-post-and-beam-attachment.jpg beam attachment.jpg
Views:	45
Size:	51.9 KB
ID:	29050



Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #5  
Old 6/4/09, 7:07 AM
John Evans John Evans is offline
InterNACHI Member
 
Join Date: Aug 2005
Location: Bel Air, MD
Posts: 522
Default Re: Porch support posts

As mentioned, attaching a ledger board to brick veneer is not recommended. It is hard to see, but there appears to be some empty nailing holes in the joist hangers.



Maryland Home Inspections
www.aimhomeinspection.com
Infraspection Certified Level 1 No. 7801
Reply With Quote
  #6  
Old 6/4/09, 8:24 AM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 5,745
Default Re: Porch support posts

It looks like the ledger to house bolts are high enough to catch the rim joist in the pictures.

Joist ends, beam ends and post ends without mechanical attachment should be noted with repairs as needed.



____________________________________________
"An Education, not just an Inspection"

Larry Kage
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector and Infrared Thermographer serving the Traverse City, Michigan area and beyond.


ITC/FLIR CERTIFIED BUILDING SCIENCES THERMOGRAPHER

ITC/FLIR CERTIFIED LEVEL 1 THERMOGRAPHER
Reply With Quote
  #7  
Old 6/4/09, 8:38 AM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 18,489
Default Re: Porch support posts

Quote:
Originally Posted by jevans View Post
As mentioned, attaching a ledger board to brick veneer is not recommended. It is hard to see, but there appears to be some empty nailing holes in the joist hangers.
True but in this case there is very little shear load at the ledger board due to the intermediate posts.

This deck could easily be made free standing by adding posts near the ledger board and eliminating that issue.



"Never underestimate the difficulty of changing false beliefs by facts."
Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI
InspectraPro
or
Minnesota Home Inspector

Reply With Quote
  #8  
Old 6/4/09, 10:24 AM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is online now
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 3,831
Send a message via Yahoo to jfunderburk
Default Re: Porch support posts

Quote:
Originally Posted by lkage View Post
It looks like the ledger to house bolts are high enough to catch the rim joist in the pictures.

Joist ends, beam ends and post ends without mechanical attachment should be noted with repairs as needed.
Ledger was bolted through the rim joist at the house. I think the issue alluded to was that the brick may shear off the bolts.



Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #9  
Old 6/4/09, 10:25 AM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is online now
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 3,831
Send a message via Yahoo to jfunderburk
Default Re: Porch support posts

Quote:
Originally Posted by jevans View Post
As mentioned, attaching a ledger board to brick veneer is not recommended. It is hard to see, but there appears to be some empty nailing holes in the joist hangers.
Good eye. Most of the hangers only had 2 screws per side. I wrote that up also.



Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #10  
Old 6/4/09, 10:12 PM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 5,745
Default Re: Porch support posts

Quote:
Originally Posted by jfunderburk View Post
Ledger was bolted through the rim joist at the house. I think the issue alluded to was that the brick may shear off the bolts.
I'm not following you.

You mean if the deck sagged the brick would shear off the bolts?

If so, it was not attached properly.



____________________________________________
"An Education, not just an Inspection"

Larry Kage
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector and Infrared Thermographer serving the Traverse City, Michigan area and beyond.


ITC/FLIR CERTIFIED BUILDING SCIENCES THERMOGRAPHER

ITC/FLIR CERTIFIED LEVEL 1 THERMOGRAPHER
Reply With Quote
  #11  
Old 6/4/09, 10:25 PM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is online now
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 3,831
Send a message via Yahoo to jfunderburk
Default Re: Porch support posts

Quote:
Originally Posted by lkage View Post
You mean if the deck sagged the brick would shear off the bolts?
That is the thinking, I believe. Sheer forces may break the bolts if the house and/or deck settles.

On brick veneer homes, another line of thought is that if there is any settlement in the deck, it will crack the brick veneer. Best to have a stand-alone deck with a 100% brick veneer home.



Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #12  
Old 6/5/09, 12:42 PM
Kenton H. Shepard, CMI's Avatar
Kenton H. Shepard, CMI Kenton H. Shepard, CMI is offline
InterNACHI Member
 
Join Date: Aug 2004
Location: Boulder, CO
Posts: 2,492
Send a message via ICQ to kshepard
Default Re: Porch support posts

Isn't that a couple of toenails through the joist into the top of the post? If so... not great, but not going anywhere.




Kenton Shepard, InterNACHI member # 04082383
Certified Master Inspector (CMI)
EXPERT WITNESS

Director of Green Building
Director for International Development

(303) 717-8940
(303) 258-8289


Last edited by kshepard; 6/5/09 at 12:47 PM..
Reply With Quote
  #13  
Old 6/5/09, 2:14 PM
Bruce A. King's Avatar
Bruce A. King Bruce A. King is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: York, SC
Posts: 2,224
Default Re: Porch support posts

Less than code decks are the norm, I have found just one deck in over 4 years that was completely built correctly. It was on a tore up foreclosure, mold infested house. The reason that the deck was correct appeared to be due to the previous use of the home (group home of some sort) and a permit was pulled for the deck. It even had grippable handrails.

Reporting on deck construction methods can range from a simple, unhelpful, "its built wrong" to trying to explain the issues with pictures etc. as Joe has done.

Both methods have possible implications and we as home inspectors have to struggle to find a good way to report deck issues. I have tweaked and tweaked my deck reporting and will continue to do so because most have their own unique issues, some of which while "wrong" are not really going to fail.



B.A. King Home Inspections, LLC
www.BAKingHomeInspections.com
Serving Charlotte NC area and Rock Hill SC areas.
CMI Certified Master Inspector and Independent
704 301-3207
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Leaning Deck Posts thance Exterior 12 2/2/08 7:37 PM
Where do I put the Aquarium? mcyr Structural 3 11/6/07 4:05 PM
Heavy timber posts and support beam hziegenbein Structural 3 9/24/07 4:38 PM


All times are GMT -4. The time now is 1:56 PM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts