Default Post Tension Cable failure

I got an emergency call from the Fire Department about a loud explosion in a 3 story condominium. I arrived within minutes and was led to a corner unit on the 2nd floor. Once inside I observed a hole in the ceiling about 5 inches in diameter and 1 inch deep. There was concrete all over the floor and in the hole was 1 strand of a post tension cable that had shot out of the slab and left a loop about 9 inches long. This building is 28 years old and I inspected all units above below and on the same floor. There was no damage anywhere. No one had done any work that day or recently. 2 Structural engineers inspected along with me and the consensus was the same. We have never seen anything like this. For 1 strand to suddenly shoot out of the slab. The explosion could be heard over 300 yards away. Any ideas on what happened here ?
Reply With Quote
  #2  
Old 4/17/08, 8:35 PM
Barry Adair's Avatar
Barry Adair Barry Adair is offline
InterNACHI Member
 
Join Date: Aug 2004
Location: TEXAS
Posts: 3,932
Default Re: Post Tension Cable failure

Anchor, wedge or tendon failure, not a whole lot left to go wrong, may be due to corrosion.

The Pope will likely chime in.

I'd like to see your photos!

I just closed the entry door and had one go on a vacant house.
Dust clouds for what seemed like days and hearing was buzzed for hours.
Scared the b-jeezuz out of me and was a shorts check time moment.
Didn't get to complete the inspection because the client was with me and walked...no doubt. He said, "Could you imagine if me, my wife or kids were in that room?" I completely understood.



ADAIR INSPECTION
972-487-5634

Commercial-Residential-Construction-EIFS-Infrared Thermography
TREC # 4563
EDI: EIFS-MA TX # 39

2008 US Member of the Year

life is the random lottery of events followed by numerous narrow escapes accept the good
Reply With Quote
  #3  
Old 4/17/08, 8:52 PM
Kenton H. Shepard, CMI's Avatar
Kenton H. Shepard, CMI Kenton H. Shepard, CMI is offline
InterNACHI Member
 
Join Date: Aug 2004
Location: Boulder, CO
Posts: 3,417
Send a message via ICQ to kshepard
Default Re: Post Tension Cable failure

Quote:
Originally Posted by badair
Anchor, wedge or tendon failure, not a whole lot left to go wrong, may be due to corrosion.



I just closed the entry door and had one go on a vacant house.
Dust clouds for what seemed like days and hearing was buzzed for hours.
Scared the b-jeezuz out of me and was a shorts check time moment.
Didn't get to complete the inspection because the client was with me and walked...no doubt. He said, "Could you imagine if me, my wife or kids were in that room?" I completely understood.
Barry, would you elaborate? We don't have many post-tensioned slabs here and I'd like to learn more about them.

What are anchors, wedges and tendons and how do they fail?

What exactly happened in the home to create the dust cloud, noise, etc.? If a cable fails, is there a life-threatening explosion?




Kenton Shepard, InterNACHI member # 04082383
Certified Master Inspector (CMI)
InterNACHI Director of International Development
Director of Green Building

EXPERT WITNESS SERVICE
Conventional and Log homes

(303) 717-8940
Reply With Quote
  #4  
Old 4/17/08, 11:15 PM
Barry Adair's Avatar
Barry Adair Barry Adair is offline
InterNACHI Member
 
Join Date: Aug 2004
Location: TEXAS
Posts: 3,932
Default Re: Post Tension Cable failure

Quote:
Originally Posted by kshepard
Barry, would you elaborate? We don't have many post-tensioned slabs here and I'd like to learn more about them.

What are anchors, wedges and tendons and how do they fail? Hope links answer these questions for you. You can also search google images. This was years ago.

What exactly happened in the home to create the dust cloud, noise, etc.? If a cable fails, is there a life-threatening explosion? I don't know all of the physics behind failure. Ever have a cumalong cable snap? Possibly hundreds of times greater. Wrong place wrong time yes! In my case failure occurred at the other end of house but concrete shrapnel went through windows and sheetrock walls like a butter knife.
http://www.icc-es.org/criteria/pdf_f...e%201-1-07.pdf

http://findarticles.com/p/articles/m..._/ai_n21359644

Get past the music 1 minute and watch this lecture and further episodes
http://youtube.com/watch?v=9ROVbBANMUU



ADAIR INSPECTION
972-487-5634

Commercial-Residential-Construction-EIFS-Infrared Thermography
TREC # 4563
EDI: EIFS-MA TX # 39

2008 US Member of the Year

life is the random lottery of events followed by numerous narrow escapes accept the good
Reply With Quote
  #5  
Old 4/17/08, 11:37 PM
Barry Adair's Avatar
Barry Adair Barry Adair is offline
InterNACHI Member
 
Join Date: Aug 2004
Location: TEXAS
Posts: 3,932
Default Re: Post Tension Cable failure

This may be simpler once you know the components
http://youtube.com/watch?v=d51lciZRwF0



ADAIR INSPECTION
972-487-5634

Commercial-Residential-Construction-EIFS-Infrared Thermography
TREC # 4563
EDI: EIFS-MA TX # 39

2008 US Member of the Year

life is the random lottery of events followed by numerous narrow escapes accept the good
Reply With Quote
  #6  
Old 4/18/08, 12:46 AM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,058
Default Re: Post Tension Cable failure

The cable may still be live if only one strand has broken. The cable should be de-tensioned (which can be very dangerous) and removed.

Cable failures can be as uneventful as a "pop," or as catastrophic as "exploding concrete," capable of severe damage and bodily injury. If the cable is still live, the potential for further events is pretty high.

Other than drilling or cutting the stressed concrete, the cause of a cable failure can be any number of things, but generally occurs from a tendon that has been damaged prior to, or during placement. A damaged tendon is like a ticking time-bomb. . .



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net



Last edited by jpope; 4/18/08 at 5:07 PM..
Reply With Quote
  #7  
Old 4/18/08, 1:02 AM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,058
Default Re: Post Tension Cable failure

Here are some pictures of the "muscle and teeth" of PT cables.

The pictures show a "triple wedge" (doubles are most common in residential PT), a double wedge that is in place prior to stressing the tendon and the hydraulic ram used to stress the cable.

The last picture shows a "multi-cable" system, used in bridge construction. I worked with all of these systems for many years. . .
Attached Thumbnails
post-tension-cable-failure-wedge.jpg   post-tension-cable-failure-single.jpg   post-tension-cable-failure-ram.jpg   post-tension-cable-failure-multi.jpg  



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #8  
Old 4/18/08, 1:25 AM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,058
Default Re: Post Tension Cable failure

Here are a couple of elevated-deck pictures. . .
Attached Thumbnails
post-tension-cable-failure-deck1.jpg   post-tension-cable-failure-deck2.jpg  



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #9  
Old 4/18/08, 6:11 AM
Robert Kuiper Robert Kuiper is offline
New User
 
Join Date: Apr 2008
Location: Miami
Posts: 3
Please Note: Robert Kuiper is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Post Tension Cable failure

Thanks for all the posts. The real question here is why after 28 years ? I'll post a picture as soon as I get to the office. My other question is now that 1 strand has "popped" will the others follow ?
Reply With Quote
  #10  
Old 4/18/08, 9:29 AM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,058
Default Re: Post Tension Cable failure

Most likely this will be an isolated event. It's very unlikely that additional cable failures will follow.

If it were to continue, the original installation methods would be suspect. The only "fix" for that would be to condemn the building.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net



Last edited by jpope; 4/18/08 at 10:19 AM..
Reply With Quote
  #11  
Old 4/18/08, 9:46 AM
Robert Kuiper Robert Kuiper is offline
New User
 
Join Date: Apr 2008
Location: Miami
Posts: 3
Please Note: Robert Kuiper is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Post Tension Cable failure

Seems to me it would require an extremely large condom.
Reply With Quote
  #12  
Old 4/18/08, 9:47 AM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 8,848
Default Re: Post Tension Cable failure

Quote:
Originally Posted by jpope
The only "fix" for that would be to condom the building.
LOL, that leaves quite a picture in my mind...



InterNachi Awards Portal: http://co.nachi.org/inachiawards/

____________________________________________
"An Education, not just an Inspection"

Larry Kage, CMI
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector serving the Traverse City, Michigan area and beyond.
Reply With Quote
  #13  
Old 4/18/08, 10:19 AM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,058
Default Re: Post Tension Cable failure

Quote:
Originally Posted by Robert Kuiper
Seems to me it would require an extremely large condom.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #14  
Old 4/18/08, 11:22 AM
Karl E. Gerhauser's Avatar
Karl E. Gerhauser Karl E. Gerhauser is offline
InterNACHI Member
 
Join Date: Oct 2006
Location: Coos Bay, OR
Posts: 438
Default Re: Post Tension Cable failure

As an ex-post tensioned concrete ICC special inspector, I want to agree with and support EVERYTHING that Jeff has said and provided. I would add that although it IS probably an isolated event due to damaged materials, I feel the engineers that were on site should contact the architect or engineer of record for the construction and get the special inspector documentation. The tendons cannot be pulled withou a special inspector documenting al the vital information. (LBS of tension, distance of pull etc) This could revel a possible installation problem though this is unlikely but no stone should be unturned when it comes to public safety. As jeff stated, if there are true issues condemnation is the only real cure.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
photo wanted of moldy bathroom in prior post psiposs Interior Inspections 8 6/11/06 8:20 AM
post tension cables jlybolt Structural Inspections 2 4/17/06 11:55 PM