Default Proper notching of floor joist

If a fellow NACHI member could further guide me...I know what the books say about notching a floor joist. What are the concerns for notching a 2 x 10 floor joist to accommodate a 3 in drain pipe to pass through. My thoughts are; that almost 1/3 of the board would be missing since the board is not exactly 10 in wide.

Some input would be helpful

Thanks


</IMG>



Dave Johnson
East China, MI
NACHI06081990
Reply With Quote
  #2  
Old 1/15/07, 2:51 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 30,554
Default Re: Proper notching of floor joist

This may be helpful.
Attached Thumbnails
proper-notching-floor-joist-notching-small-.jpg.jpg
Views:	1936
Size:	25.2 KB
ID:	8418  
Reply With Quote
  #3  
Old 1/15/07, 10:11 PM
bandag bandag is offline
Active Poster
 
Join Date: Sep 2006
Posts: 137
Please Note: bandag is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Proper notching of floor joist

Mike, where did you find that picture?
Reply With Quote
  #4  
Old 1/15/07, 10:18 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 30,554
Default Re: Proper notching of floor joist

Quote:
Originally Posted by bandag
Mike, where did you find that picture?
I don't remember for sure but there was a very recent discussion here on this issue.
Reply With Quote
  #5  
Old 1/21/07, 11:15 AM
Frank L. Bartlo Frank L. Bartlo is offline
InterNACHI Member
 
Join Date: Aug 2004
Location: SE Michigan
Posts: 236
Default Re: Proper notching of floor joist

I'd install some additional additional support in the form of one or more metal bars, boards, or the like extending at least 2 feet (or to the end) on each side of the notch, and attach it at no less than 6 points (3 each side of the notch), David.

I don't know the specific codes for such reinforcements, but since you're making about a 3.5-4" notch it stands to reason that a well-attached 2x6 or metal bar of equivalent strength should be more than sufficient. When in doubt, overbuild.

And thanks for the schematic, Michael.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
PVC waste lines lagudo Plumbing Inspections 10 3/6/11 2:57 AM
Electricians Check List pabernathy Electrical Inspections 74 12/5/07 7:39 PM
What is the proper name of this "monster"? yolhovsky Ancillary Inspection Services & Additional Topics 34 11/15/07 2:35 PM
Unable to confirm proper ground.. gmathias Electrical Inspections 22 10/27/06 9:20 PM
Are these proper connections? jweinberg Plumbing Inspections 9 5/25/06 9:32 PM


All times are GMT -4. The time now is 12:46 PM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts