Default Proper End Bearing..?

Hello everyone.. I inspected a 2yr old townhouse the other day and found a parralam beam(sorry no pics) that had 1 1/2 endbearing. It was my understanding that any main beam should have at least 3in of end bearing. I should mention it was not the only main beam for the home. There was a steel beam that supported 95% of the home(end bearing sufficient) but this one caught my eye and did not appear correct. The builder came in the next day and assured the new buyer it was fine. What do you think?

Chris
Reply With Quote
  #2  
Old 8/20/06, 10:38 PM
gbeaumont's Avatar
gbeaumont gbeaumont is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: Clearwater, FL
Posts: 6,261
Send a message via AIM to gbeaumont Send a message via MSN to gbeaumont Send a message via Yahoo to gbeaumont
Default Re: Proper End Bearing..?

Chris,

What is supporting the parallam beam?

If it is wood then 1 1/2 inches full width support is required, if it is supported by masonary then 3 1/2 inches full width support is required.

Regards

Gerry



"To realize our true destiny, we must be guided not by a myth from our past, but by a vision of our future."
(Mark B Adams)

Commercial property Inspection Tampa, Orlando, Sarasota, Jacksonville, Ft Launderdale, Miami, Florida.
NACHI cell 484-429-5466
NACHI02121106

Reply With Quote
  #3  
Old 8/20/06, 10:45 PM
Christopher Rich Iii Christopher Rich Iii is offline
InterNACHI Member
 
Join Date: Feb 2006
Location: Burlington, NJ
Posts: 138
Default Re: Proper End Bearing..?

Hi Gerry... It was sitting on a 2x4 sill plate! I should mention it looked like they started to notch the sill plate, but then left it? Is 1 1/2 enough? for such a large parralam?

Thanks,
Chris
Reply With Quote
  #4  
Old 8/20/06, 11:12 PM
Dale Duffy's Avatar
Dale Duffy Dale Duffy is offline
InterNACHI Member
 
Join Date: Oct 2005
Location: Scottsdale, AZ
Posts: 8,261
Default Re: Proper End Bearing..?

It's an 1 1/2 here Chris.
Reply With Quote
  #5  
Old 8/20/06, 11:25 PM
Dale Duffy's Avatar
Dale Duffy Dale Duffy is offline
InterNACHI Member
 
Join Date: Oct 2005
Location: Scottsdale, AZ
Posts: 8,261
Default Re: Proper End Bearing..?

R502.6 Bearing.
The ends of each joist, beam or girder shall
have not less than 1.5 inches (38 mm) of bearing on wood or
metal and not less than 3 inches (76 mm) on masonry or concrete
except where supported on a 1-inch-by-4-inch (25.4 mm
by 102 mm) ribbon strip and nailed to the adjacent stud or by
the use of approved joist hangers.


Reply With Quote
  #6  
Old 8/21/06, 12:37 AM
Bruce A. King's Avatar
Bruce A. King Bruce A. King is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: York, SC
Posts: 3,206
Default Re: Proper End Bearing..?

Engineered lumber beams must have end bearing as per the manuf. specs.

The larger beams typically require 3 to 3 1/2 inches.
Larger beams typically have longer spans or other beams (point load) on them.

Last time I looked the codes only have sawn lumber issues there and the engineered lumber refers to the manuf. specs.
Reply With Quote
  #7  
Old 8/24/06, 1:13 PM
Christopher Rich Iii Christopher Rich Iii is offline
InterNACHI Member
 
Join Date: Feb 2006
Location: Burlington, NJ
Posts: 138
Default Re: Proper End Bearing..?

Thats why I posted bruce.. I was thinking the same thing. Again this wasn't the main steel girder which did have enough end bearing on the block wall, however this beam did have a big load considering it was a 2400sq ft townhouse. I just can't see a 4x12 in parralam sitting on a 2x4 sill.. I'll check some other sites."trussjoist.com", but if anyone has any other insight I would appreciate it!

Thanks,
Chris
Reply With Quote
  #8  
Old 8/24/06, 4:42 PM
Bruce A. King's Avatar
Bruce A. King Bruce A. King is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: York, SC
Posts: 3,206
Default Re: Proper End Bearing..?

Also look for a minimum of 3 2x4's under the ends of most all engineered beams. Some need 4 or more in big houses.
Reply With Quote
  #9  
Old 8/24/06, 5:23 PM
David C. Macy's Avatar
David C. Macy David C. Macy is offline
InterNACHI Member
 
Join Date: Jan 2004
Location: NE. OH
Posts: 2,657
Default Re: Proper End Bearing..?

I just inspected this 1922 home that had no end bearing on one side. It was supported by a column. The other side of the beam was partial finished but I could see that it was in the foundation wall.

I called out the end bearing for a PE. The footer for the column was iffy. How much wait can a column support?

Dave
Attached Thumbnails
proper-end-bearing-79606-s.euclid-036-small-.jpg.jpg
Views:	114
Size:	48.9 KB
ID:	5245  
Reply With Quote
  #10  
Old 8/24/06, 6:16 PM
gbeaumont's Avatar
gbeaumont gbeaumont is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: Clearwater, FL
Posts: 6,261
Send a message via AIM to gbeaumont Send a message via MSN to gbeaumont Send a message via Yahoo to gbeaumont
Default Re: Proper End Bearing..?

Hi to all,

I did some further research on the Parallam bearing issue and found this .pdf which includes the bearing dimensions plus loads of other good installation information.

http://www.floridabuilding.org/uploa...%20parallam%22

BTW this sheet cover Floridian requirements.

Regards

Gerry



"To realize our true destiny, we must be guided not by a myth from our past, but by a vision of our future."
(Mark B Adams)

Commercial property Inspection Tampa, Orlando, Sarasota, Jacksonville, Ft Launderdale, Miami, Florida.
NACHI cell 484-429-5466
NACHI02121106

Reply With Quote
  #11  
Old 8/27/06, 2:37 PM
Robert J. OConnor's Avatar
Robert J. OConnor Robert J. OConnor is offline
InterNACHI Member
 
Join Date: Jul 2003
Location: Long Island, NY
Posts: 1,288
Default Re: Proper End Bearing..?

Bruce is right that engineered lumber is not covered by model codes like the IRC. But the bearing requirements vary greatly from 1-1/2" of bearing up to about 4-1/2" depending on the beam width and span. But since there was a main steel beam, my guess would be that the beam is lighter where 1-1/2" of bearing just may work.

Chris ... are you talking about parallel strand lumber or PSL beams ("Parallam" is one brand from TJI) which are wider/heavier engineered lumber girders that generally require more bearing ... http://www.ilevel.com/floors/f_ParallamPSL_beams.aspx

Or are you talking about laminated veneer lumber or LVL beams ("Microlam" is one brand from TJI) which mostly just requires 1-1/2" bearing for the lighter beams ... http://www.ilevel.com/floors/f_MicrollamLVL_beams.aspx



Robert O'Connor, PE
Consulting Engineer & Inspector
LIU CW Post Adjunct Professor
NACHI Education Committee
www.reporthost.com/-rjo

I am absolutely amazed sometimes by how much thought goes into doing things wrong ...
Reply With Quote
  #12  
Old 8/27/06, 4:20 PM
rwand1 rwand1 is offline
Active Poster
 
Join Date: Sep 2005
Location: Caledon, ON
Posts: 7,861
Please Note: rwand1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Proper End Bearing..?

David that would be typical for circa 1922 home and is not uncommon to see in my parts with homes that old along with improper footing for columns. Many homes that age still have wood posts. As to weight a load bearing column that would depend on thickness of metal and or diameter, or size of post if wood and how many floors above, etc.
Reply With Quote
  #13  
Old 8/27/06, 8:31 PM
Robert J. OConnor's Avatar
Robert J. OConnor Robert J. OConnor is offline
InterNACHI Member
 
Join Date: Jul 2003
Location: Long Island, NY
Posts: 1,288
Default Re: Proper End Bearing..?

P.S. Here is a link to the TJI header/beam bearing requirements ... http://www.ilevel.com/literature/TJ-9001.pdf

They have the required beam bearing on page 9-10. Notice that except for very short spans (high shear load) or very deep higher capacity beams, the minimum bearing is generally 1-1/2". But keep in mind that's just for TrussJoist products, although they are pretty common ...



Robert O'Connor, PE
Consulting Engineer & Inspector
LIU CW Post Adjunct Professor
NACHI Education Committee
www.reporthost.com/-rjo

I am absolutely amazed sometimes by how much thought goes into doing things wrong ...
Reply With Quote
  #14  
Old 8/28/06, 7:23 PM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 19,788
Default Re: Proper End Bearing..?

As usuall, Robert has supplied us with a very good example and a lot of this information should be read, for it focuses to a mirid amount of suppliers of the same product and different engineered designs.
One design by one Manufacturer does not neccessarily mean that it is the same for another.

Most Manufacturers will recommend 1 1/2" bearing, but why not give it the full 3 1/2" that is available and then it is not an issue. Reccommended practice as far as I am concerned.

Marcel
Reply With Quote
  #15  
Old 8/28/06, 8:47 PM
Christopher Rich Iii Christopher Rich Iii is offline
InterNACHI Member
 
Join Date: Feb 2006
Location: Burlington, NJ
Posts: 138
Default Re: Proper End Bearing..?

Hello Robert.. Thank you for all the info regarding proper end bearing! The beam was a parallam(truss joist product). Like I mentioned the builder said it was ok? If I can figure out how to upload the pic from my homegauge report I'll post it.

Chirs
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Electricians Check List pabernathy Electrical Inspections 74 12/5/07 6:39 PM
Where do I put the Aquarium? mcyr Structural Inspections 3 11/6/07 3:05 PM
Bearing wall support modifications bwooddell Structural Inspections 1 5/18/07 11:44 AM
Insufficient end bearing? jclark1 Structural Inspections 3 9/12/06 1:43 PM
Proper Vent - High Eff. Gas Furnace rkuntz Inspecting HVAC Systems 10 1/13/06 10:18 PM


All times are GMT -4. The time now is 9:21 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts